H3C G5 Servers Intel Platform RAS Technology White Paper-6W104
HomeSupportTechnology LiteratureTechnology White PapersH3C G5 Servers Intel Platform RAS Technology White Paper-6W104
Download Book
Copyright © 2023-2025 New H3C Technologies Co., Ltd. All rights reserved.
Overview
The server is one of the key components of any modern data center infrastructure. It includes various components such as processors, storage devices, PCIe devices, power supplies, and fans. To ensure service continuity, correct server operation based on data integrity are critical to a modern data center. In other words, we must avoid data corruption no matter data is stored in any server component (memory, cache, or processor registers) or transmitted through any platform links (Intel®UPI, PCI Express, or DMI).
When a server component fails, the set of reliability, availability and serviceability (RAS) features can meet the above requirements by maximizing service availability and maintaining data integrity.
Table 1 RAS definition based on H3C G5 servers
Item
Definition
Reliability
Probability that the system produces the correct output within a given time T, as measured by the mean time between failures (MTBF) metric.
It can be enhanced by avoiding, detecting, and repairing hardware failures. A reliable system does not provide incorrect data and calculation results, but can detect and correct data corruption.
Availability
Probability of correct system running at a given time, and the percentage of the actual running time of the server to the actual running time.
Serviceability
How easy and fast the system can be repaired or maintained.
If the time for the system to repair errors increases, the serviceability decreases.
Serviceability can be improved by simplifying system issue diagnosis and providing clear and intelligent advance warnings of failures to avoid system failures.
Figure 1 Error categories
Benefits
RAS can provide the following benefits:
·     Increased system uptime—Increases system reliability for the system to stay longer, as measured by the Mean Time To Fail (MTTF), Annual Crash Rate (ACR), or Annual Service Rate (ASR) metric.
·     Reduced the duration of unexpected downtimeAdopts Intel Xeon processors of the third generation to support synchronized hardware and firmware logging, helping users to identify and isolate errors and take preventive or proactive maintenance measures. This enables quick system restoration, reduces the cost of repairs, and mitigates the consequences of the outage to the business.
Outages are inevitable even with the best plans and processes. When an unplanned outage happens, a maintainable system can come back online quickly, as measure by the Mean Repair Time (MTTR) matric.
·     Enhanced data integrityRAS provides several mechanisms to prevent data corruption or correct corrupted data, which ensures data corruption can get contained once detected.
Applicable products
This document is applicable to the following H3C UniServer servers:
·     H3C UniServer R4300 G5
·     H3C UniServer R4700 G5
·     H3C UniServer R4900 G5
·     H3C UniServer R5300 G5
·     H3C UniServer R5500 G5
·     H3C UniServer R6900 G5
Using this document
The information in this document is subject to change over time.
The information in this document might differ from your product if it contains custom configuration options or features.
RAS system architecture
Based on MCA supported by Intel Xeon scalable processors, H3C provides a complete error management system together with hardware, the BIOS, HDM, and OS error processing mechanisms. The system can provide functions such as error diagnosis, error location, error correction, information collection, and error reporting. Since the core of the system runs on the BIOS and HDM, it does not rely on the OS and can perform all-time detection of the system and take corresponding measures once an error occurs.
As shown in Figure 2, the error management system contains the hardware layer, CPLD, processor platform, HDM (out-of-band management), the BIOS, and OS.
·     HDMCore of the error location system. It is responsible for error information collection and analysis and can display error information as event logs or alarms from the Web interface.
·     Processor platformSupported by Intel Xeon processors, which compared with the previous generation provides enhanced RAS capabilities and more powerful management of errors occurred on processors, memory modules, and PCIe devices.
·     CPLDConnects downlink hardware modules, including power supplies, fans, and other underlying hardware (except processors, memory modules, drives, and standard PCIe modules), captures hardware exceptions, connects to HDM at the uplink, and transmits error information.
·     BIOSCollects and locates errors occurred on processors, memory modules, PCIe devices, and storage devices, provides error location results to HDM, and provides OS-level error management interfaces, such as WHEA, to the OS.
·     UniSystemServer management software developed by H3C. It can decode SDS log messages to record hardware and software events occurred during each service cycle, including main processor, BIOS, OS, and BMC events. This helps customer service or engineers to fast locate server issues and improve serviceability. This component is optional.
·     iFISTSingle-server management tool embedded in each server. You can use iFIST to configure RAID settings, install the OS, install drivers, and diagnose server health conditions.
·     Web interfaceWeb interface provided by management tools, such as HDM, for users to maintain the server locally or remotely. Users can use the Web interface together with LEDs of specific server components to manage the server.
·     Involved protocolsProtocols used by the error management system includes LPC, PECI, PCIe, UART, I2C, SMBUS, and LocalBus.
Figure 2 H3C error management system architecture
RAS operating mechanism
H3C RAS technology is realized through the processes of error detection, reporting, and processing.
The basic error processing schemes of RAS are as follows:
·     For correctable errors, RAS marks the error location and fast repair the corresponding module. Users will not aware the occurrence of such errors.
·     For uncorrectable errors, RAS isolates the errors by isolating bad memory blocks or degrading the bus to maintain system operation. If severe errors occur and result in system outage, you must use HDM to restore or restart the system.
·     For permanent hardware failures, you must replace the faulty component or use the backup device. You can replace hot swappable components without powering off the server.
RAS technology is realized based on the following mechanisms:
·     Machine Check Architecture (MCA)
MCA reports and fixes system bus, ECC, parity, cache, and TLB errors, identifies the source of failures, and records the failure information in MC Bank. Through the MCA mechanism, both correctable and uncorrectable errors of the CPU can be reported and logged and correctable errors of hardware can be corrected. For uncorrectable errors, a hot restart is usually performed. MCA can take effect on all processors modules such as Core, Uncore, and IIO (via IOMCA) modules.
·     Integrated Error Handler (IEH)
IEH is a unified and clear-leveled error processing and reporting mechanism, including south satellite IEH, north satellite IEH, and global IEH. South satellite IEH is located in PCH, which collects and summarizes the fault information in PCH and reports the information to global IEH. North satellite IEH is located in each stack of CPU IIO, which collects and summarizes the fault information reported by all internal devices and downstream PCIe devices in the stack and reports the information to global IEH. Global IEH is located in Ubox, which summarizes the fault information reported by the downstream IEH and triggers the related interruption signal SMI/NMI or outputs ERRPIN in the range of 0 to 2. IEH is not supported in the R6900 G5.
·     IIO Advanced Error Reporting (AER)
AER detects, logs and sends signals for errors of various IIO sub-modules. AER can take effect on all IIO sub-modules such as PCIe interface, DMI, IIO core logic, and Intel VT-d modules.
Figure 3 RAS schemes
Error detection
As shown in Table 2, H3C G5 servers use different error detection methods for different modules to maintain high processor availability. Both error detection and correction events will be reported.
For more information about error detection methods, see "Error detection and correction (including the socket level)."
Table 2 Error detection methods for different modules
Module
Definition/Submodule
Detection method
EE
Execution/Engine
Residue check
IFU
Instruction fetch unit (L1 I-Cache)
Parity
DCU
Data cache unit (L1 D-cache)
Parity
I/DTLB
Instruction/Data translation look aside buffer
Parity
MLC
Mid-level cache
ECC
CHA
L3 cache: Data tag, MESIF state
ECC
Home agent
Parity
PCU
Power controller unit
Parity, stack overflow, time schemes
IVR
Integrated voltage regulators
Overvoltage and overcurrent
UPI
Ultra path interconnect
CRC
Rx and Tx queues
Parity
IMC
Read data buffer parity
Parity
Memory read write data byte enable
ECC
IIO/PCIe
Integrated I/O: Phy and link layer
CRC
Rx/Tx queues
Parity
IIO, IRP, Inter VT-d, MISC, DMA errors
Internal ring
Internal ring - data and command (DPPP, APPP)
Parity
Error reporting
The system reports detected errors and generates error log messages. Error reporting requires the collaboration of the MCA, IEH, AER, memory correctable error reporting, and UPI correctable error reporting mechanisms.
