12-Network Management and Monitoring Configuration Guide
HomeSupportSwitchesS7500E-X SeriesConfigure & DeployConfiguration GuidesH3C S7500E-X Configuration Guides-R7523P01-6W10012-Network Management and Monitoring Configuration Guide
02-NQA configuration
02-NQA configuration 575.85 KB
Configuring NQA·· 1
Overview· 1
NQA operation· 1
Collaboration· 2
Threshold monitoring· 2
NQA configuration task list 3
Configuring the NQA server 3
Enabling the NQA client 4
Configuring NQA operations on the NQA client 4
NQA operation configuration task list 4
Configuring the ICMP echo operation· 5
Configuring the ICMP jitter operation· 6
Configuring the DHCP operation· 7
Configuring the DNS operation· 7
Configuring the FTP operation· 8
Configuring the HTTP operation· 9
Configuring the UDP jitter operation· 10
Configuring the SNMP operation· 11
Configuring the TCP operation· 12
Configuring the UDP echo operation· 13
Configuring the UDP tracert operation· 13
Configuring the voice operation· 15
Configuring the DLSw operation· 17
Configuring the path jitter operation· 17
Configuring optional parameters for the NQA operation· 18
Configuring the collaboration feature· 19
Configuring threshold monitoring· 20
Configuring the NQA statistics collection feature· 22
Configuring the saving of NQA history records· 23
Scheduling the NQA operation on the NQA client 24
Configuring NQA templates on the NQA client 24
NQA template configuration task list 24
Configuring the ICMP template· 25
Configuring the DNS template· 26
Configuring the TCP template· 26
Configuring the TCP half open template· 27
Configuring the UDP template· 28
Configuring the HTTP template· 29
Configuring the HTTPS template· 30
Configuring the FTP template· 32
Configuring the RADIUS template· 33
Configuring the SSL template· 34
Configuring optional parameters for the NQA template· 34
Displaying and maintaining NQA· 35
NQA configuration examples· 35
ICMP echo operation configuration example· 35
ICMP jitter operation configuration example· 37
DHCP operation configuration example· 39
DNS operation configuration example· 40
FTP operation configuration example· 42
HTTP operation configuration example· 43
UDP jitter operation configuration example· 44
SNMP operation configuration example· 46
TCP operation configuration example· 48
UDP echo operation configuration example· 49
UDP tracert operation configuration example· 50
Voice operation configuration example· 52
DLSw operation configuration example· 54
Path jitter operation configuration example· 55
NQA collaboration configuration example· 57
ICMP template configuration example· 59
DNS template configuration example· 60
TCP template configuration example· 61
TCP half open template configuration example· 62
UDP template configuration example· 62
HTTP template configuration example· 63
HTTPS template configuration example· 64
FTP template configuration example· 64
RADIUS template configuration example· 65
SSL template configuration example· 66
Configuring NQA
Overview
Network quality analyzer (NQA) allows you to measure network performance, verify the service levels for IP services and applications, and troubleshoot network problems. It provides the following types of operations:
·     ICMP echo.
·     ICMP jitter.
·     DHCP.
·     DLSw.
·     DNS.
·     FTP.
·     HTTP.
·     Path jitter.
·     SNMP.
·     TCP.
·     UDP echo.
·     UDP jitter.
·     UDP tracert.
·     Voice.
As shown in Figure 1, the NQA source device (NQA client) sends data to the NQA destination device by simulating IP services and applications to measure network performance. The obtained performance metrics include the one-way latency, jitter, packet loss, voice quality, application performance, and server response time.
All types of NQA operations require the NQA client, but only the TCP, UDP echo, UDP jitter, and voice operations require the NQA server. The NQA operations for services that are already provided by the destination device such as FTP do not need the NQA server.
You can configure the NQA server to listen and respond to specific IP addresses and ports to meet various test needs.
Figure 1 Network diagram
NQA operation
The following describes how NQA performs different types of operations:
·     A TCP or DLSw operation sets up a connection.
·     An ICMP jitter, UDP jitter, or voice operation sends a number of probe packets. The number of probe packets is set by using the probe packet-number command.
·     An FTP operation uploads or downloads a file.
·     An HTTP operation gets a Web page.
·     A DHCP operation gets an IP address through DHCP.
·     A DNS operation translates a domain name to an IP address.
·     An ICMP echo operation sends an ICMP echo request.
·     A UDP echo operation sends a UDP packet.
·     An SNMP operation sends one SNMPv1 packet, one SNMPv2c packet, and one SNMPv3 packet.
·     A path jitter operation is accomplished in the following steps:
a.     The operation uses tracert to obtain the path from the NQA client to the destination. A maximum of 64 hops can be detected.
b.     The NQA client sends ICMP echo requests to each hop along the path. The number of ICMP echo requests is set by using the probe packet-number command.
·     A UDP tracert operation determines the routing path from the source to the destination. The number of the probe packets sent to each hop is set by using the probe count command.
Collaboration
NQA can collaborate with the Track module to notify application modules of state or performance changes so that the application modules can take predefined actions.
Figure 2 Collaboration
The following describes how a static route destined for 192.168.0.88 is monitored through collaboration:
1.     NQA monitors the reachability to 192.168.0.88.
2.     When 192.168.0.88 becomes unreachable, NQA notifies the Track module of the change.
3.     The Track module notifies the static routing module of the state change.
4.     The static routing module sets the static route to invalid according to a predefined action.
For more information about collaboration, see High Availability Configuration Guide.
Threshold monitoring enables the NQA client to take a predefined action when the NQA operation performance metrics violate the specified thresholds.
Table 1 describes the relationships between performance metrics and NQA operation types.
Table 1 Performance metrics and NQA operation types
Performance metric
NQA operation types that can gather the metric
Probe duration
All NQA operation types except UDP jitter, UDP tracert, path jitter, and voice
Number of probe failures
Round-trip time
ICMP jitter, UDP jitter, and voice
Number of discarded packets
One-way jitter (source-to-destination or destination-to-source)
One-way delay (source-to-destination or destination-to-source)
Calculated Planning Impairment Factor (ICPIF) (see "Configuring the voice operation")
Voice
Mean Opinion Scores (MOS) (see "Configuring the voice operation")
Voice
Tasks at a glance
Remarks
Required for TCP, UDP echo, UDP jitter, and voice operations.
(Required.) Enabling the NQA client
N/A
(Required.) Perform at least one of the following tasks:
·     Configuring NQA operations on the NQA client
·     Configuring NQA templates on the NQA client
When you configure an NQA template to analyze network performance, the feature that uses the template performs the NQA operation.
To perform TCP, UDP echo, UDP jitter, and voice operations, you must enable the NQA server on the destination device. The NQA server listens and responds to requests on the specified IP addresses and ports.
You can configure multiple TCP or UDP listening services on an NQA server, where each corresponds to a specific IP address and port number. The IP address and port number for a listening service must be unique on the NQA server and match the configuration on the NQA client.
To configure the NQA server:
Step
Remarks
N/A
2.     Enable the NQA server.
nqa server enable
By default, the NQA server is disabled.
3.     Configure a TCP or UDP listening service.
·     TCP listening service:
nqa server tcp-connect
ip-address port-number [ vpn-instance vpn-instance-name ] [ tos tos ]
·     UDP listening service:
nqa server udp-echo
The default ToS value is 0.
You can set the ToS value in the IP header of reply packets sent by the NQA server.
Step
Remarks
N/A
2.     Enable the NQA client.
nqa agent enable
By default, the NQA client is enabled.
The NQA client configuration takes effect after you enable the NQA client.
Tasks at a glance
·     Configuring the ICMP echo operation
·     Configuring the ICMP jitter operation
·     Configuring the DHCP operation
·     Configuring the DNS operation
·     Configuring the FTP operation
·     Configuring the HTTP operation
·     Configuring the UDP jitter operation
·     Configuring the SNMP operation
·     Configuring the TCP operation
·     Configuring the UDP echo operation
·     Configuring the UDP tracert operation
·     Configuring the voice operation
·     Configuring the DLSw operation
·     Configuring the path jitter operation
(Optional.) Configuring optional parameters for the NQA operation
(Optional.) Configuring the collaboration feature
(Optional.) Configuring threshold monitoring
(Optional.) Configuring the NQA statistics collection feature
(Optional.) Configuring the saving of NQA history records
(Required.) Scheduling the NQA operation on the NQA client
The ICMP echo operation measures the reachability of a destination device. It has the same function as the ping command, but provides more output information. In addition, if multiple paths exist between the source and destination devices, you can specify the next hop for the ICMP echo operation.
To configure the ICMP echo operation:
Step
Remarks
N/A
2.     Create an NQA operation and enter NQA operation view.
nqa entry admin-name operation-tag
By default, no NQA operations exist.
3.     Specify the ICMP echo type and enter its view.
type icmp-echo
N/A
4.     Specify the destination IP address for ICMP echo requests.
·     IPv4 address:
destination ip ip-address
·     IPv6 address:
destination ipv6 ipv6-address
By default, no destination IP address is specified.
5.     (Optional.) Set the payload size for each ICMP echo request.
data-size size
The default setting is 100 bytes.
6.     (Optional.) Specify the payload fill string for ICMP echo requests.
data-fill string
The default payload fill string is the hexhexadecimal string 00010203040506070809.
7.     (Optional.) Specify the output interface for ICMP echo requests.
out interface interface-type interface-number
By default, the output interface for ICMP echo requests is not specified. The NQA client determines the output interface based on the routing table lookup.
8.     (Optional.) Specify the source IP address for ICMP echo requests.
·     Use the IP address of the specified interface as the source IP address:
source interface interface-type interface-number
·     Specify the source IPv4 address:
source ip ip-address
·     Specify the source IPv6 address:
source ipv6 ipv6-address
By default, the requests take the primary IP address of the output interface as their source IP address.
If you execute the source interface, source ip, and source ipv6 commands multiple times, the most recent configuration takes effect.
The specified source interface must be up.
The specified source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
9.     (Optional.) Specify the next hop IP address for ICMP echo requests.
·     IPv4 address:
next-hop ip ip-address
·     IPv6 address:
next-hop ipv6 ipv6-address
By default, no next hop IP address is configured.
The ICMP jitter operation measures unidirectional and bidirectional jitters. The operation result helps you to determine whether the network can carry jitter-sensitive services such as real-time voice and video services.
The ICMP jitter operation works as follows:
1.     The NQA client sends ICMP packets to the destination device.
2.     The destination device time stamps each packet it receives, and then sends the packet back to the NQA client.
3.     Upon receiving the responses, the NQA client calculates the jitter according to the timestamps.
To configure the ICMP jitter operation:
Step
Remarks
N/A
3.     Specify the ICMP jitter type and enter its view.
type icmp-jitter
N/A
4.     Specify the destination address of ICMP packets.
5.     (Optional.) Set the number of ICMP packets sent in one ICMP jitter operation.
probe packet-number
packet-number
The default setting is 10.
6.     (Optional.) Set the interval for sending ICMP packets.
probe packet-interval interval
The default setting is 20 milliseconds.
