1 Product models and system features

Product models

The H3C S6850-56HF-CP cold-plate liquid-cooled Ethernet switch is a high-density, intelligent 25G access switch developed by H3C for cloud data centers and cloud computing networks. It offers 25GE and 100GE port configurations and boasts powerful hardware forwarding capabilities along with abundant data center features. The H3C S6850 series include the following models:

 

Product series

Product model

Product code

H3C S6850 series

S6850-56HF-CP

LS-6850-56HF-CP

 

 

NOTE:

·     For product selection information, see the switch data sheet: https://www.h3c.com/cn/Products_And_Solution/InterConnect/Products/Switches/. To view the switch product lifecycle management announcement, access https://www.h3c.com/cn/Service/Policy_Trends/Product_Periods/Termination_Notice/Switches_Series/

·     To view the product and software compatibility, see the release notes.

 

System features

Table1-1 Product specifications

Item

LS-6850-56HF-CP

Physical specifications

Dimensions (H × W × D)

44 × 440 × 400 mm (1.73 × 17.32 × 15.75 in)

Dimensions (including packaging) (H × W × D)

180 × 638 × 576 mm (7.09 × 25.12 × 22.68 in)

Weight (fully equipped with power modules and fan trays)

≤ 9 kg (19.84 lb)

Processor

Quad-core, 2.2 GHz

Technical specifications

DRAM Memory

4 GB

NOR Flash

2 × 32 MB (32 MB primary and 32 MB backup)

NAND Flash

EMMC 4G

Interface type and quantity

Console ports

Serial console port: 1

Management Ethernet ports

Management Ethernet copper port: 1

USB ports

USB 2.0 port: 1

SFP28 ports

48

QSFP28 ports

8

IRF physical ports

QSFP28 port can act as an IRF physical port

Fan tray and power module slots

Fan tray slots

4

Power module slots

2

Power supply specifications

Power input type

AC input

Overall power consumption

Typical power consumption

Collection standard: Fully-equipped with cables, 50% load

·     Single AC input: 143 W

·     Dual AC inputs: 150 W

Maximum power consumption

Collection standard: Full-equipped with transceiver modules, 100% load

·     Single AC input: 424 W

·     Dual AC inputs: 429 W

Overall thermal consumption

Thermal consumption (typical)

Single AC input/Dual AC inputs: 498 BTU/hr

Thermal consumption (max)

1464 BTU/hr

Heat dissipation

Heat dissipation method

Cold plate-based liquid-cooling and air cooling

Air cooling  ventilation aisles

Front-to-back or back-to-front airflow (based on the installed fans)

Reliability and availability

Power redundancy

1+1 redundancy

Fan tray redundancy

Four fan trays fully equipped

Hot swapping

Supported

Mean Time Between Failures (MTBF) (years)

78.7

Mean Time To Repair (MTTR) (hours)

1

Availability

99.999927%

Environment specifications

Sound pressure level at 27°C (80.6°F)

65.5 dB(A)

Altitude

–60 to +5000 m (–196.85 to 16404.20 ft)

Operating temperature

0ºC to 40ºC (32ºF to 113ºF)

NOTE:

The allowed maximum temperature decreases by 0.33 °C (32.59°F) as the altitude increases by 100 m (328.08 ft) from 0 m (0 ft).

Storage temperature

–40ºC to +70ºC (–40°F to +158°F)

Relative humidity (non-condensing)

5% to 90%

Certification

Certification

·     Compliant safety standards

·     Compliant EMC standards

·     Compliant environmental and eco-friendly standards

Cooling connector parameters

Quick connector type for liquid inlet and outlet

·     UQD02-T04BSSJEE

·     UQD02-T04RSSJEE

Water inlet temperature

≤ 45ºC (113°F)

Water system pressure drop (Bar)

≤ 40 kPa

Water system flow rate (L/min)

≤ 1.5 L/min

 


2 Chassis views

Figure2-1 LS-6850-56HF-CP front panel

(1) System status LED (SYS)

