H3C HDM System Log Messages Reference-6W105
HomeSupportDiagnose & MaintainAlarms ReferencesH3C HDM System Log Messages Reference-6W105
Table of Contents
Related Documents
book(CHM&PDF&Excel)
book(CHM&PDF&Excel) 1.05 MB
H3C HDM
Introduction· 1
Obtaining system log messages· 1
System log severity level 1
Using this document 1
Applicable products· 2
Event log messages· 3
Temperature· 4
Dropped below the lower minor threshold· 4
Dropped below the lower major threshold· 4
Dropped below the lower critical threshold· 5
Exceeded the upper minor threshold· 5
Exceeded the upper major threshold· 6
Exceeded the upper critical threshold· 6
Abnormal Temperature· 7
Voltage· 7
State Asserted· 7
Dropped below the lower major threshold· 8
Exceeded the upper major threshold· 8
Current 9
State Asserted· 9
Exceeded the upper minor threshold· 9
Exceeded the upper major threshold· 10
Exceeded the upper critical threshold· 10
Fan· 11
Transition to Running· 11
Fully Redundant 11
Non-redundant:Sufficient Resources from Redundant 12
Transition to Off Line· 12
Non-redundant:Insufficient Resources· 13
Transition to Degraded· 13
Install Error 14
Cooling device· 14
Liquid Cooler is not present 14
Liquid Cooler is leakage· 15
Physical security· 16
General Chassis Intrusion· 16
LAN Leash Lost 16
Processor 17
IERR· 17
State Asserted· 18
CPU Critical Temperature· 18
Thermal Trip· 19
FRB1/BIST failure· 19
Processor Presence detected· 20
Processor Automatically Throttled· 20
Machine Check Exception· 21
triggered an uncorrectable error 21
Machine Check Error 22
Machine Check Error---CPU core errors· 22
triggered a correctable error 23
Correctable Machine Check Error 23
Correctable Machine Check Error---CPU UPI errors· 24
Correctable Machine Check Error---IOH UPI errors· 24
Correctable Machine Check Error---IOH core errors· 25
Correctable Machine Check Error---VT-d errors· 25
Correctable Machine Check Error---CPU core errors· 26
Correctable Machine Check Error---Cbo error 26
Configuration Error---System is operating in KTI Link Slow Speed Mode· 27
Power supply· 27
Fully Redundant 27
Fully Redundant 28
Presence detected· 28
Redundancy Lost 29
Power Supply Failure detected· 29
Power Supply Predictive Failure---PSU Self Check Failed· 30
Power Supply Predictive Failure· 30
Power Supply input lost (AC/DC) 31
Power Supply input lost or out-of-range· 31
Power Supply input out-of-range - but present 32
Configuration error ---Vendor mismatch· 32
Configuration error---Power supply rating mismatch· 33
Exceeded the upper minor threshold· 33
Power Supply Inactive/standby state· 34
Interlock Power Down· 34
Power Supply Pwok abnormal 35
Power limit is exceeded over correction time limit 35
Power limit is exceeded over correction time limit 36
Memory· 36
Correctable ECC or other correctable memory error 36
CPU triggered a correctable error 37
Uncorrectable ECC or other uncorrectable memory error 37
triggered an uncorrectable error 38
Parity· 38
Parity---Memory Training Faulty Part Tracking Uncorrectable Error 39
Parity---Memory Receive Enable Training Error 39
Parity---Memory Write Leveling Training Error 40
Parity---Memory Write DqDqs Training Error 40
Parity---Memory Sense Amp Training Error 41
Parity---Warning Command Clock Training Error 41
Parity---An uncorrectable error occurs during the memory test phase· 42
Parity---Memory Training Error 42
Parity---The number of correctable memory errors reached the error logging threshold· 43
Parity---An error occurred on the DIMM slot 43
Parity---CMD eye width is too small 44
Parity---The command is not in the FNv table· 44
Parity---CTL is not consistent with clock in timing, and the channel is isolated· 45
Parity---Memory write flyby failed· 45
Parity---Timing error occurred during signal line adjustment for memory write leveling training· 46
Parity---Memory read DqDqs training failed· 46
Parity---Memory receive enable training failed· 47
Parity---Memory write leveling training failed· 47
Parity---Memory write DqDqs training failed· 48
Parity---An error occurs during memory test, and the rank is disabled· 48
Parity---Failed to find the RxVref for data eye training· 49
Parity---LRDIMM RCVEN training failed· 49
Parity---RCVEN CYCLE training failed· 50
Parity---Read delay training failed· 50
Parity---Memory write leveling training failed· 51
Parity---Coarse write leveling training failed· 51
Parity---Write delay training failed· 52
Parity---QxCA_CLK_NO_EYE training failed· 52
Parity---mapped out because failed critical mask test at cold boot 53
Parity---Invalid SPD contents· 53
Memory Device Disabled· 54
Memory Device Disabled---the DIMM is disabled· 54
Memory Device Disabled---the rank is disabled· 55
Memory Device Disabled---Pmem Media disabled· 55
Correctable ECC or other memory error limit reached· 56
Presence detected· 57
Configuration error---RDIMMs are installed on the server that supports only UDIMMs· 57
Configuration error---UDIMMs are installed on the server that supports only RDIMMs· 58
Configuration error---SODIMMs are installed on the server that supports only RDIMMs· 58
Configuration error---The number of ranks per channel can be only 1, 2, or 4· 59
Configuration error---Columns, rows, or banks of the DIMM cannot meet the JEDEC standards, and LRDIMMs are not supported· 59
Configuration error---The number of ranks in the channel exceeds 8· 60
Configuration error---Support for ECC on the DIMMs is not consistent with support for ECC on the server 60
Configuration error---The voltage for a DDR4 DIMM must be 12V, and the voltage for a DDR5 DIMM must be 11V  61
Configuration error---The CPU is not compatible with 3DS DIMMs· 61
Configuration error---NVDIMMs with stepping lower than 0x10 are not supported· 62
Configuration error---The CPU is not compatible with 16-GB single-rank DIMMs· 62
Configuration error---The CPU is not compatible with the DIMMs· 63
Configuration error---The frequency of the DIMM is not supported on the server 63
Configuration error---NVDIMMs are not compatible with the CPU· 64
Configuration error---DCPMMs are not supported· 64
Configuration error---Memory LockStep Disable Error 65
Configuration error---Memory Mirror Disable Error 65
Configuration error---Failed to enable the full mirror mode· 66
Configuration error---The memory interleaving configuration cannot meet the requirements of the server 66
Configuration error---The memory interleaving configuration cannot meet the requirements of the server 67
Configuration error---Failed to enable the rank sparing mode The memory RAS mode has degraded to independent 67
Configuration error---Memory Rank Sparing Error 68
Configuration error---Failed to enable patrol scrubbing· 68
Configuration error---The number of ranks in the black slot is greater than that in the white slot, or the DIMM is installed in the black slot with the white slot empty· 69
Configuration error---DIMM population error Two DDR-T memory modules cannot be installed in a channel 69
Configuration error---The DDR-T memory module is installed in the white slot 70
Configuration error---2LM IMC memory Mismatch· 70
Configuration error---ODT configuration errorThe channel is isolated· 71
Configuration error---Failed to enable ADDDC· 71
Configuration error---Failed to enable SDDC· 72
Configuration error---DCPMM firmware version not supported· 72
Configuration error---DCPMM firmware version not supported· 73
Configuration error---NVMCTRL_MEDIA_NOTREADY· 73
Configuration error---The DDR-T memory modules of the unexpected model are installed· 74
Configuration error---Failed to set the VDD voltage of the DIMM·· 74
Configuration error---Too many RIR rules· 75
Configuration error---The DIMMs for the CPU exceeded the limit 75
Drive slot 76
Drive Presence· 76
Drive Fault 77
Predictive Failure· 78
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold  79
Consistency Check / Parity Check in progress. System Source Monitor: Relieve resource alarm about Hard Disk Usage  80
In Critical Array· 81
In Failed Array· 82
Rebuild/Remap in progress· 82
The disk triggered a media error 83
The disk triggered an uncorrectable error 83
The disk is missing· 84
System firmware Progress· 84
System Firmware Error (POST Error)---CPU matching failure· 84
System Firmware Error (POST Error)---Firmware (BIOS) ROM corruption detected· 85
System Firmware Error (POST Error)---Load microcode failed· 85
System Firmware Error (POST Error)---No system memory or invalid memory configuration· 86
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image is unsigned or Certificate is invalid· 86
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate not found in Authorized database(db) 87
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate is found in Forbidden database(dbx) 87
System Firmware Error (POST Error)---Memory Population Rule Error 88
System firmware error (POST error)---DIMM installation or compatibility error occurred· 88
System firmware error (POST error)---No Memory Usable· 89
System firmware error (POST error)---No DDR Memory Error 89
System firmware error (POST error)---DIMM Compatible Error(LRDIMM and RDIMM are installed) 90
System Firmware Error (POST Error)---No DIMMs present 90
System Firmware Error (POST Error)---No DDR memory in the system·· 91
System Firmware Error (POST Error)---No DIMM is available for memory-mapping operation· 91
System Firmware Error (POST Error)---Different DIMM types detected· 92
System Firmware Error (POST Error)---DIMM population error 92
System Firmware Error (POST Error)---A maximum of two quad-rank DIMMs can be populated per channel 93
System Firmware Error (POST Error)---The third DIMM slot with green release tabs does not support UDIMMs or SODIMMs· 93
System Firmware Error (POST Error)---DIMM voltage error 94
System Firmware Error (POST Error)---DDR3 and DDR4 DIMMs cannot be mixed· 94
System Firmware Error (POST Error)---256-byte and 512-byte SPD devices cannot be mixed· 95
System Firmware Error (POST Error)---3DS and non-3DS LRDIMMs cannot be mixed· 95
System Firmware Error (POST Error)---DDR-T memory modules and UDIMMs cannot be mixed· 96
System Firmware Error (POST Error)---Memory Unrecognized Initialization Error 96
System Firmware Hang---Unspecified· 97
System firmware hang-----No DDR Memory Error 97
System firmware hang---DIMM Compatible Error(LRDIMM and RDIMM are installed) 98
System firmware hang---Memory Unrecognized Initialization Error 98
System Firmware Progress---Current Memory Ras Mode· 99
System Firmware Error (POST Error)--- Memory population enforcement mismatch, Please check the DIMM symmetry on the socket 99
System Firmware Error (POST Error)---No DIMMs installed for CPU· 100
Event Logging Disabled· 100
Log Area Reset/Cleared· 100
SEL Full 101
SEL Almost Full 101
Watchdog1· 102
BIOS Watchdog Reset 102
OS Watchdog NMI/Diagnostic Interrupt 102
OS Watchdog pre-timeout Interrupt-non-NMI 103
System Event 103
Timestamp Clock Synch---event is $1 of pair---SEL Timestamp Clock updated· 103
Timestamp clock synch---BMC Time SYNC succeed· 104
Critical Interrupt 104
Transition to Non-Critical from OK· 104
PCI: PCIE Hot Plug PCIe Pull Out 105
PCI: PCIE Hot Plug PCIe Insert 105
PCI SERR· 106
Bus Uncorrectable Error 107
Bus Fatal Error 108
Button/Switch· 109
Power Button pressed---Physical button---Button pressed· 109
Power Button pressed---Physical button---Button released· 109
Power Button pressed---Virtual button---Power cycle command· 109
Power Button pressed---Virtual button---Power off command· 110
Power Button pressed---Virtual button---Power on command· 110
Power Button pressed---Virtual button---Soft off command· 110
Reset Button pressed---Virtual button---Reset command· 111
FRU service request button---Physical button---Uid button pressed· 111
Module/Board· 112
Transition to Critical from less severe· 112
Transition to Non-Recoverable from less severe· 112
Monitor---Board found PSU output can't be enabled· 113
Add-in Card· 113
Transition to OK· 113
Transition to Critical from less severe· 114
Chassis· 114
Transition to OK· 114
State asserted· 115
Transition to Critical from less severe· 115
Transition to Non-recoverable from less severe· 115
System Boot/Restart Initiated· 116
Initiated by power up· 116
Initiated by hard reset 116
Initiated by warm reset 117
System restart---due to fan error:power off 117
System Restart 118
System Restart---due to fan error:power reset 118
System Restart---due to fan error:power cycle· 119
Boot Error 119
No bootable media· 119
OS_BOOT· 120
C: boot completed· 120
PXE boot completed· 120
OS Stop/Shutdown· 121
Run-time Critical Stop· 121
OS Graceful Stop· 121
OS Graceful Shutdown· 122
Slot/Connector 122
Device disabled: PCIe module information not obtained· 122
triggered an uncorrectable error 123
triggered a correctable error 124
Slot/Connector Device installed/attached· 124
Transition to on line· 125
Transition to off line· 125
Transition to Non-Critical from OK· 125
System ACPI Power State· 126
S0/G0 "working" 126
S5/G2 "soft-off" 126
LPC Reset occurred· 127
Watchdog2· 128
Watchdog overflowAction:Timer expired· 128
Watchdog overflowAction:Hard Reset 129
Watchdog overflowAction:Power Down· 130
Watchdog overflowAction:Power Cycle· 131
Watchdog overflowAction:Timer interrupt 132
Management subsystem health· 133
Management controller off-line· 133
Management controller off-line---BMC reset 133
Management controller off-line---HDM cold reboot 134
Management controller off-line---BMC WDT timeout event happened· 134
Management controller off-line---BMC service restart 135
Management controller unavailable· 135
Management controller unavailable---Adapter $1 RAID-P460-B4 is in a fault condition· 136
Sensor access degraded or unavailable--- Adapter $1 RAID-P460-B4 has  no response for 2 minutes in $2 slot 136
Sensor access degraded or unavailable--- Adapter $1 has  no response for 5 minutes in $2 slot 137
Sensor failure---Adapter $1 has no response for 4 minutes in $2 slot 137
Sensor failure--- Adapter $1 has no response for 10 minutes in $2 slot 138
Battery· 138
Battery low (predictive failure) 138
Battery failed· 139
Battery presence detected· 139
ME status· 140
Management controller unavailable· 140
OEM Record· 140
System Source Monitor:Mem usage exceeds the threshold· 140
System Source Monitor: Relieve resource alarm about Mem Usage· 141
System Source Monitor:Cpu usage exceeds the threshold· 141
System Source Monitor: Relieve resource alarm about Cpu Usage· 142
Memory is not certified· 142
Numbering CPUs· 142
Introduction
This document describes HDM log messages generated to notify the occurrence and removal of system exceptions detected by sensors in the server. You can use this document to obtain message details and recommended actions for server maintenance.
You can obtain system log messages through the following methods:
·     HDM Web interface—Access the HDM Web interface and click Remote O&M > Log > Log Download. On the Log Download tab, select to download the entire log or log entries for a period.
·     Alert emails—Complete alert email settings to obtain log messages.
·     Third-party platform—Complete SNMP settings to connect HDM to a third-party management platform, and obtain log messages from the platform.
·     Redfish event subscription—If a remote subscription server is configured, Redfish uploads received log messages to the remote subscription server.
·     IPMI commands—Use IPMItool commands to access the IPMI interface for HDM and enter commands to obtain event log messages.
Table 1 System log message severity levels
Severity
Critical
The target module might be powered off or the system might become unavailable. Actions must be taken immediately.
Major
The system or service modules, including computing, storage, communication, and data security, might fail to operate correctly and service interruption might occur.
Minor
Actions must be taken to prevent failure escalation, if necessary.
Info
Informational message. For example, a normal state change happened or an alarm is removed. No action is required.
Using this document
This document explains messages in tables. Table 2 describes information provided in these tables.
Table 2 Message explanation table contents
Item
Example
Event code
A hexadecimal code that uniquely represents a log message.
The parity of the last character in the event code represents the alarm type:
·     Even—An alarm was generated.
·     Odd—An alarm was removed.
0x02900002
Message text
Presents the message description. The same message description might be reported by different types of sensors.
Exceeded the upper major threshold.---Current reading:$1---Threshold reading:$2
Variable fields
Briefly describes the variable fields in the order that they appear in the message text.
The variable fields are numbered in the "$Number" form to help you identify their location in the message text.
·     $1: Current reading of the voltage sensor.
·     $2: Major overvoltage threshold of the voltage sensor.
Severity level
Provides the severity level of the message.
Major
Example
Log example.
Exceeded the upper major threshold.---Current reading:2.58---Threshold reading:2.56
Cause
Explains the message, including the event or error cause.
The total input voltage exceeds the major overvoltage alarm threshold. To locate the alarm triggering component, see the sensor name on the Event Log page from the HDM Web interface.