7.     (Optional.) Specify how long the NQA client waits for a response from the server before it regards the response times out.
probe packet-timeout timeout
The default setting is 3000 milliseconds.
8.     (Optional.) Specify the source IP address for ICMP packets.
By default, the packets take the primary IP address of the output interface as their source IP address.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no ICMP packets can be sent out.
Use the display nqa result or display nqa statistics command to verify the ICMP jitter operation. The display nqa history command does not display the ICMP jitter operation results or statistics.
The DHCP operation measures whether or not the DHCP server can respond to client requests. DHCP also measures the amount of time it takes the NQA client to obtain an IP address from a DHCP server.
The NQA client simulates the DHCP relay agent to forward DHCP requests for IP address acquisition from the DHCP server. The interface that performs the DHCP operation does not change its IP address. When the DHCP operation completes, the NQA client sends a packet to release the obtained IP address.
To configure the DHCP operation:
Step
Remarks
N/A
3.     Specify the DHCP type and enter its view.
type dhcp
N/A
4.     Specify the IP address of the DHCP server as the destination IP address of DHCP packets.
5.     (Optional.) Specify an output interface for DHCP request packets.
By default, the output interface for DHCP request packets is not specified. The NQA client determines the output interface based on the routing table lookup.
6.     (Optional.) Specify the source IP address of DHCP request packets.
The specified source IP address must be the IP address of a local interface, and the local interface must be up. Otherwise, no probe packets can be sent out.
The NQA client adds the source IP address to the giaddr field in DHCP requests to be sent to the DHCP server. For more information about the giaddr field, see Layer 3—IP Services Configuration Guide.
The DNS operation measures the time for the NQA client to translate a domain name into an IP address through a DNS server.
A DNS operation simulates domain name resolution and does not save the obtained DNS entry.
To configure the DNS operation:
Step
Remarks
N/A
3.     Specify the DNS type and enter its view.
type dns
N/A
4.     Specify the IP address of the DNS server as the destination address of DNS packets.
5.     Specify the domain name to be translated.
resolve-target domain-name
The FTP operation measures the time for the NQA client to transfer a file to or download a file from an FTP server.
When you configure the FTP operation, follow these restrictions and guidelines:
·     When you perform the put operation with the filename command configured, make sure the file exists on the NQA client.
·     If you get a file from the FTP server, make sure the file specified in the URL exists on the FTP server.
·     The NQA client does not save the file obtained from the FTP server.
·     Use a small file for the FTP operation. A big file might result in transfer failure because of timeout, or might affect other services for occupying much network bandwidth.
To configure the FTP operation:
Step
Remarks
N/A
3.     Specify the FTP type and enter its view.
type ftp
N/A
4.     Specify the URL of the destination FTP server.
url url
By default, no URL is specified for the destination FTP server.
Enter the URL in one of the following formats:
·     ftp://host/filename.
·     ftp://host:port/filename.
When you perform the get operation, the file name is required.
5.     (Optional.) Specify the source IP address of FTP request packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no FTP requests can be sent out.
6.     (Optional.) Specify the FTP operation type.
operation { get | put }
By default, the FTP operation type is get, which means obtaining files from the FTP server.
7.     Specify an FTP login username.
username username
By default, no FTP login username is configured.
8.     Specify an FTP login password.
By default, no FTP login password is configured.
9.     (Optional.) Specify the name of a file to be transferred.
filename file-name
By default, no file is specified.
This step is required if you perform the put operation.
10.     Set the data transmission mode.
mode { active | passive }
The default mode is active.
An HTTP operation measures the time for the NQA client to obtain data from an HTTP server.
To configure an HTTP operation:
Step
Remarks
N/A
3.     Specify the HTTP type and enter its view.
type http
N/A
4.     Specify the URL of the destination HTTP server.
url url
By default, no URL is specified for the destination HTTP server.
·     http://host/resource.
·     http://host:port/resource.
5.     Specify an HTTP login username.
username username
By default, no HTTP login username is specified.
6.     Specify an HTTP login password.
By default, no HTTP login password is specified.
7.     (Optional.) Specify the source IP address of request packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no request packets can be sent out.
8.     (Optional.) Specify the HTTP version.
version { v1.0 | v1.1 }
By default, HTTP 1.0 is used.
9.     (Optional.) Specify the HTTP operation type.
operation { get | post | raw }
By default, the HTTP operation type is get, which means obtaining data from the HTTP server.
If you set the HTTP operation type to raw, configure the content of the HTTP request to be sent to the HTTP server in raw request view.
10.     (Optional.) Enter raw request view.
raw-request
Every time you enter raw request view, the previously configured content of the HTTP request is removed.
11.     (Optional.) Specify the HTTP request content.
Enter or paste the content.
By default, no contents are specified.
This step is required for the raw operation.
12.     Save the input and return to HTTP operation view.
N/A
CAUTION:
To ensure successful UDP jitter operations and avoid affecting existing services, do not perform the operations on well-known ports from 1 to 1023.
Jitter means inter-packet delay variance. A UDP jitter operation measures unidirectional and bidirectional jitters. The operation result helps you to determine whether the network can carry jitter-sensitive services such as real-time voice and video services through the UDP jitter operation.
The UDP jitter operation works as follows:
1.     The NQA client sends UDP packets to the destination port.
The UDP jitter operation requires both the NQA server and the NQA client. Before you perform the UDP jitter operation, configure the UDP listening service on the NQA server. For more information about UDP listening service configuration, see "Configuring the NQA server."
To configure a UDP jitter operation:
Step
Remarks
N/A
3.     Specify the UDP jitter type and enter its view.
type udp-jitter
N/A
4.     Specify the destination address of UDP packets.
The destination IP address must be the same as the IP address of the listening service on the NQA server.
5.     Specify the destination port of UDP packets.
destination port port-number
By default, no destination port number is specified.
The destination port number must be the same as the port number of the listening service on the NQA server.
6.     (Optional.) Specify the source IP address for UDP packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no UDP packets can be sent out.
7.     (Optional.) Specify the source port number of UDP packets.
source port port-number
By default, no source port number is specified.
8.     (Optional.) Set the payload size for each UDP packet.
data-size size
9.     (Optional.) Specify the payload fill string for UDP packets.
data-fill string
10.     (Optional.) Set the number of UDP packets sent in one UDP jitter operation.
probe packet-number
packet-number
11.     (Optional.) Set the interval for sending UDP packets.
12.     (Optional.) Specify how long the NQA client waits for a response from the server before it regards the response times out.
Use the display nqa result or display nqa statistics command to verify the UDP jitter operation. The display nqa history command does not display the UDP jitter operation results or statistics.
The SNMP operation measures the time for the NQA client to get a response packet from an SNMP agent.
To configure the SNMP operation:
Step
Remarks
N/A
3.     Specify the SNMP type and enter its view.
type snmp
N/A
4.     Specify the destination address of SNMP packets.
5.     (Optional.) Specify the source port of SNMP packets.
6.     (Optional.) Specify the source IP address of SNMP packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no SNMP packets can be sent out.
7.     (Optional.) Specify the community name for the SNMP operation if the operation uses the SNMPv1 or SNMPv2c agent.
community read { cipher | simple } community-name
The default community name is public.
Make sure the specified community name is the same as the community name configured on the SNMP agent.
The TCP operation measures the time for the NQA client to establish a TCP connection to a port on the NQA server.
The TCP operation requires both the NQA server and the NQA client. Before you perform a TCP operation, configure a TCP listening service on the NQA server. For more information about the TCP listening service configuration, see "Configuring the NQA server."
To configure the TCP operation:
Step
Remarks
N/A
3.     Specify the TCP type and enter its view.
type tcp
N/A
4.     Specify the destination address of TCP packets.
The destination address must be the same as the IP address of the listening service configured on the NQA server.
5.     Specify the destination port of TCP packets.
By default, no destination port number is configured.
6.     (Optional.) Specify the source IP address of TCP packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no TCP packets can be sent out.
The UDP echo operation measures the round-trip time between the client and a UDP port on the NQA server.
The UDP echo operation requires both the NQA server and the NQA client. Before you perform a UDP echo operation, configure a UDP listening service on the NQA server. For more information about the UDP listening service configuration, see "Configuring the NQA server."
To configure the UDP echo operation:
Step
Remarks
N/A
3.     Specify the UDP echo type and enter its view.
type udp-echo
N/A
6.     (Optional.) Set the payload size for each UDP packet.
data-size size
7.     (Optional.) Specify the payload fill string for UDP packets.
data-fill string
8.     (Optional.) Specify the source port of UDP packets.
9.     (Optional.) Specify the source IP address of UDP packets.
The UDP tracert operation determines the routing path from the source device to the destination device.
Before you configure the UDP tracert operation, perform the following tasks:
·     Enable sending ICMP time exceeded messages on the intermediate devices between the source and destination devices. If the intermediate devices are H3C devices, use the ip ttl-expires enable command.
·     Enable sending ICMP destination unreachable messages on the destination device. If the destination device is an H3C device, use the ip unreachables enable command.
For more information about the ip ttl-expires enable and ip unreachables enable commands, see Layer 3—IP Services Command Reference.
The UDP tracert operation is not supported in IPv6 networks. To determine the routing path that the IPv6 packets traverse from the source to the destination, use the tracert ipv6 command. For more information about the command, see Network Management and Monitoring Command Reference.
To configure the UDP tracert operation:
Step
Remarks
N/A
3.     Specify the UDP tracert operation type and enter its view.
type udp-tracert
N/A
4.     Specify the destination device for the operation.
·     Specify the destination device by its host name:
destination host
host-name
·     Specify the destination device by its IP address:
By default, no destination IP address or host name is specified.
5.     (Optional.) Specify the destination port of UDP packets.
By default, the destination port number is 33434.
This port number must be an unused number on the destination device, so that the destination device can reply with ICMP port unreachable messages.
data-size size
7.     (Optional.) Enable the no-fragmentation feature.
no-fragment enable
By default, the no-fragmentation feature is disabled.
8.     (Optional.) Set the maximum number of consecutive probe failures.
max-failure times
The default setting is 5.
9.     (Optional.) Set the TTL value for UDP packets in the start round of the UDP tracert operation.
init-ttl value
The default setting is 1.
10.     (Optional.) Specify an output interface for UDP packets.
By default, the output interface for UDP packets is not specified. The NQA client determines the output interface based on the routing table lookup.
11.     (Optional.) Specify the source port of UDP packets.
12.     (Optional.) Specify the source IP address of UDP packets.
·     Specify the IP address of the specified interface as the source IP address:
·     Specify the source IP address:
If you execute the source ip and source interface commands multiple times, the most recent configuration takes effect.
The specified source interface must be up. The source IP address must be the IP address of a local interface, and the local interface must be up. Otherwise, no probe packets can be sent out.
CAUTION:
To ensure successful voice operations and avoid affecting existing services, do not perform the operations on well-known ports from 1 to 1023.
The voice operation measures VoIP network performance.
