13-Telemetry Configuration Guide
HomeSupportSwitchesS9850-G SeriesTechnical DocumentsConfigure & DeployConfiguration GuidesH3C S6850-G&S6805-G&S9850-G Switch Series Configuration Guides-R8336Pxx-6W10013-Telemetry Configuration Guide
06-RDMA telemetry configuration
06-RDMA telemetry configuration 258.27 KB
Configuring RDMA telemetry
About RDMA telemetry
RDMA telemetry is an intelligent network monitoring technology that divides the data center storage network into three segments. It measures the data transmission latency (I/O quality) of read and write operations for each segment in real time, and generates visual network quality reports to help administrators to quickly locate performance bottlenecks.
System model
The RDMA telemetry measurement system contains the following components:
·     Controller and analyzer.
¡     The controller deploys measurement configuration to devices through NETCONF interfaces.
¡     Devices report measurement data to the analyzer through gRPC. Then, the analyzer displays I/O performance indexes (latency).
·     Measurement devices: Network devices that support RDMA telemetry.
¡     Compute-side port—Port that connects a device to the compute node (such as a Web server or mail server). It identifies NVMe and RDMA packets, measures compute-side latency, and reports the measurement data to the analyzer.
¡     Storage-side port—Port that connects a device to the storage array. It identifies NVMe and RDMA packets, measures storage-side latency, and reports the measurement data to the analyzer.
RDMA telemetry divides the data center storage network into the following segments:
·     Compute side—The segment between a network device and the compute node.
·     Storage side—The segment between a network device and the storage array.
·     Network path—The transmission network between the compute node and the storage array.
Figure 1 RDMA telemetry system model
Measurement indexes
Based on the I/O interaction process, RDMA telemetry periodically performs measurement and calculates the average value for each of the following objects:
·     Data Preparation Latency (DPL)—Applicable only to write I/O operations. It is used for evaluating the data preparation efficiency on the compute side.
If the DPL is high, a CPU or memory bottleneck (such as thread blocking) might exist on the compute side.
·     Round-Trip Time (RTT)—Round-trip latency of packet transmission in the network used for measuring network performance. It is calculated by subtracting the total storage-side latency (IOL2) from the total compute-side latency (IOL1).
If the RTT suddenly increases, network congestion, BGP route flapping, or NIC queue backlog might exist.
·     Data Access Latency (DAL)—The time the storage device takes to process I/O requests. Read DAL and write DAL are measured separately, and they reflect different processing stages on the storage side.
If the DAL is high, high SSD latency, RAID controller bottleneck, or storage software stack overloading might exist.
Figure 2 Measurement indexes for RDMA telemetry
Read and write I/O interaction processes
Key packets and measurement indexes
Figure 3 shows the key packets that pass through the compute-side and storage-side ports, and the measurement indexes recorded by the devices in the read and write I/O interaction processes.
Figure 3 Key packets and measurement indexes in the read and write I/O interaction processes
Table 1 shows the key packets and the measurement indexes recorded by devices when the compute side reads data from the storage side.
Table 1 Key packets and measurement indexes in the read I/O interaction process
Step
Direction
Packet type
RDMA operation
Data recorded by devices
1
From compute side to storage side
NVMe CMND (read request)
RDMA Send Only
·     The compute-side port records the timestamp when packet 1 was sent and starts timing for IOL1.
·     The storage-side port records the timestamp when packet 1 was received (timestamp when the storage side received the request) to calculate the DAL and starts timing for IOL2.
2
From storage side to compute side
NVMe_DATA (first data packet)
RDMA Write First
The storage-side port records the timestamp when packet 2 was sent to calculate the read DAL.
3
NVMe_DATA (final data packet)
RDMA Write Last
No data recorded.
4
NVMe RSP (response completion)
RDMA Send Only Inval.
·     The storage-side port records the timestamp when packet 4 was sent and ends timing for IOL2.