Recommended action
Provides recommended actions. If the issue persists after the recommended actions have been taken, contact the technical support.
1.     Verify that the external power supply is operating correctly.
2.     Access the HDM Web interface and verify that the power supply is operating correctly.
3.     If the issue persists, contact Technical Support.
Applicable products
This document is available for the following product models:
·     H3C UniServer B5700 G3
·     H3C UniServer B5700 G5
·     H3C UniServer B5800 G3
·     H3C UniServer B7800 G3
·     H3C UniServer E3200 G3
·     H3C UniServer R2700 G3
·     H3C UniServer R2900 G3
·     H3C UniServer R4100 G3
·     H3C UniServer R4300 G3
·     H3C UniServer R4300 G5
·     H3C UniServer R4330 G5
·     H3C UniServer R4330 G5 H3
·     H3C UniServer R4400 G3
·     H3C UniServer R4500 G3
·     H3C UniServer R4700 G3
·     H3C UniServer R4700 G5
·     H3C UniServer R4700LC G5
·     H3C UniServer R4900 G3
·     H3C UniServer R4900 G5
·     H3C UniServer R4900LC G5
·     H3C UniServer R4930 G5
·     H3C UniServer R4930 G5 H3
·     H3C UniServer R4930LC G5 H3
·     H3C UniServer R4950 G3
·     H3C UniServer R4950 G5
·     H3C UniServer R5300 G3
·     H3C UniServer R5300 G5
·     H3C UniServer R5500 G5
·     H3C UniServer R5500 INTEL liquid cooling
·     H3C UniServer R6700 G3
·     H3C UniServer R6900 G3
·     H3C UniServer R6900 G5
·     H3C UniServer R8900 G3
Event log messages
This section contains event log messages.
Temperature
Event code
0x01000002
Message text
Dropped below the lower minor threshold.---Current reading:$1---Threshold reading:$2
Variable fields
$1: Current reading of the temperature sensor.
$2: Value of the lower minor temperature alarm threshold.
Severity level
Minor
Example
Dropped below the lower minor threshold.---Current reading:2---Threshold reading:10
Impact
Performance degradation and unstable operation might occur on the device components if the temperature is too low.
If the temperature does not rise and the alarm persists, it might result in further temperature reduction and produce alarms of the major level. Therefore, it is important to detect potential issues that might lead to low temperature alarms as early as possible to avoid escalation of the issues.
Cause
The temperature is too low.
Recommended action
1.     Verify that the temperature of the equipment room is as required.
2.     Log in to HDM, access the Fans page, and verify if the fan speed is too high. If yes, adjust the fan speed mode or fan speed level.
Event code
0x01200002
Message text
Dropped below the lower major threshold.---Current reading:$1---Threshold reading:$2
Variable fields
$2: Value of the lower major temperature alarm threshold.
Severity level
Major
Example
Dropped below the lower major threshold.---Current reading:2---Threshold reading:5
Impact
If the temperature does not rise and the alarm persists, it might result in further temperature reduction and generate alarms of the critical level. Therefore, it is important to detect potential issues that might lead to low temperature alarms as early as possible in order to avoid issue escalation.
Cause
Recommended action
Event code
0x01400002
Message text
Dropped below the lower critical threshold.---Current reading:$1---Threshold reading:$2
Variable fields
$2: Value of the lower critical temperature alarm threshold.
Severity level
Critical
Example
Dropped below the lower critical threshold.---Current reading:2---Threshold reading:3
Impact
Operating devices in ultra-low temperature environments can reduce device performance, impact device lifespan, disrupt business operations, and lead to system downtime.
Cause
Recommended action
Event code
0x01700002
Message text
Exceeded the upper minor threshold.---Current reading:$1---Threshold reading:$2
Variable fields
$2: Value of the minor overtemperature alarm threshold.
Severity level
Minor
Example
Exceeded the upper minor threshold.---Current reading:100---Threshold reading:80
Impact
Performance degradation and unstable operation might occur on the device components if the temperature is too high.
If the temperature does not decrease and the alarm persists, it might result in further temperature rise and generate major-level alarms. Therefore, it is important to detect potential issues that might lead to high temperature alarms as early as possible in order to avoid problem escalation.
Cause
High ambient temperature, blockage of air intake or exhaust, and low fan speed.
Recommended action
2.     Verify that the server's air inlet and outlet are not blocked.
3.     Log in to HDM, access the Fans page, and verify that all the fans are operating correctly, and the fan speed is not too low. If the fan speed is low, adjust the fan speed mode or fan speed level.
4.     If the issue persists, contact Technical Support.
Event code
0x01900002
Message text
Variable fields
$2: Value of the major overtemperature alarm threshold.
Severity level
Major
Example
Exceeded the upper major threshold.---Current reading:100---Threshold reading:85
Impact
If the temperature does not decrease and the alarm persists, it might result in further temperature rise and generate critical-level alarms. Therefore, it is important to detect potential issues that might lead to high temperature alarms as early as possible in order to avoid problem escalation.
Cause
High ambient temperature, blocked air intake or exhaust, and low fan speed.
Recommended action
Event code
0x01b00002
Message text
Exceeded the upper critical threshold.---Current reading:$1---Threshold reading:$2
Variable fields
$2: Value of the critical overtemperature alarm threshold.
Severity level
Critical
Example
Exceeded the upper critical threshold.---Current reading:100---Threshold reading:90
Impact
Operating devices in high-temperature environments can reduce device performance, impact device lifespan, increase energy consumption, disrupt business operations, and cause system crashes.
Cause
Recommended action
Event code
0x011000de
Message text
Abnormal Temperature---GPU Card Temperature Error---Register location:$1--- GPU location:$2
Variable fields
$1: State register.
$2: GPU slot number.
Severity level
Major
Example
Abnormal Temperature---GPU Card Temperature Error---Register location:0x6--- GPU location:11
Impact
Cause
Recommended action
Voltage
State Asserted
Event code
0x02100006
Message text
State Asserted
Variable fields
N/A
Severity level
Critical
Example
State Asserted
Impact
Performance degradation and unstable operation might occur on the device components if the voltage is too high.
Cause
Overvoltage was detected on the system board. To locate the alarm triggering component, see the sensor name on the Event Log page from the HDM Web interface.
Recommended action
1.     Power off and then restart the server.
2.     If the issue persists, contact Technical Support.
Event code
0x02200002
Message text
Variable fields
$1: Current value of the total input voltage.
$2: Lower major voltage alarm threshold.
Severity level
Major
Example
Dropped below the lower major threshold.---Current reading:2.58---Threshold reading:2.60
Impact
Performance degradation and unstable operation might occur on the device components if the voltage is too low.
Cause
Abnormal board voltage.
Recommended action
2.     Log in to HDM and verify that the power supply is operating correctly.
3.     Power off and then restart the server.
Event code
0x02900002
Message text
Variable fields
$2: Upper major voltage alarm threshold.
Severity level
Major
Example
Impact
Cause
Recommended action
Current
State Asserted
Event code
0x03100006
Message text
State Asserted
Variable fields
N/A
Severity level
Critical
Example
State Asserted
Impact
The system might be shut down and powered off.
Cause
Overcurrent was detected for a component on the system board.
Recommended action
1.     Log in to HDM, access the Logs page, and verify that no alarm is present for the power supply or system board.
2.     Verify that power can be supplied to the server correctly and the voltage is within the normal range.
Event code
0x03700002
Message text
Variable fields
$1: Real-time current value.
$2: Value for the minor current alarm threshold.
Severity level
Minor
Example
Exceeded the upper minor threshold.---Current reading:20---Threshold reading:18
Impact
Performance degradation and unstable operation might occur on the device components if the current is too high.
Cause
The current of the corresponding component is abnormal.
Recommended action
1.     Verify that the threshold has a reasonable value.
2.     Verify that the system is not overloaded according to the server rated power.
Event code
0x03900002
Message text
Variable fields
$2: Value for the major current alarm threshold.
Severity level
Major
Example
Exceeded the upper major threshold.---Current reading:25---Threshold reading:22
Impact
Cause
Abnormal board current.
Recommended action
Event code
0x03b00002
Message text
Variable fields
$2: Value for the critical current alarm threshold.
Severity level
Critical
Example
Exceeded the upper critical threshold.---Current reading:30---Threshold reading:25
Impact
This could potentially cause component damage, leading to a system crash.
Cause
Recommended action
Fan
Event code
0x04000014
Message text
Transition to Running.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The fan is operating correctly.
Recommended action
1.     Verify that the fan is present.
2.     Re-install the fan.
Fully Redundant
Event code
0x04000017
Message text
Fully Redundant.
Variable fields
N/A
Severity level
Major
Example
Fully Redundant
Impact
Depending on the severity of redundancy loss, it might affect the normal heat dissipation of the server.
Cause
A fan redundancy error is present because a fan is absent, or a fan was removed or failed.
Recommended action
1.     Re-install the removed fans.
2.     Remove and re-install the fans, and make sure the fans are in good contact.
3.     If a fan status sensor reports an error, replace the faulty fan.
Event code
0x04300016
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
This issue does not affect system heat dissipation.
Cause
The fan is invalid or is absent.
Recommended action
Event code
0x04400014
Message text
Transition to Off Line.
Variable fields
N/A
Severity level
Info
Example
Impact
This affects system heat dissipation and reduces the performance of the system board components.
Cause
The fan module has been unplugged or the fan module and the system board have poor contact.
Recommended action
Event code
0x04500016
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
This affects system heat dissipation, causing the system to overheat and automatically shut down.
Cause
Recommended action
2.     If a fan status sensor reports an error, replace the faulty fan.
3.     Remove and re-install the fans, and make sure the fans are in good contact.
Event code
0x04600014
Message text
Transition to Degraded.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
The fan speed is abnormal.
Recommended action
1.     Log in to HDM and view the fan speed. If the speed is low, a fan might have aged. If the speed is almost zero, a fan might be blocked or have failed.
2.     Verify that the fans are not blocked.
4.     Replace the aged fans.
5.     If the issue persists, contact Technical Support.
Install Error
Event code
0x04800014
Message text
Install Error.
Variable fields
N/A
Severity level
Minor
Example
Install Error
Impact
The system might fail to be powered on.
Cause
The fan was incorrectly installed.
Recommended action
1.     Verify that the fans are installed as instructed. For more information about the installation principles, see the user guide for the server.
Cooling device
Event code
0x0a5000de
Message text
Liquid Cooler is not present.
Variable fields
N/A
Severity level
Minor
Example
Impact
This affects system heat dissipation and system performance.
Cause
The liquid-cooled module is installed incorrectly. This message is available only for liquid-cooled servers.
Recommended action
1.     Verify that the liquid-cooled module is present.
2.     Verify that the liquid leakage sensor is installed correctly.
3.     Replace the liquid-cooled module.
Event code
0x0a6000de
Message text
Liquid Cooler is leakage.
Variable fields
N/A
Severity level
Critical
Example
Impact
This might cause system crashes.
Cause
Liquid leakage occurred to the liquid-cooled module. This message is available only for liquid-cooled servers.
Recommended action
1.     Verify that the liquid-cooled module is operating correctly and liquid leakage does not occur.
2.     Replace the liquid-cooled module.
Event code
0x0a7000de
Message text
Variable fields
N/A
Severity level
Critical
Example
Impact
Cause
Recommended action
Physical security
Event code
0x050000de
Message text
General Chassis Intrusion.
Variable fields
N/A
Severity level
Minor
Example
Impact
No negative impact.
Cause
The access panel was removed from the server.
Recommended action
1.     Verify that the access panel was removed.
2.     Verify that the access panel is installed correctly.
3.     Verify that the chassis-open alarm module has a good contact with the chassis ear.
LAN Leash Lost
Event code
0x054000de
Message text
LAN Leash Lost.
Variable fields
N/A
Severity level
Info
Example
LAN Leash Lost
Impact
No negative impact.
Cause
The NCSI channel detection of BMC detected that the network is disconnected at the physical layer.
Recommended action
1.     Verify that an Ethernet adapter was disabled in the OS.
2.     Verify that the message was reported on a power-on or power-off operation.
3.     Verify that the Ethernet cable is connected correctly to the shared network port.
4.     Disable the shared network port if the shared network port is not necessary.
Processor
IERR
Event code
0x070000de
Message text
Intel:
$1 $2 err---Socket $3
AMD:
GMI/xGMI err---Socket$1 Die$2 LinkID$3
Variable fields
·     Intel:
¡     $1: Signal type. Options include MSMI and CATERR.
¡     $2: Error type. Options include IERR and MCERR.
¡     $3: CPU number.
·     AMD:
¡     $1: CPU number.
¡     $2: Die number.
¡     $3: Link number.
Severity level
Critical
Example
Intel:
CATERR IERR err---Socket 1
AMD:
GMI/xGMI err---Socket1 Die1 LinkID1
Impact
This can cause system crashes. By default, the system will then automatically restart.
Cause
A processor internal error, such as a Package Control Unit (PCU) uncorrectable error, occurred.
Recommended action
1.     Upgrade the BIOS and HDM firmware to the latest version.
2.     Review logs to troubleshoot the issue as instructed.
State Asserted
Event code
0x07100006
Message text
State Asserted.
Variable fields
N/A
Severity level
Major
Example
State Asserted
Impact
Cause
A processor was overheated.
Recommended action
1.     Log in to HDM and verify that the fans are operating correctly.
2.     If low-speed alarms are present, re-install or replace the faulty fans.
3.     View resource summary to identify system service loads. If the system is overloaded, close uncritical services to reduce service loads.
4.     Verify that the ambient temperature of the server is within the normal operation range.
5.     Verify that the air inlets and outlets are not blocked.
6.     Power off the server, and verify that the processor heatsink has a good contact. Smear the thermal grease onto the heatsink, install the heatsink, and power on the server.
7.     If the issue persists, contact Technical Support.
Event code
0x071000de
Message text
CPU Critical Temperature.
Variable fields
N/A
Severity level
Critical
Example
Impact
Cause
The temperature of a processor exceeded the critical overtemperature alarm threshold.
Recommended action
2.     If a low-speed alarm is present, re-install or replace the faulty fan.
4.     Verify that the temperature in the equipment room is within the normal range.
Thermal Trip
Event code
0x071000de
Message text
Thermal Trip
Variable fields
N/A
Severity level
Critical
Example
Thermal Trip
Impact
Cause
A processor was overheated, which might cause system power-off.
Recommended action
1.     Log in to HDM and verify that all fans are operating correctly.
5.     Verify the air inlets and outlets are not blocked.
FRB1/BIST failure
Event code
0x072000de
Message text
FRB1/BIST failure
Variable fields
N/A
Severity level
Minor
Example
FRB1/BIST failure
Impact
It might result in the operating system failing to start up normally and hardware being downgraded.
Cause
The processor core BIST failed.
Recommended action
1.     Power off and power on the server to clear the alarm.
2.     If the issue persists, replace the processors.
Event code
0x077000df
Message text
Processor Presence detected.
Variable fields
N/A
Severity level
Info/Critical
Example
Impact
The system cannot start up if the primary processor is absent.
Cause
The system detected the absence or misinstallation of the primary processor.
Recommended action
1.     Verify that the primary processor is installed correctly.
2.     Replace the faulty primary processor.
Event code
0x07a000de
Message text
Processor Automatically Throttled---due to fan error.
Variable fields
N/A
Severity level
Minor
Example
Impact
CPU underclocking causes a decrease in system performance.
Cause
The processor was underclocked because a fan fails.
Recommended action
1.     Verify that the heat dissipation setting meets the requirements of the running services.
2.     Verify that the temperature in the equipment room is within the normal range and the air inlet and outlet are not blocked.
3.     Verify that the fans are not blocked and are operating correctly.
4.     Replace the faulty fans.
Event code
0x07b000de
Message text
Machine Check Exception---$1---$2---Location: Socket:$3
Variable fields
$1: Error type.
$2: Indicates whether the error occurred during this system boot. Options include:
¡     Current Boot Error.
¡     Last Boot Error.
$3: CPU number.
Severity level
Critical
Example
Machine Check Exception---SMN---Last Boot Error---Location: Socket:1
Impact
The system stops responding.
Cause
An uncorrectable error occurred.
Recommended action
2.     Review event logs to locate the failed processor or other components.
3.     Reboot the device.
4.     Verify that the processor and memories are operating correctly.
Event code
0x07b000de
Message text
CPU $1 triggered an uncorrectable error.
Variable fields
$1: CPU number.
Severity level
Critical
Example
CPU 1 triggered an uncorrectable error.
Impact
Cause
An IERR or MCERR error occurred. The BMC diagnostic result is "CPU uncorrectable error."