(2) Power supply status LED (PSU)

(3) Fan tray status LED (FAN)

(4) SFP28 Ethernet fiber port

(5) SFP28 port status LED

(6) QSFP28 Ethernet fiber port

(7) QSFP28 port status LED

 

Figure2-2 LS-6850-56HF-CP left panel

(1) Power module latch

(2) Mounting bracket installation position at the power module side

(3) Switch grounding point 1

(4) Switch grounding point 2

(5) Mounting bracket installation position at the port side

(6) Power module handle

(7) Liquid cooling quick-connect male connector

 

Figure2-3 LS-6850-56HF-CP rear panel

(1) Power module 1

(2) Fan tray 1

(3) Fan tray 2

(4) Fan tray 3

(5) Fan tray 4

(6) Water leak LED

(7) Quick-connect male connector for liquid cooling outlet

(8) Quick-connect male connector for liquid cooling inlet

(9) Management Ethernet copper port LED (LINK/ACT)

(10) Management Ethernet copper port

(11) USB port

(12) System status LED (SYS)

(13) Power module 2

(14) RESET button

(15) Serial console port

 

 

NOTE:

·     The rear panel of the LS-6850-56HF-CP has two power module slots. By default, no power modules are installed. Slot PWR1 is empty, and slot PWR2 comes with a filler panel. You can install one or two power modules for the switch as needed. In the figure, two SW-A-PSR550-12A-B AC power modules are installed.

·     The rear panel of the LS-6850-56HF-CP has four fan tray slots. By default, all the four slots are empty. You must install four fan trays of the same model. In this figure, the switch is fully equipped with FAN-40B-1-C fan trays.

·     The LS-6850-56HF-CP supports delivery with fan trays and power modules. If you need the purchased modules installed on the device before shipping, contact H3C marketing personnel in advance to make a note on the order.

·     The LS-6850-56HF-CP provides a RESET button on the back panel for you to immediately reboot the device.

 

3 FRUs and compatibility matrixes

The S6850-56HF-CP cold plate liquid-cooled Ethernet switch features a modular design. See Table3-1 for details.

Table3-1 FRUs and compatibility matrix for the S6850-56HF-CP

Removable component model

Component code

LS-6850-56HF-CP

SW-A-PSR550-12A-B

0231AKX6

Yes

FAN-40B-1-C

9803A00F

Yes

FAN-40F-1-D

0231AKLC

Yes

 

 

NOTE:

·     One power supply can meet the power requirement of the switch. You can install two power supplies on the switch for 1+1 redundancy.

·     To ensure device heat dissipation, fully install fan trays of the same model.

 

4 Removable power modules

The S6850-56HF-CP cold plate liquid-cooled Ethernet switch features a modular design.

 

WARNING

WARNING!

The S6850-56HF-CP supports the replacement of redundant backup power modules without powering off the device. To avoid device damage or even bodily injury, before removing or installing a power module, make sure the power module has no power input.

 

Appearance

Figure4-1 SW-A-PSR550-12A-B power module

 

Figure4-2 Front panel of the SW-A-PSR550-12A-B power module

电源6-前面板标号

 

(1) Power module status LED

(2) Power module latch

(3) Power input receptacle

(4) Handle

 

For more information about LED description, see "Power module status LED."

Functions

The SW-A-PSR550-12A-B is an AC input or high-voltage DC input and DC output power module. It provides a maximum output of 550 W. The main features are as shown in Table4-1.

Table4-1 SW-A-PSR550-12A-B power supply features

Feature

Description

Protection function

The power supply provides protection against input overcurrent, input undervoltage, output overvoltage, output shortcircuit, and overtemperature conditions.

Support for redundancy

Multiple power supplies can be connected in parallel to achieve N+1 or N+N redundancy and load balancing.

Support for hot swapping

You can remove one of the power supplies in redundancy when the switch is operating.