Error reporting modes
The following error reporting modes are available:
·     Legacy IA-32 MCA modeSupported by several generations of Intel processors and most operating systems.
·     Corrupt Data Containment (CDC) modeAn enhancement to the MCA mechanism. When the CDC mode detects an uncorrectable error, the detection agent forwards the error data with the poison flag set to the request agent.
·     Enhanced MCA Gen2 (EMCA Gen2) modeSecond-generation enhancement to the Legacy IA-32 MCA mode. It was developed to create a mode that can be enabled in the OS and further expanded the error reporting coverage of FFM.
·     IOMCA modeAllows IIO correctable and uncorrectable fatal errors to be signaled through MCE.
·     Viral modeAdopts hardware measures to improve error tolerance. The CDC mode can tolerate data errors, but the viral mode can tolerate address, control, and other fatal errors. This prevents errors from being submitted to drives or networks.
Some of the above modes are complementary to each other and can be enabled at the same time. Table 3 describes mode compatibility.
Table 3 Error reporting mode compatibility
Mode
CDC mode
EMCA Gen2 mode
IO MCA mode
Viral mode
Yes
N/A
N/A
N/A
N/A
CDC mode
No
Yes
N/A
N/A
N/A
EMCA Gen2 mode
No
Yes
Yes
N/A
N/A
IO MCA mode
Yes
Yes
Yes
N/A
N/A
Viral mode
Yes
Yes
Yes
Yes
N/A
As shown in Table 4, the interrupt type used for error reporting depends on the error type.
Table 4 Error reporting interrupt
Error type
Interrupt type
Range
Remarks
Correctable errors
Corrected Machine Check Interrupt (CMCI)
Core/uncore
Available only in Legacy IA-32 MCA mode
Corrected SMI (CSMI)
Core/uncore
Available only in eMCA2 mode
System Management Interrupt (SMI)
Memory errors
In-band communication between all sockets through UPI bus
Message Signaled Interrupt (MSI)
PCIe errors
N/A
ERROR_N[0] pin
IIO AER and memory errors
Can be used for BMC-based RAS
Uncorrectable errors
UCNA
CMCI
Core/uncore errors at the source
MSMI
MSI and ERROR_N[1] pin
Severity 1 IIO AER nonfatal errors
N/A
SRAO and SRAR
MCERR
Core/uncore errors
MSMI
Catastrophic errors
IERR
Core/uncore errors
MSMI
As shown in Figure 4, the system processes errors as follows:
·     For correctable errors, when frequently occurred correctable errors reach the threshold based on the leaky bucket algorithm, the system triggers an SMI to notify the BIOS to process the errors. Upon receiving the interrupt request, the BIOS performs the following tasks while ensuring the normal operation of the system:
¡     Take the corresponding measures based on the interrupt type.
¡     Locate and isolate the failed component.
¡     Collect information about the register failure.
¡     Report error events and register information to HDM.
·     For uncorrectable errors that can be recovered, the system labels error data and triggers an SMI. Upon receiving the interrupt request, the BIOS collects information about the failed register, locates the failed component, and reports error events and register information to HDM. Such errors will not affect the operation of the system.
·     For uncorrectable errors that cannot be recovered, such errors can pull the CATERR_N pin low and causes system outage, which then will triggers HDM to collect information about the failed register in the x86 system. This ensures that users can obtain error information even if the system gets stuck.
Figure 4 Error processing
Error logging
The system uses MCA Bank status registers, AER status registers, memory correctable error status registers, and Intel UPI error status registers to log and record log messages for the Core, Uncore, and IIO modules.
To prevent new error logs from overwriting existing log messages, enable the FCERR mode. For more information, see "First corrected error mode."
To set the PCIe correctable error reporting thresholds, see "PCIe correctable error reporting." To set the correctable error threshold for SMI triggering, see "Threshold for correctable errors."
Table 5 Error severity and reporting methods
Error type
Range
Error logging
Corrected or advisory
non-fatal
MCA
MCA Bank registers
AER (severity 0)
IIO error registers
IMC
CORRERRSTATUS (per rank)
Uncorrected recoverable or non-fatal
MCA
MCA Bank registers
AER (severity 1)
IIO error registers
Uncorrected fatal
MCA
MCA Bank registers
AER (Severity 2)
IIO error registers
Catastrophic
MCA
MCA Bank registers
Error processing
Memory error processing
As shown in Table 6, the memory error processing method varies by memory error type.
Table 6 Memory error processing
Error type
Possible causes
Processing method
Bit (Cell) error
High energy particle strike-soft error (SE), or transient error
SDDC, patrol scrub, and demand scrub
For more information about SDDC, see "Memory single-device data correction."
Persistent fault
PCLS
For more information, see "Partial cache line sparing."
Row error
Persistent fault
SDDC and PPR
Bank error
Persistent fault
ADC(SR) and ADDDC(MR)+1
For more information about ADDDC(MR), see "Adaptive double device data correction (multi region) [ADDDC (MR) +1]."
Rank/Device error
Persistent fault
ADDDC(MR)+1, SDDC+1, and rank sparing
Addr/Cmd error
Transient/Persistent fault
DDR4 CMD/ADDR parity error check and retry
Multi-device error(UCE)
Persistent fault + SE
MCA-recovery and address range mirroring
Connector error
Electrical noise or transient error
Transaction retry and DDR4 write data CRC
Wear-out or manufacturing defect or persistent fault
Memory disable/mapout for FRB
Channel failure
Board defect
CPU error processing
CPU errors are mainly processed by using the Core Disable For Fault Resilient Boot (FRB), Core Corrupt Data Containment Enabled for DCU/IFU, and Core DCU Scrubbing functions.
·     Core Disable For FRBAllows the system to power-on despite a failing core-pair. It requires a minimum of one active core-pair for the system to start up.
·     Core Corrupt Data Containment Enabled for DCU/IFU—Allows the system to report uncorrectable errors as recoverable errors (SRAR type) instead of fatal errors when the MCA Recovery – Execution path feature is enabled. This feature transmits corrupted data to DCU/IFU with the error containment bit set. DCU/IFU records the errors in MC Bank of MC1/MC0 and triggers MCERR signals. Then, the software will query error flags to identify whether the errors can be recovered.
·     Core DCU ScrubbingAllows the system to write the DCU data in M state to MLC and leave a data copy in E state in DCU when soft error occurs to DCU data. This write back algorithm has the minimal impact on performance and the fatal MCERR error can be transformed to a correctable error because MLC is protected by the ECC mechanism.
PCIe error processing
PCIe errors are mainly processed by using the PCIe Link Retraining and Recovery and PCI Express Corrup Data Containment functions.
·     PCIe Link Retraining and RecoveryAllows link rebuilding in case of link degrading on PCI Express interfaces without affecting hung processes. If link degrading occurs on a specific lane, the recovery mechanism reduces the link width (for example, from x16 to x8) based on the link degrading rules defined by Platform Design Guide (PDG). If link degrading occurs on multiple lanes, the recovery mechanism attempts to rebuild links at the next available speed.
·     PCI Express Corrup Data ContainmentAlso known as Data Poisoning. This feature allows the system to mark received uncorrectable data errors as bad data and then send the data to the destination. The destination ignores the data or saves the data with the poison bit set. The poison flag can be set by both the transmitter and receiver.