Recommended action
2.     Review event logs to locate the failed memory, PCIe module, or processor.
3.     Power off the server, and replace the failed component.
4.     Replace the system board.
Machine Check Error
Event code
0x07b100de
Message text
Machine Check Error ---Location: Processor:$1 ---IIO Stack number:$2 ---$3---$4
Variable fields
$1: CPU number.
$2: IIO Stack number (IIO port number).
$3: Current boot or last boot.
$4: Error type.
Severity level
Critical
Example
Machine Check Exception---Location: Processor:1 ---IIO Stack number:1 --Last Boot---ITC Error:ECC uncorrectable error in the ITC dat_dword RF
Impact
Cause
Internal uncorrectable errors were detected on the processor, such as VT-d errors, ITC errors, OTC errors, DMA errors, IRP errors, and Ring errors.
This error also triggers other alarms.
Recommended action
1.     Review event logs.
Event code
0x07b150de
Message text
Machine Check Error ---CPU core errors --- ErrorType:$1---Location: Processor:$2  core MCA bank: $(3)
Variable fields
$1: General error type.
$2: CPU number.
$3: Error type.
Severity level
Critical
Example
Machine Check Exception---CPU core errors--ErrorType:Unknow--Fatal Error--Last Boot---Location: Processor:1 core MCA bank: instruction fetch unit
Impact
Cause
Internal uncorrectable errors were detected on the processor, such as CPU core errors.
Recommended action
Event code
0x07c000de
Message text
CPU $1 triggered a correctable error.
Variable fields
$1: CPU number.
Severity level
Minor
Example
CPU 1 triggered a correctable error.
Impact
No negative impact.
Cause
Recommended action
2.     Review event logs to locate the failed CPU or other components.
Event code
0x07c100de
Message text
Correctable Machine Check Error ---location: Processor:$1 ---IIO Stack number:$2 ---$3---$4
Variable fields
$1: CPU number.
$2: IIO Stack number.
$4: Error type.
Severity level
Minor
Example
Correctable Machine Check Error---Location: Processor:1 ---IIO Stack number:1 --Last Boot---DMA Error:Descriptor Count Error
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as VT-d errors, ITC errors, OTC errors, DMA errors, IRP errors, and Ring errors.
Recommended action
1.     Review event logs and troubleshoot the present errors.
Event code
0x07c110de
Message text
Correctable Machine Check Error ---CPU UPI errors ---Location: Processor:$1  UPI port number:$2
Variable fields
$1: CPU number.
$2: UPI port.
Severity level
Minor
Example
Correctable Machine Check Error---CPU UPI errors---Location: Processor:2 UPI port number:0x1
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as CPU UPI errors.
Recommended action
Event code
0x07c120de
Message text
Correctable Machine Check Error ---IOH UPI errors ---Location: Processor:$1  UPI port number:$2 ---Coherent interface (IRP) local group error code:$3
Variable fields
$1: CPU number.
$2: UPI port.
$3: Error code.
Severity level
Minor
Example
Correctable Machine Check Error---IOH UPI errors---Location: Processor:1 UPI port number:0x1---Coherent interface (IRP) local group error code:0x6
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as IOH UPI errors.
Recommended action
Event code
0x07c130de
Message text
Correctable Machine Check Error ---IOH core errors ---Location:Processor:$1  ---IIO core local group error code:$2
Variable fields
$1: CPU number.
$2: Error code.
Severity level
Minor
Example
Correctable Machine Check Error---IOH core errors---Location: Processor:2---IIO core local group error code:0x6
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as IOH core errors.
Recommended action
Event code
0x07c140de
Message text
Correctable Machine Check Error ---VT-d errors ---Location: Processor:$1  ---VT-d local group error code:$2
Variable fields
$1: CPU number.
$2: Error code.
Severity level
Minor
Example
Correctable Machine Check Error---VT-d errors---Location: Processor:2---VT-d local group error code:0x6
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as VT-d errors.
Recommended action
Event code
0x07c150de
Message text
Correctable Machine Check Error ---CPU core errors ---ErrorType:$1 ---Location: Processor:$2  core MCA bank: $3
Variable fields
$2: CPU number.
$3: Error type.
Severity level
Minor
Example
Correctable Machine Check Error---CPU core errors--ErrorType:Unknow--Current Boot---Location: Processor:2 core MCA bank: mid level cache
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as CPU core errors.
Recommended action
Event code
0x07c160de
Message text
Correctable Machine Check Error ---Cbo error--location: CPU core ID:$1  thread ID:$2 caching agent MCA bank: Cbo$3
Variable fields
$1: Core number.
$2: Thread number.
$3: Cbo number.
Severity level
Minor
Example
Correctable Machine Check Error---Cbo error---Location: CPU core ID:0x0 thread ID:0x0 caching agent MCA bank: Cbo0
Impact
No negative impact.
Cause
Internal correctable errors were detected on the processor, such as Cbo error.
Recommended action
Event code
0x075d7010
Message text
Configuration Error---System is operating in KTI Link Slow Speed Mode- Location:CPU:$1
Variable fields
$1: Core number.
Severity level
Minor
Example
Configuration Error---System is operating in KTI Link Slow Speed Mode- Location:CPU:1
Impact
No negative impact.
Cause
The system is operating in Keizer Technology Interconnect (KTI) low speed mode.
Recommended action
1.     Verify that the processors are installed correctly as instructed. For more information about the installation principles, see the user guide for the server.
Power supply
Fully Redundant
Event code
0x08000016
Message text
Fully Redundant
Variable fields
N/A
Severity level
Info
Example
Fully Redundant
Impact
No negative impact.
Cause
Power redundancy.
Recommended action
Fully Redundant
Event code
0x08100017
Message text
Fully Redundant
Variable fields
N/A
Severity level
Major
Example
Fully Redundant
Impact
Power redundancy failure reduces the reliability of device power supply.
Cause
The power supply redundancy was lost.
Recommended action
1.     Verify that the environment is normal.
2.     Verify that no power supply is removed.
3.     Verify that the power supplies have good contacts with the power cords.
4.     Verify that all power supplies are operating correctly.
Presence detected
Event code
0x080000df
Message text
Presence detected.
Variable fields
N/A
Severity level
Info
Example
Presence detected
Impact
No negative impact.
Cause
0x080000de: When the power supply is detected as being inserted, this event is triggered, indicating a transition from the power supply not being in place to being in place.
0x080000df: When the power supply is detected as being removed, this event is cleared, indicating a transition from the power supply being in place to not being in place.
Recommended action
1.     Verify that the power module is not removed.
2.     Verify that the power module is installed correctly.
Redundancy Lost
Event code
0x08100016
Message text
Redundancy Lost.
Variable fields
N/A
Severity level
Major
Example
Redundancy Lost
Impact
Cause
Recommended action
Event code
0x081000de
Message text
Power Supply Failure detected.
Variable fields
N/A
Severity level
Major
Example
Impact
It affects system power supply and may result in abnormal system power-off.
Cause
A power supply fault was detected.
Recommended action
1.     Verify that the power supply fans are operating correctly.
2.     Re-install the power supplies.
3.     Verify that the input voltage of the power supply is normal.
4.     Replace the faulty power supply.
Event code
0x082000de
Message text
Power Supply Predictive Failure---PSU Self Check Failed---Id: $1
Variable fields
$1: Number of a power supply.
Severity level
Minor
Example
Power Supply Predictive Failure---PSU Self Check Failed---Id: 1
Impact
The power supply may have malfunctions that affect system power supply.
Cause
Power supply self-check failed.
Recommended action
1.     Verify that the power supply LED is operating correctly.
2.     Verify that the power supply fans are operating correctly.
3.     Verify that the power supply is compatible with the server.
Event code
0x082000de
Message text
Power Supply Predictive Failure.
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
A predictive power supply fault is detected.
Recommended action
Event code
0x083000de
Message text
Power Supply input lost (AC/DC).
Variable fields
N/A
Severity level
Major
Example
Impact
It may cause the server to power off abnormally.
Cause
The AC power cable of the power supply is unplugged or the AC input is abnormal.
Recommended action
1.     Verify that all power cords are not damaged and are correctly connected.
2.     Verify that all power supplies are correctly installed.
3.     Verify that the power supply fans are operating correctly.
4.     Verify that the power input is normal.
Event code
0x084000de
Message text
Power Supply input lost or out-of-range.
Variable fields
N/A
Severity level
Major
Example
Impact
This might cause the server to be powered off abnormally.
Cause
The input voltage of the power supply exceeded the rated range.
Recommended action
1.     Verify that the power supply has not been cut off manually.
2.     Verify that the input voltage of the power supply is normal.
3.     Verify that the power cords and power modules are installed correctly.
4.     Re-install the power supplies. Make sure the power supplies have a good contact.
5.     Verify that the power supply fans are operating correctly.
6.     If the issue persists, contact Technical Support.
Event code
0x085000de
Message text
Power Supply input out-of-range - but present.
Variable fields
N/A
Severity level
Major
Example
Impact
Abnormal power input beyond the supported range might cause the server to be powered off.
Cause
The input voltage was too high.
Recommended action
1.     Verify that the input voltage of the power supply is normal.
2.     Verify that the power cords and power modules are installed correctly.
3.     Re-install the power supplies. Make sure the power supplies have a good contact.
4.     Verify that the power supply fans are operating correctly.
Event code
0x086000de
Message text
Configuration error ---Vendor mismatch.
Variable fields
N/A
Severity level
Minor
Example
Impact
An unknown risk exists due to the use of non-originally certified components.
Cause
Non-originally certified power supplies are installed.
Recommended action
1.     Verify that all power supplies are compatible with the server.
Event code
0x086000de
Message text
Configuration error---Power supply rating mismatch:PSU$1,POUT:$2
Variable fields
$1: Power supply ID.
$2: Output power of the power supply.
Severity level
Minor
Example
Configuration error---Power supply rating mismatch:PSU1,POUT:2000
Impact
This might result in unstable power supply and abnormal system shutdown.
Cause
Originally certified power supplies are installed, but the models of the two power supplies do not match.
Recommended action
1.     If the rated power of the installed power supplies is consistent, remove and install the power supplies in sequence.
2.     If the rated power of the installed power supplies is inconsistent, replace the power supplies to make sure they are of the same rated power.
Event code
0x08700002
Message text
Exceeded the upper minor threshold. ---Current reading:$1---Threshold reading:$2
Variable fields
$1: Current reading.
$2: Total power alarm threshold.
Severity level
Minor
Example
Exceeded the upper minor threshold.---Current reading:2030---Threshold reading:493
Impact
The power exceeded the upper limit and will cause system shutdown.
Cause
The power exceeded the threshold.
Recommended action
1.     Log in to HDM and verify that the alarm threshold is appropriate.
2.     Log in to HDM and verify that the total power is not too high.
3.     Verify that the total power of the power supplies can meet service requirements.
Event code
0x087000df
Message text
Power Supply Inactive/standby state.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
A power supply exited the cold standby state.
If power redundancy is configured, a standby power supply automatically exits the cold standby state and supplies power to the server when the system power consumption is too high.
Recommended action
1.     Log in to HDM and verify if the total power of the server is too high.
Event code
0x093000de
Message text
Variable fields
N/A
Severity level
Critical
Example
Impact
This might lead to a system crash.
Cause
Fluctuations in the power grid can cause an AC momentary interruption.
Recommended action
1.     Verify that the external power supply environment of the server is in normal state.
2.     Press and hold the power button until the UID LED stops flashing.
Event code
0x08a000de
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
This might affect the system power supply and eventually leads to system crashes.
Cause
Power output is normal but the Pwok signal on the system board is abnormal and the health LED is on.
Recommended action
1.     Verify that the power input is correct.
2.     Verify that the system board is in operating correctly.
3.     Verify that power supplies are connected correctly to the system board.
Event code
0x095000de
Message text
Power limit is exceeded over correction time limit---Current Power: $1W.
Variable fields
$1: Current power threshold value.
Severity level
Minor
Example
Power limit is exceeded over correction time limit---Current Power: 2000W.
Impact
The specified action will be taken if power capping fails.
Cause
This alarm is generated if the power exceeds the cap value for a period of time.
Recommended action
1.     Adjust the power cap value or the server work load.
Event code
0x095010de
Message text
Power limit is exceeded over correction time limit---GPU Current Power: $1W.
Variable fields
$1: Configured power threshold value.
Severity level
Minor
Example
Power limit is exceeded over correction time limit---GPU Current Power: 2000W.
Impact
Cause
Recommended action
1.     Adjust the power cap value or the GPU work load.
Memory
Event code
0x0c0000de
Message text
Correctable ECC or other correctable memory error--$1-Location:CPU:$2 MEM CTRL:$3 CH:$4 DIMM:$5 $6
Variable fields
$1: Indicates whether the error occurred during this system boot. Options include:
·     Current Boot Error.
·     Last Boot Error.
$2: CPU number.
$3: Memory controller number.
$4: Channel number.
$5: DIMM number.
$6: DIMM mark.
Severity level
Minor
Example
Correctable ECC or other correctable memory error---Current Boot Error-Location:CPU:1 MEM CTRL:1 CH:1 DIMM:0 A1
Impact
No negative impact.
Cause
A correctable memory error occurred.
Recommended action
Event code
0x0c0000de
Message text
CPU $1 $2 triggered a correctable error
Variable fields
$1: CPU number.
$2: DIMM number.
Severity level
Minor
Example
CPU 1 A0 triggered a correctable error
Impact
No negative impact.
Cause
An IERR or MCERR error was triggered. The error was identified by HDM as a correctable error.
Recommended action
Event code
0x0c1000de
Message text
Uncorrectable ECC or other uncorrectable memory error--$1-Location:CPU:$2 MEM CTRL:$3 CH:$4 DIMM:$5 $6
Variable fields
·     Last Boot Error.
$2: CPU number.
$4: Channel number.
$5: DIMM number.
$6: DIMM mark.
Severity level
Major
Example
Uncorrectable ECC or other uncorrectable memory error---Current Boot Error-Location:CPU:1 MEM CTRL:1 CH:1 DIMM:0 A1
Impact
It can cause the system to stop sending responses, unless the memory is in certain RAS modes, such as mirror or MCA recovery.
Cause
A non-correctable (multiple bit flip) ECC error has occurred.
Recommended action
1.     Verify that the ambient temperature and humidity are as required.
2.     Re-install the DIMM. Verify that the gold contacts on the DIMM are not contaminated and the DIMM slot does not contain any foreign objects.
3.     Verify that the pins in the processor socket are not bent. If any pins are bent, replace the system board.
4.     Replace the DIMM.
Event code
0x0c1000de
Message text
CPU$1 $2 triggered an uncorrectable error
Variable fields
$1: CPU number.
$2: DIMM number.
Severity level
Major
Example
CPU1 A0 triggered an uncorrectable error
Impact
It can cause the system to restart or stop sending responses.
Cause
An IERR or MCERR error was triggered. The error was identified by BMC as a memory uncorrectable error.
Recommended action
3.     Verify that the pins in the CPU socket are not bent. If any pins are bent, replace the system board.
Parity
Event code
0x0c2000de
Message text
Parity---$1---Location: Location:CPU:$2 MEM CTRL:$3  CH:$4 DIMM:$5 $6
Variable fields
·     Last Boot Error.
$2: CPU number.
$4: Channel number.
$5: DIMM number.
$6: DIMM mark.
Severity level
Minor
Example
Parity---Current Boot Error-Location:CPU:1 MEM CTRL:1 CH:1 DIMM:0 A0
Impact
No negative impact.
Cause
This error message is generated when a failure occurs in data parity on the command/address lines while the system is reading the memory cell data, resulting in abnormal data access to the memory.
Recommended action
Event code
0x0c201310
Message text
Parity---Memory Training Faulty Part Tracking Uncorrectable Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Training Faulty Part Tracking Uncorrectable Error-Location:CPU:2 CH:1 DIMM:B1 Rank:0
Impact
No negative impact.
Cause
A Faulty Parts Tracking error occurred because of an uncorrectable error.
Recommended action
Event code
0x0c204140
Message text
Parity---Memory Receive Enable Training Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Receive Enable Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
This might lead to a decrease in system performance.
Cause
A Faulty Parts Tracking error occurred because memory receive enable training failed.
Recommended action
Event code
0x0c205150
Message text
Parity---Memory Write Leveling Training Error-Location:CPU:&1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Write Leveling Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
A Faulty Parts Tracking error occurred because memory write leveling training failed.
Recommended action
Event code
0x0c206160
Message text
Parity---Memory Write DqDqs Training Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Write DqDqs Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Memory write Dq and Dqs training failed.
Recommended action
Event code
0x0c2072f0
Message text
Parity---Memory Sense Amp Training Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Sense Amp Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Sense Amp Training failed because a voltage input error occurred.
