H3C G3&G5 Servers HDM IPMI Basics Command Reference-6W103
HomeSupportDeveloper DocumentsAPI ReferencesH3C G3&G5 Servers HDM IPMI Basics Command Reference-6W103
Download Book
Table of Contents
Related Documents
New H3C Technologies Co., Ltd.
http://www.h3c.com
Software version: HDM-3.50 and later or HDM-6.17 and later
Document version: V3.52
Copyright © 2025, New H3C Technologies Co., Ltd. and its licensors
All rights reserved
Trademarks
Notice
The information in this document is subject to change without notice. All contents in this document, including statements, information, and recommendations, are believed to be accurate, but they are presented without warranty of any kind, express or implied. H3C shall not be liable for technical or editorial errors or omissions contained herein.
Revision records
Version
Date
HDM version
Interface name
V1.0
2019-03-30
HDM-1.11.25P01
First release
V1.1
2019-04-15
HDM-1.11.26
Modification of description.
V1.2
2019-05-23
HDM-1.11.27
Obtain the SEL storage mode
Added interface.
Set the SEL storage mode
Added interface.
Obtain overall information about SEL logs
Added interface.
Obtain information about an SEL log
Added interface.
Obtain information about a packet transmitted for an SEL log
Added interface.
Configure LDAP settings
Added interface.
V1.3
2019-05-27
HDM-1.11.28
Modified the description
V1.4
2019-06-05
HDM-1.11.29
Obtain the total drive usage
Added interface.
Specify the drive usage
Added interface.
Obtain LD information
Added the following fields: physical drive cache policy and whether the current logical drive is the boot drive.
Configure basic SNMP settings
Added two reserved fields and changed the position of the Longpassword field.
V1.6
2019-07-05
HDM-1.11.31 P03
Obtain information about the serial port connected to the SOL
Added interface.
Obtain information about the serial port connected to a panel
Added interface.
V2.0
2019-07-22
HDM-1.12.05
Specify the primary NTP server
Removed the fixed 128-byte length limit on the IP addresses of NTP servers.
Specify the secondary NTP server
Configure a logical drive
Added support for PMC storage controllers.
V2.1
2019-08-15
HDM-1.30.06
Added the SpanNumber and NumDrivePerSpan fields.
V2.2
2019-09-10
HDM-1.30.07
Configure HDM network service settings
Added return code 0xF5, which indicates that a VNC session exists.
Added the IO bypass option to the physical drive cache policy field.
Obtain the status of KVM encryption
Added interface.
Set the status of KVM encryption
Added interface.
Obtain the status of VM encryption
Added interface.
Set the status of VM encryption
Added interface.
V2.3
2019-10-10
HDM-1.30.08
Obtain card insertion information
Added the serial number and part number fields.
Set the severity levels for SMTP alert emails
Added interface.
Obtain the severity levels for SMTP alert emails
Added interface.
Set the enabling status of SNMP traps
Added interface.
Set the SNMP trap version
Added interface.
Set the location of an SNMP trap node
Added interface.
Set the SNMP trap contact information
Added interface.
Configure an SNMP community
Added interface.
Specify the severity levels of SNMP traps to be reported
Added interface.
Configure an SNMP trap server
Added interface.
Obtain syslog information
Added interface.
Configure syslog settings
Added interface.
Obtain syslog server settings
Added interface.
Configure syslog server settings
Added interface.
Obtain CPU information
Added the CPU SN and CPU PPIN fields.
V2.4
2019-10-25
HDM-1.30.09
Obtain the address of the SMTP server
Added support for FQDN address to the address types of the SMTP trap server and extended the address length (including the terminator) from 46 bytes to 128 bytes.
Specify the SMTP server
Obtain PCIe module information
Added the PciBaseClassCode, PciSubClassCode, PciProgIF, Device, and Function fields.
Obtain IPv4 firewall rule information
Added support for whitelist rule and blacklist rule, and modified the types of firewall rules.
Obtain IPv6 firewall rule information
Added the strip size and accelerator type fields.
Obtain PD information
Added the rebuilding progress, total power-on hours, number of media errors, number of other errors, and number of predictive errors fields.
V2.5
2019-11-08
HDM-1.30.10
Merged two reserved fields to the Read community and Write community fields, respectively.
Added transmission types TLS (one-way authentication) and TLS (two-way authentication).
Obtain the number of storage controllers and their indexes and names
Added the out-of-band configuration flag field that can help identify the MR, IR, or IT type of LSI storage controllers, and resolved the output alignment issue.
Obtain server health status
Added the logical drive status field.
V2.6
2019-11-15
HDM-1.30.11
Added the CapableSpeed field.
Set the fan speed mode
Added the fan speed mode field.
Obtain storage controller information
Resolved the output alignment issue. The actual output is not changed.