UPI error processing
UPI errors are mainly processed by using the Intel UPI Corrupt Data Containment and Intel UPI Dynamic Link Width Reduction functions.
·     Intel UPI Corrupt Data Containment—Adds a global POISON_ENABLE bit to each UPI link, which can be set from the BIOS to enable data poison. With Intel UPI Date Poison enabled, UPI forwards received poison data to the destination without triggering error signal reporting or logging. It is determined by data consumers how to process uncorrectable data errors.
With UPI Data Poison disabled, UPI cannot identify poison data, and all units operate in Legacy MCA mode. Once poison data is received, Intel UPI will send an error signal and log the error.
·     Intel UPI Dynamic Link Width Reduction—Dynamically adjusts lane width to recover from hard failures occurred on one or multiple data lanes of an Intel UPI link. If possible, the link will keep operating over the narrow width. In case of a physical lane failure, width reduction from full-width to x8 is supported. Half-width support is only available for a minimal set of a x8 bits to allow for the failure of any single data lane. The supported dynamic link width reduction modes are lanes [7:0] or [19:12], which means that a multi lane failure will recover as long as not all failures are on [7:0] and [19:12]. L0p is supported from a full-width Intel UPI link to x8 for power savings and L0p will be disabled if dynamic link width reduction results in a degraded port.
RAS features
Hardware compatibility with RAS features
Table 7 RAS feature and server compatibility (1)
Feature
R6900 G5
R4900 G5
R4700 G5
R4300 G5
R5500 G5
R5300 G5
CPU
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Corrupt data containment mode – Poison mode
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Complex instruction recovery improvements
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Time-out timer schemes
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Error reporting (MCA, AER) – Core, Uncore, and IIO
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Error reporting through MCA 2.0 (EMCA Gen2)
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Processor BIST
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Error Reporting via IOMCA
Yes
Yes
Yes
Yes
Yes
Yes
CPU
MCA bank error control
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Yes
Yes
Yes
Yes
Yes
Yes
CPU
CSR error log cloaking
Yes
Yes
Yes
Yes
Yes
Yes
CPU
Core DCU scrubbing
No
Yes
Yes
Yes
Yes
Yes
CPU
Corrupt data containment – Core
No for 4xxx and xxxxP CPUs
CPU
Viral mode of error containment
No for 4xxx and XXXXP CPUs
CPU
Advanced error detection and correction
Memory
Yes
Yes
Yes
Yes
Yes
Yes
Memory
No
Yes
Yes
Yes
Yes
Yes
Memory
DDR4 command/address parity check and retry
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Memory data scrambling
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Memory demand and patrol scrubbing
Yes
Yes
Yes
Yes
Yes
Yes
Memory
DDR4 memory multi rank sparing
Yes
No
No
No
No
No
Memory
Memory mirroring-intra iMC
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Adaptive data correction (single region) [ADC(SR)]
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Memory corrected error reporting
Yes
Yes
Yes
Yes
Yes
Yes
Memory
DDR4 write data CRC check and retry
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Address range/partial memory mirroring
No for 4xxx xxxxP CPUs
Memory
Memory
Memory disable/map-out for FRB
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Power-up DDR4 post package repair (PPR)
Yes
Yes
Yes
Yes
Yes
Yes
Memory
Failed DIMM isolation
Yes
Yes
Yes
Yes
Yes
Yes
Memory
PMem single device data correct (SDDC)
Yes
Yes
Yes
Yes
Yes
Yes
Memory
PMem double device data correction (DDDC)
Yes
Yes
Yes
Yes
Yes
Yes
Memory
DDRT data ECC (read & write)
Yes
Yes
Yes
Yes
Yes
Yes
Memory
PMem address verification and retry
Yes
Yes
Yes
Yes
Yes
Yes
Memory
PMem memory address range scrub (ARS)
Yes
Yes
Yes
Yes
Yes
Yes
UPI
UPI link level CRC check
Yes
Yes
Yes
Yes
Yes
Yes
UPI
UPI link level retry
Yes
Yes
Yes
Yes
Yes
Yes
UPI
Intel® Ultra Path Interconnect (Intel® UPI) failing lane isolation
Yes
Yes
Yes
Yes
Yes
Yes
UPI
Intel® UPI protocol protection via CRC (16 bit)
Yes
Yes
Yes
Yes
Yes
Yes
UPI
Intel® UPI dynamic link width reduction
UPI
Intel® Ultra Path Interconnect (Intel® UPI) link hot-plugability
UPI
Intel® UPI system quiescence
PCH
PCH end-to-end parity protection
Yes
Yes
Yes
Yes
Yes
Yes
IIO
PCIe link retraining and recovery
Yes
Yes
Yes
Yes
Yes
Yes
IIO
PCIe link CRC error check and retry
Yes
Yes
Yes
Yes
Yes
Yes
IIO
PCIe corrupt data containment (data poisoning)
Yes
No
No
No
No
No
IIO
PCIe ECRC
Yes
Yes
Yes
Yes
Yes
Yes
IIO
PCIe stop and scream
Yes
No
No
No
No
No
IIO
PCIe live error recovery (LER)
Yes
No
No
No
No
No
IIO
PCIe enhanced downstream port containment (EDPC)
No
Yes
Yes
Yes
Yes
Yes
IIO
PCIe card surprise hot plug
Yes
Yes
Yes
Yes
Yes
Yes
IIO
PCIe card hot-plug (add/remove/swap)
Yes
Yes
Yes
Yes
Yes
Yes
System
Faulty DIMM isolation
Yes
Yes
Yes
Yes
Yes
Yes
System
Memory thermal throttling
Yes
Yes
Yes
Yes
Yes
Yes
System
Mem SMBus hang recovery
Yes
Yes
Yes
Yes
Yes
Yes
System
OOB access to error logs
Yes
Yes
Yes
Yes
Yes
Yes
System
Async warm reset (AWR – was previously DWR)
Yes
Yes
Yes
Yes
Yes
Yes
System
Socket disable for FRB
Yes
Yes
Yes
Yes
Yes
Yes
System
Core disable for FRB
Yes
Yes
Yes
Yes
Yes
Yes
System
Enhanced SMM (ESMM)
Yes
Yes
Yes
Yes
Yes
Yes
System
Error injection
Yes
Yes
Yes
Yes
Yes
Yes
System
MCA recovery – execution path
System
MCA recovery – non-execution path
System
MCA 2.0 recovery
System
Local machine check exceptions (LMCE) based recovery
System
Autonomous crash dump (ACD)
Yes
Yes
Yes
Yes
Yes
Yes
Power supply
Hot swappable power supplies in redundancy
Yes
Yes
Yes
Yes
Yes
Yes
Fan
Hot swappable fan modules in N+1 redundancy
Yes
Yes
Yes
Yes
Yes
Yes
Network adapter
Hot swappable OCP network adapters
Yes
Yes
Yes
Yes
Yes
Yes
Drive
Hot swappable drives and RAID controllers
Yes
Yes
Yes
Yes
Yes
Yes
Drive
Drive fault location
Yes
Yes
Yes
Yes
 Yes
Yes
RAID controller
Power fail safeguard
Yes (with supercapacitor installed)
RAID controller
Drive fault monitoring and data recovery
Yes
Yes
Yes
Yes
Yes
Yes
RAID controller
RAID controller fault location
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Dual out-of-band management software images
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Centralized fault management system
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Location of faulty processors
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Location of faulty DIMMs
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Location of faulty PCIe devices
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Location of faulty fan modules
Yes
Yes
Yes
Yes
Yes
Yes
HDM
System board monitoring and environment information from HDM
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Remote update of system software and firmware from HDM
Yes
Yes
Yes
Yes
Yes
Yes
HDM
BSoD screenshots
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Video replay
Yes
Yes
Yes
Yes
Yes
Yes
HDM
Log download
Yes
Yes
Yes
Yes
Yes
Yes
RAS feature overview
Feature name
This feature covers the error detection and correction capability at the entire processor level. It provides data protection and data integrity through enhanced cache error reporting, data path parity protection (DPPP) and address path parity protection (APPP).