Recommended action
Event code
0x0c208260
Message text
Parity---Warning Command Clock Training Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Warning Command Clock Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
An error occurred for command clock training.
Recommended action
Event code
0x0c20b1c0
Message text
Parity---An uncorrectable error occurs during the memory test phase-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---An uncorrectable error occurs during the memory test phase-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
An uncorrectable error occurred during the memory test phase.
Recommended action
1.     Replace the DIMM.
Event code
0x0c20c290
Message text
Parity---Memory Training Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory Training Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
A memory training error occurred on the DIMM during the POST phase.
Recommended action
2.     Re-install the target DIMM. Verify that the gold contacts on the DIMM are not contaminated and the DIMM slot does not contain any foreign objects.
Event code
0x0c21f010
Message text
Parity---The number of correctable memory errors reached the error logging threshold-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---The number of correctable memory errors reached the error logging threshold-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The number of correctable memory errors reached the error logging threshold.
Recommended action
Event code
0x0c21f020
Message text
Parity---An error occurred on the DIMM slot-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---An error occurred on the DIMM slot-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
An error occurred on the DIMM slot.
Recommended action
Event code
0x0c226010
Message text
Parity---CMD eye width is too small-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---CMD eye width is too small-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
CMD eye width was too small.
Recommended action
Event code
0x0c228000
Message text
Parity---The command is not in the FNv table-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---The command is not in the FNv table-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
The command was not in the FNv table.
Recommended action
1.     Update BIOS and DCPMM controller firmware to the latest version.
Event code
0x0c229020
Message text
Parity---CTL is not consistent with clock in timing, and the channel is isolated-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---CTL is not consistent with clock in timing, and the channel is isolated-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
CTL was inconsistent with Clock in timing and the channel was isolated.
Recommended action
Event code
0x0c231000
Message text
Parity---Memory write flyby failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory write flyby failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory write flyby failed.
Recommended action
Event code
0x0c231010
Message text
Parity---Timing error occurred during signal line adjustment for memory write leveling training-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Timing error occurred during signal line adjustment for memory write leveling training-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Timing error occurred during signal line adjustment for write leveling training.
Recommended action
Event code
0x0c231130
Message text
Parity---Memory read DqDqs training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory read DqDqs training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory read Dq and Dqs training failed.
Recommended action
Event code
0x0c231140
Message text
Parity---Memory receive enable training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory receive enable training failed-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Memory Faulty Parts Tracking failed, causing the memory Receive Enable signal to fail to train the corresponding timing.
Recommended action
Event code
0x0c231150
Message text
Parity---Memory write leveling training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory write leveling training failed-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Memory write leveling training failed.
Recommended action
Event code
0x0c231160
Message text
Parity---Memory write DqDqs training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory write DqDqs training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Recommended action
Event code
0x0c2311c0
Message text
Parity---An error occurs during memory test, and the rank is disabled-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---An error occurs during memory test, and the rank is disabled-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
An error occurred during the memory test phase. The rank is disabled.
Recommended action
Event code
0x0c231250
Message text
Parity---Failed to find the RxVref for data eye training-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Failed to find the RxVref for data eye training-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory parity check failed and LRDIMM RCVEN training failed.
Recommended action
Event code
0x0c231260
Message text
Parity---LRDIMM RCVEN training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---LRDIMM RCVEN training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Recommended action
Event code
0x0c231270
Message text
Parity---RCVEN CYCLE training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---RCVEN CYCLE training failed-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
RCVEN CYCLE training failed.
Recommended action
Event code
0x0c231280
Message text
Parity---Read delay training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Read delay training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Read delay training failed.
Recommended action
Event code
0x0c231290
Message text
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Memory write leveling training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory parity check error occurred and memory write leveling training failed.
Recommended action
Event code
0x0c2312a0
Message text
Parity---Coarse write leveling training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Coarse write leveling training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory parity check error occurred and coarse write leveling training failed.
Recommended action
Event code
0x0c2312b0
Message text
Parity---Write delay training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Write delay training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Write delay training failed.
Recommended action
Event code
0x0c2312c0
Message text
Parity---QxCA_CLK_NO_EYE training failed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---QxCA_CLK_NO_EYE training failed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory parity check error occurred and QxCA_CLK_NO_EYE training failed.
Recommended action
Parity---mapped out because failed critical mask test at cold boot
Event code
0x0c28c020
Message text
Parity---mapped out because failed critical mask test at cold boot-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---mapped out because failed critical mask test at cold boot-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
During the cold start process, the critical mask detection of the memory failed and was marked as a defect area.
Recommended action
Parity---Invalid SPD contents
Event code
0x0c2ed090
Message text
Parity---Invalid SPD contents-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Parity---Invalid SPD contents-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Invalid SPD contents.
Recommended action
Memory Device Disabled
Event code
0x0c4000de
Message text
Memory Device Disabled---Location:CPU:$1 Channel:$2 Dimm:$3 $4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: DIMM mark.
Severity level
Major
Example
Memory Device Disabled---Location:Socket:1 Channel:1 Dimm:1 A1
Impact
Cause
The system detected a memory error during startup.
Recommended action
1.     Verify if the DIMM is disabled from the BIOS. If yes, enable the DIMM from the BIOS.
2.     Verify that the DIMM channel is not faulty.
Memory Device Disabled---the DIMM is disabled
Event code
0x0c40a040
Message text
Memory Device Disabled---The DIMM is disabled-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Major
Example
Memory Device Disabled---The rank is disabled-Location:CPU:2 CH:1 DIMM:B1 Rank:1
Impact
Cause
The DIMM is disabled.
Recommended action
Memory Device Disabled---the rank is disabled
Event code
0x0c40a030
Message text
Memory Device Disabled---The rank is disabled-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Major
Example
Impact
Cause
A rank was disabled.
Recommended action
1.     Verify that the DIMM is disabled from the BIOS. If yes, enable the DIMM from the BIOS.
Memory Device Disabled---Pmem Media disabled
Event code
0x0c484030
Message text
Memory Device Disabled---Pmem Media disabled-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Major
Example
Memory Device Disabled---Pmem Media disabled-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
This might lead to a decrease in system performance. If critical system components exist in PMem, the system might fail to function properly.
Cause
An error was detected during PMem initialization, which disabled the PMem media. The PMem can be reached and managed in an in-band manner, but the PMem was non-functional and data in the PMem cannot be accessed.
Recommended action
1.     Replace the faulty DIMM.
Correctable ECC or other memory error limit reached
Event code
0x0c5000de
Message text
Correctable ECC or other memory error limit reached--$1-Location:CPU:$2 MEM CTRL:$3 CH:$4 DIMM:$5 $6
Variable fields
·     Last Boot Error.
$2: CPU number.
$4: Channel number.
$5: DIMM number.
$6: DIMM mark.
Severity level
Minor
Example
Correctable ECC or other memory error limit reached---Current Boot Error-Location:CPU:1 MEM CTRL:1 CH:1 DIMM:0 A1
Impact
This might result in a restart or stop the system from responding.
Cause
The number of correctable memory errors reached the logging threshold. A correctable memory error might occur if a DIMM is installed incorrectly or an internal memory error occurs.
If the memory RAS mode is set, the system performs the specified operation.
In memory repair mode, the system still generates the message if the logging threshold is exceeded.
Recommended action
1.     Re-install the target DIMM. Verify that the gold contacts on the DIMM are not contaminated and the DIMM slot does not contain any foreign objects
2.     Verify that the ambient temperature and humidity are as required.
3.     Access the BIOS setup utility, and verify that the correctable error threshold setting is proper.
Presence detected
Event code
0x0c6000de/0x0c6000df
Message text
Presence detected.
Variable fields
N/A
Severity level
Info/Minor
Example
Presence detected
Impact
If the memory module is present, this alarm has no negative impact. If the memory module is absent, this might reduce the system performance.
Cause
0x0c6000de: The system detected the presence of a DIMM.
0x0c6000df: The system detected the absence of a DIMM.
Recommended action
1.     Access the BIOS setup utility, and verify if the server starts up with the minimum configuration. If yes, components that are not started are isolated by the BIOS and cannot be detected by HDM.
2.     Install or re-install DIMMs. Make sure the gold contacts on the DIMMs are not contaminated, and DIMM slots do not contain any foreign objects.
Configuration error---RDIMMs are installed on the server that supports only UDIMMs
Event code
0x0c701010
Message text
Configuration error---RDIMMs are installed on the server that supports only UDIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---RDIMMs are installed on the server that supports only UDIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
RDIMMs are installed for a processor platform that supports only UDIMMs.
Recommended action
1.     Access the component compatibility query tool at http://www.h3c.com/cn/Service/Document_Software/Document_Center/Server/ and verify that the DIMMs are compatible with the server.
Configuration error---UDIMMs are installed on the server that supports only RDIMMs
Event code
0x0c702010
Message text
Configuration error---UDIMMs are installed on the server that supports only RDIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---UDIMMs are installed on the server that supports only RDIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
UDIMMs are installed on a server that supports only RDIMMs.
Recommended action
Configuration error---SODIMMs are installed on the server that supports only RDIMMs
Event code
0x0c703010
Message text
Configuration error---SODIMMs are installed on the server that supports only RDIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---SODIMMs are installed on the server that supports only RDIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
SODIMMs are installed on a server that supports only RDIMMs.
Recommended action
Configuration error---The number of ranks per channel can be only 1, 2, or 4
Event code
0x0c707020
Message text
Configuration error---The number of ranks per channel can be only 1, 2, or 4-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The number of ranks per channel can be only 1, 2, or 4-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The number of ranks per channel does not meet the requirements of  the processor platform. The processor platform supports only 1, 2, or 4 ranks.
Recommended action
1.     Verify that the number of ranks is as required. If not, replace the DIMMs.
Configuration error---Columns, rows, or banks of the DIMM cannot meet the JEDEC standards, and LRDIMMs are not supported
Event code
0x0c707040
Message text
Configuration error---Columns, rows, or banks of the DIMM cannot meet the JEDEC standards, and LRDIMMs are not supported-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Columns, rows, or banks of the DIMM cannot meet the JEDEC standards, and LRDIMMs are not supported-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Columns, rows, or banks of the DIMM cannot meet the JEDEC standards, or LRDIMMs are not supported.
Recommended action
Configuration error---The number of ranks in the channel exceeds 8
Event code
0x0c707050
Message text
Configuration error---The number of ranks in the channel exceeds 8-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The number of ranks in the channel exceeds 8-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The number of ranks in the channel exceeded 8 (maximum supported number).
Recommended action
1.     Verify that the number of ranks in the channel does not exceed upper limit.
Configuration error---Support for ECC on the DIMMs is not consistent with support for ECC on the server
Event code
0x0c707090
Message text
Configuration error---Support for ECC on the DIMMs is not consistent with support for ECC on the server-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Support for ECC on the DIMMs is not consistent with support for ECC on the server-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Support for ECC on the DIMMs is inconsistent with support for ECC on the server.
Recommended action
1.     Identify the DIMM type. Log in to HDM and view ECC support details. If the inconsistency is confirmed, replace the DIMMs.
Configuration error---The voltage for a DDR4 DIMM must be 12V, and the voltage for a DDR5 DIMM must be 11V
Event code
0x0c7070a0
Message text
Configuration error---The voltage for a DDR4 DIMM must be 12V, and the voltage for a DDR5 DIMM must be 11V-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The voltage for a DDR4 DIMM must be 12V, and the voltage for a DDR5 DIMM must be 11V-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The current voltage cannot meet the requirement of the present DIMMs. The voltage for a DDR4 DIMM must be 12V, and the voltage for a DDR5 DIMM must be 11V.
Recommended action
1.     Replace with DIMMs compatible with the current voltage.
Configuration error---The CPU is not compatible with 3DS DIMMs
Event code
0x0c707100
Message text
Configuration error---The CPU is not compatible with 3DS DIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The CPU is not compatible with 3DS DIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The processor is not compatible with 3DS DIMMs.
Recommended action
1.     Replace the DIMMs.
Configuration error---NVDIMMs with stepping lower than 0x10 are not supported
Event code
0x0c707110
Message text
Configuration error---NVDIMMs with stepping lower than 0x10 are not supported-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---NVDIMMs with stepping lower than 0x10 are not supported-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The configuration is incorrect. NVDIMMs with stepping lower than 16 are not supported.
Recommended action
1.     Access the BIOS setup utility and verify that the DIMMs are supported by the processor. If not, replace the DIMMs.
Configuration error---The CPU is not compatible with 16-GB single-rank DIMMs
Event code
0x0c707120
Message text
Configuration error---The CPU is not compatible with 16-GB single-rank DIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The CPU is not compatible with 16-GB single-rank DIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The processor is not compatible with 16GB single-rank DIMMs.
Recommended action
1.     Examine whether the DIMM is a 16GB single-rank DIMM. If yes, replace the DIMM.
Configuration error---The CPU is not compatible with the DIMMs
Event code
0x0c707140
Message text
Configuration error---The CPU is not compatible with the DIMMs-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The CPU is not compatible with the DIMMs-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The processor is not compatible with the DIMMs.
Recommended action
Configuration error---The frequency of the DIMM is not supported on the server
Event code
0x0c707150
Message text
Configuration error---The frequency of the DIMM is not supported on the server-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The frequency of the DIMM is not supported on the server-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The frequency of the DIMM is not supported on the server.
Recommended action
2.     Access the BIOS setup utility and verify that Enforce POR is enabled.
3.     If the issue persists, contact Technical Support.
Configuration error---NVDIMMs are not compatible with the CPU
Event code
0x0c7071a0
Message text
Configuration error---NVDIMMs are not compatible with the CPU-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---NVDIMMs are not compatible with the CPU-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
DCPMMs are not compatible with the processor.
Recommended action
Configuration error---DCPMMs are not supported
Event code
0x0c7071d0
Message text
Configuration error---DCPMMs are not supported-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---DCPMMs are not supported-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
This might result in a decrease in system performance.
Cause
DCPMMs are not supported.
Recommended action
Configuration error---Memory LockStep Disable Error
Event code
0x0c709090
Message text
Configuration error---Memory LockStep Disable Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Memory LockStep Disable Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Failed to enable the LockStep mode. The mode was degraded to independent.
Recommended action
1.     Verify that the installed DIMMs meet the requirements of the LockStep mode. For the DIMM installation requirements, see the user guide for the server.
Configuration error---Memory Mirror Disable Error
Event code
0x0c70a0c0
Message text
Configuration error---Memory Mirror Disable Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Memory Mirror Disable Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
A memory error that BIOS cannot identify occurred. The memory installation does not meet the requirements of the mirror mode.
Recommended action
1.     Verify that the installed DIMMs meet the requirements of the Mirror mode. For the DIMM installation requirements, see the user guide for the server.
Configuration error---Failed to enable the full mirror mode
Event code
0x0c70c010
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
Failed to enable the Full Mirror RAS mode. The mirror configuration degraded.
Recommended action
Configuration error---The memory interleaving configuration cannot meet the requirements of the server
Event code
0x0c70e030
Message text
Configuration error---The memory interleaving configuration cannot meet the requirements of the server-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The memory interleaving configuration cannot meet the requirements of the server-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Memory configuration is incorrect. The memory interleaving configuration cannot meet the requirements of the server.
Recommended action
1.     Access the BIOS setup utility, and verify that the memory interleaving configuration (such as NUMA and interleave) can meet the server requirements.
2.     Upgrade the BIOS firmware to the latest version.
Event code
0x0c70e080
Message text
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Impact
Cause
Recommended action
Configuration error---Failed to enable the rank sparing mode The memory RAS mode has degraded to independent
Event code
0x0c710010
Message text
Configuration error---Failed to enable the rank sparing mode The memory RAS mode has degraded to independent-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Failed to enable the rank sparing mode The memory RAS mode has degraded to independent-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Failed to enable the Rank Sparing mode. The memory RAS mode has degraded to independent mode.
Recommended action
1.     Verify that the installed DIMMs meet the requirements of the Rank Sparing mode. For the DIMM installation requirements, see the user guide for the server.
Configuration error---Memory Rank Sparing Error
Event code
0x0c710100
Message text
Configuration error---Memory Rank Sparing Error-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Memory Rank Sparing Error-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The memory rank sparing configuration does not take effect.
Recommended action
1.     Access the BIOS setup utility and verify that Rank Sparing is enabled.
2.     Verify that the installed DIMMs meet the requirements of the Rank Sparing mode. For the DIMM installation requirements, see the user guide for the server.
Configuration error---Failed to enable patrol scrubbing
Event code
0x0c711000
Message text
Configuration error---Failed to enable patrol scrubbing-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---Failed to enable patrol scrubbing-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Failed to enable memory patrol.