The voice operation works as follows:
1.     The NQA client sends voice packets at sending intervals to the destination device (NQA server).
The voice packets are of one of the following codec types:
¡     G.711 A-law.
¡     G.711 µ-law.
¡     G.729 A-law.
2.     The destination device time stamps each voice packet it receives and sends it back to the source.
3.     Upon receiving the packet, the source device calculates the jitter and one-way delay based on the timestamp.
The following parameters that reflect VoIP network performance can be calculated by using the metrics gathered by the voice operation:
·     Calculated Planning Impairment Factor (ICPIF)—Measures impairment to voice quality in a VoIP network. It is decided by packet loss and delay. A higher value represents a lower service quality.
·     Mean Opinion Scores (MOS)—A MOS value can be evaluated by using the ICPIF value, in the range of 1 to 5. A higher value represents a higher service quality.
The evaluation of voice quality depends on users' tolerance for voice quality. For users with higher tolerance for voice quality, use the advantage-factor command to set an advantage factor. When the system calculates the ICPIF value, it subtracts the advantage factor to modify ICPIF and MOS values for voice quality evaluation.
The voice operation requires both the NQA server and the NQA client. Before you perform a voice operation, configure a UDP listening service on the NQA server. For more information about UDP listening service configuration, see "Configuring the NQA server."
The voice operation cannot repeat.
To configure the voice operation:
Step
Remarks
N/A
3.     Specify the voice type and enter its view.
type voice
N/A
4.     Specify the destination address of voice packets.
By default, no destination IP address is configured.
5.     Specify the destination port of voice packets.
6.     (Optional.) Specify the codec type.
codec-type { g711a | g711u | g729a }
By default, the codec type is G.711 A-law.
7.     (Optional.) Set the advantage factor for calculating MOS and ICPIF values.
advantage-factor factor
By default, the advantage factor is 0.
8.     (Optional.) Specify the source IP address of voice packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no voice packets can be sent out.
9.     (Optional.) Specify the source port number of voice packets.
10.     (Optional.) Set the payload size for each voice packet.
data-size size
By default, the voice packet size varies by codec type. The default packet size is 172 bytes for G.711A-law and G.711 µ-law codec type, and 32 bytes for G.729 A-law codec type.
11.     (Optional.) Specify the payload fill string for voice packets.
data-fill string
12.     (Optional.) Set the number of voice packets to be sent in a voice probe.
probe packet-number packet-number
The default setting is 1000.
13.     (Optional.) Set the interval for sending voice packets.
14.     (Optional.) Specify how long the NQA client waits for a response from the server before it regards the response times out.
The default setting is 5000 milliseconds.
Use the display nqa result or display nqa statistics command to verify the voice operation. The display nqa history command does not display the voice operation results or statistics.
The DLSw operation measures the response time of a DLSw device.
To configure the DLSw operation:
Step
Remarks
N/A
3.     Specify the DLSw type and enter its view.
type dlsw
N/A
4.     Specify the destination IP address of probe packets.
5.     (Optional.) Specify the source IP address of probe packets.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
The path jitter operation measures the jitter, negative jitters, and positive jitters from the NQA client to each hop on the path to the destination.
Before you configure the path jitter operation, perform the following tasks:
To configure the path jitter operation:
Step
Remarks
N/A
3.     Specify the path jitter type and enter its view.
type path-jitter
N/A
4.     Specify the destination address of ICMP echo requests.
data-size size
data-fill string
7.     Specify the source IP address of ICMP echo requests.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no ICMP echo requests can be sent out.
8.     (Optional.) Set the number of ICMP echo requests to be sent in a path jitter operation.
9.     (Optional.) Set the interval for sending ICMP echo requests.
10.     (Optional.) Specify how long the NQA client waits for a response from the server before it regards the response times out.
11.     (Optional.) Specify an LSR path.
lsr-path ip-address&<1-8>
By default, no LSR path is specified.
The path jitter operation uses the tracert to detect the LSR path to the destination, and sends ICMP echo requests to each hop on the LSR.
12.     (Optional.) Perform the path jitter operation only on the destination address.
target-only
By default, the path jitter operation is performed on each hop on the path to the destination.
Unless otherwise specified, the following optional parameters apply to all types of NQA operations.
The parameter settings take effect only on the current operation.
To configure optional parameters for an NQA operation:
Step
Remarks
N/A
3.     Specify an NQA operation type and enter its view.
type { dhcp | dlsw | dns | ftp | http | icmp-echo | icmp-jitter | path-jitter | snmp | tcp | udp-echo | udp-jitter | udp-tracert | voice }
N/A
4.     Configure a description.
By default, no description is configured.
5.     Set the interval at which the NQA operation repeats.
frequency interval
For a voice or path jitter operation, the default setting is 60000 milliseconds.
For other types of operations, the default setting is 0 milliseconds, and only one operation is performed.
If the operation is not completed when the interval expires, the next operation does not start.
6.     Specify the probe times.
probe count times
By default:
·     In an UDP tracert operation, the NQA client performs three probes to each hop to the destination.
·     In other types of operations, the NQA client performs one probe to the destination per operation.
This command is not available for the path jitter and voice operations. Each of these operations performs only one probe.
7.     Set the probe timeout time.
probe timeout timeout
This command is not available for the ICMP jitter, path jitter, UDP jitter, or voice operations.
8.     Set the maximum number of hops that the probe packets can traverse.
ttl value
The default setting is 30 for probe packets of the UDP tracert operation, and is 20 for probe packets of other types of operations.
This command is not available for the DHCP or path jitter operation.
9.     Set the ToS value in the IP header of probe packets.
tos value
The default setting is 0.
10.     Enable the routing table bypass feature.
route-option bypass-route
By default, the routing table bypass feature is disabled.
This command is not available for the DHCP and path jitter operations.
11.     Specify the VPN instance where the operation is performed.
By default, the operation is performed on the public network.
Collaboration is implemented by associating a reaction entry of an NQA operation with a track entry. The reaction entry monitors the NQA operation. If the number of operation failures reaches the specified threshold, the configured action is triggered.
To configure the collaboration feature:
Step
Remarks
N/A
type { dhcp | dlsw | dns | ftp | http | icmp-echo | snmp | tcp | udp-echo }
The collaboration feature is not available for the ICMP jitter, path jitter, UDP tracert, UDP jitter, or voice operations.
4.     Configure a reaction entry.
reaction item-number checked-element probe-fail threshold-type consecutive consecutive-occurrences action-type trigger-only
By default, no reaction entry is configured.
You cannot modify the content of an existing reaction entry.
5.     Return to system view.
N/A
6.     Associate Track with NQA.
See High Availability Configuration Guide.
N/A
7.     Associate Track with an application module.
N/A
This feature allows you to monitor the NQA operation running status.
Threshold types
An NQA operation supports the following threshold types:
·     average—If the average value for the monitored performance metric either exceeds the upper threshold or goes below the lower threshold, a threshold violation occurs.
·     accumulate—If the total number of times that the monitored performance metric is out of the specified value range reaches or exceeds the specified threshold, a threshold violation occurs.
·     consecutive—If the number of consecutive times that the monitored performance metric is out of the specified value range reaches or exceeds the specified threshold, a threshold violation occurs.
Threshold violations for the average or accumulate threshold type are determined on a per NQA operation basis. The threshold violations for the consecutive type are determined from the time the NQA operation starts.
Triggered actions
The following actions might be triggered:
·     none—NQA displays results only on the terminal screen. It does not send traps to the NMS.
·     trap-only—NQA displays results on the terminal screen, and meanwhile it sends traps to the NMS.
·     trigger-only—NQA displays results on the terminal screen, and meanwhile triggers other modules for collaboration.
The DNS operation does not support the action of sending trap messages.
Reaction entry
In a reaction entry, configure a monitored element, a threshold type, and an action to be triggered to implement threshold monitoring.
The state of a reaction entry can be invalid, over-threshold, or below-threshold.
·     Before an NQA operation starts, the reaction entry is in invalid state.
·     If the threshold is violated, the state of the entry is set to over-threshold. Otherwise, the state of the entry is set to below-threshold.
If the action is trap-only for a reaction entry, a trap message is sent to the NMS when the state of the entry changes.
Configuration procedure
Before you configure threshold monitoring, configure the destination address of the trap messages by using the snmp-agent target-host command. For more information about the command, see Network Management and Monitoring Command Reference.
To configure threshold monitoring:
Step
Remarks
N/A
3.     Enter NQA operation view.
type { dhcp | dlsw | dns | ftp | http | icmp-echo | icmp-jitter | snmp | tcp | udp-echo | udp-jitter | udp-tracert | voice }
The threshold monitoring feature is not available for the path jitter operation.
4.     Enable sending traps to the NMS when specific conditions are met.
reaction trap { path-change | probe-failure consecutive-probe-failures | test-complete | test-failure [ accumulate-probe-failures ] }
By default, no traps are sent to the NMS.
The ICMP jitter, UDP jitter, and voice operations support only the test-complete keyword.
The following parameters are not available for the UDP tracert operation:
·     The probe-failure consecutive-probe-failures option.
·     The accumulate-probe-failures argument.
5.     Configure threshold monitoring.
·     Monitor the operation duration (not supported in the ICMP jitter, UDP jitter, UDP tracert, or voice operations):
reaction item-number checked-element probe-duration threshold-type { accumulate accumulate-occurrences | average | consecutive consecutive-occurrences } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
·     Monitor failure times (not supported in the ICMP jitter, UDP jitter, UDP tracert, or voice operations):
reaction item-number checked-element probe-fail threshold-type { accumulate accumulate-occurrences | consecutive consecutive-occurrences } [ action-type { none | trap-only } ]
·     Monitor the round-trip time (only for the ICMP jitter, UDP jitter, and voice operations):
reaction item-number checked-element rtt threshold-type { accumulate accumulate-occurrences | average } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
·     Monitor packet loss (only for the ICMP jitter, UDP jitter, and voice operations):
reaction item-number checked-element packet-loss threshold-type accumulate accumulate-occurrences [ action-type { none | trap-only } ]
·     Monitor the one-way jitter (only for the ICMP jitter, UDP jitter, and voice operations):
reaction item-number checked-element { jitter-ds | jitter-sd } threshold-type { accumulate accumulate-occurrences | average } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
·     Monitor the one-way delay (only for the ICMP jitter, UDP jitter, and voice operations):
reaction item-number checked-element { owd-ds | owd-sd } threshold-value upper-threshold lower-threshold
·     Monitor the ICPIF value (only for the voice operation):
reaction item-number checked-element icpif threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
·     Monitor the MOS value (only for the voice operation):
reaction item-number checked-element mos threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
N/A
NQA forms statistics within the same collection interval as a statistics group. To display information about the statistics groups, use the display nqa statistics command.
If you use the frequency command to set the interval to 0 milliseconds for an NQA operation, NQA does not generate any statistics group for the operation.