 

Technical specifications

Table4-2 SW-A-PSR550-12A-B specifications

Item

Specifications

Dimensions (H × W × D, including the handle)

73.5 × 185 × 40 mm (2.89 × 7.28 × 1.57 in)

Weight

0.75 kg (1.65 lb)

Rated input voltage range

100 to 240 VAC @ 50/60Hz

Max input voltage range

90 to 264 VAC

High voltage DC rated input voltage range

240 VDC

High voltage DC maximum input voltage range

190 to 310 VDC

Rated input current

7.0A Max @ 100 to 240 VAC

3.5A Max @ 240 VDC

Rated output current

45A

Rated output voltage

12V

Rated output power

550W

Fuse rated current

10A

 

5 Removable fan trays

CAUTION

CAUTION:

The S6850-56HF-CP has multiple fan tray slots. To ensure proper heat dissipation, follow these restrictions and guideline:

·     Fully install fan trays of the same model. If a fan tray slot is empty or the installed fan trays are of different models, the device will display a prompt and prevent power-up.

·     During device operation, make sure all module slots are filled. You must install the corresponding module or filler panel in each module slot.

·     During the device operation, if multiple fan trays fail, do not remove several fan trays at the same time when replacing them. Replace the faulty fan trays one by one, and make sure the replacement time for a single fan tray does not exceed 3 minutes.

 

The S6850-56HF-CP supports the following fan trays: FAN-40B-1-C and FAN-40F-1-D.

Appearance

 

For more information about LED description, see Table7-6.

Functions

The FAN-40B-1-C fan tray provides port-to-power module airflow and the FAN-40F-1-D fan tray provides power supply-to-port airflow. The fan tray is characterized by its compact size, rapid heat dissipation, and hot-swappable feature. It can also automatically adjust the fan speed according to the device temperature, providing strong cooling capabilities for the device.

Technical specifications

Item

Fan-40B-1-C specifications

FAN-40F-1-D specifications

Dimensions (H × W × D, including the handle)

40 × 40 × 136 mm (1.57 × 1.57 × 5.35 in)

Weight

0.12 kg (0.26 lb)

Airflow direction

Air outlet from the fan tray panel

Air inlet from the fan tray panel

Max fan speed

29000 RPM

Maximum air flow rate

38 CFM

Input voltage

12V

Maximum power consumption

60W

50.4W

 

6 Ports

 

NOTE:

·     As a best practice, use H3C transceiver modules and cables on this series of switches.

·     The H3C transceiver modules and cables are subject to change over time. For the most recent list of H3C transceiver modules and cables, contact your H3C Support or marketing staff.

·     For the specifications of H3C transceiver modules and cables, see H3C Transceiver Modules User Guide.

 

Console port

The S6850-56HF-CP provides a console port. See Table6-1 for details.

Table6-1 Console port specifications

Item

Description

Connector type

RJ-45

Compliant standard

EIA/TIA-232

Operating mode

Duplex Universal Asynchronous Receiver/Transmitter (UART)

Transmission baud rate

9600 bps (default) to 115200 bps

Support services

·     Provides connection to an ASCII terminal.

·     Provides connection to the serial port of a local terminal (for example, a PC) running a terminal emulation program

 

Management Ethernet port

The S6850-56HF-CP provides a management Ethernet copper port. You can connect the port to a local PC for software loading and debugging or to a remote management station for remote management.

Table6-2 Management Ethernet port specifications

Item

Description

Connector type

RJ-45/LC

Number of connectors

One 10/100/1000BASE-T management port

Compliant standard

Management 10/100/1000BASE-T ports: IEEE802.3ab

Port transmission rate

Management 10/100/1000BASE-T ports:

·     10M full duplex/half duplex

·     100M full duplex/half duplex

·     1000M full duplex

·     MDI/MDI-X, auto-sensing

Interface cable media and maximum transmission distance

Management 10/100/1000BASE-T interface: Copper ports with Category 5 unshielded twisted pair (UTP), supporting a transmission distance of 100 meters.