Purpose
Ensure the reliability at the component level.
Configuration
Enabled by default and cannot be disabled.
Remarks
N/A
Feature name
The processor supports Legacy IA-32 MCA mode and corrupt data containment mode
In Legacy IA-32 MCA mode, if the system detects an uncorrectable error on a module (including error-generating modules and data-transmitting modules), an MCE is directly triggered to reset the system. In corrupt data containment mode, if the system detects an uncorrectable error on a module (including error-generating modules and data-transmitting modules), an MCE will not be triggered. On the detection of an uncorrected error, the detector sets a poison bit, and the system continues data transmission with the poison bit and triggers CMCI interrupt. The receiver can perform various processing operations as needed, including ignoring errors (for example, an error of a certain pixel on the screen), discarding data, initiating retransmission, and triggering MCE.
Purpose
Improve the fault tolerance of the entire system.
Configuration
Enabled by default and can be disabled from the BIOS.
Remarks
N/A
Feature name
Most complex instruction flows are recoverable on processors.
This feature is used to improve the probability of system recovery when the following events occur simultaneously:
·     An SRAR event occurs.
·     A complex instruction is being processed.
Purpose
Improve system reliability.
Configuration
Remarks
N/A
Feature name
This feature allows timeout timers within various sub-modules to report the faults as close as possible to the fault source. The following timeout features are implemented on the processors installed on G5 rack servers:
·     Core 3-strike.
·     CHA TOR timeout
·     Intel UPI link level retry timeout.
·     Mesh-to-Memory (M2Mem) timeout (formerly referred to as CHA BT timeout).
·     IRP Config_retry_time-out.
·     PCIe port Completion Timeout (CTO).
Purpose
Improve the server availability and serviceability.
Configuration
Enabled by default, and partially configurable.
Remarks
N/A
Error reporting (MCA, AER)Core, Uncore, and IIO
Feature name
Error reporting includes logging and error signaling. The G5 rack servers mainly support error reporting through Machine Check Architecture (MCA) and Advanced Error Reporting (AER). Platform-specific memory and UPI error reporting mechanisms are also available.
Purpose
·     Report various types of errors occurring in a chassis.
·     Improve mean time to repair (MTTR).
·     Accelerate error debugging, especially in the field.
Configuration
Enabled by default and not configurable.
Remarks
N/A
Feature name
Prior to EMCA Gen2, Legacy IA-32 MCA directly reports error signals to OS/VMM, which does not utilize the UEFI firmware capability on fault diagnosis. EMCA Gen2 allows the firmware to strengthen the error logging capability of MCA.
When this feature is enabled, UEFI-FW SMI handler can read MCA bank registers and other error logging registers before the OS machine check handler reads and clears the MCA banks.
Purpose
Provide UEFI FW recovery mechanism.
Configuration
Enabled by default and configurable from the BIOS.
Remarks
Mutually exclusive with EMCA Gen1.
Processor BIST
Feature name
Processor BIST
BIST a self-check module inside the processor. It performs self-check on each core of the processor during the BIOS startup process and records the self-check result.
Purpose
Detect errors in the processor.
Configuration
Remarks
N/A
Feature name
Error reporting via IOMCA
This feature allows IIO uncorrectable fatal and nonfatal errors to send error signals through MCE to improve the platform's diagnostic capabilities. If this feature is not available, all the IIO uncorrectable errors are reported through NMI or platform-specific error handlers that use SMI or ERROR_N[2:1] pins.
Purpose
Provide a uniform error reporting mechanism aligned with MCA for uncorrectable error signaling without relying on NMI.
Configuration
Disabled by default and configurable from the BIOS.
Remarks
N/A
Feature name
This feature allows the BIOS to hide correctable errors and UCNA errors from the operating system because these errors are already corrected by the hardware. Thus, a certain number of correctable errors can be regarded as normal system actions. This feature prevents the operating system from taking any action until the BIOS is ready to expose such errors. When this feature is enabled, only SMM and PECI can access this type of error logs.
Purpose
Enhance BIOS control over errors.
Configuration
Remarks
N/A
Feature name
First corrected error (FCERR) mode of error reporting
This feature avoids correctable error overwriting when multiple correctable errors are reported.
In the case of a correctable error burst, the error handling FW/SW will be able to capture all error logs associated with a given event before clearing the logs. The hardware will not rewrite log registers before error log registers are cleared.
Purpose
Improve serviceability and faulty FRU identification capability.
Configuration
Remarks
N/A
Feature name
You set PCIe correctable error thresholds on the root port basis and implement a better correctable error reporting system through SMI.
Purpose
Implement a better correctable error reporting architecture.
Configuration
Enabled by default. You can set the thresholds from the BIOS.
Remarks
N/A
Feature name
Threshold for corrected errors
This feature applies to PCIe and UPI links, and controls the thresholds of correctable error events.
This feature allows triggering an SMI when a certain number of correctable errors occur on the PCIe links.
When EMCA Gen2 is enabled, this feature allows triggering CSMI after a certain number of correctable errors occur on UPI links.
Purpose
Capture threshold-based error logs for FRU isolation, PFA, and debugging when FFM is enabled.
Configuration
Remarks
N/A
Feature name
The operating system generally does not obtain error logs from control and status registers (CSR), but some drivers might be able to access the error logs. Because these errors are already corrected by the hardware, we allow certain levels of errors to be considered normal system behavior.
This feature hides part of the CSR error log registers and prevents the operating system from processing these registers until the BIOS is ready to expose these errors.
Purpose
With BIOS-based error handling code, system developers can manage system error log capturing and reporting in absence of any interference from the error handling code in the operating system. This enhances the serviceability of the server.
Configuration
Remarks
N/A
Core DCU scrubbing
Feature name
Core DCU scrubbing
This feature enables the system to write the DCU data in M state to MLC and leave a data copy in E state in DCU when soft error occurs to DCU data. This write back algorithm has the minimal impact on performance and the fatal MCERR error can be transformed to a correctable error because MLC is protected by the ECC mechanism.
Purpose
Improve the system availability.
Configuration
Remarks
N/A
Feature name
This feature enables a system recovery when a hardware uncorrectable error is detected in the memory or MLC/LLC caches. It can cooperates with the uncore corrupt data containment feature.
If the corrupted data receiver is a core like obtaining data from memory, the data is discarded or the core triggers a fatal MCERR or a recoverable MCERR (SRAR event). Thus, the operating system is allowed to make an attempt to recover the system.
Purpose
Improve the system reliability.
Configuration
Remarks
N/A
Feature name
The viral mode is an advanced fault-tolerant feature designed for fatal errors. It is used to prevent faults from spreading to non-volatile storage devices or network devices. Errors that can cause the processor to enter the viral mode are all uncorrectable errors.
Purpose
Control the spread of errors.
Configuration
Remarks
Enable the poison mode first.
Feature name
Advanced error detection and correction (AEDC)
AEDC enables fault detection by using residue checking and parity protection techniques. Fault correction is completed by instruction retry. Correctable error events are logged in IFU MCA bank. If the retry did not correct a fault, a MCERR signal is triggered. AEDC does not need any additional support of SW/OS, but relies on the current error reporting mechanism. The AEDC-based error recording and signal triggering are managed by IFU MCA bank and is disabled by default. The error recording and signal triggering can be enabled through OS/UEFI-FW during the system initialization phase.