To configure the NQA statistics collection feature:
Step
Remarks
N/A
type { dhcp | dlsw | dns | ftp | http | icmp-echo | icmp-jitter | path-jitter | snmp | tcp | udp-echo | udp-jitter | voice }
The NQA statistics collection feature is not available for UDP tracert operation.
4.     (Optional.) Set the interval for collecting the statistics.
statistics interval interval
The default setting is 60 minutes.
5.     (Optional.) Set the maximum number of statistics groups that can be saved.
statistics max-group number
The default setting is two groups.
To disable the NQA statistics collection feature, set the maximum number to 0.
When the maximum number of statistics groups is reached, to save a new statistics group, the oldest statistics group is deleted.
6.     (Optional.) Set the hold time of statistics groups.
statistics hold-time hold-time
The default setting is 120 minutes.
A statistics group is deleted when its hold time expires.
Step
Remarks
N/A
3.     Enter NQA operation type view.
type { dhcp | dlsw | dns | ftp | http | icmp-echo | snmp | tcp | udp-echo | udp-tracert }
The history record saving feature is not available for the ICMP jitter, UDP jitter, path jitter, or voice operations.
4.     Enable the saving of history records for the NQA operation.
history-record enable
By default, this feature is enabled only for the UDP tracert operation.
5.     (Optional.) Set the lifetime of history records.
history-record keep-time keep-time
A record is deleted when its lifetime is reached.
6.     (Optional.) Set the maximum number of history records that can be saved.
history-record number number
The default setting is 50.
If the maximum number of history records for an NQA operation is reached, the earliest history records are deleted.
7.     (Optional.) Display NQA history records.
display nqa history
N/A
The NQA operation works between the specified start time and the end time (the start time plus operation duration). If the specified start time is ahead of the system time, the operation starts immediately. If both the specified start and end time are ahead of the system time, the operation does not start. To display the current system time, use the display clock command.
When you schedule an NQA operation, follow these restrictions and guidelines:
·     You cannot enter the operation type view or the operation view of a scheduled NQA operation.
·     A system time adjustment does not affect started or completed NQA operations. It affects only the NQA operations that have not started.
To schedule the NQA operation on the NQA client:
Step
2.     Specify the scheduling parameters for an NQA operation.
nqa schedule admin-name operation-tag start-time { hh:mm:ss [ yyyy/mm/dd | mm/dd/yyyy ] | now } lifetime { lifetime | forever } [ recurring ]
An NQA template is a set of operation parameters, such as the destination address, the destination port number, and the destination server URL. You can use an NQA template in other feature modules to provide statistics. You can create multiple templates on a device, and each template must be uniquely named.
NQA template supports the DNS, FTP, HTTP, HTTPS, ICMP, RADIUS, SSL, TCP, TCP half open, and UDP operation types.
Some operation parameters for an NQA template can be specified by the template configuration or the feature that uses the template. When both are specified, the parameters in the template configuration take effect.
Tasks at a glance
·     Configuring the ICMP template
·     Configuring the DNS template
·     Configuring the TCP template
·     Configuring the TCP half open template
·     Configuring the UDP template
·     Configuring the HTTP template
·     Configuring the HTTPS template
·     Configuring the FTP template
·     Configuring the RADIUS template
·     Configuring the SSL template
(Optional.) Configuring optional parameters for the NQA template
A feature that uses the ICMP template performs the ICMP operation to measure the reachability of a destination device. The ICMP template is supported in both IPv4 and IPv6 networks.
To configure the ICMP template:
Step
Remarks
N/A
2.     Create an ICMP template and enter its view.
nqa template icmp name
By default, no ICMP templates exist.
3.     (Optional.) Specify the destination IP address of the operation.
·     IPv4 address:
·     IPv6 address:
4.     (Optional.) Set the payload size for each ICMP request.
data-size size
5.     (Optional.) Specify the payload fill string for requests.
data-fill string
6.     (Optional.) Specify the source IP address for ICMP echo requests.
·     Use the IPv4 address of the specified interface as the source IP address:
7.     (Optional.) Specify the next hop IP address for ICMP echo requests.
·     IPv4 address:
·     IPv6 address:
By default, no IP address of the next hop is configured.
8.     (Optional.) Configure the probe result sending on a per-probe basis.
reaction trigger per-probe
By default, the probe result is sent to the feature that uses the template after three consecutive failed or successful probes.
If you execute the reaction trigger per-probe and reaction trigger probe-pass commands multiple times, the most recent configuration takes effect.
If you execute the reaction trigger per-probe and reaction trigger probe-fail commands multiple times, the most recent configuration takes effect.
A feature that uses the DNS template performs the DNS operation to determine the status of the server. It is supported in both IPv4 and IPv6 networks.
In DNS template view, you can specify the address expected to be returned. If the returned IP addresses include the expected address, the DNS server is valid and the operation succeeds. Otherwise, the operation fails.
Create a mapping between the domain name and an address before you perform the DNS operation. For information about configuring the DNS server, see Layer 3—IP Services Configuration Guide.
To configure the DNS template:
Step
Remarks
N/A
2.     Create a DNS template and enter DNS template view.
nqa template dns name
By default, no DNS templates exist.
3.     (Optional.) Specify the destination IP address of DNS packets.
·     IPv4 address:
·     IPv6 address:
By default, no destination address is specified.
4.     (Optional.) Specify the destination port number for the operation.
By default, the destination port number is 53.
6.     Specify the domain name resolution type.
resolve-type { A | AAAA }
By default, the type is type A.
A type A query resolves a domain name to a mapped IPv4 address, and a type AAAA query to a mapped IPv6 address.
7.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
8.     (Optional.) Specify the source port for probe packets.
9.     (Optional.) Specify the IP address that is expected to be returned.
·     IPv4 address:
expect ip ip-address
·     IPv6 address:
expect ipv6 ipv6-address
By default, no expected IP address is specified.
A feature that uses the TCP template performs the TCP operation to test whether the NQA client can establish a TCP connection to a specific port on the server.
In TCP template view, you can specify the expected data to be returned. If you do not specify the expected data, the TCP operation tests only whether the client can establish a TCP connection to the server.
To configure the TCP template:
Step
Remarks
N/A
2.     Create a TCP template and enter its view.
nqa template tcp name
By default, no TCP templates exist.
·     IPv4 address:
·     IPv6 address:
data-fill string
6.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
7.     (Optional.) Configure the expected data.
expect data expression [ offset number ]
By default, no expected data is configured.
The NQA client performs expect data check only when you configure both the data-fill and expect-data commands.
A feature that uses the TCP half open template performs the TCP half open operation to test whether the TCP service is available on the server. The TCP half open operation is used when the feature cannot get a response from the TCP server through an existing TCP connection.
In the TCP half open operation, the NQA client sends a TCP ACK packet to the server. If the client receives an RST packet, it considers that the TCP service is available on the server.
To configure the TCP half open template:
Step
Remarks
N/A
2.     Create a TCP half open template and enter its view.
nqa template tcphalfopen name
By default, no TCP half open templates exist.
·     IPv4 address:
·     IPv6 address:
4.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
5.     (Optional.) Specify the next hop IP address for the probe packets.
·     IPv4 address:
·     IPv6 address:
By default, the IP address of the next hop is configured.
6.     (Optional.) Configure the probe result sending on a per-probe basis.
A feature that uses the UDP template performs the UDP operation to test the following items:
·     Reachability of a specific port on the NQA server.
·     Availability of the requested service on the NQA server.
In UDP template view, you can specify the expected data to be returned. If you do not specify the expected data, the UDP operation tests only whether the client can receive the response packet from the server.
The UDP operation requires both the NQA server and the NQA client. Before you perform a UDP operation, configure a UDP listening service on the NQA server. For more information about the UDP listening service configuration, see "Configuring the NQA server."
To configure the UDP template:
Step
Remarks
N/A
2.     Create a UDP template and enter its view.
nqa template udp name
By default, no UDP templates exist.
·     IPv4 address:
·     IPv6 address:
5.     (Optional.) Specify the payload fill string for the probe packets.
data-fill string
6.     (Optional.) Set the payload size for the probe packets.
data-size size
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
8.     (Optional.) Configure the expected data.
If you want to configure this command, make sure the data-fill command is already executed.
A feature that uses the HTTP template performs the HTTP operation to measure the time it takes the NQA client to obtain data from an HTTP server.
The expected data is checked only when the data is configured and the HTTP response contains the Content-Length field in the HTTP header.
The status code of the HTTP packet is a three-digit field in decimal notation, and it includes the status information for the HTTP server. The first digit defines the class of response.
Configure the HTTP server before you perform the HTTP operation.
To configure the HTTP template:
Step
Remarks
N/A
2.     Create an HTTP template and enter its view.
nqa template http name
By default, no HTTP templates exist.
3.     Specify the URL of the destination HTTP server.
url url
4.     Specify an HTTP login username.
username username
5.     Specify an HTTP login password.
6.     (Optional.) Specify the HTTP version.
7.     (Optional.) Specify the HTTP operation type.
If you set the HTTP operation type to raw, use the raw-request command to specify the content of the HTTP request to be sent to the HTTP server.
8.     (Optional.) Enter raw request view.
raw-request
Every time you enter the raw request view, the existing request content configuration is removed.
9.     (Optional.) Enter or paste the content of the HTTP request for the HTTP operation.
N/A
By default, the HTTP request content is not specified.
10.     (Optional.) Return to HTTP template view.
The system automatically saves the configuration in raw request view before it returns to HTTP template view.
11.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
12.     (Optional.) Configure the expected status codes.
expect status status-list
By default, no expected status code is configured.
13.     (Optional.) Configure the expected data.
A feature that uses the HTTPS template performs the HTTPS operation to measure the time it takes for the NQA client to obtain data from an HTTPS server.
The expected data is checked only when the expected data is configured and the HTTPS response contains the Content-Length field in the HTTPS header.
The status code of the HTTPS packet is a three-digit field in decimal notation, and it includes the status information for the HTTPS server. The first digit defines the class of response.
Before you perform the HTTPS operation, configure the HTTPS server and the SSL client policy for the SSL client. For information about configuring SSL client policies, see Security Configuration Guide.
To configure the HTTPS template:
Step
Remarks
N/A
2.     Create an HTTPS template and enter its view.
nqa template https name
By default, no HTTPS templates exist.
3.     Specify the URL of the destination HTTPS server.
url url
By default, no URL is specified for the destination HTTPS server.
·     https://host/resource.
·     https://host:port/resource.
4.     Specify an HTTPS login username.
username username
By default, no HTTPS login username is specified.
5.     Specify an HTTPS login password.
By default, no HTTPS login password is specified.
6.     Specify an SSL client policy.
ssl-client-policy policy-name
By default, no SSL client policy is specified.
7.     (Optional.) Specify the HTTPS version.
By default, HTTPS 1.0 is used.
8.     (Optional.) Specify the HTTPS operation type.
By default, the HTTPS operation type is get, which means obtaining data from the HTTPS server.
If you set the HTTPS operation type to raw, use the raw-request command to configure the content of the request to be sent to the HTTPS server.