·     The compute-side port records the timestamp when packet 4 was received and ends timing for IOL1.
Table 2 shows the key packets and the measurement indexes recorded by devices when the compute side writes data to the storage side.
Table 2 Key packets and measurement indexes in the write I/O interaction process
Step
Direction
Packet type
RDMA operation
Telemetry measurement data
5
NVMe CMND (write request)
RDMA Send Only
·     The compute-side port records the timestamp when packet 5 was sent and starts timing for IOL1.
·     The storage-side port records the timestamp when packet 5 was received to calculate the write DAL.
6
NVMe Read Request (data pull request)
RDMA Read Request
·     The storage-side port records the timestamp when packet 6 was sent to calculate the DAL.
·     The compute-side port records the timestamp when packet 6 was received to calculate the DPL.
7
RDMA Read Resp First
The compute-side port records the timestamp when packet 7 was sent to calculate the DPL.
8
RDMA Read Resp Last
No data recorded.
9
NVMe RS (write acknowledgement)
·     The storage-side port records the timestamp when packet 9 was sent and ends timing for IOL2.
·     The compute-side port records the timestamp when packet 9 was received and ends timing for IOL1.
Calculating measurement indexes
·     Read DAL: time difference between receiving a read request (packet 1) and sending the first data packet (packet 2) on the storage-side port.
Read DAL = timestamp when packet 2 was sent − timestamp when packet 1 was received
·     Write DAL: time difference between receiving a write request (packet 5) and sending a data pull request (packet 6) on the storage-side port.
Write DAL = timestamp when packet 6 was sent − timestamp when packet 5 was received
·     DPL: time difference between receiving the data pull quest (packet 6) and sending the first data response (packet 7) on the compute side.
DPL = timestamp when packet 7 was sent − timestamp when packet 6 was received
·     IOL1 (total compute-side latency):
IOL1 = response timestamp − request timestamp = timestamp when packet 4 was received − timestamp when packet 1 was sent
¡     Read operation: time difference between sending packet 1 and receiving packet 4 on the compute side.
¡     Write operation: time difference between sending packet 5 and receiving packet 9 on the compute side.
·     IOL2 (total storage-side latency):
IOL2 = timestamp for storage-side response sending − timestamp for storage-side request receiving = timestamp when packet 4 was sent − timestamp when packet 1 was received
¡     Read operation: time difference between receiving packet 1 and sending packet 4 on the storage side.
¡     Write operation: time difference between receiving packet 5 and sending packet 9 on the storage side.
·     RTT = IOL1 − IOL2
Data acquisition process
The following uses data acquisition of a common user as an example to describe the complete RDMA telemetry measurement process.
1.     The user sends a request, and the compute side processes the request.
The user clicks an app, which triggers the compute side (such as a Web server) to generate a data request. The application service encapsulates the request into an NVMe over Fabrics (NoF) packet (such as RDMA Send Only).
2.     The request traverses network devices (RTT measurement points).
The compute side sends the request through the RDMA NIC, and the network devices forward the request to the storage side. The network devices record packet timestamps and associate requests and responses (such as packet 1 and packet 4).
3.     The storage-side (DAL measurement point) processes the request.
The storage-side port receives the request (such as packet 1), reads data from flash memory, and then sends data to the compute side (such as packet 2).
The storage device directly writes or pulls data through RDMA write or read, respectively.
The DAL is the time difference between receiving the request (packet 1) and sending data (packet 2) on the storage side.
4.     Data is returned to the user (end-to-end closed loop).
The storage-side data is returned to the compute side. The compute-side application service assembles the response data and sends it back to the user in an HTTP message.
RDMA telemetry is supported only in expert operating mode. For more information about the device operating modes, see device management configuration in Fundamentals Configuration Guide.
You can configure RDMA telemetry only on Ethernet interfaces, and you cannot configure it on member ports of an aggregation group.