Recommended action
1.     Identify RAS features supported by the processor specifications as instructed in H3C G3 Servers RAS Technology White Paper. If Patrol Scrub is not supported, disable Patrol Scrub.
Configuration error---The number of ranks in the black slot is greater than that in the white slot, or the DIMM is installed in the black slot with the white slot empty
Event code
0x0c717010
Message text
Configuration error---The number of ranks in the black slot is greater than that in the white slot, or the DIMM is installed in the black slot with the white slot empty-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The number of ranks in the black slot is greater than that in the white slot, or the DIMM is installed in the black slot with the white slot empty-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The memory installation is incorrect. Make sure memory installation follows these restrictions:
·     Populate the DIMM with more ranks in the white slot in each channel.
·     Populate DIMMs first in white slots.
Recommended action
1.     Re-install DIMMs as required in the user guide for the server.
2.     If the issue persists, contact Technical Support.
Configuration error---DIMM population error Two DDR-T memory modules cannot be installed in a channel
Event code
0x0c717030
Message text
Configuration error---DIMM population error Two DDR-T memory modules cannot be installed in a channel-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---DIMM population error Two DDR-T memory modules cannot be installed in a channel-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
Two DCPMM memory modules cannot be installed in the same channel.
Recommended action
Configuration error---The DDR-T memory module is installed in the white slot
Event code
0x0c717050
Message text
Configuration error---The DDR-T memory module is installed in the white slot-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The DDR-T memory module is installed in the white slot-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The DCPMM memory module is installed in the white slot.
Recommended action
Configuration error---2LM IMC memory Mismatch
Event code
0x0c7170c0
Message text
Configuration error---2LM IMC memory Mismatch-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---2LM IMC memory Mismatch-Location:CPU:1 CH:1 DIMM:A1 Rank:0
Impact
Cause
The memory installation did not meet the requirement for single Integrated Memory Controller (IMC) installation in 2LM mode.
Recommended action
1.     Verify that DIMMs are installed as required in 2LM mode. Make sure each IMC contains a minimum of one DDR and one DCPMM whose available capacity is larger than 0.
Configuration error---ODT configuration errorThe channel is isolated
Event code
0x0c729030
Message text
Configuration error---ODT configuration error The channel is isolated-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---ODT configuration errorThe channel is isolated-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory ODT is configured incorrectly, and the channel is isolated.
Recommended action
1.     Re-install the DIMM. Make sure the gold contacts on the DIMM and the DIMM slot are clean.
2.     Replace the DIMM.
Configuration error---Failed to enable ADDDC
Event code
0x0c73a010
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
Failed to enable ADDDC.
Recommended action
1.     Access the BIOS setup utility and verify that the memory configuration meets the ADDDC requirements.
Configuration error---Failed to enable SDDC
Event code
0x0c73b020
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
Memory configuration is incorrect. Failed to enable SDDC.
Recommended action
1.     Access the BIOS setup utility and verify that the memory configuration meets the SDDC requirements.
Configuration error---DCPMM firmware version not supported
Event code
0x0c73c000
Message text
Configuration error---DCPMM firmware version not supported-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---DCPMM firmware version not supported-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory configuration is incorrect. The DCPMM firmware version is not supported.
Recommended action
1.     Update the DCPMM firmware to the latest version.
Event code
0x0c73c010
Message text
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Impact
Cause
Recommended action
Configuration error---NVMCTRL_MEDIA_NOTREADY
Event code
0x0c784020
Message text
Configuration error---NVMCTRL_MEDIA_NOTREADY-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---NVMCTRL_MEDIA_NOTREADY-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
The DCPMM firmware medium is not ready.
Recommended action
Configuration error---The DDR-T memory modules of the unexpected model are installed
Event code
0x0c7ed0c0
Message text
Configuration error---The DDR-T memory modules of the unexpected model are installed-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The DDR-T memory modules of the unexpected model are installed-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory configuration is incorrect. The DCPMMs are incompatible with the server.
Recommended action
Configuration error---Failed to set the VDD voltage of the DIMM
Event code
0x0c7f0010
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
Memory configuration is incorrect. Failed to set the DIMM VDD voltage.
Recommended action
2.     Replace the system board.
Configuration error---Too many RIR rules
Event code
0x0c7f9010
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
Memory configuration is incorrect. Too many RIR rules.
Recommended action
1.     Upgrade the BIOS to the latest version.
2.     Verify that the DIMMs and processors are installed correctly according to the user guide for the server.
3.     Access the BIOS setup utility and verify that the memory interleaving and NUMA settings are correct.
4.     If the issue persists, contact Technical Support.
Configuration error---The DIMMs for the CPU exceeded the limit
Event code
0x0c7fa010
Message text
Configuration error---The DIMMs for the CPU exceeded the limit-Location:CPU:$1 CH:$2 DIMM:$3 Rank:$4
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: Rank number.
Severity level
Minor
Example
Configuration error---The DIMMs for the CPU exceeded the limit-Location:CPU:1 CH:2 DIMM:A0 Rank:0
Impact
Cause
Memory configuration is incorrect. The DIMMs for the processor exceeded the limit.
Recommended action
1.     Verify that the memory configuration is supported by the processor specifications.
Drive slot
Drive Presence
Event code
0x0d0000df
Message text
Drive Presence --- $1: $2, HDD Slot: $3.
Variable fields
$1: Drive bay slot in HDD bay deployment or JBOD slot in a cabinet server.
$2:
¡     When $1 is a drive bay slot, this parameter represents the drive bay slot number, which can be 1, 2, 5, 6, 9, 10, 13, or 14.
¡     When $1 is a JBOD slot, this parameter represents the JBOD slot number in the range of 1 to 8.
$3:
¡     When $1 is a drive bay slot, this parameter represents the drive identifier in the range of 0 to 39.
¡     When $1 is a JBOD slot, this parameter represents the drive slot number in the range of 0 to 22.
Severity level
Info
Example
Drive Presence --- Bay Slot: 1, HDD Slot: 2
Impact
The drive presence changed.
Cause
Recommended action
No action is required.
Drive Fault
Event code
0x0d1000de
Message text
Drive Fault --- $1: $2, HDD Slot: $3
Variable fields
$2:
$3:
Severity level
Major
Example
Drive Fault --- Bay Slot: 1, HDD Slot: 2
Impact
Data loss might occur due to the drive fault.
Cause
The drive was faulty.
Recommended action
1.     Log in to HDM, view drive information, and verify that all drives in the logical drive are identified correctly. If a drive cannot be identified, re-install the drive. If the drive cannot be identified after re-installation, replace the drive.
2.     View drive information and verify that the status of the drive is Unconfigured Good.
3.     View drive information and verify that the drive can be identified and is normal, and the drive number on HDM is consistent with the drive number in the message. If the drive number on HDM is different from the drive number in the message, verify that the drive cables are connected correctly.
4.     If multiple drives are absent, examine if the data cables and RAID controllers are faulty. If multiple drives are in place but not displayed, examine if the signal cables and the drive backplane are faulty.
5.     Verify that drive LEDs are normal, and the drive can be identified and is accessible in the OS. If a drive LED is orange, the drive is faulty. Replace the faulty components, if any.
6.     Verify that the storage controller is in normal state.
7.     If the issue persists, contact Technical Support.
Predictive Failure
Event code
0x0d2000de
Message text
Predictive Failure---Bay Slot: $1, HDD Slot: $2
Variable fields
$1: Bay slot number, which can be 1, 2, 5, 6, 9, 10, 13, or 14.
$2: Drive identifier in the range of 0 to 39.
Severity level
Minor
Example
Predictive Failure---Bay Slot: 1, HDD Slot: 2
Impact
The decrease in drive reliability might affect the operating system's storage performance and service operations.
Cause
The RAID controller reports a predictive failure, which can be a storage medium reserved block alarm, drive lifetime alarm, Prefail alarm, or bad sector alarm.
Recommended action
1.     Log in to HDM to verify that the drive is in normal state.
2.     Replace the drive.
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold
Event code
0x0d4000de
Message text
Linux:
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold---OS:Linux/Unix,See disk details about Logical disk name, Threshold $1: ---Current usage $2
Windows:
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold---OS:Windows, Logical disk $1:---Current usage $2
Variable fields
Linux:
·     $1: Drive space usage threshold.
·     $2: Current drive space usage.
Windows:
·     $1: Drive letter.
Severity level
Info
Example
Linux:
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold --OS:Linux/Unix,See disk details about Logical disk name, Threshold 75%: ---Current usage 80%
Windows:
Consistency Check / Parity Check in progress. System Source Monitor: Hard Disk usage exceeds the threshold ---OS:Windows, Logical disk d: ---Current usage 80%
Impact
A high usage will result in decreased performance, task backlog, decreased system stability, and data loss or corruption.
Cause
Drive usage exceeded the threshold.
You can configure the processor usage, memory usage, and drive usage thresholds from HDM. During operation, FIST SMS obtains system resource usage information, and sends the information to HDM through IPMI commands. HDM generates this message if a threshold is exceeded.
Recommended action
1.     Use the HDM system resource monitoring feature to monitor the drive usage. If the usage is abnormal, contact Technical Support.
2.     If the drive usage is normally high, back up data and expand the drive capacity.
Consistency Check / Parity Check in progress. System Source Monitor: Relieve resource alarm about Hard Disk Usage
Event code
0x0d4000df
Message text
Linux:
Consistency Check / Parity Check in progress. System Source Monitor: System Source Monitor: Relieve resource alarm about Hard Disk Usage ---OS:Linux/Unix,See disk details about Logical disk name, Threshold $1: ---Current usage $2
Windows:
Consistency Check / Parity Check in progress. System Source Monitor: System Source Monitor: Relieve resource alarm about Hard Disk Usage ---OS:Windows, Logical disk $1:---Current usage $2
Variable fields
Linux:
Windows:
·     $1: Drive letter.
Severity level
Info
Example
Linux:
Consistency Check / Parity Check in progress. System Source Monitor: Relieve resource alarm about Hard Disk Usage ---OS:Linux/Unix,See disk details about Logical disk name, Threshold 80%: ---Current usage 75%
Windows:
Consistency Check / Parity Check in progress. System Source Monitor: Relieve resource alarm about Hard Disk Usage ---OS:Windows, Logical disk d: ---Current usage 80%
Impact
Performance decrease, system crashes, data corruption, and security issues might occur.
Cause
This message is generated when the system resource usage drops below the alarm threshold. This is an alarm removal log for event 0x0d4000de.
Recommended action
In Critical Array
Event code
0x0d5000de
Message text
In Critical Array---$1:$2$3 :$4.
Variable fields
$1: Drive bay slot or PCIe slot.
$2: When $1 is a drive bay slot, this parameter represents the drive bay slot number, which can be 1, 2, 5, 6, 9, 10, 13, or 14. When $1 is a PCIe slot, this parameter represents the slot number of the storage controller that manages the logical drive.
$3: HDD slot or LDDevno.
$4: When $3 represents HDD slot, this parameter represents the drive identifier in the range of 0 to 39. When $3 represents LDDevno, this parameter represents the logical drive number.
Severity level
Major
Example
In Critical Array---PCIe slot:1---LDDevno :2
Impact
The RAID array is degraded, which will affect data reliability.
Cause
A drive in a logical drive was removed or failed and the logical drive degraded.
Recommended action
1.     Verify that the drive is not removed. If the drive is removed, re-install the drive and recreate the RAID array.
2.     Log in to HDM, view drive information, and verify that all drives in the logical drive are identified correctly. If a drive cannot be identified, re-install the drive. If the drive cannot be identified after re-installation, replace the drive.
3.     Log in to HDM, view drive information, and verify that the status of the drive is Unconfigured Good.
4.     After the drive is identified correctly, recreate the RAID array.
5.     If the issue persists, contact Technical Support.
In Failed Array
Event code
0x0d6000de
Message text
In Failed Array---$1:$2$3 :$4.
Variable fields
$2: When $1 is a drive bay slot, this parameter represents the drive bay slot number. When $1 is a PCIe slot, this parameter represents the slot number of the storage controller that manages the logical drive.
$4: When $3 represents HDD slot, this parameter represents the drive identifier. When $3 represents LDDevno, this parameter represents the logical drive number.
Severity level
Major
Example
In Failed Array---PCIe slot:1---LDDevno :2
Impact
The RAID array becomes invalid, which causes the loss of the offline data.
Cause
A drive in a logical drive was removed or failed and the logical drive was totally corrupted.
Recommended action
4.     After the drive is identified correctly, verify that the RAID array is normal. If the RAID array is faulty, recreate the RAID array.
Rebuild/Remap in progress
Event code
0x0d7000de
Message text
Rebuild/Remap in progress---Bay Slot: $1, HDD Slot: $2.
Variable fields
$1: Drive bay number, including 1, 2, 5, 6, 9, 10, 13, and 14.
$2: Drive number on a drive bay in the range of 0 to 39.
Severity level
Info
Example
Rebuild/Remap in progress---Bay Slot: 1, HDD Slot: 2
Impact
No negative impact.
Cause
The message is generated when a drive is installed during RAID rebuilding.
Recommended action
The disk triggered a media error
Event code
0x0da000de
Message text
The disk triggered a media error--$1.
Variable fields
$1: Drive location.
Severity level
Info
Example
The disk triggered an media error--Front 1
Impact
Data loss might occur due the occurrence of media errors on the storage media.
Cause
The number of media errors exceeded the threshold.
Recommended action
1.     Upgrade the firmware of the drive.
The disk triggered an uncorrectable error
Event code
0x0db000de
Message text
The disk triggered an uncorrectable error--$1.
Variable fields
$1: Drive location.
Severity level
Minor
Example
The disk triggered an uncorrectable error--Front 1
Impact
Data loss might occur due the occurrence of uncorrectable errors on the storage media.
Cause
The number of uncorrectable errors exceeded the threshold.
Recommended action
The disk is missing
Event code
0x0dc000de
Message text
The disk is missing.
Variable fields
N/A
Severity level
Major
Example
The disk is missing
Impact
The reliability of the storage system might be affected due to the removal or incorrect installation of a drive.
Cause
This message is generated when the storage system fails to identify this drive or a cable connection error occurs.
Recommended action
2.     Verify that the drive data cables, power cords, and signal cables are connected correctly.
3.     Re-install the drive.
4.     Replace the drive.
5.     Verify that the storage controller is in normal state.
System firmware Progress
System Firmware Error (POST Error)---CPU matching failure
Event code
0x0f0000de
Message text
System Firmware Error (POST Error)---CPU matching failure.
Variable fields
N/A
Severity level
Major
Example
Impact
The system might fail to start up correctly. The system might fail to start up correctly.
Cause
The BIOS detected a CPU frequency, microcode, or UPI matching error at POST.
Recommended action
1.     Verify that the processors are installed correctly as required in the user guide for the server.
2.     Verify that the CPUs have the same model.
System Firmware Error (POST Error)---Firmware (BIOS) ROM corruption detected
Event code
0x0f0000de
Message text
System Firmware Error (POST Error)---Firmware (BIOS) ROM corruption detected.
Variable fields
N/A
Severity level
Major
Example
Impact
The system cannot start up correctly.
Cause
The BIOS detected ROM corruption at POST. The BIOS firmware is damaged when this message is generated.
Recommended action
1.     Upgrade the BIOS firmware.
2.     Upgrade the BIOS with the factory defaults (if any) or default settings of the BIOS restored.
System Firmware Error (POST Error)---Load microcode failed
Event code
0x0f0000de
Message text
System Firmware Error (POST Error)---Load microcode failed.
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
The BIOS detected errors at POST because CPU microcode failed to be loaded, but the system did not hang.
Recommended action
1.     Power off and then power on the server.
2.     Upgrade HDM and the BIOS firmware to the latest version.
System Firmware Error (POST Error)---No system memory or invalid memory configuration
Event code
0x0f0000de
Message text
System Firmware Error (POST Error)---No system memory or invalid memory configuration.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
No DIMM was detected during BIOS startup. This symptom might occur if DIMMs are installed incorrectly.
Recommended action
1.     Verify that the DIMMs are installed correctly as required in the user guide of the server. Re-install all DIMMs if needed.
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image is unsigned or Certificate is invalid
Event code
0x0f0000de
Message text
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image is unsigned or Certificate is invalid.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
Recommended action
1.     Verify if the BIOS boot mode meets the requirements of secure boot. If not, change the boot mode to UEFI.
2.     Verify that the BIOS firmware is upgraded successfully.
3.     Upgrade the BIOS with the factory defaults (if any) or default settings of the BIOS restored.
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate not found in Authorized database(db)
Event code
0x0f0000de
Message text
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate not found in Authorized database(db).