9.     (Optional.) Enter raw request view.
raw-request
Every time you enter the raw request view, the previously configured request content is removed.
10.     (Optional.) Enter or paste the content of the HTTPS request for the HTTPS operation.
N/A
By default, the HTTPS request content is not specified.
11.     (Optional.) Return to HTTPS template view.
The system automatically saves the configuration in raw request view before it returns to HTTPS template view.
12.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
14.     (Optional.) Configure the expected status codes.
A feature that uses the FTP template performs the FTP operation. The operation measures the time it takes the NQA client to transfer a file to or download a file from an FTP server.
Configure the username and password for the FTP client to log in to the FTP server before you perform an FTP operation. For information about configuring the FTP server, see Fundamentals Configuration Guide.
To configure the FTP template:
Step
Remarks
N/A
2.     Create an FTP template and enter its view.
nqa template ftp name
By default, no FTP templates exist.
3.     Specify the URL of the destination FTP server.
url url
When you perform the put operation, the filename argument does not take effect, even if it is specified. The file name for the put operation is determined by the filename command.
4.     (Optional.) Specify the FTP operation type.
5.     Specify an FTP login username.
username username
By default, no FTP login username is specified.
6.     Specify an FTP login password.
password { cipher | simple } sting
By default, no FTP login password is specified.
7.     (Optional.) Specify the name of a file to be transferred.
filename filename
This configuration does not take effect for the get operation.
8.     Set the data transmission mode.
9.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
A feature that uses the RADIUS template performs the RADIUS operation to check the availability of the authentication service on the RADIUS server.
The RADIUS operation authentication workflow is as follows:
1.     The NQA client sends an authentication request (Access-Request) to the RADIUS server. The request includes the username and the user's password. The password has been encrypted by the MD5 algorithm and the shared key.
2.     The RADIUS server authenticates the username and password.
¡     If the authentication succeeds, the server sends an Access-Accept packet to the NQA client.
¡     If the authentication fails, the server sends an Access-Reject packet to the NQA client.
If the NQA client can receive the Access-Accept packet from the RADIUS server, the authentication service is available on the RADIUS server. Otherwise, the authentication service is not available on the RADIUS server.
Before you configure the RADIUS template, specify a username, password, and shared key on the RADIUS server. For more information about configuring the RADIUS server, see Security Configuration Guide.
To configure the RADIUS template:
Step
Remarks
N/A
2.     Create a RADIUS template and enter its view.
nqa template radius name
By default, no RADIUS templates exist.
·     IPv4 address:
·     IPv6 address:
By default, the destination port number is 1812.
5.     Specify a username.
username username
By default, no username is specified.
6.     Specify a password.
By default, no password is specified.
7.     Specify a shared key for secure RADIUS authentication.
key { cipher | simple } string
By default, no shared key is specified for RADIUS authentication.
8.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
A feature that uses the SSL template performs the SSL operation to measure the time required to establish an SSL connection to an SSL server.
Before you configure the SSL template, configure the SSL client policy. For information about configuring SSL client policies, see Security Configuration Guide.
To configure the SSL template:
Step
Remarks
N/A
2.     Create an SSL template and enter its view.
nqa template ssl name
By default, no SSL templates exist.
·     IPv4 address:
·     IPv6 address:
By default, the destination port number is not specified.
5.     (Optional.) Specify the source IP address for the probe packets.
·     IPv4 address:
source ip
ip-address
·     IPv6 address:
source ipv6
ipv6-address
Unless otherwise specified, the following optional parameters apply to all types of NQA templates.
The parameter settings take effect only on the current NQA template.
To configure optional parameters for an NQA template:
Step
Remarks
N/A
2.     Create an NQA template and enter its view.
nqa template { dns | ftp | http | https | icmp | ssl | tcp | tcphalfopen | udp } name
By default, no NQA templates exist.
3.     Configure a description.
4.     Set the interval at which the NQA operation repeats.
frequency interval
5.     Set the probe timeout time.
6.     Set the TTL for probe packets.
ttl value
The default setting is 20.
7.     Set the ToS value in the IP header of probe packets.
tos value
8.     Specify the VPN instance where the operation is performed.
9.     Set the number of consecutive successful probes to determine a successful operation event.
reaction trigger probe-pass count
The default setting is 3.
If the number of consecutive successful probes for an NQA operation is reached, the NQA client notifies the feature that uses the template of the successful operation event.
10.     Set the number of consecutive probe failures to determine an operation failure.
reaction trigger probe-fail count
If the number of consecutive probe failures for an NQA operation is reached, the NQA client notifies the feature that uses the NQA template of the operation failure.
Display history records of NQA operations.
display nqa history [ admin-name operation-tag ]
Display the current monitoring results of reaction entries.
display nqa reaction counters [ admin-name operation-tag [ item-number ] ]
Display the most recent result of the NQA operation.
display nqa result [ admin-name operation-tag ]
Display NQA statistics.
display nqa statistics [ admin-name operation-tag ]
Display NQA server status.
display nqa server status
Network requirements
As shown in Figure 3, configure an ICMP echo operation on the NQA client (Device A) to test the round-trip time to Device B. The next hop of Device A is Device C.
Figure 3 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 3. (Details not shown.)
# Configure static routes or a routing protocol to make sure the devices can reach each other. (Details not shown.)
# Create an ICMP echo operation.
[DeviceA] nqa entry admin test1
[DeviceA-nqa-admin-test1] type icmp-echo
# Specify 10.2.2.2 as the destination IP address of ICMP echo requests.
[DeviceA-nqa-admin-test1-icmp-echo] destination ip 10.2.2.2
# Specify 10.1.1.2 as the next hop. The ICMP echo requests are sent through Device C to Device B.
[DeviceA-nqa-admin-test1-icmp-echo] next-hop ip 10.1.1.2
# Configure the ICMP echo operation to perform 10 probes.
[DeviceA-nqa-admin-test1-icmp-echo] probe count 10
# Set the probe timeout time to 500 milliseconds for the ICMP echo operation.
[DeviceA-nqa-admin-test1-icmp-echo] probe timeout 500
# Configure the ICMP echo operation to repeat every 5000 milliseconds.
[DeviceA-nqa-admin-test1-icmp-echo] frequency 5000
# Enable saving history records.
[DeviceA-nqa-admin-test1-icmp-echo] history-record enable
# Set the maximum number of history records to 10.
[DeviceA-nqa-admin-test1-icmp-echo] history-record number 10
[DeviceA-nqa-admin-test1-icmp-echo] quit
# Start the ICMP echo operation.
[DeviceA] nqa schedule admin test1 start-time now lifetime forever
# After the ICMP echo operation runs for a period of time, stop the operation.
[DeviceA] undo nqa schedule admin test1
# Display the most recent result of the ICMP echo operation.
[DeviceA] display nqa result admin test1
NQA entry (admin admin, tag test1) test results:
    Send operation times: 10             Receive response times: 10
    Min/Max/Average round trip time: 2/5/3
    Square-Sum of round trip time: 96
    Last succeeded probe time: 2011-08-23 15:00:01.2
  Extended results:
    Packet loss ratio: 0%
    Failures due to timeout: 0
    Failures due to internal error: 0
    Failures due to other errors: 0
# Display the history records of the ICMP echo operation.
[DeviceA] display nqa history admin test1
NQA entry (admin admin, tag test) history records:
  Index      Response     Status           Time
  370        3            Succeeded        2007-08-23 15:00:01.2
  369        3            Succeeded        2007-08-23 15:00:01.2
  368        3            Succeeded        2007-08-23 15:00:01.2
  367        5            Succeeded        2007-08-23 15:00:01.2
  366        3            Succeeded        2007-08-23 15:00:01.2
  365        3            Succeeded        2007-08-23 15:00:01.2
  364        3            Succeeded        2007-08-23 15:00:01.1
  363        2            Succeeded        2007-08-23 15:00:01.1
  362        3            Succeeded        2007-08-23 15:00:01.1
  361        2            Succeeded        2007-08-23 15:00:01.1
The output shows that the packets sent by Device A can reach Device B through Device C. No packet loss occurs during the operation. The minimum, maximum, and average round-trip times are 2, 5, and 3 milliseconds, respectively.
ICMP jitter operation configuration example
As shown in Figure 4, configure an ICMP jitter operation to test the jitter between Device A and Device B.
Figure 4 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 4. (Details not shown.)
2.     Configure static routes or a routing protocol to make sure the devices can reach each other. (Details not shown.)
3.     Configure Device A:
# Create an ICMP jitter operation.
[DeviceA-nqa-admin-test1] type icmp-jitter
# Specify 10.2.2.2 as the destination address for the operation.
[DeviceA-nqa-admin-test1-icmp-jitter] destination ip 10.2.2.2
# Configure the operation to repeat every 1000 milliseconds.
[DeviceA-nqa-admin-test1-icmp-jitter] frequency 1000
[DeviceA-nqa-admin-test1-icmp-jitter] quit
# Start the ICMP jitter operation.
# After the ICMP jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the ICMP jitter operation.
    Min/Max/Average round trip time: 1/2/1
    Square-Sum of round trip time: 13
    Last packet received time: 2015-03-09 17:40:29.8
  Extended results:
    Packets out of sequence: 0
    Packets arrived late: 0
  ICMP-jitter results:
   RTT number: 10
    Min positive SD: 0                     Min positive DS: 0
    Max positive SD: 0                     Max positive DS: 0
    Positive SD number: 0                  Positive DS number: 0
    Positive SD sum: 0                     Positive DS sum: 0
    Positive SD average: 0                 Positive DS average: 0
    Positive SD square-sum: 0              Positive DS square-sum: 0
    Min negative SD: 1                     Min negative DS: 2
    Max negative SD: 1                     Max negative DS: 2
    Negative SD number: 1                  Negative DS number: 1
    Negative SD sum: 1                     Negative DS sum: 2
    Negative SD average: 1                 Negative DS average: 2
    Negative SD square-sum: 1              Negative DS square-sum: 4
  One way results:
    Max SD delay: 1                        Max DS delay: 2
    Min SD delay: 1                        Min DS delay: 2
    Number of SD delay: 1                  Number of DS delay: 1
    Sum of SD delay: 1                     Sum of DS delay: 2
    Square-Sum of SD delay: 1              Square-Sum of DS delay: 4
    Lost packets for unknown reason: 0
# Display the statistics of the ICMP jitter operation.
[DeviceA] display nqa statistics admin test1
NQA entry (admin admin, tag test1) test statistics:
  NO. : 1
    Start time: 2015-03-09 17:42:10.7
    Life time: 156 seconds
    Send operation times: 1560           Receive response times: 1560
    Square-Sum of round trip time: 1563
  Extended results:
   RTT number: 1560
    Min positive SD: 1                     Min positive DS: 1
    Max positive SD: 1                     Max positive DS: 2
    Positive SD number: 18                 Positive DS number: 46
    Positive SD sum: 18                    Positive DS sum: 49
    Positive SD average: 1                 Positive DS average: 1
    Positive SD square-sum: 18             Positive DS square-sum: 55
    Min negative SD: 1                     Min negative DS: 1
    Negative SD number: 24                 Negative DS number: 57
    Negative SD sum: 24                    Negative DS sum: 58
    Negative SD average: 1                 Negative DS average: 1
    Negative SD square-sum: 24             Negative DS square-sum: 60
  One way results:
    Min SD delay: 1                        Min DS delay: 1
    Number of SD delay: 4                  Number of DS delay: 4
    Sum of SD delay: 4                     Sum of DS delay: 5
    Square-Sum of SD delay: 4              Square-Sum of DS delay: 7
DHCP operation configuration example
As shown in Figure 5, configure a DHCP operation to test the time required for Switch A to obtain an IP address from the DHCP server (Switch B).