Functions and services

For device software update and network management

 

USB port

The S6850-56HF-CP provides a USB 2.0 port that complies with the OHCI standard and supports a 480Mbps uploading and downloading rate. Through this interface, users can interact with the Flash file system on the switch, for example, uploading or downloading application files or configuration files.

 

IMPORTANT

IMPORTANT:

·     Due to compatibility and driver differences among USB devices of different manufacturers, H3C does not guarantee that USB devices from all manufacturers will function normally on this series of switches. If a USB device is not functioning properly, it is not due to a switch fault. Try using a USB device from a different manufacturer.

·     The USB port on the switch is designed to output current strictly in accordance with the USB 2.0 standard. Use USB storage devices that fully comply with USB 2.0 standards. If the USB storage device you use does not fully comply with the USB 2.0 standard, the USB port of this switch might fail to recognize the USB device.

 

QSFP28 ports

Table6-3 QSFP28 port description

Item

Description

Port name

40GE/100GE QSFP28 fiber port

Product support status

The front panel provides eight QSFP28 ports

Connector type

LC/MPO

Description

The 40GE/100GE QSFP28 Ethernet fiber ports are mainly used for transmitting and receiving 40GE/100GE fiber port services.

Compliant standard

IEEE802.3ba

Fiber port properties

Depends on the transceiver modules or cables installed

Operating mode

Full Duplex

Available transceiver modules and cables

·     100G QSFP28 module

·     100G QSFP28 cable

·     100G QSFP28 optical fiber (AOC)

·     100G QSFP28 to 4*25G SFP28 cable

·     40G QSFP+ module

·     40G QSFP+ cable

·     40G QSFP+ optical fiber (AOC)

·     40G QSFP+ to 4*10G SFP+ cable

·     You can install a QSFP+ to SFP+ adapter to support 10G SFP+ modules. Before using this adapter, manually execute the using tengige command on the port where the adapter is to be installed to split the interface.

NOTE:

·     For more information about the transceiver modules and cables supported by a QSFP28 port, see H3C S6850 & S9850 Switch Series Transceiver Module Compatibility Matrixes.

·     The QSFP-40G-SR4-MM850 and QSFP-40G-CSR4-MM850 modules both support the 1-to-4 port split function, enabling interconnection between one 100G QSFP28 port and four 10G SFP+ ports. The connected QSFP+ and SFP+ modules must have matching specifications, including center wavelength and fiber optic type.

Split support status

Support splitting into four 25G ports or four 10G ports.

Other restrictions and guidelines

When using a 100G DAC cable to connect a 100G port on the device to certain Intel network cards, for example, Intel (rainbow) Eth E810-CQDA2, the port might fail to come up. As a best practice, use an AOC optical fiber or an transceiver module for connections with Intel network cards.

 

SFP28 ports

Table6-4 SFP28 port description

Item

Description

Port name

25GE SFP28 Ethernet fiber port

Product support status

The front panel provides 48 SFP28 ports.

Connector type

LC

Description

The 25GE SFP28 Ethernet fiber ports support autosensing to 10GE/1GE and is primarily used for transmitting and receiving signals for 25GE/10GE/1GE Ethernet optical services.

Compliant standard

IEEE802.3by

Fiber port properties

Depends on the transceiver modules or cables installed

Operating mode

·     When using an SFP28 cable or SFP+ cable to connect an SFP28 port to the peer end, if the peer end does not support rate and duplex auto-negotiation, execute the speed and duplex full commands on both ends. For the port to come up, make sure the rate configured by the speed command must match the rate of the transceiver module.

·     When you use an SFP module other than SFP-GE-T and SFP-GE-T-D on a SFP28 port to establish a connection, disable autonegotiation on the remote end.

·     For more information about configuration restrictions and guidance for SFP28 ports, see Layer 2 — LAN Switching Configuration Guide.

Available transceiver modules and cables

Supports 25G SFP28 modules/cables, 10G SFP+ modules/cables, and 1G SFP modules

NOTE:

·     For more information about the transceiver modules and cables supported by a SFP28 port, see H3C S6850 & S9850 Switch Series Transceiver Module Compatibility Matrixes.