Resolved the output alignment issue and changed a reserved field to an out-of-band configuration flag field.
Set the physical drive status
Added the health LED status field.
Set the SNMP trap mode
Added interface.
V2.7
2019-12-06
HDM-1.30.12
Obtain the link status of dedicated and shared network ports
Added interface.
Obtain the IP address of the tertiary NTP server
Added interface.
Modified the severity level of "major + critical" to "minor + major + critical."
Configure AD settings
Added interface.
V2.8
2019-12-12
HDM-1.30.13
Added the PCIe health LED redirection field.
Added the maximum CPU frequency field.
V2.9
2019-12-24
HDM-1.30.14
Added the total drive capacity and used drive capacity fields. The two fields are supported only in FIST SMS D018 and later versions.
Added the system module health status field.
V2.10
2020-01-09
HDM-1.30.15
Modified the error description
Obtain MCA policy information
Added the ACD enabling status field.
Configure MCA policy settings
Added the ACD enabling status field (rsv field).
V2.11
2020-02-20
HDM-1.30.16
Added the following fields: number of physical drives and DevIDs of physical drives for the current logical drive.
Added the SasAddr field.
V2.12
2020-03-05
HDM-1.30.17
Added the PortNum field.
V2.13
2020-03-19
HDM-1.30.18
Changed ProductSN in field 0x02 to BoardSN and incorporated this change to HDM-1.30.18SP52.
V2.14
2020-04-22
HDM-1.30.19
V3.01
2020-05-20
HDM-2.0.03
Added the JBOD drive status for physical drives.
Added the adapter configuration version field. 32 more bytes were added to the response length.
Print LAN card information
G5:
·     0x01—Specifies the dedicated network port.
·     0x08—Specifies the shared network port.
G3:
·     0x01—Specifies the shared network port.
·     0x08—Specifies the dedicated network port.
Obtain channel information of a network port
G5: Network port eth0 corresponds to channel 8 and network port eth1 corresponds to channel 1.
G3: Network port eth0 corresponds to channel 1 and network port eth1 corresponds to channel 8.
All HDM IPv4 management commands
G5:
G3:
All HDM IPv6 management commands
G5:
G3:
V3.01
2020-05-20
HDM-2.0.04
Obtain permission of all user roles
Added interface.
Set permissions for a custom user role
Added interface.
Obtain server power status and UID LED status
Changed the UID LED status for G5 servers according to the standard.
Added user roles custom 1 to custom 5.
Specify the HDM user role
V3.01
2020-05-20
HDM-2.0.05
Obtain memory information
Added Data[56:177] to obtain G5 memory information.
V3.02
2020-06-06
HDM-2.0.06
Added description of the permission module to which it belongs
V3.03
2020-06-19
HDM-2.0.07
Obtain FRU information
Added interface.
Trigger NMI diagnosis
Added interface.
Added the operating system health status field.
V3.04
2020-07-10
HDM-2.06.00
V3.05
2020-08-06
HDM-2.08.00
V3.06
2020-08-17
HDM-2.09.00
Obtain PFR firmware information about a system board
Added interface.
V3.06
2020-09-07
HDM-2.10.00
Added the JBOD mode to storage controllers and the package version field.
Added the PdType field.
V3.07
2020-09-17
HDM-2.11.00
V3.08
2020-10-20
HDM-2.13.00
Obtain the NTP synchronization interval
Added interface.
Set security bezel LEDs
Added interface.
Obtain security bezel LED configuration
Added interface.
Obtain the status of the hard disk indicator light
Optimized Web display and Added interface.
Configure the status of the hard disk indicator light
Added the CPU Id, SlotDesc, and PCIe device type fields and optimized Web display.
Optimized Web display. The return field of Data[19] is meaningless, which used to represent PCIe health LED redirection.
Added the CPU bus, CPU device, and CPU function fields. Compatibility issues exist.
Added the IsLSI field.
Obtain SDR server settings
Added interface.
Added the Copyback status for physical drives managed by an LSI storage controller.
Configure SDR server settings
Added interface.
V3.09
2020-11-10
HDM-2.16.00
Set the power-on delay time
Added support for setting the random delay time.
Obtain the power-on delay time
Added support for obtaining the random delay time.
Added support for OCP health status for G5 products.
G5 servers do not support disabling the ACD function.
Added values 11 (U2 NVME) and 12 (REDRIVER) for the PCIe device type.
V3.10
2020-11-23
HDM-2.17.00
V3.11
2020-12-01
HDM-2.17.00
Moved the CPU bus, CPU device, and CPU function fields to the rear of the PortNum field and shielded the compatibility issue in 2.13.00.
V3.12
2020-12-17
HDM-2.19
Restore factory HDM settings
Added interface.