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
Recommended action
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate is found in Forbidden database(dbx)
Event code
0x0f0000de
Message text
System firmware error (POST error)---Firmware (BIOS) ROM corruption detected:Image Certificate is found in Forbidden database(dbx).
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
Recommended action
System Firmware Error (POST Error)---Memory Population Rule Error
Event code
0x0f002170
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
The system might fail to start correctly, or the system performance might decrease.
Cause
DIMM Faulty Parts Tracking error occurred because of incorrect DIMM population.
Recommended action
1.     Verify that DIMMs are installed correctly base on the user guide of the server. Re-install the DIMMs if needed.
System firmware error (POST error)---DIMM installation or compatibility error occurred
Event code
0x0f003070
Message text
System firmware error (POST error)---DIMM installation or compatibility error occurred.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
DIMMs were installed incorrectly.
Recommended action
1.     Log in to HDM, access the Memory page, and verify that the no faulty DIMMs exist.
2.     Verify that DIMMs are installed correctly as required in the user guide for the server.
3.     Verify that a minimum of one DIMM operates correctly for each processor.
System firmware error (POST error)---No Memory Usable
Event code
0x0f003e80
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
No memory was available.
Recommended action
1.     Verify that the DIMM s are installed as required in the user guide for the server.
2.     Upgrade the BIOS and HDM firmware to the latest version.
3.     Power off the server, reconnect all power cords, and then power on the server. Make sure the server is completely powered off before powering on the server.
4.     Re-install the DIMM. Verify that the gold contacts on the DIMM are not contaminated and the DIMM slot does not contain any foreign objects.
5.     Replace the DIMM, and then restart the server.
6.     If the issue persists, contact Technical Support.
System firmware error (POST error)---No DDR Memory Error
Event code
0x0f0082a0
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
No DDR memory module was available.
Recommended action
1.     Verify that the DIMMs are installed as required in the user guide for the server.
4.     Re-install the DIMM correctly. Verify that the gold contacts on the DIMM are not contaminated and the DIMM slot does not contain any foreign objects.
System firmware error (POST error)---DIMM Compatible Error(LRDIMM and RDIMM are installed)
Event code
0x0f00bed0
Message text
Variable fields
N/A
Severity level
Major
Example
System Firmware Error (POST Error)---DIMM Compatible Error(LRDIMM and RDIMM are installed)
Impact
Cause
Both LRDIMM and RDIMM DIMMs are installed on the same server.
Recommended action
2.     Install DIMMs as required in the user guide for the server.
System Firmware Error (POST Error)---No DIMMs present
Event code
0x0f02a010
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
No DIMM is available for the G5 server.
Recommended action
1.     Verify that the DIMMs are installed correctly as required in the user guide for the server.
System Firmware Error (POST Error)---No DDR memory in the system
Event code
0x0f02a040
Message text
Variable fields
N/A
Severity level
Major
Example
Cause
No DDR memory module is available for the G5 server.
Impact
Recommended action
1.     Verify that the DIMM is installed correctly as required in the user guide for the server.
System Firmware Error (POST Error)---No DIMM is available for memory-mapping operation
Event code
0x0f0e8020
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
The system performance might decrease.
Cause
No DIMMs is available for memory mapping.
Recommended action
1.     Log in to HDM, access the Memory page, and verify that available DIMMs exist.
System Firmware Error (POST Error)---Different DIMM types detected
Event code
0x0f0ed010
Message text
System Firmware Error (POST Error)---Different DIMM types detected.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
Different DIMM types were detected.
Recommended action
1.     Log in to HDM, access the Event Log page, and identify the slot of the faulty DIMM.
2.     Access the component compatibility query tool at http://www.h3c.com/cn/Service/Document_Software/Document_Center/Server/ and verify that the DIMMs are compatible with the server.
3.     Use the memory configuration query tool on the website accessed at step 2 to verify that the DIMMs are correctly installed.
4.     Re-install the DIMMs as required in the user guide for the server.
System Firmware Error (POST Error)---DIMM population error
Event code
0x0f0ed020
Message text
System Firmware Error (POST Error)---DIMM population error.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A memory compatibility error occurs.
Recommended action
1.     Log in to HDM, access the Event Log page, and identify the slot of the faulty DIMM slot.
2.     Re-install the DIMMs as required in the user guide for the server.
System Firmware Error (POST Error)---A maximum of two quad-rank DIMMs can be populated per channel
Event code
0x0f0ed030
Message text
System Firmware Error (POST Error)---A maximum of two quad-rank DIMMs can be populated per channel.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. You can install a maximum of two quad-rank DIMMs per channel.
Recommended action
1.     Re-install the DIMMs as required in the user guide for the server.
System Firmware Error (POST Error)---The third DIMM slot with green release tabs does not support UDIMMs or SODIMMs
Event code
0x0f0ed040
Message text
System Firmware Error (POST Error)---The third DIMM slot with green release tabs does not support UDIMMs or SODIMMs.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. The third DIMM slot does not support UDIMMs or SODIMMs.
Recommended action
1.     Access the component compatibility query tool at http://www.h3c.com/cn/Service/Document_Software/Document_Center/Server/ to identify DIMMs compatible with the server. Replace the UDIMMs or SODIMMs with compatible DIMMs.
System Firmware Error (POST Error)---DIMM voltage error
Event code
0x0f0ed050
Message text
System Firmware Error (POST Error)---DIMM voltage error.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. A DIMM voltage fault is present.
Recommended action
1.     Log in to HDM, access the Event Log page, and identify the slot of the faulty DIMM. Cross-validate the DIMM with other DIMMs. If the issue persists, replace the system board because the error is caused by a faulty memory slot. If the issue does not re-occur, replace the faulty DIMM.
System Firmware Error (POST Error)---DDR3 and DDR4 DIMMs cannot be mixed
Event code
0x0f0ed060
Message text
System Firmware Error (POST Error)---DDR3 and DDR4 DIMMs cannot be mixed.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. You cannot install both DDR3 DIMMs and DDR4 DIMMs on the same server.
Recommended action
1.     Replace the DDR3 DIMMs or DDR4 DIMMs to make sure DIMMs installed on the server are of the same type.
System Firmware Error (POST Error)---256-byte and 512-byte SPD devices cannot be mixed
Event code
0x0f0ed070
Message text
System Firmware Error (POST Error)---256-byte and 512-byte SPD devices cannot be mixed.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. You cannot use both 256-byte and 512-byte SPD devices at the same time.
Recommended action
1.     Replace the 256-byte or 512-byte SPD devices to make sure devices installed on the server are of the same type.
System Firmware Error (POST Error)---3DS and non-3DS LRDIMMs cannot be mixed
Event code
0x0f0ed080
Message text
System Firmware Error (POST Error)---3DS and non-3DS LRDIMMs cannot be mixed.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. You cannot use both 3DS and non-3DS LRDIMMs on the same server.
Recommended action
1.     Replace the 3DS or non-3DS LRDIMMs to make sure DIMMs installed on the server are of the same type.
System Firmware Error (POST Error)---DDR-T memory modules and UDIMMs cannot be mixed
Event code
0x0f0ed0b0
Message text
System Firmware Error (POST Error)---DDR-T memory modules and UDIMMs cannot be mixed.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
A system firmware error (POST error) occurred. You cannot use both DDR-T DIMMs and UDIMMs on the same server.
Recommended action
1.     Replace the DDR-T DIMMs or UDIMMs to make sure DIMMs installed on the server are of the same type.
System Firmware Error (POST Error)---Memory Unrecognized Initialization Error
Event code
0x0f0ffff0
Message text
System Firmware Error (POST Error)---Memory Unrecognized Initialization Error.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
An initialization error was detected on the initialization of some memory modules.
Recommended action
1.     Resolve the issue as instructed by the log reported simultaneously for the component.
System Firmware Hang---Unspecified
Event code
0x0f1000de
Message text
System Firmware Hang---Unspecified.
Variable fields
N/A
Severity level
Major
Example
Impact
The system cannot operate correctly.
Cause
The BIOS hangs during startup.
Recommended action
1.     Resolve the issue based on other event logs reported simultaneously for the component.
System firmware hang-----No DDR Memory Error
Event code
0x0f103e80
Message text
System firmware hang-----No DDR Memory Error.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
The operating system hanged because no DDR DIMMs were available.
Recommended action
1.     Make sure the device is installed with DDR DIMMs as required in the user guide for the server.
4.     Re-install the DIMMs. Make sure that the golden plating is not contaminated, no foreign objects are in the memory slots, and the memory installation complies with the requirements.
5.     Replace the DIMMs and power cycle the server again.
System firmware hang---DIMM Compatible Error(LRDIMM and RDIMM are installed)
Event code
0x0f10bed0
Message text
System firmware hang---DIMM Compatible Error(LRDIMM and RDIMM are installed).
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
Both LRDIMMs and RDIMMs are installed on the device.
Recommended action
3.     If the server persists, contact Technical Support.
System firmware hang---Memory Unrecognized Initialization Error
Event code
0x0f1ffff0
Message text
System firmware hang---Memory Unrecognized Initialization Error.
Variable fields
N/A
Severity level
Critical
Example
Impact
Cause
A memory initialization error occurred. An error occurs on the DIMMs for the primary CPU. Then, no DIMMs are available for the primary CPU, which causes system hanging.
Recommended action
1.     Resolve the issue as instructed by the logs reported simultaneously for the component.
System Firmware Progress---Current Memory Ras Mode
Event code
0x0f20eff0
Message text
System Firmware Progress---Current Memory Ras Mode.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The memory is in RAS mode.
Recommended action
System Firmware Error (POST Error)--- Memory population enforcement mismatch, Please check the DIMM symmetry on the socket
Event code
0x0f017130
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
Cause
The DIMMs are installed incorrectly.
Recommended action
System Firmware Error (POST Error)---No DIMMs installed for CPU
Event code
0x0f017180
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
No DIMM is installed.
Recommended action
1.     Verify that DIMMs are installed correctly as required in the user guide for the server.
Event Logging Disabled
Log Area Reset/Cleared
Event code
0x102000de
Message text
Log Area Reset/Cleared.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
This message is displayed if all event logs are cleared.
Recommended action
SEL Full
Event code
0x104000de
Message text
SEL Full.
Variable fields
N/A
Severity level
Minor
Example
SEL Full.
Impact
The system cannot continue recording event logs.
Cause
This message might be displayed if one of the following occurs:
·     The event log reaches its maximum size. The system stops logging new events, and the old logs might be overwritten.
·     A user disables event logging.
Recommended action
Log in to HDM, enter the Event Log page, and clear all event logs.
SEL Almost Full
Event code
0x105000de
Message text
SEL Almost Full.
Variable fields
N/A
Severity level
Minor
Example
SEL Almost Full.
Impact
No negative impact,
Cause
The log file is reaching its maximum size.
Recommended action
Watchdog1
BIOS Watchdog Reset
Event code
0x110000de
Message text
BIOS Watchdog Reset.
Variable fields
N/A
Severity level
Major
Example
Impact
The system restarts.
Cause
This message is displayed if one of the following occurs:
·     The BIOS startup time exceeds the threshold.
·     The BIOS gets stuck during startup.
Recommended action
1.     Verify that the BIOS is operating correctly:
a.     Verify that the peripheral modules operate correctly and the BIOS settings are configured correctly.
b.     Verify that the BIOS debug mode is disabled.
OS Watchdog NMI/Diagnostic Interrupt
Event code
0x115000de
Message text
OS Watchdog NMI/Diagnostic Interrupt.
Variable fields
N/A
Severity level
Major
Example
Impact
If this message is manually triggered, the system might fail to start up correctly.
Cause
Non-Maskable Interrupt (NMI) was triggered after OS Watchdog is enabled.
Recommended action
1.     Verify that the service software is operating correctly.
2.     Disable the watchdog from the BIOS. Access the BIOS setup utility, and set OS Watchdog Timer to Disabled.
OS Watchdog pre-timeout Interrupt-non-NMI
Event code
0x117000de
Message text
OS Watchdog pre-timeout Interrupt-non-NMI.
Variable fields
N/A
Severity level
Major
Example
Impact
Cause
The OS failed to start up after a long time, and non-NMI was triggered by OS watchdog pre-timeout.
Recommended action
1.     Check the boot options for exceptions, and fix the OS boot environment if any exception is detected.
System Event
Timestamp Clock Synch---event is $1 of pair---SEL Timestamp Clock updated
Event code
0x125000de
Message text
Timestamp Clock Synch---event is $1 of pair---SEL Timestamp Clock updated.
Variable fields
$1: Options include:
·     first—Pre-synchronization event.
·     second—Post-synchronization event.
Severity level
Info
Example
Timestamp Clock Synch---event is first of pair---SEL Timestamp Clock updated.
Impact
No negative impact,
Cause
HDM synchronizes the time with the server each time the server is powered up. The first event is triggered before the synchronization, and the second event is triggered after the synchronization.
Recommended action
Timestamp clock synch---BMC Time SYNC succeed
Event code
0x125000de
Message text
Timestamp Clock Synch---BMC Time SYNC succeed.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact,
Cause
BMC synchronized its time with the ME successfully.
Recommended action
Critical Interrupt
Transition to Non-Critical from OK
Event code
0x1300000e
Message text
Transition to Non-Critical from OK--- Single-bit ECC error---PCIe slot:$1
Variable fields
$1: Slot number.
Severity level
Major
Example
Transition to Non-Critical from OK--- Single-bit ECC error---PCIe slot: 2
Impact
An error occurred during the access to a PCIe module. This has no negative impact on the system operation.
Cause
The PCIe module in the slot is faulty.
Recommended action
This message is generated when an error is detected by PCIe hardware check. Review the related event log messages and replace the faulty PCIe module or contact Technical Support.
PCI: PCIE Hot Plug PCIe Pull Out
Event code
0x13000010
Message text
PCI: PCIE Hot Plug PCIe Pull Out---Slot number $1.
Variable fields
$1: Slot number.
Severity level
Info
Example
PCI: PCIE Hot Plug PCIe Pull Out---Slot number 34.
Impact
No negative impact.
Cause
A PCIe module was removed from the riser card on the operating server.
This message is available only for an R8900 G3 server.
Recommended action
1.     Verify that the removal operation has been performed.
2.     If the PCIe module is not removed, ensure secure installation of the module.
PCI: PCIE Hot Plug PCIe Insert
Event code
0x13100010
Message text
PCI: PCIE Hot Plug PCIe Insert---Slot number $1.
Variable fields
$1: Slot number
Severity level
Info
Example
PCI: PCIE Hot Plug PCIe Insert---Slot number 34.
Impact
No negative impact,
Cause
A PCIe module was inserted into the riser card on the operating server.
Recommended action
1.     Verify that the insert operation has been performed.
2.     Ensure secure installation of the module.
PCI SERR
Event code
0x135000de
Message text
PCI SERR ------Slot $1---PCIE Name: $2.
Variable fields
$1: PCIe device slot number.
$2: PCIe device name.
Severity level
Major
Example
PCI SERR ------Slot 5---PCIE Name: EF-I20.
Impact
The system might crash.
Cause
An uncorrectable error occurred on the PCIe device.
Recommended action
1.     If the message is reported serval times during a period of time, ensure that the riser card is securely connected to the system board.
2.     Reboot the server.
3.     Locate the PCIe device based on the slot number.
4.     If the PCIe device is a removable component, perform the following actions:
a.     Verify that the PCIe device is installed correctly.
b.     Verify that the golden plating on the PCIe device is not contaminated.
c.     Install the PCIe device into another slot to verify whether the error is present on the PCIe device or the slot.
d.     If the error occurs on the PCIe device, upgrade firmware and drivers of the PCIe device.
e.     If the error occurs on the slot, verify that the gold plating on the riser card is not contaminated.
f.     Replace the PCIe device.
5.     If the PCIe device is embedded on the system board, perform the following actions:
a.     Update the BIOS, firmware, and drivers.
b.     Replace the system board.
Bus Uncorrectable Error
Event code
0x138000de
Message text
Bus Uncorrectable Error ---Slot $1---PCIE Name:$2.
Variable fields
Severity level
Major
Example
Bus Uncorrectable Error---Slot 3---PCIE Name: RAID-LSI-9361-8i.
Impact
An error occurred on a PCIe device. If the error is severe, it might become an error at the host system level.
Cause
An internal uncorrectable error occurred on the PCIe device.
Recommended action
1.     If the message is reported serval times during a period of time, ensure that the server components such as riser cards are securely connected to the system board.
e.     If the error occurs on the slot, verify that the gold plating on the riser card or other components is not contaminated.
f.     Verify that the server component where the PCIe device is installed is normal.
g.     Replace the PCIe device.