Figure 5 Network diagram
# Create a DHCP operation.
[SwitchA] nqa entry admin test1
[SwitchA-nqa-admin-test1] type dhcp
# Specify the DHCP server address 10.1.1.2 as the destination address.
[SwitchA-nqa-admin-test1-dhcp] destination ip 10.1.1.2
# Enable the saving of history records.
[SwitchA-nqa-admin-test1-dhcp] history-record enable
[SwitchA-nqa-admin-test1-dhcp] quit
# Start the DHCP operation.
[SwitchA] nqa schedule admin test1 start-time now lifetime forever
# After the DHCP operation runs for a period of time, stop the operation.
[SwitchA] undo nqa schedule admin test1
# Display the most recent result of the DHCP operation.
[SwitchA] display nqa result admin test1
    Send operation times: 1              Receive response times: 1
    Min/Max/Average round trip time: 512/512/512
    Square-Sum of round trip time: 262144
    Last succeeded probe time: 2011-11-22 09:56:03.2
  Extended results:
# Display the history records of the DHCP operation.
[SwitchA] display nqa history admin test1
NQA entry (admin admin, tag test1) history records:
  1          512          Succeeded        2011-11-22 09:56:03.2
The output shows that it took Switch A 512 milliseconds to obtain an IP address from the DHCP server.
DNS operation configuration example
As shown in Figure 6, configure a DNS operation to test whether Device A can perform address resolution through the DNS server and test the resolution time.
Figure 6 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 6. (Details not shown.)
# Create a DNS operation.
[DeviceA-nqa-admin-test1] type dns
# Specify the IP address of the DNS server 10.2.2.2 as the destination address.
[DeviceA-nqa-admin-test1-dns] destination ip 10.2.2.2
# Specify host.com as the domain name to be translated.
[DeviceA-nqa-admin-test1-dns] resolve-target host.com
[DeviceA-nqa-admin-test1-dns] history-record enable
[DeviceA-nqa-admin-test1-dns] quit
# Start the DNS operation.
# After the DNS operation runs for a period of time, stop the operation.
# Display the most recent result of the DNS operation.
    Min/Max/Average round trip time: 62/62/62
    Square-Sum of round trip time: 3844
    Last succeeded probe time: 2011-11-10 10:49:37.3
  Extended results:
# Display the history records of the DNS operation.
  1          62           Succeeded        2011-11-10 10:49:37.3
The output shows that it took Device A 62 milliseconds to translate domain name host.com into an IP address.
FTP operation configuration example
As shown in Figure 7, configure an FTP operation to test the time required for Device A to upload a file to the FTP server. The login username and password are admin and systemtest, respectively. The file to be transferred to the FTP server is config.txt.
Figure 7 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 7. (Details not shown.)
# Create an FTP operation.
[DeviceA-nqa-admin-test1] type ftp
# Specify the URL of the FTP server.
[DeviceA-nqa-admin-test-ftp] url ftp://10.2.2.2
# Specify 10.1.1.1 as the source IP address.
[DeviceA-nqa-admin-test1-ftp] source ip 10.1.1.1
# Configure the device to upload file config.txt to the FTP server.
[DeviceA-nqa-admin-test1-ftp] operation put
[DeviceA-nqa-admin-test1-ftp] filename config.txt
# Set the username to admin for the FTP operation.
[DeviceA-nqa-admin-test1-ftp] username admin
# Set the password to systemtest for the FTP operation.
[DeviceA-nqa-admin-test1-ftp] password simple systemtest
[DeviceA-nqa-admin-test1-ftp] history-record enable
[DeviceA-nqa-admin-test1-ftp] quit
# Start the FTP operation.
# After the FTP operation runs for a period of time, stop the operation.
# Display the most recent result of the FTP operation.
    Min/Max/Average round trip time: 173/173/173
    Square-Sum of round trip time: 29929
    Last succeeded probe time: 2011-11-22 10:07:28.6
  Extended results:
    Failures due to disconnect: 0
    Failures due to no connection: 0
# Display the history records of the FTP operation.
  1          173          Succeeded        2011-11-22 10:07:28.6
The output shows that it took Device A 173 milliseconds to upload a file to the FTP server.
HTTP operation configuration example
As shown in Figure 8, configure an HTTP operation on the NQA client to test the time required to obtain data from the HTTP server.
Figure 8 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 8. (Details not shown.)
# Create an HTTP operation.
[DeviceA-nqa-admin-test1] type http
# Specify the URL of the HTTP server.
[DeviceA-nqa-admin-test-http] url http://10.2.2.2/index.htm
# Configure the HTTP operation to get data from the HTTP server.
[DeviceA-nqa-admin-test1-http] operation get
# Configure the operation to use HTTP version 1.0.
[DeviceA-nqa-admin-test1-http] version v1.0
[DeviceA-nqa-admin-test1-http] history-record enable
[DeviceA-nqa-admin-test1-http] quit
# Start the HTTP operation.
# After the HTTP operation runs for a period of time, stop the operation.
# Display the most recent result of the HTTP operation.
    Min/Max/Average round trip time: 64/64/64
    Square-Sum of round trip time: 4096
    Last succeeded probe time: 2011-11-22 10:12:47.9
  Extended results:
# Display the history records of the HTTP operation.
  1          64           Succeeded        2011-11-22 10:12:47.9
The output shows that it took Device A 64 milliseconds to obtain data from the HTTP server.
UDP jitter operation configuration example
As shown in Figure 9, configure a UDP jitter operation to test the jitter, delay, and round-trip time between Device A and Device B.
Figure 9 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 9. (Details not shown.)
3.     Configure Device B:
# Enable the NQA server.
[DeviceB] nqa server enable
# Configure a listening service to listen on the IP address 10.2.2.2 and UDP port 9000.
[DeviceB] nqa server udp-echo 10.2.2.2 9000
4.     Configure Device A:
# Create a UDP jitter operation.
[DeviceA-nqa-admin-test1] type udp-jitter
# Specify 10.2.2.2 as the destination address of the operation.
[DeviceA-nqa-admin-test1-udp-jitter] destination ip 10.2.2.2
# Set the destination port number to 9000.
[DeviceA-nqa-admin-test1-udp-jitter] destination port 9000
[DeviceA-nqa-admin-test1-udp-jitter] frequency 1000
[DeviceA-nqa-admin-test1-udp-jitter] quit
# Start the UDP jitter operation.
# After the UDP jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP jitter operation.
    Min/Max/Average round trip time: 15/32/17
    Square-Sum of round trip time: 3235
    Last packet received time: 2011-05-29 13:56:17.6
  Extended results:
  UDP-jitter results:
   RTT number: 10
    Min positive SD: 4                     Min positive DS: 1
    Max positive SD: 21                    Max positive DS: 28
    Positive SD number: 5                  Positive DS number: 4
    Positive SD sum: 52                    Positive DS sum: 38
    Positive SD average: 10                Positive DS average: 10
    Positive SD square-sum: 754            Positive DS square-sum: 460
    Min negative SD: 1                     Min negative DS: 6
    Max negative SD: 13                    Max negative DS: 22
    Negative SD number: 4                  Negative DS number: 5
    Negative SD sum: 38                    Negative DS sum: 52
    Negative SD average: 10                Negative DS average: 10
    Negative SD square-sum: 460            Negative DS square-sum: 754
  One way results:
    Max SD delay: 15                       Max DS delay: 16
    Min SD delay: 7                        Min DS delay: 7
    Number of SD delay: 10                 Number of DS delay: 10
    Sum of SD delay: 78                    Sum of DS delay: 85
    Square-Sum of SD delay: 666            Square-Sum of DS delay: 787
    SD lost packets: 0                   DS lost packets: 0
# Display the statistics of the UDP jitter operation.
  NO. : 1
    Start time: 2011-05-29 13:56:14.0
    Life time: 47 seconds
    Send operation times: 410            Receive response times: 410
    Min/Max/Average round trip time: 1/93/19
    Square-Sum of round trip time: 206176
  Extended results:
  UDP-jitter results:
   RTT number: 410
    Min positive SD: 3                     Min positive DS: 1
    Max positive SD: 30                    Max positive DS: 79
    Positive SD number: 186                Positive DS number: 158
    Positive SD sum: 2602                  Positive DS sum: 1928
    Positive SD average: 13                Positive DS average: 12
    Positive SD square-sum: 45304          Positive DS square-sum: 31682
    Max negative SD: 30                    Max negative DS: 78
    Negative SD number: 181                Negative DS number: 209
    Negative SD sum: 181                   Negative DS sum: 209
    Negative SD average: 13                Negative DS average: 14
    Negative SD square-sum: 46994          Negative DS square-sum: 3030
  One way results:
    Max SD delay: 46                       Max DS delay: 46
    Number of SD delay: 410                Number of DS delay: 410
    Sum of SD delay: 3705                  Sum of DS delay: 3891
    Square-Sum of SD delay: 45987          Square-Sum of DS delay: 49393
SNMP operation configuration example
As shown in Figure 10, configure an SNMP operation to test the time the NQA client uses to get a response from the SNMP agent.
Figure 10 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 10. (Details not shown.)
3.     Configure the SNMP agent (Device B):
# Set the SNMP version to all.
[DeviceB] snmp-agent sys-info version all
# Set the read community to public.
[DeviceB] snmp-agent community read public
# Set the write community to private.
[DeviceB] snmp-agent community write private
# Create an SNMP operation.
[DeviceA-nqa-admin-test1] type snmp
# Specify 10.2.2.2 as the destination IP address of the SNMP operation.
[DeviceA-nqa-admin-test1-snmp] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-snmp] history-record enable
[DeviceA-nqa-admin-test1-snmp] quit
# Start the SNMP operation.
# After the SNMP operation runs for a period of time, stop the operation.
# Display the most recent result of the SNMP operation.
    Min/Max/Average round trip time: 50/50/50
    Square-Sum of round trip time: 2500
    Last succeeded probe time: 2011-11-22 10:24:41.1
  Extended results:
# Display the history records of the SNMP operation.
  1          50           Succeeded        2011-11-22 10:24:41.1
The output shows that it took Device A 50 milliseconds to receive a response from the SNMP agent.
TCP operation configuration example
As shown in Figure 11, configure a TCP operation to test the time required for Device A to establish a TCP connection with Device B.