·     Use BIDI optical modules in pairs. For example, if one end uses SFP-XG-LX-SM1270-BIDI, use FP-XG-LX-SM1330-BIDI at the other end.

·     The maximum transmission distance of the SFP-25G-SR-MM850 module varies by the enabling status of the FEC negotiation feature. For more information, see Table6-5. For more information about FEC negotiation, see Layer 2—LAN Switching Configuration Guide.

Other restrictions and guidelines

You can use a maximum of four long-distance SFP+ transceiver modules of the following models on a device:

·     SFP-XG-LH40-SM1550

·     SFP-XG-LH40-SM1550-D

·     SFP-XG-LH80-SM1550

·     SFP-XG-LH80-SM1550-D

Only the 1G rate is supported on a port installed with the SFP-GE-T or SFP-GE-T-D module.

When a device uses the SFP-GE-T/SFP-GE-T-D module to connect to the peer end, the peer port might come online before the local port comes online, resulting in packet loss. As a best practice to avoid the issue mentioned above, use dynamic aggregation if you are to aggregate the links between the device and a remote device.

 

Table6-5 Maximum transmission distance of the SFP-25G-SR-MM850

Transceiver module/cable name

Central wavelength (nm)

Connector

Cable specifications

Mode bandwidth (MHz*km)

Max transmission distance

SFP-25G-SR-MM850

850

LC

50/125µm multimode fiber

2000

FEC negotiation disabled: 30 m (98.43 ft)

FEC negotiation disabled: 70 m (229.66 ft)

4700

FEC negotiation disabled: 40 m (131.23 ft)

FEC negotiation disabled: 100 m (328.08 ft)

 

7 LEDs

System status LED

Through the system status LED, you can preliminarily determine the working state of the switch. For more information, see Table7-1.

Table7-1 Description of the system status LED

LED

Status

Description

SYS

Steady green

The switch has been normally started

Flashing green

The switch is performing power-on self test (POST).

Steady red

The switch has failed POST or the switch is faulty.

Flashing red

Some ports failed the power-on self-test (POST) and their functionality fails.

NOTE:

When the Bootware boot mode is set to Fast Mode, the system does not perform POST.

Flashing blue (3 Hz)

UID LED

NOTE:

The LED is on to help device location after you execute the locator blink blink-time command on the device.

Off

The switch is powered off or has not started up correctly

 

QSFP28 port status LED

Table7-2 Description of the QSFP28 port status LED

Status

Description

Steady green

A module has been installed. The port operates in 100G mode, and the port link is up.

Flashing green

The port is sending or receiving data at 100G.

Steady yellow

A module has been installed. The port operates in 10G, 25G, or 10G mode, and the port link is up.

Flashing yellow (3 Hz)

The port operates in 10G, 25G, or 40G mode and is receiving or transmitting data.

Off

No module has been installed or no link is present on the port.

 

SFP28 port status LED

Table7-3 Description of the SFP28 port status LED

Status

Description

Steady green

A module has been installed. The port operates with the highest rate, and the port link is up.

Flashing green

The port operates with the highest rate, and is receiving or sending data.

Steady yellow

A module has been installed. The port operates with the highest rate, and the port link is up.

Flashing yellow (3 Hz)

The port operates with the highest rate, and is receiving or sending data.

Off

No module has been installed or no link is present on the port.

 

Management Ethernet port status LED

The S6850-56HF-CP provides one LINK/ACT status LED for the management Ethernet copper port. Through the status LED, you can preliminarily determine the working state of the management Ethernet port. For more information, see Table7-4.

Table7-4 Description of the management Ethernet port status LED

LED

Status

Description

LINK/ACT

Steady green

The management Ethernet port operates at 10/100/1000 Mbps and the port link is up.

Steady green, flashing yellow

The port is in sending or receiving data.

Off

The management Ethernet port does not have a connection.