Purpose
Improve the error coverage in the core execution engine.
Configuration
Disabled by default.
Remarks
N/A
Feature name
Memory single-device data correction (SDDC)
SDDC can correct multi-bit errors on a single x4 or x8 DRAM device. SDDC uses a read retry method to correct errors. That is, SDDC sets a certain bit to the opposite value one by one, and then calculate whether the CRC matches successfully.
Purpose
Effectively handle hard failures on DRAM devices, improving the availability of the memory.
Configuration
Remarks
·     X8 SDDC is available only when the operating mode of the memory is set to lockstep from the BIOS.
·     Though a hard failure on a DRAM device can be corrected by SDDC, the performance of the memory will degrade sharply.
Feature name
PCLS can correct single-bit errors. When a permanent single-bit error occurs on the cache line, a backup bit can be used to replace the error bit, which makes PCLS performance better than ADDDC(MR)+1 and ADC(SR)+1. A single memory channel can support a maximum of 16 sets of PCLS.
Purpose
Configuration
Remarks
PCLS and ADDDC(MR)/ADC(SR) cannot exist in the same bank or rank at the same time.
Feature name
The DDR4 command/address parity check and retry feature include logging of the address after command/address parity check errors and retrying the command/address. Command/address parity check errors are reported via Alert PIN and can be resolved. Although one alert signal is shared by ranks/DIMMs in one channel, which causes the IMC to fail to determine which rank/DIMM or which command triggers the alert signal, the system still locates the source of the error and attempts to restore during the error processing phase. This feature equals to memory address parity protection.
Purpose
Detect and handle errors during read, write, or various other protocol-related transmissions on the memory command/address bus to improve reliability.
Configuration
Remarks
N/A
Feature name
The memory data stream is pseudo-randomly coded through the linear shift register to balance the 0/1 distribution and reduce the probability of soft errors. In addition, the memory address double-bit error detection is realized.
Purpose
Prevent a large number of high and low voltages, reducing electrical shock and increasing reliability.
Configuration
Remarks
N/A
Feature name
Demand scrubbing is the ability to write the corrected data back to the memory if a correctable error is detected on a read transaction. If an uncorrectable error is detected in the data, another read operation will be tried.
Patrol scrubbing is the ability to proactively searching system memory and attempting to correct any errors. The scrubbing and sparing (SSR) engine in the CHA reads the contents of the memory when it memory is idle according to the set frequency and step size. If a correctable error is detected in the read data, patrol scrubbing will write the corrected data back to the memory.
This feature reduces the occurrence of uncorrectable errors by read retry and correcting single-bit errors.
Purpose
Reduce the possibility of memory error occurrence.
Configuration
Remarks
·     Once this feature is enabled, even if the MCA corrupt data containment mode is set, an MCE interrupt will be reported by default on the detection of an unrecoverable error. Then, a reset operation is triggered.
·     An error might be detected on the unused memory through writing memory.
·     This feature might increases power consumption.
Feature name
During memory initialization, this feature allows the system to select one rank as a spare rank per channel. When the system predicts that an error is to occur on a memory block, the data in the memory block that might fail will be copied to the backup memory. This prevents the system crash due to uncorrectable errors. The implementation of this feature requires the cooperation of the BIOS and the support of chipset.
Purpose
Handle hard failures on DRAM devices, greatly improving the availability of the memory, which is more robust than SDDC and DDDC.
Configuration
Disabled by default and can enabled from the BIOS.
Remarks
·     Each memory channel the memory capacity of one rank, but memory bandwidth will not be affected.
·     Memory rank sparing is mutually exclusive with memory mirroring.
Feature name
The feature saves two copies of memory data in the primary memory and mirroring memory respectively. This can ensure that when a DIMM chip fails, the memory protection technology can use the backup bits to retrieve data automatically. Since cross mirroring between channels is used, each channel has a complete set of memory data copy, which ensures a smooth server operation.
Purpose
Avoid data loss and device shutdown caused by memory failures and improve the availability of the memory through redundancy.
Configuration
Disabled by default and can be enabled from the BIOS.
Remarks
·     Make sure the installation of DIMMs meets the requirements of memory mirroring.
·     Only 50% of the memory capacity is exposed to the operating system.
·     Memory mirroring is mutually exclusive with memory rank sparing.
Feature name
This feature generates multiple data groups related to data flows and corrects memory data unit errors.
Purpose
Correct memory data errors automatically after the errors occur. The memory correction of DIMMs does not affect each other.
Configuration
This feature takes effect automatically and cannot be disabled.
Remarks
N/A
Feature name
This feature provides leaky bucket algorithm and SMI/NMI/ERROR_N [0] per rank. Error signaling for platform use only and are not visible to standard OS/VMM. According to the number of correctable error records in each rank, various RAS features can be activated, such as SDC(SR), ADDDC(MR)+1, SDDC, x8 SDDC+1 and rank sparing.
Purpose
Provide correctable error counters per rank.
Configuration
Remarks
N/A
Feature name
This feature enables the system to check DDR4 specification-based write data CRC check in the DRAM devices and sends an event back to the processor or iMC for retry. The DIMMs will use the PAR_ALERT signal to handle the CRC mismatch.
When this feature is enabled, two additional bursts are added (10 bursts in total) to transmit the write CRC bits. This improves the coverage for bus transient and persistent errors on the system board and detects all of 1B, 2B, odd bits, and vertical column errors.
Purpose
DDR4 write data CRC protection detects DDR4 data bus failures during write operations.
Configuration
Remarks
N/A
Feature name
In partial mirror mode, you can set the size of mirrored memory. All error detection, signaling, and correction operations in the full mirror mode can be applied to the partial mirror mode in the mirroring region.
Purpose
Save critical codes or data by using the partial mirror mode.
Configuration
Remarks
Feature name
In virtual lockstep mode, the ADDDC (MR) feature can repair hard failures on DRAM devices.
If a hard failure on a DRAM device occurs at bank/rank region granularity, it is mapped out through the adaptive virtual lockstep mode. The ADDDC(MR)+1 feature allows a maximum of two such hard failures and is able to correct a single-bit error subsequently.
Purpose
Handle hard failures on DRAM devices.
Configuration
Remarks
This feature cannot be used together with mirror mode or rank sparing.
Feature name
This feature allows the memory to be initializes and to boot the operating system even in the event of a memory failure. Memory initialization consists of four phases: memory discovery phase, memory training phase, memory test phase, and DDR4 DRAM PPR (Post Package Repair) phase.
Purpose
Avoid and isolate memory failures at the system startup to improve the system availability.
Configuration
Enabled by default.
Remarks
N/A
Feature name
This feature uses row redundancy circuit to resolve single row failures for a DRAM device. It mirrors the faulty row to the built-in redundant row.
Purpose
DRAM units are increasingly susceptible to electrical, thermal, and mechanical stresses. PPR provides a memory repair solution to enhance the system reliability.
Configuration
Enabled by default.
Remarks
The DRAM must be larger than 4 GB.
Feature name
Faulty DIMM isolation is one of the fault management features of the servers using Intel Xeon processors. The platform can keep track of the number of correctable errors, carry out failure prediction analysis and scheduled services, and replace faulty components before the severity of the errors becomes uncorrectable. The platform system management will identify the root cause of the DIMM failure, map the faulty device, and schedule a repair.
Purpose
Identify the faulty DIMM for replacement to improve maintainability.
Configuration
Enabled by default.