Figure 11 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 11. (Details not shown.)
# Configure a listening service to listen on the IP address 10.2.2.2 and TCP port 9000.
[DeviceB] nqa server tcp-connect 10.2.2.2 9000
# Create a TCP operation.
[DeviceA-nqa-admin-test1] type tcp
# Specify 10.2.2.2 as the destination IP address.
[DeviceA-nqa-admin-test1-tcp] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-tcp] destination port 9000
[DeviceA-nqa-admin-test1-tcp] history-record enable
[DeviceA-nqa-admin-test1-tcp] quit
# Start the TCP operation.
# After the TCP operation runs for a period of time, stop the operation.
# Display the most recent result of the TCP operation.
    Min/Max/Average round trip time: 13/13/13
    Square-Sum of round trip time: 169
    Last succeeded probe time: 2011-11-22 10:27:25.1
  Extended results:
# Display the history records of the TCP operation.
  1          13           Succeeded        2011-11-22 10:27:25.1
The output shows that it took Device A 13 milliseconds to establish a TCP connection to port 9000 on the NQA server.
UDP echo operation configuration example
As shown in Figure 12, configure a UDP echo operation on the NQA client to test the round-trip time to Device B. The destination port number is 8000.
Figure 12 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 12. (Details not shown.)
# Configure a listening service to listen on the IP address 10.2.2.2 and UDP port 8000.
[DeviceB] nqa server udp-echo 10.2.2.2 8000
# Create a UDP echo operation.
[DeviceA-nqa-admin-test1] type udp-echo
[DeviceA-nqa-admin-test1-udp-echo] destination ip 10.2.2.2
# Set the destination port number to 8000.
[DeviceA-nqa-admin-test1-udp-echo] destination port 8000
[DeviceA-nqa-admin-test1-udp-echo] history-record enable
[DeviceA-nqa-admin-test1-udp-echo] quit
# Start the UDP echo operation.
# After the UDP echo operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP echo operation.
    Min/Max/Average round trip time: 25/25/25
    Square-Sum of round trip time: 625
    Last succeeded probe time: 2011-11-22 10:36:17.9
  Extended results:
# Display the history records of the UDP echo operation.
  1          25           Succeeded        2011-11-22 10:36:17.9
The output shows that the round-trip time between Device A and port 8000 on Device B is 25 milliseconds.
UDP tracert operation configuration example
As shown in Figure 13, configure a UDP tracert operation to determine the routing path from Device A to Device B.
Figure 13 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 13. (Details not shown.)
3.     Execute the ip ttl-expires enable command on the intermediate devices and execute the ip unreachables enable command on Device B.
# Create a UDP tracert operation.
[DeviceA-nqa-admin-test1] type udp-tracert
[DeviceA-nqa-admin-test1-udp-tracert] destination ip 10.2.2.2
# Set the destination port number to 33434.
[DeviceA-nqa-admin-test1-udp-tracert] destination port 33434
# Configure Device A to perform three probes to each hop.
[DeviceA-nqa-admin-test1-udp-tracert] probe count 3
# Set the probe timeout time to 500 milliseconds.
[DeviceA-nqa-admin-test1-udp-tracert] probe timeout 500
# Configure the UDP tracert operation to repeat every 5000 milliseconds.
[DeviceA-nqa-admin-test1-udp-tracert] frequency 5000
# Specify GigabitEthernet 1/0/1 as the output interface for UDP packets.
[DeviceA-nqa-admin-test1-udp-tracert] out interface gigabitethernet 1/0/1
# Enable the no-fragmentation feature.
[DeviceA-nqa-admin-test1-udp-tracert] no-fragment enable
# Set the maximum number of consecutive probe failures to 6.
[DeviceA-nqa-admin-test1-udp-tracert] max-failure 6
# Set the TTL value to 1 for UDP packets in the start round of the UDP tracert operation.
[DeviceA-nqa-admin-test1-udp-tracert] init-ttl 1
# Start the UDP tracert operation.
# After the UDP tracert operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP tracert operation.
    Send operation times: 6              Receive response times: 6
    Min/Max/Average round trip time: 1/1/1
    Last succeeded probe time: 2013-09-09 14:46:06.2
  Extended results:
    Packet loss in test: 0%
  UDP-tracert results:
    TTL    Hop IP             Time
    1      3.1.1.1            2013-09-09 14:46:03.2
    2      10.2.2.2           2013-09-09 14:46:06.2
# Display the history records of the UDP tracert operation.
Index      TTL  Response  Hop IP           Status          Time
1          2    2         10.2.2.2         Succeeded       2013-09-09 14:46:06.2
1          2    1         10.2.2.2         Succeeded       2013-09-09 14:46:05.2
1          2    2         10.2.2.2         Succeeded       2013-09-09 14:46:04.2
1          1    1         3.1.1.1          Succeeded       2013-09-09 14:46:03.2
1          1    2         3.1.1.1          Succeeded       2013-09-09 14:46:02.2
1          1    1         3.1.1.1          Succeeded       2013-09-09 14:46:01.2
Voice operation configuration example
As shown in Figure 14, configure a voice operation to test jitters, delay, MOS, and ICPIF between Device A and Device B.
Figure 14 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 14. (Details not shown.)
# Configure a listening service to listen on IP address 10.2.2.2 and UDP port 9000.
# Create a voice operation.
[DeviceA-nqa-admin-test1] type voice
[DeviceA-nqa-admin-test1-voice] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-voice] destination port 9000
[DeviceA-nqa-admin-test1-voice] quit
# Start the voice operation.
# After the voice operation runs for a period of time, stop the operation.
# Display the most recent result of the voice operation.
    Send operation times: 1000           Receive response times: 1000
    Min/Max/Average round trip time: 31/1328/33
    Square-Sum of round trip time: 2844813
    Last packet received time: 2011-06-13 09:49:31.1
  Extended results:
  Voice results:
   RTT number: 1000
    Max positive SD: 204                   Max positive DS: 1297
    Positive SD number: 257                Positive DS number: 259
    Positive SD sum: 759                   Positive DS sum: 1797
    Positive SD average: 2                 Positive DS average: 6
    Positive SD square-sum: 54127          Positive DS square-sum: 1691967
    Max negative SD: 203                   Max negative DS: 1297
    Negative SD number: 255                Negative DS number: 259
    Negative SD sum: 759                   Negative DS sum: 1796
    Negative SD average: 2                 Negative DS average: 6
    Negative SD square-sum: 53655          Negative DS square-sum: 1691776
  One way results:
    Max SD delay: 343                      Max DS delay: 985
    Min SD delay: 343                      Min DS delay: 985
    Sum of SD delay: 343                   Sum of DS delay: 985
    Square-Sum of SD delay: 117649         Square-Sum of DS delay: 970225
  Voice scores:
    MOS value: 4.38                        ICPIF value: 0
# Display the statistics of the voice operation.
  NO. : 1
    Start time: 2011-06-13 09:45:37.8
    Life time: 331 seconds
    Send operation times: 4000           Receive response times: 4000
    Min/Max/Average round trip time: 15/1328/32
    Square-Sum of round trip time: 7160528
  Extended results:
  Voice results:
   RTT number: 4000
    Max positive SD: 360                   Max positive DS: 1297
    Positive SD number: 1030               Positive DS number: 1024
    Positive SD sum: 4363                  Positive DS sum: 5423
    Positive SD average: 4                 Positive DS average: 5
    Positive SD square-sum: 497725         Positive DS square-sum: 2254957
    Max negative SD: 360                   Max negative DS: 1297
    Negative SD number: 1028               Negative DS number: 1022
    Negative SD sum: 1028                  Negative DS sum: 1022
    Negative SD average: 4                 Negative DS average: 5
    Negative SD square-sum: 495901         Negative DS square-sum: 5419
  One way results:
    Max SD delay: 359                      Max DS delay: 985
    Min SD delay: 0                        Min DS delay: 0
    Sum of SD delay: 1390                  Sum of DS delay: 1079
    Square-Sum of SD delay: 483202         Square-Sum of DS delay: 973651
  Voice scores:
    Max MOS value: 4.38                    Min MOS value: 4.38
    Max ICPIF value: 0                     Min ICPIF value: 0
DLSw operation configuration example
As shown in Figure 15, configure a DLSw operation to test the response time of the DLSw device.
Figure 15 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 15. (Details not shown.)
# Create a DLSw operation.
[DeviceA-nqa-admin-test1] type dlsw
[DeviceA-nqa-admin-test1-dlsw] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-dlsw] history-record enable
[DeviceA-nqa-admin-test1-dlsw] quit
# Start the DLSw operation.
# After the DLSw operation runs for a period of time, stop the operation.
# Display the most recent result of the DLSw operation.
    Min/Max/Average round trip time: 19/19/19
    Square-Sum of round trip time: 361
    Last succeeded probe time: 2011-11-22 10:40:27.7
  Extended results:
# Display the history records of the DLSw operation.
  1          19           Succeeded        2011-11-22 10:40:27.7
The output shows that the response time of the DLSw device is 19 milliseconds.
Path jitter operation configuration example
As shown in Figure 16, configure a path jitter operation to test the round trip time and jitters from Device A to Device B and Device C.
Figure 16 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 16. (Details not shown.)
# Execute the ip ttl-expires enable command on Device B and execute the ip unreachables enable command on Device C.
# Create a path jitter operation.
[DeviceA-nqa-admin-test1] type path-jitter
[DeviceA-nqa-admin-test1-path-jitter] destination ip 10.2.2.2
# Configure the path jitter operation to repeat every 10000 milliseconds.
[DeviceA-nqa-admin-test1-path-jitter] frequency 10000
[DeviceA-nqa-admin-test1-path-jitter] quit
# Start the path jitter operation.
# After the path jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the path jitter operation.
  Hop IP 10.1.1.2
    Basic Results
      Min/Max/Average round trip time: 9/21/14
      Square-Sum of round trip time: 2419
    Extended Results
    Path-Jitter Results
      Jitter number: 9
        Min/Max/Average jitter: 1/10/4
      Positive jitter number: 6
        Min/Max/Average positive jitter: 1/9/4
        Sum/Square-Sum positive jitter: 25/173
      Negative jitter number: 3
        Min/Max/Average negative jitter: 2/10/6
        Sum/Square-Sum positive jitter: 19/153
  Hop IP 10.2.2.2
    Basic Results
      Min/Max/Average round trip time: 15/40/28
      Square-Sum of round trip time: 4493
    Extended Results
    Path-Jitter Results
      Jitter number: 9
NQA collaboration configuration example
As shown in Figure 17, configure a static route to Switch C with Switch B as the next hop on Switch A. Associate the static route, a track entry, and an ICMP echo operation to monitor the state of the static route.
Figure 17 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 17. (Details not shown.)