Obtain HDM network service information
Added support for the iHDT service.
V3.13
2021-01-08
HDM-2.25
Changed the module permission settings to basic configuration.
Added the health status sync field. Compatibility issues exist.
Added three reserved fields for internal use.
Added the negotiation rate field.
Obtain service USB device configuration
Added interface.
Set service USB device configuration
Added interface.
Obtain expander information
Added interface.
Obtain KVM modes
Added interface.
Set KVM modes
Added interface.
V3.14
2021-01-21
HDM-2.26
Added the CardBandwidth field.
V3.15
2021-02-04
HDM-2.27
Added type value of 13 (QAT) for PCIe devices.
Added the Rebuilding and RebuildWait states for physical drives managed by a PMC storage controller.
V3.16
2021-02-23
HDM-2.28
Added type value of 14 (Clock card) for PCIe devices.
V3.17
2021-03-02
HDM-2.29
V3.18
2021-03-19
HDM-2.33
Obtain FlyFish fan version
Added interface.
Obtain serial server settings
Added interface.
Configure serial server settings
Added interface.
Added the Auto volume and Simple volume modes to the storage controller mode.
Obtain GPU power capping information
Added interface.
Configure GPU power capping
Added interface.
Added the number of supported syslog servers to 8.
Changed the number of supported SNMP Trap servers from 4 to 8.
Configure logical drive attributes
Added interface.
V3.19
2021-04-09
HDM-2.38
V3.20
2021-04-21
HDM-2.42
V3.21
2021-05-13
HDM-2.51
Added type value of 15 (MOC card) for PCIe devices.
Fixed the errors in the returned information of system power-on status.
V3.22
2021-05-27
HDM-2.52
V3.23
2021-06-07
HDM-2.54
V3.24
2021-06-22
HDM-2.55
Obtain power information of the past day or week
Added interface.
V3.25
2021-07-19
HDM-2.60
V3.26
2021-09-13
HDM-2.75
Added product serial number as an option to the host identifier.
V3.27
2021-10-18
HDM-2.80
V3.28
2021-11-12
HDM-2.85
Configure a physical hot spare drive
Added interface.
V3.29
2021-12-13
HDM-2.90
V3.30
2022-01-25
HDM-2.96
V3.31
2022-02-21
HDM-2.97
V3.32
2022-03-25
HDM-2.98
V3.33
2022-05-25
HDM-3.10
V3.34
2022-06-30
HDM-3.11
Configure a BIOS setting
Added support of G5 Intel servers for the BIOS options.
Obtain a BIOS setting
V3.34
2022-07-20
HDM-3.13
V3.35
2022-10-22
HDM-3.18
Obtain the next boot option
Added Remote Connect Hard Drive as a boot device.
Set the next boot option
Added Remote Connect Hard Drive field as a boot device.
Set Wi-Fi service enabling status
Added interface.
Obtain Wi-Fi service enabling status
Added interface.
HDM-3.26
V3.36
2022-11-20
HDM-3.30
Added major + critical as an option to the severity level.
V3.37
2022-12-18
HDM-3.31
V3.38
2023-01-15
HDM-3.32
Added options 1 to 5 for the MaxSpeed field.
Corrected example title and added example description.
V3.38
2023-03-13
HDM-3.34
Added support of some AMD and Hygon products for the BIOS options.
V3.39
2023-04-06
HDM-3.35
Set the enabling status of DNS registration
Added the description that this command takes effect after a restart.
V3.40
2023-05-22
HDM-3.36
HDM-6.01
Support status or revisions are subject to specific commands.
Corrected the error description for Data[74-75]. The features supported by the processor should be analyzed and interpreted according to bit positions.
Corrected the description for setting a dedicated hot spare.
Added restrictions and guidelines for specifying IPv6 addresses or domain names for Data[12].
V3.41
2023-7-6
HDM-3.37
HDM-6.02
Changed supercapacitor status Fatal to Fault for Data[128:159].
Corrected response Data[264-289].
Added the Data[290:337] field to record PD model information.
V3.42
2023-08-10
HDM-3.38
HDM-6.03
Updated the manual version number.
V3.43
2023-09-06
HDM-3.38
HDM-6.03
V3.44
2023-9-25
HDM-3.40
HDM-6.05
Obtain product generation information
No functional changes. Added Data[14] occupancy description, which can be used to distinguish generation information of HDM software. G3/G5 products still return 00h.
V3.45
2023-11-8
HDM-3.41
HDM-6.06
Functionality has expanded. Data[19] now supports setting additional physical disk cache policies, and Data[15] supports more access strategies. Fields Data[4:13] that were previously supported are supplemented to the return value and and status code fields Data[14:17] are added to the return value.