 

Power module status LED

The SW-A-PSR550-12A-B provides a power LED at the panel to show the input and output state of the power module. For more information about the status of the LED, see Table7-5.

Table7-5 Description of the power module status LED

Status

Description

Steady green

The power supply system is operating correctly.

Flashing green (1 Hz)

The power input is normal, and the system is not powered on and is in standby state.

Flashing green (0.33Hz)

The power module is in standby mode and not outputting power.

Flashing green (2Hz)

The power module is in firmware update state.

Steady amber

·     The power module has experienced a critical fault.

·     The power module has no input, but the other power module has normal input.

Flashing amber (1 Hz)

The power module has triggered an alarm.

Off

The power module has no input. Possible reasons include:

·     The power cord connection fails.

·     The external power supply system has lost power.

 

Fan tray alarm LED

Each fan tray has an alarm LED on the panel. For the meaning of the alarm LED on the FAN-40B-1-C/FAN-40F-1-D fan tray, see Table7-6.

Table7-6 Description of the fan tray alarm LED

Status

Description

Steady green

The fan tray is running normally.

Steady red

The fan tray is abnormal.

Off

The fan tray is not properly inserted or powered.

 

Power status LED

The LS-6850-56HF-CP provides a power status LED on the panel. You can view the LED to identify the operating status of the power modules in the chassis. For more information, see Table7-7.

Table7-7 Description of the power status LED

LED

Status

Description

PSU

Steady green

The power modules are running normally.

Steady yellow

The number of faulty power modules or absent power modules is 1.

Off

The number of faulty power modules or absent power modules is 2.

 

Fan tray status LED

The LS-6850-56HF-CP provides a fan tray status LED on the panel. You can view the LED to identify the operating status of the fan trays in the chassis. For more information, see Table7-8.

Table7-8 Description of the fan tray status LED

LED

LED status

Description

FAN

Steady green

The fan tray is running normally.

Steady yellow

The number of faulty fan trays or absent fan trays is 1.

Steady red

The number of faulty fan trays or absent fan trays is equal to or larger than 2.

 

Water leak LED

The LS-6850-56HF-CP provides one water leak LED on the panel. You can view the LED to identify the water leak status. For more information, see Table7-8.

Table7-9 Water leak LED status and description

LED

LED status

Description

LEAK

Steady green

The liquid cooling system is running normally.

Steady red

A leak alarm has been triggered, or an alarm indicating a break in leak detection is present.

 


8 Cooling system

The S6850-56HF-CP cold plate liquid-cooled Ethernet switch employs both a cold plate and fan trays to remove all heat from the switch and thus significantly reduce the number of required air conditioners.

·     The liquid cooling system uses a cold plate to directly exchange heat with the casings of high-power consumption components such as chips. It utilizes a CDU to provide circulation power, allowing the flowing water to carry the heat out of the equipment room.

·     The liquid cooling system provides circulation power through the switch's own cooling fans, and with powerful cooling fans, it removes the heat from low-power consumption components within the switch from the equipment room.

For more information about the cold plate-based liquid-cooled system of the S6850-56HF-CP Ethernet switch, see H3C Cold Plate-Based Liquid-Cooled System User Guide.

Table8-1 Fan tray cooling system

Device model

Optional fan tray

Airflow direction

S6850-56HF-CP

FAN-40F-1-D

From the power module side to the port side

FAN-40B-1-C

From the port side to the power module side

 

  • Cloud & AI
  • InterConnect
  • Intelligent Computing
  • Intelligent Storage
  • Security
  • SMB Products
  • Intelligent Terminal Products
  • Product Support Services
  • Technical Service Solutions
All Services
  • Resource Center
  • Policy
  • Online Help
  • Technical Blogs
All Support
  • Become A Partner
  • Partner Policy & Program
  • Global Learning
  • Partner Sales Resources
  • Partner Business Management
  • Service Business
All Partners
  • Profile
  • News & Events
  • Online Exhibition Center
  • Contact Us
All About Us
新华三官网