RDMA telemetry does not support measuring VPN or M-LAG traffic. For more information about VPN, see MPLS Configuration Guide. For more information about M-LAG configuration, see Layer 2—LAN Switching Configuration Guide.
Only Layer 3 known unicast transmission supports RDMA telemetry measurement.
RDMA telemetry does not support measuring traffic in VXLAN networks. For more information about VXLAN, see VXLAN Configuration Guide.
RDMA telemetry periodically performs sampling and measurement and calculates average values. Because it does not sample each I/O, the latency statistics about non-sampled packets cannot be displayed.
RDMA telemetry does not perform full measurement on all I/Os. Some latency statistics are not effectively monitored.
In the current software version, RDMA telemetry does not measure small-byte I/Os.
When the compute-side and storage-side ports reside on the same card, the packet receiver and sender cannot be distinguished. Inbound packets might be sent to the analyzer in advance, distorting latency measurement.
When you configure RDMA telemetry, follow these guidelines:
·     The RDMA telemetry feature is mutually exclusive with the netanalysis udp command.
·     For RDMA telemetry to operate correctly, do not use it together with the ip load-sharing mode per-packet or ip load-sharing mode per-flow ingress-port command.
·     As a best practice, do not use IPv6 flow filtering rules for RDMA telemetry together with the unified flow analysis (UFA) feature.
For more information about the netanalysis udp command and UFA, see NetAnalysis configuration in Network Management and Monitoring Configuration Guide. For more information about the ip load-sharing mode command, see IP forwarding basics configuration in Layer 3—IP services Configuration Guide.
Table 1 Enter system view.
2.     Enter RDMA-telemetry view.
rdma-telemetry
3.     Configure a flow filtering rule for RDMA telemetry.
flow flow-name [ ipv6 ] { destination destination-ip-address | source source-ip-address } *
By default, no flow filtering rule is configured for RDMA telemetry.
RDMA telemetry measures only the service traffic that matches filtering rules.
4.     Set the measurement interval for I/O quality visualization.
interval interval-value
By default, the measurement interval is 10 seconds for I/O quality visualization.
After you configure RDMA telemetry, the device calculates the DAL, DPL, and IOL for each read and write operation. It also calculates the average DAL, average DPL, and average IOL within a measurement interval. To view the average statistics, execute the display rdma-telemetry statistics command or configure the device to report the statistics to the analyzer through gRPC.
5.     Enable global I/O quality visualization.
rdma-telemetry global enable
By default, global I/O quality visualization is disabled.
6.     Enter interface view.
7.     Enable I/O quality visualization on the interface.
rdma-telemetry enable
By default, I/O quality visualization is disabled on an interface.
Display and maintenance commands for RDMA telemetry
Display RDMA telemetry statistics.
RDMA telemetry configuration examples
Example: Configuring RDMA telemetry
A PC accesses the Web server to read and write webpages. The process is as follows:
Table 2 The PC (Web access endpoint) sends read and write requests to the compute node (Web server).
2.     The compute node reads data from and writes data to the storage array.
3.     The compute node returns the result to the PC.
Configure RDMA telemetry to measure and display the latency of each segment in a single I/O read/write operation. The latency statistics include the compute-side latency, the transmission network latency, and the storage-side latency.
Figure 4 Network diagram
Table 3 Interface label and interface name mappings
Interface label
Interface name
Interface1
Ten-GigabitEthernet 1/0/1
Make sure the compute node, devices, and storage array can reach each other, and the devices and the analyzer can reach each other. (In this example, RDMA telemetry is directly configured on the devices. You do not need to deploy a controller to issue configuration to the devices.)