V3.46
2024-1-8
HDM-3.43
HDM-6.08
Description for Data[16-N] was supplemented to add an explanation for the terminator.
V3.47
2024-3-21
HDM-3.45
HDM-6.10
Added description for support of Data[96-103] and Data[104-111] for CPUs.
Added fields for numbers of internal ports and external ports of storage controllers.
V3.48
2024-6-30
HDM-3.48
HDM-6.13
Obtain the number of supported CPUs and DIMMs
Supplemented the application scope of Data[4] to indicate that the field has been discarded for new products.
Added support of BIOS boot modes UEFI and Legacy for BIOS options.
V3.49
2024-8-8
HDM-3.49
HDM-6.14
Set the alarm threshold for a sensor
Revised the relationship description for lnr, lcr, and lnc.
Obtain the fan speed mode
Added description for the existing interface.
Added the IPv6 description.
Added support for the B5700 G5 blade server.
Reload the configuration file for fans
V3.50
2024-9-19
HDM-3.50
HDM-6.15
Corrected the unit for the memory speed to MT/s.
Set an SNMP v3 user
Added interface.
V3.51
2024-10-17
HDM-3.50
HDM-6.16
Add the description for logical drive status, read policy, write policy, and physical drive cache policy for logical drives under the 3SNIC storage controller.
Added the description for the initialization state, read policy, write policy, and physical drive cache policy for creating a logical drive under a 3SNIC storage controller.
Added the physical drive state description for the 3SNIC storage controller.
·     Added Voltage_low as a supercapacitor status.
·     Added Warning as a cache module status.
Added roaming hot spare as a hot spare status for Data[265].
Configure all BIOS settings
Revised the description in the example.
Changed the unit of the memory capacity to MiB.
Changed the memory frequency to DIMM speed.
Revised the data range in the response.
Changed the syslog server address to 48-bit.
Set an SNMP v3 user
Revised the description by deleting unnecessary authentication and encryption algorithms.
Revised the display of memory information and extended the length of the part number field.
V3.52
2024-11-29
HDM-3.50
HDM-6.17
Obtain the number of present PCIe modules
Revised the description for Data[4].
Syslog added eight bytes to the original information for eight server addresses.
Added support for roaming hot spares.
Revised command description.
Revised example descripton.
Edited the stripe size and the description for the initialization status.
Revised the description for the physical drive status.
Specify the tertiary NTP server
Revised incorrect IP addresses.
Obtain the firmware revision of a power supply
Revised the command title.
Revised the display of memory information and reduced the length of the part number field for G3 servers.
Revised the response description for Data[62].
Revised the response description for Data[10].
V3.5x
2025-02-12
HDM-3.5x
HDM-6.1x
Revision records· 3
Contents· i
IPMI command conventions· 6
About IPMI 6
About IPMItool 6
Command format 6
Request and response· 7
Applicable products· 7
Permissions· 7
Port description· 8
Standard IPMI commands· 9
Chassis management 9
Obtain current chassis status· 9
Obtain the reason for the most recent restart 9
Obtain total power-on time of a chassis· 10
Obtain the chassis self-test result 10
Chassis power management 11
Obtain the current chassis power status· 11
Power on a chassis· 11
Power off a chassis· 11
Restart a chassis· 12
Trigger NMI diagnosis· 12
Set the power-on policy for a chassis· 13
Obtain the supported power-on policies of a chassis· 13
Server information obtaining· 14
Obtain server version information· 14
Obtain server GUID information· 14
Obtain the current status of all sensors· 15
Obtain sensor type information· 18
Obtain the list of supported sensors in a chassis· 19
Obtain fan status information· 22
Obtain fan speed information· 23
Perform a server self-test on HDM·· 23
Reset HDM·· 24
Obtain the reading of a sensor 24
Set the alarm threshold for a sensor 25
Obtain SEL information· 26
Obtain FRU information· 27
Obtain current session information· 29
Obtain server power status and UID LED status· 30
Set server UID LED status· 31
Obtain FRU information· 31
User management 32
Obtain information about all HDM users· 32
Obtain brief HDM user information· 32
Add an HDM user 32
Set the password for an HDM user 33
Verify an HDM user password· 34
Disable HDM access· 35
Enable HDM access· 35
Delete an HDM access· 36
Specify the HDM user role· 36
HDM IPv4 management 37
Obtain the IP address obtaining method for a network port 37
Obtain the IP address of a network port 38
Obtain the MAC address of a network port 39
Obtain the subnet mask of a network port 40
Obtain the gateway address· 41
Set the IP address obtaining method for a network port 42
Specify a static IP address for a network port 43
Specify the subnet mask for a network port 44
Specify the gateway address for a network port 45
HDM IPv6 management 46
Obtain the IPv6 address of a network port 46
Specify a static IPv6 address for a network port 47
Specify the prefix length for a network port 48