2.     On Switch A, configure a static route, and associate the static route with track entry 1.
[SwitchA] ip route-static 10.1.1.2 24 10.2.1.1 track 1
3.     On Switch A, configure an ICMP echo operation:
# Create an NQA operation with the administrator name admin and operation tag test1.
# Configure the NQA operation type as ICMP echo.
[SwitchA-nqa-admin-test1] type icmp-echo
# Specify 10.2.1.1 as the destination IP address.
[SwitchA-nqa-admin-test1-icmp-echo] destination ip 10.2.1.1
# Configure the operation to repeat every 100 milliseconds.
[SwitchA-nqa-admin-test1-icmp-echo] frequency 100
# Create reaction entry 1. If the number of consecutive probe failures reaches 5, collaboration is triggered.
[SwitchA-nqa-admin-test1-icmp-echo] reaction 1 checked-element probe-fail threshold-type consecutive 5 action-type trigger-only
[SwitchA-nqa-admin-test1-icmp-echo] quit
# Start the ICMP operation.
4.     On Switch A, create track entry 1, and associate it with reaction entry 1 of the NQA operation.
[SwitchA] track 1 nqa entry admin test1 reaction 1
# Display information about all the track entries on Switch A.
[SwitchA] display track all
Track ID: 1
  State: Positive
  Duration: 0 days 0 hours 0 minutes 0 seconds
  Notification delay: Positive 0, Negative 0 (in seconds)
  Tracked object:
    NQA entry: admin test1
    Reaction: 1
# Display brief information about active routes in the routing table on Switch A.
Destinations : 13        Routes : 13
Destination/Mask    Proto  Pre  Cost         NextHop         Interface
0.0.0.0/32          Direct 0    0            127.0.0.1       InLoop0
10.1.1.0/24         Static 60   0            10.2.1.1        Vlan3
10.2.1.0/24         Direct 0    0            10.2.1.2        Vlan3
10.2.1.0/32         Direct 0    0            10.2.1.2        Vlan3
10.2.1.2/32         Direct 0    0            127.0.0.1       InLoop0
10.2.1.255/32       Direct 0    0            10.2.1.2        Vlan3
224.0.0.0/4         Direct 0    0            0.0.0.0         NULL0
224.0.0.0/24        Direct 0    0            0.0.0.0         NULL0
255.255.255.255/32  Direct 0    0            127.0.0.1       InLoop0
The output shows that the static route with the next hop 10.2.1.1 is active, and the status of the track entry is positive.
# Remove the IP address of VLAN-interface 3 on Switch B.
[SwitchB-Vlan-interface3] undo ip address
Track ID: 1
  State: Negative
  Tracked object:
    Reaction: 1
Destinations : 12        Routes : 12
The output shows that the static route does not exist, and the status of the track entry is negative.
ICMP template configuration example
As shown in Figure 18, configure an ICMP template for a feature to perform the ICMP echo operation from Device A to Device B.
Figure 18 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 18. (Details not shown.)
# Create ICMP template icmp.
[DeviceA] nqa template icmp icmp
[DeviceA-nqatplt-icmp-icmp] destination ip 10.2.2.2
[DeviceA-nqatplt-icmp-icmp] probe timeout 500
# Configure the ICMP echo operation to repeat every 3000 milliseconds.
[DeviceA-nqatplt-icmp-icmp] frequency 3000
# Configure the NQA client to notify the feature of the successful operation event if the number of consecutive successful probes reaches 2.
[DeviceA-nqatplt-icmp-icmp] reaction trigger probe-pass 2
# Configure the NQA client to notify the feature of the operation failure if the number of consecutive failed probes reaches 2.
[DeviceA-nqatplt-icmp-icmp] reaction trigger probe-fail 2
DNS template configuration example
As shown in Figure 19, configure a DNS template for a feature to perform the DNS operation. The operation tests whether Device A can perform the address resolution through the DNS server.
Figure 19 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 19. (Details not shown.)
# Create DNS template dns.
[DeviceA] nqa template dns dns
# Specify the IP address of the DNS server 10.2.2.2 as the destination IP address.
[DeviceA-nqatplt-dns-dns] destination ip 10.2.2.2
[DeviceA-nqatplt-dns-dns] resolve-target host.com
# Set the domain name resolution type to type A.
[DeviceA-nqatplt-dns-dns] resolve-type A
# Specify 3.3.3.3 as the expected IP address.
[DeviceA-nqatplt-dns-dns] expect ip 3.3.3.3
[DeviceA-nqatplt-dns-dns] reaction trigger probe-pass 2
[DeviceA-nqatplt-dns-dns] reaction trigger probe-fail 2
TCP template configuration example
As shown in Figure 20, configure a TCP template for a feature to perform the TCP operation. The operation tests whether Device A can establish a TCP connection to Device B.
Figure 20 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 20. (Details not shown.)
# Configure a listening service to listen to the IP address 10.2.2.2 and TCP port 9000.
# Create TCP template tcp.
[DeviceA] nqa template tcp tcp
[DeviceA-nqatplt-tcp-tcp] destination ip 10.2.2.2
[DeviceA-nqatplt-tcp-tcp] destination port 9000
[DeviceA-nqatplt-tcp-tcp] reaction trigger probe-pass 2
[DeviceA-nqatplt-tcp-tcp] reaction trigger probe-fail 2
TCP half open template configuration example
As shown in Figure 21, configure a TCP half open template for a feature to test whether Device B can provide the TCP service for Device A.
Figure 21 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 21. (Details not shown.)
# Create TCP half open template test.
[DeviceA] nqa template tcphalfopen test
[DeviceA-nqatplt-tcphalfopen-test] destination ip 10.2.2.2
[DeviceA-nqatplt-tcphalfopen-test] reaction trigger probe-pass 2
[DeviceA-nqatplt-tcphalfopen-test] reaction trigger probe-fail 2
UDP template configuration example
As shown in Figure 22, configure a UDP template for a feature to perform the UDP operation. The operation tests whether Device A can receive a response from Device B.
Figure 22 Network diagram
1.     Assign IP addresses to interfaces, as shown in Figure 22. (Details not shown.)
# Configure a listening service to listen to the IP address 10.2.2.2 and UDP port 9000.
# Create UDP template udp.
[DeviceA] nqa template udp udp
[DeviceA-nqatplt-udp-udp] destination ip 10.2.2.2
[DeviceA-nqatplt-udp-udp] destination port 9000
[DeviceA-nqatplt-udp-udp] reaction trigger probe-pass 2
[DeviceA-nqatplt-udp-udp] reaction trigger probe-fail 2
HTTP template configuration example
As shown in Figure 23, configure an HTTP template for a feature to perform the HTTP operation. The operation tests whether the NQA client can get data from the HTTP server.
Figure 23 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 23. (Details not shown.)
# Create the HTTP template http.
[DeviceA] nqa template http http
# Specify http://10.2.2.2/index.htm as the URL of the HTTP server.
[DeviceA-nqatplt-http-http] url http://10.2.2.2/index.htm
# Set the HTTP operation type to get.
[DeviceA-nqatplt-http-http] operation get
[DeviceA-nqatplt-http-http] reaction trigger probe-pass 2
[DeviceA-nqatplt-http-http] reaction trigger probe-fail 2
HTTPS template configuration example
As shown in Figure 24, configure an HTTPS template for a feature to test whether the NQA client can get data from the HTTPS server (Device B).
Figure 24 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 24. (Details not shown.)
# Configure an SSL client policy named abc on Device A, and make sure Device A can use the policy to connect to the HTTPS server. (Details not shown.)
# Create HTTPS template test.
[DeviceA] nqa template https https
# Specify http://10.2.2.2/index.htm as the URL of the HTTPS server.
[DeviceA-nqatplt-https- https] url https://10.2.2.2/index.htm
# Specify SSL client policy abc for the HTTPS template.
[DeviceA-nqatplt-https- https] ssl-client-policy abc
# Set the HTTPS operation type to get (the default HTTPS operation type).
[DeviceA-nqatplt-https- https] operation get
# Set the HTTPS version to 1.0 (the default HTTPS version).
 [DeviceA-nqatplt-https- https] version v1.0
[DeviceA-nqatplt-https- https] reaction trigger probe-pass 2
[DeviceA-nqatplt-https- https] reaction trigger probe-fail 2
FTP template configuration example
As shown in Figure 25, configure an FTP template for a feature to perform the FTP operation. The operation tests whether Device A can upload a file to the FTP server. The login username and password are admin and systemtest, respectively. The file to be transferred to the FTP server is config.txt.
Figure 25 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 25. (Details not shown.)
# Create FTP template ftp.
[DeviceA] nqa template ftp ftp
[DeviceA-nqatplt-ftp-ftp] url ftp://10.2.2.2
[DeviceA-nqatplt-ftp-ftp] source ip 10.1.1.1
[DeviceA-nqatplt-ftp-ftp] operation put
[DeviceA-nqatplt-ftp-ftp] filename config.txt
# Set the username to admin for the FTP server login.
[DeviceA-nqatplt-ftp-ftp] username admin
# Set the password to systemtest for the FTP server login.
[DeviceA-nqatplt-ftp-ftp] password simple systemtest
[DeviceA-nqatplt-ftp-ftp] reaction trigger probe-pass 2
[DeviceA-nqatplt-ftp-ftp] reaction trigger probe-fail 2
RADIUS template configuration example
As shown in Figure 26, configure a RADIUS template for a feature to test whether the RADIUS server (Device B) can provide authentication service for Device A. The username and password are admin and systemtest, respectively. The shared key is 123456 for secure RADIUS authentication.
Figure 26 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 26. (Details not shown.)
# Configure the RADIUS server. (Details not shown.)
# Create RADIUS template radius.
[DeviceA] nqa template radius radius
# Specify 10.2.2.2 as the destination IP address of the operation.
[DeviceA-nqatplt-radius-radius] destination ip 10.2.2.2
# Set the username to admin.
[DeviceA-nqatplt-radius-radius] username admin
# Set the password to systemtest.
[DeviceA-nqatplt-radius-radius] password simple systemtest
# Set the shared key to 123456 in plain text for secure RADIUS authentication.
[DeviceA-nqatplt-radius-radius] key simple 123456
[DeviceA-nqatplt-radius-radius] reaction trigger probe-pass 2
[DeviceA-nqatplt-radius-radius] reaction trigger probe-fail 2
SSL template configuration example
As shown in Figure 27, configure an SSL template for a feature to test whether Device A can establish an SSL connection to the SSL server on Device B.
Figure 27 Network diagram
# Assign IP addresses to interfaces, as shown in Figure 27. (Details not shown.)
# Configure an SSL client policy named abc on Device A, and make sure Device A can use the policy to connect to the SSL server on Device B. (Details not shown.)
# Create SSL template ssl.
[DeviceA] nqa template ssl ssl
# Set the destination IP address and port number to 10.2.2.2 and 9000, respectively.
[DeviceA-nqatplt-ssl-ssl] destination ip 10.2.2.2
[DeviceA-nqatplt-ssl-ssl] destination port 9000
# Specify SSL client policy abc for the SSL template.
[DeviceA-nqatplt-ssl-ssl] ssl-client-policy abc
[DeviceA-nqatplt-ssl-ssl] reaction trigger probe-pass 2