Configuring Device A
Table 1 Configure gRPC to report RDMA telemetry measurement data to the analyzer:
# Enable the gRPC service.
[Sysname] sysname DeviceA
[DeviceA] grpc enable
# Create a sensor group named test, and add sensor path rdmatelemetry/rdmaserviceevent.
[DeviceA] telemetry
[DeviceA-telemetry] sensor-group test
[DeviceA-telemetry-sensor-group-test] sensor path rdmatelemetry/rdmaserviceevent
[DeviceA-telemetry-sensor-group-test] quit
# Create a destination group named collector1 and add a collector to the group.
[DeviceA-telemetry] destination-group collector1
[DeviceA-telemetry-destination-group-collector1] ipv4-address 10.1.3.1 port 50050
[DeviceA-telemetry-destination-group-collector1] quit
# Configure a subscription named A to bind sensor group test with destination group collector1.
[DeviceA-telemetry] subscription A
[DeviceA-telemetry-subscription-A] sensor-group test
[DeviceA-telemetry-subscription-A] destination-group collector1
[DeviceA-telemetry-subscription-A] quit
[DeviceA-telemetry] quit
2.     Configure I/O quality visualization:
# Enable I/O quality visualization on Ten-GigabitEthernet 1/0/1.
[DeviceA-Ten-GigabitEthernet1/0/1] rdma-telemetry enable
# Enable global I/O quality visualization.
[DeviceA] rdma-telemetry
[DeviceA-rdma-telemetry] rdma-telemetry global enable
# Configure a flow filtering rule for RDMA telemetry.
[DeviceA-rdma-telemetry] flow test source 10.1.1.1 destination 10.1.2.1
Configuring Device B
[Sysname] sysname DeviceB
[DeviceB] grpc enable
[DeviceB] telemetry
[DeviceB-telemetry] sensor-group test
[DeviceB-telemetry-sensor-group-test] sensor path rdmatelemetry/rdmaserviceevent
[DeviceB-telemetry-sensor-group-test] quit
[DeviceB-telemetry] destination-group collector1
[DeviceB-telemetry-destination-group-collector1] ipv4-address 10.1.3.1 port 50050
[DeviceB-telemetry-destination-group-collector1] quit
[DeviceB-telemetry] subscription A
[DeviceB-telemetry-subscription-A] sensor-group test
[DeviceB-telemetry-subscription-A] destination-group collector1
[DeviceB-telemetry-subscription-A] quit
[DeviceB-telemetry] quit
[DeviceB-Ten-GigabitEthernet1/0/1] rdma-telemetry enable
[DeviceB] rdma-telemetry
[DeviceB-rdma-telemetry] rdma-telemetry global enable
[DeviceB-rdma-telemetry] flow test source 10.1.1.1 destination 10.1.2.1
Table 1 Display RDMA telemetry statistics on Device A. Verify that you can view the latency statistics about read and write operations (AIOL, ADAL, and ADPL).
<DeviceA> display rdma-telemetry statistics
AIOL: Average I/O latency(us)
ADAL: Average data access latency(us)
ADPL: Average data preparation latency(us)
R: Read   W: Write
Measurement interval: 10s
Measured at: 2025-8-20 08:20:19
SIP                                 DIP                                   Type
AIOL(R/W)             ADAL(R/W)             ADPL(R/W)
10.1.1.1                             10.1.2.1                              Initiator
1345/1246             --/--                 --/48
2.     Display RDMA telemetry statistics on Device B. Verify that you can view the latency statistics about read and write operations (AIOL, ADAL, and ADPL).
<DeviceB> display rdma-telemetry statistics
R: Read   W: Write
SIP                                  DIP                                  Type
10.1.1.1                             10.1.2.1                              Target
1332/1224             34/56                 --/--
Configuration files
·     Device A:
sysname DeviceA
grpc enable
telemetry
  sensor-group test
    ipv4-address 192.168.134.1 port 50050
  subscription A
    sensor-group test
rdma-telemetry
·     Device B:
sysname DeviceB
grpc enable
telemetry
  sensor-group test
  subscription A
    sensor-group test
rdma-telemetry