Remarks
N/A
Feature name
This feature enables PMem to have the ability to correct errors of a single device through erasure and error decoding processes. When the data can be corrected, the PMem controller corrects the data and sends the corrected data to the host and cleans the data according to the PMem correctable error processing policy that is set by the PMem firmware.
Purpose
Correct errors and send the corrected data back to the host.
Configuration
Remarks
In the case of memory failures, although SDDC can realize error correction, continuous correction may increase the delay from sending the correction data.
Feature name
This feature corrects errors caused by dual device failures and records events that cannot be corrected.
Purpose
Configuration
Remarks
Feature name
This feature protects DDRT data by ECC. It enables ECC check and correction during the write and read operations of CSCRIPTS DCPMMs.
Purpose
Ensure DDRT data correctness during write and read operations.
Configuration
Remarks
N/A
Feature name
This feature checks the PMem memory address and provides a mechanism to detect errors that are correctable most of the time through retry.
Purpose
Ensure the correctness of the PMem memory address and the reliability of the system memory.
Configuration
Remarks
N/A
Feature name
Before contiguous memory space is allocated to an application, AD mode can check whether ARS is complete and identify bad memory areas (system physical addresses) allocated to the file system. Then, the OS can map out/avoid using the bad memory areas. If an application accesses a bad memory area, the issue occurred at next access to a known bad memory area will be processed by software event instead of the MCA.
Purpose
Prevent the system from using DRAM devices that are known to be damaged or faulty and prevent applications from crashing due to accessing these address spaces.
Configuration
Enabled by default.
Remarks
This operation is realized based on the OS/UEFI code and is often enabled during OS boot.
Feature name
This feature allows the system to perform CRC check on data packets transmitting on the UPI links to detect errors.
Purpose
Enhance the UPI interconnect reliability.
Configuration
Remarks
N/A
Feature name
This feature allows a link to continue the normal operation when the receiver detects a CRC error. On the detection of a CRC error, the receiver sends a retry request to the transmitter. If the CRC error occurs due to a transient event, the retry operation is expected not to experience an error. This feature allows a maximum of two retry attempts. If the error continues after two retry attempts, the physical layer will be initialized. If the error still exits after the initialization, an uncorrectable error is triggered.
Purpose
Avoid transmission errors caused by transient data errors, improving the transmission reliability of UPI links.
Configuration
Remarks
N/A
Feature name
This feature enabled the processor to capture CRC error logs and use the Intel provided software utility to analyze the logs and determine the mapping to a specific channel.
Purpose
Determine the source of CRC errors at Intel® UPI channel granularity and determine whether CRC errors are random events or are associated with a specific lane due to persistent lane failures (or stuck at a lane failure).
Configuration
N/A
Remarks
If multiple lanes fail, the software utility will not be able to locate the affected lane.
Feature name
This feature achieves more reliable inter-processor links through 16-bit CRC and improves data integrity through error detection. You can configure notifications for the system to detect CRC errors and identify potential link degradation issues that could lead to future link failures through the logs.
Purpose
Configuration
Remarks
N/A
Feature name
Dynamic link width reduction clears hard failure for one or multiple data channels on a physical Intel UPI link through dynamically adjusting the link width. If the system detects persistent errors on the link, the Intel UPI link width can be halved.
Purpose
Improve the uptime and reliability of the system by enabling the system to continue running even when hard failure is detected in some channels.
Configuration
Remarks
·     If the clock link fails, the UPI link width narrows by 50%.
·     After the link width is reduced, fault tolerance is not available for new failures.
·     As a best practice, arrange the maintenance when the issue is present.
Feature name
The Intel UPI specification defines the mechanism for enabling and disabling Intel UPI links without a cold reboot. Only in the slow mode, the newly added Intel UPI link can reach the operation speed directly and can be reconfigured.
Purpose
Realize the ability to operate independently of another link in the slow mode.
Configuration
Remarks
N/A
Feature name
This feature provides a mechanism to change Intel UPI link from L0 to L1 and then end running transactions in the UPI interface cache, preventing new transaction requests from being issued without resetting the entire system.
Purpose
This is a fundamental building block for the serviceability and scalability characteristics of the system. UPI silence is required before the link is connected or disconnected.
Configuration
Remarks
N/A
Feature name
This feature protects data and command paths in PCH.
Purpose
Improve the system reliability and lower the data damage impact to the minimal degree.
Configuration
Remarks
N/A
Feature name
This feature allows the processor to start a PCIe link retraining based on error conditions defined by PCI Express Base Specification, v3.0.
Retraining the link includes resetting the link training and status state machine (LTSSM) to the recovery state and continuing the operation. LTSSM in the recovery state can start a speed or width degradation if errors are further detected during the retraining sequence.
Purpose
Improve the PCIe link reliability through error detection and retraining during link operation.
Configuration
Remarks
N/A
Feature name
This feature provides the ability of CRC error detection and transaction retry on error occurrence. The point is to protect the link from signal integrity issues caused by EMI, marginal links, poor connectors, long trace lengths, and so on. This feature provides a mechanism to detect and correct errors that can be corrected most of the time through retry.
Purpose
Improve the PCIe link reliability in case of low signal integrity.
Configuration
Remarks
N/A
Feature name
This feature attached an EP bit to the header any time the system detects an uncorrectable error before forwarding the packet to the next agent. This is used to achieve data integrity in both directions at the transaction level. The receiver detects the poison TLP and redirects the error event as a non-fatal warning (correctable error event) instead of sending it as an uncorrectable error signal, to avoid system reset.
Purpose
Improve the uptime and reliability of the system by allowing the system to continue operation when a poison mark is present on faulty data.
Configuration
Remarks
N/A
PCIe ECRC
Feature name
PCIe ECRC
This feature implements PCIe end-to-end CRC depending on the PCI Express Gen 3 specification. When the system detects an ECRC error, the root port reports it as uncorrectable non-fatal error.
Purpose
ECRC applies to the storage segment to achieve higher data integrity during data exchange between two PCIe ends.
Configuration
Remarks
N/A
Feature name
This feature allows the PCIe port to be disabled when a poison is detected in the outbound data. This can prevent corrupt data from being used by PCIe devices that do not support corrupt data containment. Once the IIO sub-module detects corrupt data in the TX direction, it drops the data packet, disable the port, record fatal error logs, and send error signals.
Purpose
Achieve high serviceability in a system where non-compliant PCIe ends are used. This feature detects poison packets in PCIe outbound direction and flags errors without sending poison data. This minimizes the system downtime by identifying the precise source of corrupt data and simplifying the repair process.
Configuration
Remarks
Enable this feature on PCIe devices that do not support poison TLP.
Feature name
When a PCIe root port detects an error, LER can shut down the PCIe link of the root port and then restore the link via OS/driver/UEFI-FW in a cycle. LER consists of two phases: error suppression and recovery.
Error suppression phase: When a root port detects an uncorrectable error, the link affected by the error is shut down and all transmissions on the link can be processed properly, allowing the system to continue to work correctly.
Recovery phase: When the error is properly resolved, the link can be restored via OS/driver/UEFI-FW.
Purpose
Configuration
Remarks
N/A
Feature name
Downstream Port Containment (EDPC) allows data transmission to be stopped when an uncorrectable error is detected on the downstream port or on a device connected to the downstream port. This can avoid the propagation of potentially corrupted data and allow software to restore the data. EDPC is an enhancement to the DPC function, which adds support for the Root Port Programmable IO (RPPIO) error.
Purpose
Configuration
Remarks
N/A
Feature name
This feature complies with the PCI Express protocol and does not require the OOB SMBus mechanism for hot removal and insertion.