Obtain the prefix length of a network port 49
Obtain the IPv6 address obtaining method for a network port 50
Set the IPv6 address obtaining method for a network port 51
Specify the IPv6 gateway address for a network port 51
System boot 53
Set the one-time next boot option· 53
Remove the configured one-time next boot option· 53
Configure the server to enter the BIOS setup utility after startup· 54
Device extended commands· 54
Hardware information· 54
Obtain the number of present PCIe modules· 54
Obtain PCIe module information· 55
Obtain port information on an Ethernet adapter 58
Obtain the number of supported CPUs and DIMMs· 59
Obtain CPU information· 59
Obtain memory information· 61
Obtain product generation· 65
Obtain expander information· 66
Obtain server health status· 67
Host 70
Obtain security bezel LED configuration· 70
Set security bezel LEDs· 71
Obtain MCA policy information· 73
Configure MCA policy settings· 74
Storage· 75
Obtain storage controller information· 75
Obtain the number of LDs and their offset indexes· 78
Obtain LD information· 78
Obtain the number of PDs and their offset indexes· 82
Obtain PD information· 83
Obtain the number of storage controllers and their indexes and names· 87
Set the physical drive status· 90
Configure a logical drive· 91
Delete a logical drive· 94
Configure logical drive attributes· 95
Configure a physical hot spare drive· 97
Obtain the total drive usage· 99
Specify the drive usage· 100
BMC and BIOS interaction· 101
Obtain the next boot option· 101
Set the next boot option· 102
Obtain the next boot mode· 103
Set the next boot mode· 104
Obtain the power-on delay time· 105
Set the power-on delay time· 106
Obtain Port80 information· 107
Configure a BIOS setting· 109
Obtain a BIOS setting· 118
Configure all BIOS settings· 127
DNS· 131
Obtain host name setting· 131
Obtain DNS registration settings· 132
Obtain DNS domain settings· 133
Obtain the domain suffix· 134
Obtain the DNS sever settings· 135
Obtain the IP addresses of DNS servers· 136
Obtain the enabling status of DNS registration· 137
Configure the host name settings· 138
Configure DNS registration options· 138
Configure DNS domain settings· 139
Set the domain suffix· 140
Configure DNS server settings· 141
Specify the IP address of a DNS server 142
Commit DNS configuration changes· 143
Set the enabling status of DNS registration· 143
Firewall 144
Obtain IPv4 firewall rule information· 144
Obtain IPv6 firewall rule information· 145
Network· 147
Obtain the status of a network port 147
Obtain bond settings· 148
Obtain the enabling status of a bond port 149
Obtain the number of network ports· 150
Obtain channel information of a network port 151
Obtain the name of a network port 151
Obtain the primary port of a bond port 152
Set the status of a network port 153
Configure the bond settings· 154
Set the primary port for a bond port 155
Obtain the link status of dedicated and shared network ports· 155
Network-related settings· 156
Obtain HDM network service information· 156
Configure HDM network service settings· 158
Configure LDAP settings· 160
Configure Active Directory (AD) settings· 165
Obtain permission of all user roles· 169
Set permissions for a custom user role· 170
SNMP· 172
Obtain basic SNMP settings· 172
Configure basic SNMP settings· 173
Set the enabling status of SNMP traps· 174
Set the SNMP trap version· 175
Set the location of an SNMP trap node· 176
Set the SNMP trap contact information· 176
Configure an SNMP community· 177
Specify the severity levels of SNMP traps to be reported· 178
Configure an SNMP trap server 179
Set the SNMP trap mode· 180
Set an SNMP v3 user 181
NTP· 182
Obtain NTP server addresses· 182
Obtain the NTP time zone· 183
Specify the primary NTP server 184
Specify the secondary NTP server 184
Specify the tertiary NTP server 185
Configure time synchronization with NTP servers· 186
Set the time zone· 187
Set the NTP refresh interval 187
Obtain the IP address of the tertiary NTP server 188
Obtain the NTP synchronization interval 189
HDM maintenance· 190
Obtain HDM firmware information· 190
Obtain BIOS firmware information· 191
Restore default HDM settings· 192
Restore factory HDM settings· 193
Obtain PFR firmware information about a system board· 193
Obtain service USB device configuration· 194
Set service USB device configuration· 195
Obtain Wi-Fi service enabling status· 196
Set Wi-Fi service enabling status· 197
System maintenance· 198
Obtain the SEL storage mode· 198
Set the SEL storage mode· 199
Obtain overall information about SEL logs· 200
Obtain information about an SEL log· 201
Obtain information about a packet transmitted for an SEL log· 202
Obtain information about the serial port connected to the SOL· 204
Obtain information about the serial port connected to a panel 205
Set the severity levels for SMTP alert emails· 205
Obtain the severity levels for SMTP alert emails· 206
Obtain the address of the SMTP server 207
Specify the SMTP server 208
Obtain syslog information· 209
Configure syslog settings· 211
Obtain syslog server settings· 213