6.     If multiple GPU modules or multiple network adapters in the network adapter cage encounter errors, replace the SW module or system board.
Bus Fatal Error
Event code
0x13a000de
Message text
Bus Fatal Error ------Slot $1---PCIE Name: $2.
Variable fields
Severity level
Major
Example
Bus Fatal Error---Slot 3---PCIE Name: RAID-LSI-9361-8i.
Impact
An access error occurred on a PCIe device. If the error is severe, it might become an error at the host system level.
Cause
An internal fatal error occurred on the PCIe device.
Recommended action
2.     Reboot the server and verify that the message is not generated again.
3.     Locate the failed PCIe device based on the slot number.
4.     If the PCIe device is removable, perform the following actions:
b.     Verify that the gold plating on the PCIe device is not contaminated.
c.     Install the PCIe device into another slot to determine whether the error is present on the PCIe device or the slot.
e.     If the error occurs on the slot, verify that the gold plating on the riser card or components is not contaminated.
Button/Switch
Power Button pressed---Physical button---Button pressed
Event code
0x140000de
Message text
Power Button pressed---Physical button---Button pressed.
Variable fields
N/A
Severity level
Info
Example
Impact
The system is powered on and powered off.
Cause
This message is displayed if the power button on the front panel of the server is pressed.
Recommended action
Power Button pressed---Physical button---Button released
Event code
0x140000de
Message text
Power Button pressed---Physical button---Button released.
Variable fields
N/A
Severity level
Info
Example
Impact
Cause
This message is displayed if the power button on the front panel of the server is released.
Recommended action
Power Button pressed---Virtual button---Power cycle command
Event code
0x140000de
Message text
Power Button pressed---Virtual button---Power cycle command.
Variable fields
N/A
Severity level
Info
Example
Impact
The server restarts.
Cause
This message is displayed if a power-cycle operation (Force System Cycle) is performed from HDM or a KVM console.
Recommended action
Power Button pressed---Virtual button---Power off command
Event code
0x140000de
Message text
Power Button pressed---Virtual button---Power off command.
Variable fields
N/A
Severity level
Info
Example
Impact
The server is powered off.
Cause
This message is generated when you press the physical power button on the front panel of the server or execute commands to forcedly power off the server, gracefully power off the server, or power cycle the server.
Recommended action
Power Button pressed---Virtual button---Power on command
Event code
0x140000de
Message text
Power Button pressed---Virtual button---Power on command.
Variable fields
N/A
Severity level
Info
Example
Impact
The server is powered on.
Cause
Recommended action
Power Button pressed---Virtual button---Soft off command
Event code
0x140000de
Message text
Power Button pressed---Virtual button---Soft off command.
Variable fields
N/A
Severity level
Info
Example
Impact
Cause
Recommended action
Reset Button pressed---Virtual button---Reset command
Event code
0x142000de
Message text
Reset Button pressed---Virtual button---Reset command.
Variable fields
N/A
Severity level
Info
Example
Impact
Cause
This message is generated when one of the conditions is met:
·     The reset command was executed.
·     An IERR error occurred.
Recommended action
1.     Verify that the reset command was executed. If the command was executed, no action is required.
2.     Check whether an IERR error occurred.
FRU service request button---Physical button---Uid button pressed
Event code
0x144000de
Message text
FRU service request button---Physical button---Uid button pressed.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
This message is displayed if the UID button is pressed.
Recommended action
Module/Board
Transition to Critical from less severe
Event code
0x1520000e
Message text
Transition to Critical from less severe.
Variable fields
N/A
Severity level
Major
Example
Impact
An access error occurred on a PCIe BUS0 device, If the error is severe, it might become an error at the primary system-level error.
Cause
An internal uncorrectable error occurs on a PCIe BUS0 device.
Recommended action
1.     Verify that the system power is being supplied correctly.
2.     Replace the component to verify if the component is faulty.
Transition to Non-Recoverable from less severe
Event code
0x1530000e
Message text
Transition to Non-recoverable from less severe---System detected a power supply failure on $1($2).
Variable fields
$1: Component, such as Motherboard, PDB, CMOD, and riser card.
$2: Fault location, such as P5V, P5V_STBY, CPU1_PVCSA, and CPU2_PVCCIO.
Severity level
Critical
Example
Transition to Non-recoverable from less severe---System detected a power supply failure on Motherboard(P5V).
Impact
The system might be powered off.
Cause
The voltage inside the card is abnormal.
Recommended action
1.     Ignore this message if it is triggered by a system power-on or power-off event.
2.     Reconnect power cords and verify whether the server can be powered on correctly.
¡     If the server can be powered on, the message might be generated because the detection signals were interfered. No action is required.
¡     If the server cannot be powered on, review the SDS logs to locate the fault and replace the faulty component.
3.     If the error occurs again, replace the component.
Monitor---Board found PSU output can't be enabled
Event code
0x1570000e
Message text
Monitor---Board found PSU output can't be enabled($1)
Variable fields
$1: Faulty module.
Severity level
Major
Example
Monitor---Board found PSU output can't be enabled(PSU2)
Impact
Cause
This message is generated when the power supply fails to provide power to the
System board.
Recommended action
1.     Verify that the power supply LED is normal.
¡     If the LED is abnormal, replace the power supply.
¡     If the LED is normal, install the power supply to another normal slot to identify whether the power supply is operating correctly. If the issue persists, replace the system board because the error is caused by a faulty slot. If the issue does not re-occur, verify that the power supply is installed correctly. If the power supply has been installed correctly, replace the power supply.
Add-in Card
Transition to OK
Event code
0x1700000e
Message text
Transition to OK---PCIe slot: $1---LDDevno:$2.
Variable fields
$1: Slot number of the storage controller.
$2: Logical drive number.
Severity level
Info
Example
Transition to OK---PCIe slot:1---LDDevno:0.
Impact
No negative impact.
Cause
This message is generated if the logical drive managed by the storage controller changes from abnormal to normal.
Recommended action
Event code
0x1720000e
Message text
Transition to Critical from less severe---PCIe slot: $1---LDDevno:$2
Variable fields
Severity level
Major
Example
Transition to Critical from less severe---PCIe slot: 1---LDDevno:0
Impact
Cause
This message is generated when the logical drive managed by the storage controller is degraded or faulty, or the backplane power is faulty.
Recommended action
1.     Log in to HDM to verify whether the logical drive is degraded or faulty.
2.     If the logical drive is degraded, perform the following actions:
¡     Verify that all member drives in the logical drives are operating correctly.
¡     Re-install member drives to verify whether the drives can be correctly identified.
¡     Access the BIOS to verify whether all member drives have been configured correctly.
¡     Check the error logs for the drives.
¡     Replace the faulty drives.
¡     If the issue persists, contact Technical Support.
3.     If the logical drive is faulty, perform the following tasks:
¡     Verify that the drive has not been uninstalled.
¡     Re-install the member drives and rebuild the RAID.
¡     Replace the faulty drives and then restart the server.
Chassis
Transition to OK
Event code
0x1800000e
Message text
Transition to OK.
Variable fields
N/A
Severity level
Info
Example
Transition to OK.
Impact
No negative impact.
Cause
The chassis status changed from abnormal to normal.
Recommended action
If the event code is 0x1800000e, no action is required.
If the event code is 0x1800000f, perform the following operations:
1.     Review the logs to identify the failure reason and examine if any other component is faulty.
State asserted
Event code
0x18100006
Message text
State asserted.
Variable fields
N/A
Severity level
Major
Example
State asserted.
Impact
The impact depends on the component where the error occurs.
Cause
The system detected an error.
Recommended action
1.     Review the event log reported simultaneously for the component to correct the error.
Event code
0x1820000e
Message text
Variable fields
N/A
Severity level
Major
Example
Impact
If the error is severe, it will become a host system-level error.
Cause
The chassis status changed from less severe to critical.
Recommended action
1.     Verify that power is being supplied correctly.
2.     Review the other logs and examine whether a component is faulty.
Event code
0x1830000e
Message text
Transition to Non-recoverable from less severe.
Variable fields
N/A
Severity level
Major
Example
Impact
The system will be powered off.
Cause
The chassis state changed from less severe to non-recoverable.
Recommended action
System Boot/Restart Initiated
Initiated by power up
Event code
0x1d0000de
Message text
Initiated by power up---$1 reset by $2.
Variable fields
$1: System or module. Options include:
¡     BIOS.
¡     BMC.
$2: Reboot method. Options include:
·     Power up.
·     Power recycle.
·     Power reset.
Severity level
Info
Example
Initiated by power up---BIOS reset by power up.
Impact
No negative impact.
Cause
This alarm is triggered by system power-on.
The message content after "---" is displayed only for a server that has a BIOS_Boot_Up sensor.
Recommended action
1.     See related logs for more information.
Initiated by hard reset
Event code
0x1d1000de
Message text
Initiated by hard reset---$1 reset by $2.
Variable fields
¡     BIOS.
¡     BMC.
·     Power up.
·     Power recycle.
·     Power reset.
Severity level
Info
Example
Initiated by hard reset---BIOS reset by power reset.
Impact
No negative impact.
Cause
This alarm is triggered by system restart.
Recommended action
Initiated by warm reset
Event code
0x1d2000de
Message text
Initiated by warm reset---$1 reset by $2.
Variable fields
¡     BIOS.
¡     BMC.
·     Power up.
·     Power recycle.
·     Power reset.
Severity level
Info
Example
Initiated by warm reset---BIOS reset by power reset.
Impact
No negative impact.
Cause
This alarm is triggered by system warm restart.
Recommended action
System restart---due to fan error:power off
Event code
0x1d7000de
Message text
System restart---due to fan error:power off.
Variable fields
N/A
Severity level
Info
Example
System Restart---due to fan error:power off.
Impact
No negative impact.
Cause
The server was powered off because two or more fans at critical locations were absent or faulty.
Recommended action
1.     Verify that the air inlets and outlets of the server are not blocked
2.     Log in to HDM, access the Fan page, and verify that all fans are working correctly.
3.     Log in to HDM, access the Fan page, and verify that the fan speed is not too low. If the speed is low, adjust the fan speed mode or fan speed level as needed.
System Restart
Event code
0x1d7000de
Message text
System Restart---$1.
Variable fields
$1: Reason for the system restart. Possible options include:
·     Unknown cause.
·     Chassis control command—IPMI commands or power options from HDM.
·     Reset via pushbutton.
·     Power-up via power pushbutton.
·     Watchdog expiration.
·     AC lost.
Severity level
Info
Example
System Restart---Reset via pushbutton.
Impact
No negative impact.
Cause
The system restarted.
Recommended action
System Restart---due to fan error:power reset
Event code
0x1d7000de
Message text
System Restart---due to fan error:power reset.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The system was reset because two or more fans at critical locations were absent or faulty.
Recommended action
System Restart---due to fan error:power cycle
Event code
0x1d7000de
Message text
System Restart---due to fan error:power cycle.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The system was cold reset because two or more fans at critical locations were absent or faulty.
Recommended action
Boot Error
No bootable media
Event code
0x1e0000de
Message text
No bootable media.
Variable fields
N/A
Severity level
Info
Example
No bootable media.
Impact
No negative impact.
Cause
No bootable media was found.
Recommended action
1.     Specify an available boot device.
OS_BOOT
C: boot completed
Event code
0x1f1000de
Message text
C: boot completed.
Variable fields
N/A
Severity level
Info
Example
C: boot completed.
Impact
No negative impact.
Cause
The operating system booted from a hard drive. This event happens for most Windows OSs.
Recommended action
PXE boot completed
Event code
0x1f2000de
Message text
PXE boot completed.
Variable fields
N/A
Severity level
Info
Example
PXE boot completed.
Impact
No negative impact.
Cause
The operating system booted from a PXE boot device. This event happens for most Windows OSs.
Recommended action
OS Stop/Shutdown
Run-time Critical Stop
Event code
0x201000de
Message text
Run-time Critical Stop--$1.
Variable fields
$1: Reason for the OS crash. This field is optional.
Severity level
Critical
Example
Run-time Critical Stop--System Shut Down Cause by DFC Critical Warning.
Impact
The system crashes.
Cause
A critical error occurred during operating system operation, which caused system crash.
Recommended action
1.     Verify that the installed system, drivers, firmware, and software do not have bugs and are compatible with the server.
2.     Update the versions if bugs or compatibility issues exist.
3.     Verify that the installed hardware options are compatible with the server. For more information about component and server compatibility, access the component compatibility query tool at http://www.h3c.com/cn/Service/Document_Software/Document_Center/Server/.
OS Graceful Stop
Event code
0x202000de
Message text
OS Graceful Stop.
Variable fields
N/A
Severity level
Info
Example
OS Graceful Stop.
Impact
The system is powered off.
Cause
The Windows OS was forcedly stopped.
Recommended action
OS Graceful Shutdown
Event code
0x203000de
Message text
OS Graceful Shutdown.
Variable fields
N/A
Severity level
Info
Example
Impact
Cause
The Windows OS was shut down gracefully.
Recommended action
Slot/Connector
Device disabled: PCIe module information not obtained
Event code
0x21000012
Message text
Device disabled: PCIe module information not obtained---Slot $1.
Variable fields
$1: PCIe slot number.
Severity level
Minor
Example
Device Disabled: PCIe module information not obtained---Slot 1.
Impact
The system performance might decrease due to the failure of PCIe module identification.
Cause
The PCIe module is faulty.
Recommended action
1.     Verify that the server starts up with the minimum configuration. For more information, see H3C Servers Troubleshooting Guide.
2.     Verify that port is disabled in the BIOS.
3.     Verify that the PCIe module is compatible with the server.
4.     Verify that the PCIe module is installed correctly.
5.     Install the PCIe module into another slot to verify that the PCIe module is not faulty.
Event code
0x210000de
Message text
$1 triggered an uncorrectable error.
Variable fields
$1: PCIe module type.
Severity level
Major
Example
NIC triggered an uncorrectable error.
Impact
Cause
An IERR or MCERR error was triggered. The error was identified as a PCIe uncorrectable error by SHD.
Recommended action
1.     Use the slot number to locate the fault PCIe module.
2.     If the PCIe module is removable, perform the following tasks:
a.     Update the firmware and drivers for the PCIe module to the latest version.
b.     Verify that the PCIe module is installed correctly as required.
c.     Install the PCIe module into another slot to determine whether the error is present on the module or the slot.
3.     If the PCIe module is embedded on the system board, perform the following tasks:
a.     Update the BIOS firmware and drivers to the latest version.
triggered a correctable error
Event code
0x211000de
Message text
$1 triggered a correctable error.
Variable fields
Severity level
Minor
Example
NIC triggered a correctable error.
Impact
Cause
An IERR or MCERR error was triggered. The error was identified as a PCIe correctable error by SHD.
Recommended action
1.     Ignore this message if it is an occasional event.
2.     If the same message is generated repeatedly, use the slot number to locate the fault PCIe module.
3.     If the PCIe module is removable, perform the following tasks:
a.     Upgrade firmware and drivers for the PCIe module.
b.     Verify that the PCIe module is installed correctly.
4.     If the PCIe module is embedded on the system board:
a.     Update the BIOS firmware and drivers.
Slot/Connector Device installed/attached
Event code
0x212000de
Message text
Slot/Connector Device installed/attached.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
A module was installed.
Recommended action
Transition to on line
Event code
0x21300014
Message text
Transition to on line.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The shared network port is connected to the network.
Recommended action
Transition to off line
Event code
0x21300015
Message text
Transition to off line.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The shared network port lost network connection.
Recommended action
Verify that the network cable is removed from the shared network port. If the cable is still connected, contact Technical Support.
Event code
0x2110000e
Message text
Transition to Non-Critical from OK---Slot $1
Variable fields
$1: Slot number of the network adapter.
Severity level
Major
Example
Transition to Non-Critical from OK---Slot 6
Impact
The system performance might decrease due to an error on the PCIe module.
Cause
This message is generated when network adapter is disconnected unexpectedly.
Recommended action
1.     Verify that the network adapter is not faulty.
2.     Verify that the related links such as I2C or MCTP link are in correct status.
3.     If the issue persists, contact Technical Support.
System ACPI Power State
S0/G0 "working"
Event code
0x220000de
Message text
S0/G0 "working".
Variable fields
N/A
Severity level
Info
Example
S0/G0 "working".
Impact
No negative impact.
Cause
The system is operating correctly.
G(0-2) indicate the global states. S(0-5) indicate the sleep states.
In G0 state, applications can operate.
In S0 state, the system is operating correctly.
Recommended action
S5/G2 "soft-off"
Event code
0x225000de
Message text
S5/G2 "soft-off".
Variable fields
N/A
Severity level
Info
Example
S5/G2 "soft-off".
Impact
No negative impact.