Purpose
Remove or install a PCIe module during the system operation.
Configuration
Remarks
Proper software operations are required for the unexpected removal.
Feature name
This feature complies with the PCI Express protocol and requires the OOB SMBus mechanism for hot removal and insertion.
Purpose
Configuration
Remarks
Feature name
The fault management system tracks the number of correctable errors and performs predictive failure analysis to notify the user before the error severity becomes uncorrectable. This feature identifies specific failed DIMMs and sends alarms through HDM to facilitate users to replace the target DIMMs.
Purpose
Configuration
Remarks
N/A
Feature name
This feature allows the system to slow down memory access rate when the memory temperature exceeds the set threshold.
Purpose
Prevent memory data errors or device damage caused by overheating, reducing the risk of server shutdown.
Configuration
Enabled by default.
Remarks
Memory overheating might degrade the memory performance.
Feature name
This feature enables the BIOS to perform SMBus error recovery by using SMI in runtime.
You can configure the memory controller of the server to generate an SMI on SMBus error occurrence. If the SMI occurs, the BIOS SMI handler perform the following operations:
1.     Save the TSOD address issued last time.
2.     Save the current settings of TSOD polling and error recovery.
3.     Disable both TSOD polling and error recovery.
4.     Program safe temperature.
5.     Save the current settings of closed loop thermal throttling (CLTT) and disable CLTT.
6.     Trigger the hardware timer, activate the soft reset for the SMBus, and start the periodic SMI of N ms. The value N depends on the platform.
7.     When the periodic SMI expires, identify whether the recovery is completed and disable the periodic timer. If the recovery is not completed, the periodic SMI handler will be executed again.
8.     After the SMBus recovery is completed, disable soft reset, and restore the system state saved in steps 1 to 5 above.
Purpose
Perform SMBus error recovery in runtime, improving the availability of the system.
Configuration
Remarks
N/A
Feature name
This feature is an HDM-based RAS implementation. It uses a PECI interface to access MCA bank registers to obtain memory error logs, UPI error logs, and IIO AER logs.
Purpose
Improve the monitoring ability of HDM fault management system.
Configuration
Remarks
N/A
Feature name
In some cases, global reset is downgraded to warm reset for the BIOS to collect error information after reboot. When the system encounters a catastrophic error and the error information cannot be collected through OOB, use this feature to collect some sticky registers after the system warm reset. These error messages can be used as an important reference for error location.
Purpose
Improve the system maintainability.
Configuration
Remarks
N/A
Feature name
This feature selectively disables sockets during system boot, which allows the system to boot in the event of processor failures. The platform needs appropriate logic to detect failed processors during the boot and to ensure that accidental socket disabling will not happen.
Purpose
During the system boot, if any failure that affects the entire CPU or the system management engine occurs, the FRB flow is triggered to disable the affected CPU and complete the boot. This system will provide logs for the maintenance personnel to quickly diagnose issues. Without this feature, the system might hang during the boot and maintenance personnel might need additional resources and time to diagnose the root cause.
Configuration
Remarks
You cannot disable legacy socket.
Feature name
Core disable for FRB (fault resilient booting)
This feature disables a failed core, and allows the system to continue the boot process. The platform uses processor BIST results on each core to identify the failed cores and disables or maps out the failed cores in subsequent boots. UEFI will map out the affected processor cores and report the cores to the operating system.
Purpose
Ensure the server availability by allowing the system to boot successfully with failed cores.
Configuration
Enabled by default.
Remarks
A minimum of one core is operating correctly in each processor.
Enhanced SMM (ESMM)
Feature name
Enhanced SMM (ESMM)
Multiple RAS features report faults through eMCA gen2, and SMM is part of eMCA gen2. This feature facilitates the SMM mode by improving the following attributes:
·     Threads in long flow/blocked indicators.
·     Target SMI.
·     SMM dump state storage into internal MSRs.
Purpose
Improve the existing SMM mode and promote the use of eMCA gen2 for error reporting.
Configuration
Remarks
This feature is available only in eMCA mode.
Error injection
Feature name
Error injection
You can configure error ejection settings from the BIOS. After enabled, this feature tests the system performance by injection error.
Purpose
Improve the system reliability by providing the ability to verify RAS features.
Configuration
Remarks
N/A
Feature name
This feature assists the server to recover from uncorrectable errors through the software layers. The software layers including OS, VMM, DBMS, and applications, can assist the system to recover from uncorrectable errors at the hardware level, and mark the errors as corrupt data through the processors.
If a processor identifies an error that cannot be corrected by hardware, the processor marks the data as corrupt data and hands the error event firmware and/or the OS. If the firmware or operating system has a redundant copy of the data, the error might be corrected. If the error occurs in the application space, the operating system can use the SIGBUS event to signal the application and allow further recovery or termination of the application and keep the operating system running. If the error occurs in the kernel space, the operating system will trigger a kernel panic.
Purpose
Recover the system from uncorrectable errors through the software layers.
Configuration
Remarks
OSs recommended: WS 2008 or higher, REHL 6 or higher, and SUSE 11 or higher.
Feature name
For some uncorrectable errors on non-execution paths, the OS can recover or isolate faulty data. The non-execution paths include patrol scrub events or LLC explicit write back transaction processing.
If a processor identifies an error that cannot be corrected by hardware, the processor marks the data as corrupted data and hands the error to firmware and/or the OS. The OS isolates the affected page and prevents applications from using it. This allows the system to continue to operate correctly. If the error occurs in the kernel space, the OS might not be able to isolate the faulty page and can only log the error and continue normal operation.
Purpose
Improve the system availability through the software layers.
Configuration
Remarks
MCA 2.0 recovery
Feature name
MCA 2.0 recovery (as per EMCA gen2 architecture)
EMCA gen2 allows firmware to intercept errors (correctable and uncorrectable errors) triggered by MCA and enables FFM of error handling and possible recovery.
Purpose
Recover the system from uncorrectable errors defined by the EMCA Gen2 specification through the software layers.
Configuration
Remarks
N/A
Feature name
LMCE allows the system to deliver the SRAR-type UCR events to the affected logical processors receiving poison data. LMCE implements following functions:
·     Enumeration—Identifies the hardware that supports LMCE through software.
·     Control mechanism—UEFI has the ability to enable or disable LMCE. This requires the software to enter LMCE.
·     Identification of LMCE—The software can identify whether the delivered MCE is only for one logical processor on MCE delivery, and global participation is not required.
Purpose
Prevent software from broadcasting an MCE of recoverable error type to all threads.
Configuration
Remarks
Corrupt data containment – Uncore must be enabled.
Feature name
This feature enables HDM to collect crash records through OOB. Crash records have the following characteristics:
·     Provide standard debugging data.
·     Available for debugging personnel.
·     Available for external customers.
·     Contain abundant CPU information for failure location.
Purpose
Collect fault information as detailed as possible to improve maintainability.
Configuration
Remarks
N/A
Feature name
Hot swappable power supplies in N+N redundancy
The power supplies can be hot swapped at the server rear.
Purpose
Ensure the availability of the power system.
Configuration
Remarks
N/A
Feature name
The fan modules support N+1 redundancy. The server can operate correctly when a single fan module fails. You can hot swap a power supply at the server rear.
Purpose
Ensure the availability of the server heat dissipation system.
Configuration
Remarks
N/A
Feature name
This feature provides the support of an OCP slot. You can hot insert or remove an OCP network adapter directly from the device back panel.
Purpose
Ensure that the OCP network adapter can be hot swappable.
Configuration
Remarks
You must use OCP network adapters and operating systems specified in H3C compatibility matrixes..