Configure syslog server settings· 215
Obtain SDR server settings· 217
Configure SDR server settings· 218
Obtain serial server settings· 219
Configure serial server settings· 220
Fans· 221
Set the fan speed mode· 221
Obtain the fan speed mode· 222
Reload the configuration file for fans· 224
Obtain FlyFish fan version· 224
Power supplies· 225
Obtain the maximum number of supported power supplies· 225
Obtain the presence, AC input, and DC input status of a power supply· 226
Obtain the cold backup state of a power supply· 227
Configure a power supply to enter in cold backup· 228
Configure a power supply to exit from cold backup· 229
Obtain the maximum output power of a power supply· 230
Obtain the current output power of a power supply· 231
Obtain the range of the power cap value· 231
Obtain the power information of a power supply· 232
Obtain the firmware revision of a power supply· 233
Obtain model match information for all presented power supplies· 234
Obtain the manufacturer information of a power module· 234
Obtain the model of a power supply· 235
Obtain power supply information displayed on the Web interface· 236
Obtain GPU power capping information· 237
Configure GPU power capping· 238
Obtain power information of the past day or week· 239
KVM and virtual media· 240
Obtain the status of KVM encryption· 240
Set the status of KVM encryption· 241
Obtain the status of virtual media encryption· 242
Set the status of virtual media encryption· 242
Obtain KVM modes· 243
Set KVM modes· 244
Examples· 245
Using IPMItool to obtain chassis status· 245
Network configuration· 245
Using IPMItool software· 246
Using IPMItool to obtain chassis information· 246
About IPMI
Intelligent Platform Management Interface (IPMI) is an industry standard for managing peripheral devices in server systems. You can use IPMI to monitor the physical health status of servers from different vendors, such as temperature, voltage, fan modules, power supplies to achieve unified management of servers from different vendors.
About IPMItool
IPMItool is an open source IPMI client tool that supports both Linux and Windows operating systems and is the most commonly used IPMI client tool. IPMItool accesses the IPMI interface of a server through commands. As shown in Figure 1, open the Windows cmd and access the IPMItool directory to execute IPMI commands.
Figure 1 Windows Command Prompt
Command format
An IPMI command uses the ipmitool -I connect_type -H hostname -U username -P password <command> format, where:
·     -I connect_typeSpecifies the connection method used to access the device to be managed. The connect_type argument is fixed to lanplus, which indicates that the device to be managed will be accessed as required in the IPMI 2.0 specification.
·     -H hostnameSpecifies the IP address of the device to be managed.
·     -U username -P passwordSpecifies the HDM username and password of the device to be managed.
·     <command>—Specifies the action to be taken. This argument can be a string (chassis status for example) or a hexadecimal raw code (raw 0x00 0x01). For more information about this argument, see the specific command.
·     -LSpecifies the session privilege, which is Administrator by default. This keyword is required in commands for the user or operator role. For custom users, the -L oem keyword is required.
The length of the raw code (raw 0x00 0x01) in a command cannot exceed 255 bytes.
For some commands, the request and response will be displayed as a hexadecimal raw string. Table 1 and Table 2 display the example data fields in such a request and a response, respectively.
Table 1 Example data fields in a request
Data[1]
Specifies a single-byte field. The byte is displayed as 2-digit hexadecimal numbers. For more information, see the parameters of the specific command.
Data[1:3]
Specifies a multi-byte field. This field contains three bytes: Data[1], Data[2], and Data[3]. Each byte is displayed as 2-digit hexadecimal numbers. For more information, see the parameters of the specific command.
Table 2 Example data fields in a response
Data[1]
Specifies the first returned byte. For more information, see the response of the specific command.
Data[9:16]
Specifies the 9th to 16th returned bytes. For more information, see the response of the specific command.
Bits[7:1]
Specifies the seven highest bits of a byte. In a response, each byte contains eight bits: 7, 6, 5, 4, 3, 2, 1, and 0, where 7 represents the highest bit and 0 represents the second lowest bit.
Bits[5:4]
Specifies the fifth and fourth lowest bits of a byte. In a response, each byte contains eight bits: 7, 6, 5, 4, 3, 2, 1, and 0, where 7 represents the highest bit and 0 represents the second lowest bit.
Applicable products
Interfaces described in this document are only applicable to H3C servers. For more information, see HDM user guide for 2.xx and 3.xx HDM versions.
Permissions
A command involves the following permissions:
·     User roleApplicable to HDM-1.30.xx versions. Options include User, Operator, and Administrator.