Cause
The device is software shutdown. You cannot run applications or the operating system when the device is software shutdown. Software shutdown shuts down the entire operating system except the main power supply unit. Almost no power is consumed during software shutdown. The waking time will be longer to reboot the system after a soft shutdown.
Recommended action
LPC Reset occurred
Event code
0x22d000de
Message text
LPC Reset occurred.
Variable fields
N/A
Severity level
Info
Example
LPC Reset occurred.
Impact
No negative impact.
Cause
The server was reset.
This message is available only for servers that use Intel processors.
Recommended action
Watchdog2
Watchdog overflowAction:Timer expired
Event code
0x230000de
Message text
Watchdog overflow.Action:Timer expired - status only (no action and no interrupt)---interrupt type:$1---timer use at expiration:$2.
Variable fields
$1: Type of the interruption. Options include:
¡     none.
¡     SMI.
¡     NMI.
¡     Messaging Interrupt.
¡     unspecified.
$2: Type of the watchdog timer. Options include:
¡     reserved.
¡     BIOS FRB2.
¡     BIOS POST.
¡     OS Load.
¡     SMS OS.
¡     OEM.
¡     unspecified.
Severity level
Info
Example
Watchdog overflow.Action:Timer expired - status only (no action and no interrupt)---interrupt type:none---timer use at expiration:BIOS FRB2.
Impact
The system cannot start up.
Cause
This message is generated when the following conditions are met:
·     The watchdog is enabled in the BIOS.
·     The watchdog timer expires during the BIOS POST, OS Load, or OS operation.
·     The timeout action is set to no action.
Recommended action
1.     For a BIOS POST watchdog timeout, review the event logs to identify hardware errors or BIOS startup errors, and troubleshoot the errors as instructed in the logs.
2.     For an OS Load watchdog timeout, verify that no error is present in the system startup environment. If no error is present, proceed to step 5.
3.     For an OS Running watchdog timeout, review the OS logs to verify if software exceptions occurred and troubleshoot the exceptions as instructed in the logs.
4.     Verify whether data storms have occurred. If yes, troubleshoot network errors.
Watchdog overflowAction:Hard Reset
Event code
0x231000de
Message text
Watchdog overflow.Action:Hard Reset---interrupt type:$1---timer use at expiration:$2.
Variable fields
¡     none.
¡     SMI.
¡     NMI.
¡     unspecified.
¡     reserved.
¡     BIOS FRB2.
¡     BIOS POST.
¡     OS Load.
¡     SMS OS.
¡     OEM.
¡     unspecified.
Severity level
Major
Example
Watchdog overflow.Action:Hard Reset---interrupt type:none---timer use at expiration:BIOS FRB2.
Impact
Cause
·     The watchdog timer expires during the BIOS POST, OS Load, or SMS/OS phase (indicated by the watchdog timer type).
·     The timeout action is set to hard reset.
Recommended action
Watchdog overflowAction:Power Down
Event code
0x232000de
Message text
Watchdog overflow.Action:Power Down---interrupt type:$1---timer use at expiration:$2.
Variable fields
¡     none.
¡     SMI.
¡     NMI.
¡     unspecified.
¡     reserved.
¡     BIOS FRB2.
¡     BIOS POST.
¡     OS Load.
¡     SMS OS.
¡     OEM.
¡     unspecified.
Severity level
Major
Example
Watchdog overflow.Action:Power Down---interrupt type:none---timer use at expiration:BIOS FRB2.
Impact
Cause
·     The timeout action is set to power down.
The watchdog powered off the system forcibly. Services are interrupted and the data that has not been saved will get lost.
Recommended action
Watchdog overflowAction:Power Cycle
Event code
0x233000de
Message text
Watchdog overflow.Action:Power Cycle---interrupt type:$1---timer use at expiration:$2.
Variable fields
¡     none.
¡     SMI.
¡     NMI.
¡     unspecified.
¡     reserved.
¡     BIOS FRB2.
¡     BIOS POST.
¡     OS Load.
¡     SMS OS.
¡     OEM.
¡     unspecified.
Severity level
Major
Example
Watchdog overflow.Action:Power Cycle---interrupt type:none---timer use at expiration:BIOS FRB2.
Impact
Cause
·     The timeout action is set to power cycle.
Recommended action
Watchdog overflowAction:Timer interrupt
Event code
0x238000de
Message text
Watchdog overflow.Action:Timer interrupt---interrupt type:$1---timer use at expiration:$2.
Variable fields
¡     none.
¡     SMI.
¡     NMI.
¡     unspecified.
¡     reserved.
¡     BIOS FRB2.
¡     BIOS POST.
¡     OS Load.
¡     SMS OS.
¡     OEM.
¡     unspecified.
Severity level
Minor
Example
Watchdog overflow.Action:Timer interrupt---interrupt type:none---timer use at expiration:BIOS FRB2.
Impact
Cause
·     The timeout action is set to timer interrupt.
Recommended action
Management subsystem health
Management controller off-line
Event code
0x282000de
Message text
Management controller off-line.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
HDM is offline. Possible reasons include HDM shutdown or no power input (AC gets lost).
Recommended action
1.     Review operation logs and verify if a power-off operation was performed by a user. If yes, wait for HDM to restart.
2.     If no power-off operation was performed or if the issue occurs again after HDM restarts, examine if an AC lost event has occurred or a power supply is operating incorrectly.
3.     Replace the power supply.
Management controller off-line---BMC reset
Event code
0x282000de
Message text
Management controller off-line---BMC reset.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
This message is often generated when a user resets HDM.
Recommended action
1.     Review operation logs and verify if a warm reset operation was performed by a user. If yes, wait for HDM to restart.
2.     Verify that no system board or power supply error is present.
Management controller off-line---HDM cold reboot
Event code
0x282000de
Message text
Management controller off-line---HDM cold reboot.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
This message is often generated when a user performs cold HDM reboot.
Recommended action
1.     Review operation logs and verify if a cold reboot operation was performed by a user. If yes, wait for HDM to restart.
2.     Verify if an AC lost event has occurred or the power cord is disconnected or faulty.
¡     If an AC lost event occurred or a power supply fails or is faulty, replace the power supply.
¡     If the power cord is disconnected, reconnect the power cord.
¡     If the power cord is faulty, replace the power cord.
Management controller off-line---BMC WDT timeout event happened
Event code
0x282000de
Message text
Management controller off-line---BMC WDT timeout event happened.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
The management controller went offline because the system was restarted by the watchdog.
Recommended action
1.     Review event logs to identify the cause of watchdog timeout.
2.     Upgrade HDM to the latest version.
Management controller off-line---BMC service restart
Event code
0x282000de
Message text
Management controller off-line---BMC service restart.
Variable fields
N/A
Severity level
Info
Example
Impact
No negative impact.
Cause
HDM restarted proactively.
Recommended action
1.     Verify if HDM restarted or was upgraded and if HDM is operating correctly. If the issue rarely occurs and HDM operates correctly, no action is required.
2.     If the issue persists, contact Technical Support.
Management controller unavailable
Event code
0x283000de
Message text
Management controller unavailable.
Variable fields
N/A
Severity level
Major
Example
Impact
No negative impact.
Cause
The management controller is unavailable. Possible reasons include unavailable HDM or ME.
Recommended action
1.     Wait for one or two minutes and then refresh the page.
Management controller unavailable---Adapter $1 RAID-P460-B4 is in a fault condition
Event code
0x283000de
Message text
Management controller unavailable---Adapter $1 is in a fault condition
Variable fields
$1: Storage controller model.
Severity level
Major
Example
Management controller unavailable---Adapter RAID-P460-B4 is in a fault condition.
Impact
The system might crash depending on the installation location of the system.
Cause
This message is generated when the PMC storage controller is abnormal.
Recommended action
1.     Restart HDM and identify whether the alarm is cleared from the Event Log tab.
2.     Restart the server and identify whether the alarm is cleared from the Event Log tab.
Sensor access degraded or unavailable--- Adapter $1 RAID-P460-B4 has  no response for 2 minutes in $2 slot
Event code
0x280000de
Message text
Sensor access degraded or unavailable--- Adapter $1 has no response for 2 minutes in $2 slot.
Variable fields
$2: Slot of the storage controller where the alarm occurs.
Severity level
Minor
Example
Sensor access degraded or unavailable--- Adapter RAID-P460-B4 has no response for 2 minutes in 1 slot
Impact
Out-of-band identification is abnormal. If in-band identification is also abnormal, the system might crash.
Cause
This message is generated when HDM fails to identify the PMC storage controller in slot $2 within 2 minutes.
Recommended action
Sensor access degraded or unavailable--- Adapter $1 has  no response for 5 minutes in $2 slot
Event code
0x280000de
Message text
Variable fields
Severity level
Minor
Example
Sensor access degraded or unavailable--- Adapter HBA-LAI-9300-8i-A1-X has no response for 5 minutes in 1 slot
Impact
Cause
This message is generated when HDM fails to identify the LSI storage controller in slot $2 within 5 minutes.
Recommended action
Sensor failure---Adapter $1 has no response for 4 minutes in $2 slot
Event code
0x284000de
Message text
Management controller unavailable---Adapter $1 has no response for 4 minutes in $2 slot
Variable fields
·     $1: Storage controller model.
·     $2: Slot of the storage controller where the alarm occurs.
Severity level
Major
Example
Management controller unavailable---Adapter RAID-P460-B4 has no response  for 4 minutes in 1 slot
Impact
Cause
This message is generated when HDM fails to identify the PMC storage controller in slot $2 within 5 minutes.
Recommended action
Sensor failure--- Adapter $1 has no response for 10 minutes in $2 slot
Event code
0x284000de
Message text
Management controller unavailable---Adapter $1 has no response for 10 minutes in $2 slot.
Variable fields
$1: Slot of the storage controller where the alarm occurs.
Severity level
Major
Example
Management controller unavailable---Adapter HBA-LAI-9300-8i-A1-X has no response  for 10 minutes in 1 slot
Impact
Cause
This message is generated when HDM fails to identify the PMC storage controller in slot $2 within 10 minutes.
Recommended action
Battery
Battery low (predictive failure)
Event code
0x290000de
Message text
Battery low (predictive failure)---PCIe slot:$1.
Variable fields
$1: PCIe slot number of the storage controller.
Severity level
Minor
Example
Battery low (predictive failure)---PCIe slot:1
Impact
The reliability of the storage controller decreases, which might cause the decrease of the system performance.
Cause
The supercapacitor of the storage controller has a low charge, overtemperature, overvoltage, or overcurrent condition.
Recommended action
1.     Power on the server to charge the supercapacitor. Log in to HDM to view the supercapacitor status and verify whether the alarm is cleared after a period of time.
2.     Verify that the power fail safeguard module is installed correctly.
3.     Replace the supercapacitor or corresponding flash card (if any), and then restart the server.
4.     If the issue persists, contact Technical Support.
Battery failed
Event code
0x291000de
Message text
Battery failed---PCIe slot:$1.
Variable fields
Severity level
Minor
Example
Battery failed---PCIe slot:1.
Impact
Cause
An internal error occurred on the power fail safeguard module of the storage controller.
Possible reasons include:
·     The supercapacitor is exhausted or has expired.
·     The power fail safeguard module failed to be initialized.
·     The power fail safeguard module subsystem failed.
·     The supercapacitor failed to be charged.
·     The supercapacitor fails.
Recommended action
1.     Log in to HDM and view the supercapacitor status.
Battery presence detected
Event code
0x292000df
Message text
Battery presence detected---PCIe slot:$1.
Variable fields
Severity level
Info
Example
Battery presence detected---PCIe slot:1.
Impact
Cause
The supercapacitor of the storage controller is not detected.
Recommended action
2.     Verify that the supercapacitor is installed correctly and the supercapacitor cable is connected correctly.
3.     Replace the supercapacitor or the corresponding flash card (if any), and then restart the server.
ME status
Event code
0xb03000de
Message text
Variable fields
N/A
Severity level
Minor
Example
Impact
No negative impact.
Cause
This message is displayed if the ME self-test fails.
Recommended action
1.     Identify the current ME version and update the ME to the latest version if a new version is available.
2.     Update the BIOS to the latest version.
OEM Record
System Source Monitor:Mem usage exceeds the threshold
Event code
0xe01000de
Message text
System Source Monitor:Mem usage exceeds the threshold---Current usage $1 Threshold $2.
Variable fields
$1: Memory usage.
$2: Memory usage threshold.
Severity level
Info
Example
System Source Monitor:Mem usage exceeds the threshold---Current usage 100%, Threshold 80%.
Impact
The system might get stuck.
Cause
The memory usage exceeded the alarm threshold. This alarm is triggered by FIST SMS.
Recommended action
1.     Verify that the memory usage threshold setting is reasonable.
2.     Check the current memory usage. Adjust the running services to lower the memory usage or expand the memory capacity.
System Source Monitor: Relieve resource alarm about Mem Usage
Event code
0xe01000df
Message text
System Source Monitor: Relieve resource alarm about Mem Usage---Current usage $1 Threshold $2.
Variable fields
$1: Memory usage.
Severity level
Info
Example
System Source Monitor:Relieve resource alarm about Mem Usage---Current usage 80%, Threshold 100%.
Impact
No negative impact.
Cause
The memory usage dropped below the alarm threshold. This alarm is triggered by FIST SMS.
Recommended action
System Source Monitor:Cpu usage exceeds the threshold
Event code
0xe02000de
Message text
System Source Monitor:Cpu usage exceeds the threshold---Current usage $1 Threshold $2.
Variable fields
$1: CPU usage.
$2: CPU usage threshold.
Severity level
Info
Example
System Source Monitor:Cpu usage exceeds the threshold---Current usage 100%, Threshold 80%.
Impact
Cause
The processor usage exceeded the alarm threshold. This alarm is triggered by FIST SMS.
Recommended action
1.     Verify that the processor usage threshold setting is reasonable.
2.     Check the current processor usage. Adjust the running services to lower the processor usage.
3.     .If the issue persists, contact Technical Support.
System Source Monitor: Relieve resource alarm about Cpu Usage
Event code
0xe02000df
Message text
System Source Monitor: Relieve resource alarm about Cpu Usage---Current usage $1 Threshold $2.
Variable fields
$1: CPU usage.
Severity level
Info
Example
System Source Monitor:Relieve resource alarm about Cpu Usage---Current usage 80%, Threshold 100%.
Impact
No negative impact.
Cause
The processor usage dropped below the alarm threshold. This alarm is triggered by FIST SMS.
Recommended action
Memory is not certified
Event code
0xe11000de
Message text
Memory is not certified---Location: CPU:$1 CH:$2 DIMM:$3 $4.
Variable fields
$1: CPU number.
$2: Channel number.
$3: DIMM number.
$4: DIMM identifier.
Severity level
Minor
Example
Memory is not certified---Location:CPU:1 CH:1 DIMM:0 A1
Impact
No negative impact.
Cause
HDM performs anti-counterfeit verification on DIMMs every time the BIOS restarts. This message is displayed if a DIMM is not certified by H3C.
Recommended action
1.     Log in to HDM, access the Memory page, and verify that all DIMMs are H3C certified. Using a non-H3C-certified DIMM can cause stability issues.
2.     Verify that the DIMMs are correctly installed.
Numbering CPUs
CPUs are numbered starting from different numbers for different servers, as shown in Table 3.
Table 3 CPU numbering for different servers
Servers
Starting number for CPUs
·     H3C UniServer B5700 G3
·     H3C UniServer B5700 G5
·     H3C UniServer B5800 G3
·     H3C UniServer B7800 G3
·     H3C UniServer E3200 G3
·     H3C UniServer R2700 G3
·     H3C UniServer R2900 G3
·     H3C UniServer R4300 G3
·     H3C UniServer R4300 G5
·     H3C UniServer R4330 G5
·     H3C UniServer R4400 G3
·     H3C UniServer R4500 G3
·     H3C UniServer R4700 G3
·     H3C UniServer R4700 G5
·     H3C UniServer R4900 G3
·     H3C UniServer R4900 G5
·     H3C UniServer R4900LC G5
·     H3C UniServer R4930 G5
·     H3C UniServer R4950 G5
·     H3C UniServer R5300 G3
·     H3C UniServer R5300 G5
·     H3C UniServer R5500 G5
·     H3C UniServer R6700 G3
·     H3C UniServer R6900 G3
·     H3C UniServer R6900 G5
·     H3C UniServer R8900 G3
CPU 1
·     H3C UniServer R4950 G3 (Hygon)
·     H3C UniServer R4950 G3 (Naples)
·     H3C UniServer R4950 G3 (Rome)
CPU 0
H3C UniServer R4100 G3
The server comes with only one CPU and does not require CPU numbering.