Feature name
RAID levels 0, 1, 1 ADM, 10, 10 ADM, 1E, 5, 50, and 60 are supported. The drives are hot swappable.
Purpose
Ensure the availability of the storage system.
Configuration
RAID arrays require scheduled configuration
Remarks
Support for RAID levels varies by RAID controller configuration.
Feature name
The server supports locating a single drive fault.
Purpose
Quickly locate drive faults.
Configuration
Remarks
N/A
Feature name
When a system power failure occurs, the supercapacitor of a power fail safeguard module can provide power for a short period of time for data to be transferred from the DDR memory to the flash card. When the power recovers, the data can be transferred back to drives.
Purpose
Prevents data loss caused by unexpected power failure.
Configuration
Remarks
Because of RAM battery capacity limit, the data can be protected for hours or tens of hours. The actual time depends on the supercapacitor model.
Feature name
Drive fault monitoring and recovery
This feature enables the system to inform users of physical drive or logical drive faults through in-band or out-of-band (SEL log reporting) channels.
If RAID is configured, the feature can use RAID features to recover data in failed drives.
Purpose
Enables fast fault identification to prevent error expansion and helps data recovery through RAID.
Configuration
Remarks
N/A
Feature name
RAID controller faults can be displayed in many ways. For example, overtemperature errors can be reported by sensors and RAID controller operation events can be logged as log messages.
Purpose
Simplifies monitoring of RAID controller status and identifies RAID controller faults to accelerate troubleshooting.
Configuration
Remarks
This feature is only supported by LSI RAID controllers except the 9300, 9311, and 9400 LSI RAID controllers.
Feature name
If the one image fails, HDM can start up by using the other image.
Purpose
Ensure the availability of HDM.
Configuration
Remarks
N/A
Feature name
The fault management system comprehensively monitors the server, provides a reliable fault detection and prediction mechanism, notify users of faults through HDM. The following faults can be detected:
·     Processor hardware failure, including CAT errors, self-check failure, and configuration errors.
·     Overtemperature alarms, including alarms at air inlet and outlet, processors, memory, power supplies, and drives.
·     Voltage faults on the server boards.
·     Fan module faults.
·     Power source faults, including power supply input lost (AC/DC), overtemperature conditions, and power supply fan failure.
·     DDR3 and DDR4 DIMM faults, including correctable ECC errors exceeding threshold, overtemperature conditions, and configuration errors.
·     Storage system faults, including LSI storage controller errors, SAS/SATA drive faults, and logical drive exception.
·     System shutdown.
·     Hardware operation status (via system health LED).
·     Faulty components (via SEL log messages)
·     HDM and OS reboot errors (via SEL log messages).
Purpose
Provide a unified fault management.
Configuration
Remarks
N/A
Feature name
Review the SEL log for the location of a faulty processor from HDM.
Purpose
Quickly locate a faulty processor.
Configuration
Remarks
N/A
Feature name
Review the SEL log for the location of a faulty DIMM from HDM.
Purpose
Precisely locate a faulty DIMM.
Configuration
Remarks
N/A
Feature name
Review the SEL log for the location of a faulty PCIe device from HDM.
Purpose
Precisely locate a faulty PCIe device.
Configuration
Remarks
N/A
Location of faulty power supplies
Feature name
Review the SEL log for the location of a faulty power supply from HDM or use power supply LEDs to identify the faulty power supply.
Purpose
Quickly locate a faulty power supply.
Configuration
Remarks
N/A
Feature name
Review the SEL log for the location of a faulty fan module from HDM.
Purpose
Quickly locate a faulty fan module.
Configuration
Remarks
N/A
Feature name
HDM monitors the voltage, current, temperature, and power of key components in real time and provides corresponding graphics. Data are recorded by period.
Purpose
Configuration
Remarks
N/A
Feature name
HDM supports remote update of the system software and firmware
Purpose
Improve the serviceability.
Configuration
Enabled by default and cannot be disabled. You can update the software and firmware from HDM.
Remarks
N/A
BSoD screenshots
Feature name
BSoD screenshots
This feature automatically takes a bluescreen of death (BSoD) screenshot upon a system crash of Windows for future troubleshooting. HDM can save a maximum of 10 BSoD screenshots, which are named with a sequence number and the screenshot time. When the maximum number of screenshots is reached, a new BSoD screenshot overwrites the oldest one.
Purpose
Help locate faults when a system shutdown occurs.
Configuration
Enabled by default and can be disabled from HDM.
Remarks
·     Make sure the KVM service has been enabled.
·     HDM can save a maximum of 10 BSoD screenshots
Video replay
Feature name
Video replay
This feature records the server status upon occurrence of severe operating system events, including crash, restart, and shutdown. You can replay these videos to analyze or troubleshoot the recorded events.
Purpose
Help locate faults by viewing videos from HDM.
Configuration
Remarks
·     If the remote console is open when an event triggers video recording, video recording will fail.
·     Crash event recording is available only for the Windows operating system.
·     If the operating system is in sleep state when an event occurs, the video replay displays no signal.
Log download
Feature name
Log download
This feature enables users to download records about events, storage, configuration, and HDM throughout the lifecycle of the server. You can use UniSystem to parse event logs and storage logs to learn about the server operation status. You can download the log entries for a period or download the entire log to an .sds log file.
SDS log messages record context for every error, provide simple recommended actions, and allow message obtaining through multiple in-band or out-of-band methods. Information is provided in plaintext and is easy to use.
Purpose
Improve the serviceability by providing fault location ability through faulty data collection, fault analysis, and fault diagnosis.
Configuration
Enabled by default and can be downloaded from HDM.
Remarks
You cannot view the logs from HDM. To view the log entries, download the log entries to an .sds log file and import the .sds log file to UniSystem.
Appendix A Glossary
Word/Acronym
Definition
AER
BIOS
Basic Input Output System
BIST
Built in Self-Test
CDC
Corrupt Data Containment, also known as Data Poisoning
Core
A portion of a processor containing the processing units such as Execution Engine (EE) and the dedicated caches
CHA
Cache and Home Agent
CMCI
CRC
Cyclic Redundancy Check
DCU
Data Cache Unit, a L1 cache
DMI
Direct Media Interface, proprietary data path between Intel CPU and PCH
DIMM
Dual-Inline-Memory-Module, a memory device on a socketable substrate
ECC
Error Checking and Correcting
EDPC
Enhanced Downstream Port Containment
EMCA
Enhanced Machine Check Architecture
FFM
Firmware First Model
FW
Firmware
FRB
HDM
H3C Device Management, IPMI-compliant module-level management controller developed by H3C
HW
Hardware
ICU
Instruction Cache Unit
IEH
Integrated Error Handler
IFU
Instruction Fetch Unit
IIO
Integrated I/O Module
IMC
Integrated Memory Controller
LLC
Last Level Cache (L3 cache)
LPC
Low Pin Count, used to connect to I/O devices
MCA
MCE
Machine-Check Exception
MLC
Mid Level Cache
MRC
Memory Reference Code
OS
Operating system
PCH
Platform Controller Hub
PCIe
Peripheral Component Interconnect Express
PCLS
Partial Cache Line Sparing
POST
Power On Self Test
RAS
Reliability, availability, serviceability
Runtime
OS runtime
SDDC
Single device data correction (DIMM CRC)
SMI
TLP
PCI Express Transaction Layer Packet
UEFI
Unified Extensible Firmware Interface
Uncore
Functionality in processor socket other than processor cores.
It encompasses CHA, M2M, Intel®UPI, IMC, IVR, PCU, and UBOX. Note that IIO module is considered as outside of the Uncore but it is still integrated in the same die.
UPI
VT-d
Intel Virtualization Technology For Directed I/O