·     Required permissionApplicable to HDM-2.xx.xx versions. Options include user accounts, basic configuration, remote control, remote media, security, power control, maintenance, password modification, and information query.
Port description
Server generation
Port type
Channel
HDM interface
G3
Dedicated port
8
eth1
Shared port
1
eth0
G5
Dedicated port
1
eth1
Shared port
8
eth0
Chassis management
Use chassis status to obtain the current status of a chassis.
ipmitool -I connect_type -H hostname -U username -P password chassis status
User role
User
Required permission
Information query
# Obtain the current chassis status.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis status
System Power         : on
Power Overload       : false
Power Interlock      : inactive
Main Power Fault     : false
Power Control Fault  : false
Power Restore Policy : previous
Last Power Event     : command
Chassis Intrusion    : inactive
Front-Panel Lockout  : inactive
Drive Fault          : false
Cooling/Fan Fault    : false
Sleep Button Disable : allowed
Diag Button Disable  : allowed
Reset Button Disable : allowed
Power Button Disable : allowed
Sleep Button Disabled: true
Diag Button Disabled : true
Reset Button Disabled: true
Power Button Disabled: true
Use chassis restart_cause to obtain the reason for the most recent restart.
ipmitool -I connect_type -H hostname -U username -P password chassis restart_cause
User role
User
Required permission
Information query
# Obtain the reason for the most recent restart.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_  chassis restart_cause
System restart cause: chassis power control command
Use chassis poh to obtain the total power-on time of a chassis.
ipmitool -I connect_type -H hostname -U username -P password chassis poh
User role
User
Required permission
Information query
# Obtain the total power-on time of a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis poh
POH Counter  : 8 days, 13 hours
Use chassis selftest to obtain the self-test result of a chassis.
ipmitool -I connect_type -H hostname -U username -P password chassis selftest
User role
User
Required permission
Information query
# Obtain the self-test result of a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis selftest
Self Test Results    : passed
Use power status to obtain the current power status of a chassis.
ipmitool -I connect_type -H hostname -U username -P password power status
User role
User
Required permission
Information query
# Obtain the current power status of a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ power status
Chassis Power is on
Power on a chassis
Use power on to power on a chassis.
ipmitool -I connect_type -H hostname -U username -P password power { up | on }
User role
Operator
Required permission
Power control
The up and on keyword function the same. You can use either keyword to power on the chassis.
# Power on a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ power on
Chassis Power Control: Up/On
Power off a chassis
Use power off to power off a chassis.
ipmitool -I connect_type -H hostname -U username -P password power { down | off }
User role
Operator
Required permission
Power control
The down and off keyword function the same. You can use either keyword to power off the chassis.
# Power off a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ power off
Chassis Power Control: Down/Off
Restart a chassis
Use power reset to restart a chassis. This operation disconnects the server power.
ipmitool -I connect_type -H hostname -U username -P password power reset
User role
Operator
Required permission
Power control
# Restart a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ power reset
Chassis Power Control: Reset
Use this command to trigger NMI diagnosis.
ipmitool -I connect_type -H hostname -U username -P password power diag
User role
Operator
Required permission
Power control
# Trigger NMI diagnosis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ power diag
Chassis Power Control: Diag
Change history
Version
Change description
HDM-2.0.07
Added this command.
Use chassis policy to set the power-on policy that takes effect when the server is connected to the power source.
ipmitool -I connect_type -H hostname -U username -P password chassis policy power_policy
Table 3 Request field description
power_policy
Specify the power-on policy. Supported options:
·     always-on—Enables the server to power on automatically.
·     previous—Enables the server to return to the power state on the previous power-off.
·     always-off—Enables the server to stay off.
The power-on policy is previous. The server returns to the power state on the previous power-off.
User role
Operator
Required permission
Power control
# Set the power-on policy for a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis policy always-on
Set chassis power restore policy to always-on
Use chassis policy list to obtain the supported power-on policies of a chassis.
ipmitool -I connect_type -H hostname -U username -P password chassis policy list
User role
Operator
Required permission
Information query
# Obtain the supported power-on policies of a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis policy list
Supported chassis power policy:  always-off always-on previous
Use mc info to obtain server version information.
ipmitool -I connect_type -H hostname -U username -P password mc info
User role
User
Required permission
Information query
# Obtain server version information from HDM 1.11.9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ mc info
Device ID                 : 32
Device Revision           : 1
Firmware Revision         : 1.11
IPMI Version              : 2.0
Manufacturer ID           : 25506
Manufacturer Name         : Unknown (0x63A2)
Product ID                : 27 (0x001b)
Product Name              : Unknown (0x1B)
Device Available          : yes
Provides Device SDRs      : no
Additional Device Support :
    Sensor Device
    SDR Repository Device
    SEL Device
    FRU Inventory Device
    IPMB Event Receiver
    IPMB Event Generator
    Chassis Device
Aux Firmware Rev Info     :
    0x09
    0x00
    0x00
    0x00
Use mc guid to obtain the globally unique identifier (GUID) information of the server.
ipmitool -I connect_type -H hostname -U username -P password mc guid
User role
User
Required permission
Information query
# Obtain server GUID information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ mc guid
System GUID  : 65e3328a-1019-04b0-e611-0edc168afafa
Timestamp    : 03/02/2024 22:07:06
Use sdr to obtain the current status of sensors in a chassis.
ipmitool -I connect_type -H hostname -U username -P password sdr
ipmitool -I connect_type -H hostname -U username -P password sdr list
User role
User
Required permission
Information query
This command returns the readings and status of all sensors in the chassis. The server is in healthy state only when all sensors are in heathy state.
# Obtain the current status and readings of all sensors in a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sdr
18-P/S 1 Zone    | 39 degrees C      | ok
19-P/S 2 Zone    | 36 degrees C      | ok
24-BMC Zone      | 44 degrees C      | ok
32-Outlet_Temp 1 | 45 degrees C      | ok
33-Outlet_Temp 2 | 41 degrees C      | ok
16-P/S 1         | 36 degrees C      | ok
17-P/S 2         | 36 degrees C      | ok
02-CPU 1         | 52 degrees C      | ok
03-CPU 2         | 51 degrees C      | ok
04-CPU 1 DTS     | -40 degrees C     | ok
05-CPU 2 DTS     | -41 degrees C     | ok
06-P1 DIMM Ch1-3 | 36 degrees C      | ok
07-P1 DIMM Ch4-6 | 38 degrees C      | ok
08-P2 DIMM Ch1-3 | 39 degrees C      | ok
25-PCI 1         | 61 degrees C      | ok
26-PCI 2         | no reading        | ns
28-PCI 1 Zone    | 44 degrees C      | ok
29-PCI 2 Zone    | no reading        | ns
10-Front HD Max  | 35 degrees C      | ok
12-Rear HD Max   | no reading        | ns
22-HD Controller | 38 degrees C      | ok
31-LOM Card      | 43 degrees C      | ok
01-Inlet Temp    | 28 degrees C      | ok
23-Expander Card | no reading        | ns
13-Rear HD Zone  | no reading        | ns
09-P2 DIMM Ch4-6 | 37 degrees C      | ok
15-PCH           | 55 degrees C      | ok
20-VR P1         | 43 degrees C      | ok
21-VR P2         | 45 degrees C      | ok
14-M.2 Zone      | no reading        | ns
FAN5_F_Speed     | 5000 RPM          | ok
FAN4_R_Speed     | no reading        | ns
FAN5_R_Speed     | 5300 RPM          | ok
FAN7_F_Speed     | 5000 RPM          | ok
FAN2_F_Speed     | 4900 RPM          | ok
FAN4_F_Speed     | no reading        | ns
FAN7_R_Speed     | 5200 RPM          | ok
FAN3_R_Speed     | 5200 RPM          | ok
FAN6_R_Speed     | 5300 RPM          | ok
FAN1_R_Speed     | 5300 RPM          | ok
FAN6_F_Speed     | 5000 RPM          | ok
FAN2_R_Speed     | 5300 RPM          | ok
FAN3_F_Speed     | 5000 RPM          | ok
FAN1_F_Speed     | 5000 RPM          | ok
CPU1_Status      | 0x80              | ok
CPU2_Status      | 0x80              | ok
PSU1_PIN         | 95 Watts          | ok
PSU2_PIN         | 85 Watts          | ok
PSU1_Status      | 0x01              | ok
PSU2_Status      | 0x01              | ok
FAN1_F_Status    | 0x01              | ok
FAN2_F_Status    | 0x01              | ok
FAN3_F_Status    | 0x01              | ok
FAN4_F_Status    | Not Readable      | ns
FAN5_F_Status    | 0x01              | ok
FAN6_F_Status    | 0x01              | ok
FAN7_F_Status    | 0x01              | ok
FAN1_R_Status    | 0x01              | ok
FAN2_R_Status    | 0x01              | ok
FAN3_R_Status    | 0x01              | ok
FAN4_R_Status    | Not Readable      | ns
FAN5_R_Status    | 0x01              | ok
FAN6_R_Status    | 0x01              | ok
FAN7_R_Status    | 0x01              | ok
27-PCI 3         | no reading        | ns
30-PCI 3 Zone    | no reading        | ns
SEL_sensor       | 0x00              | ok
Watchdog2        | 0x00              | ok
OverCurrent      | 0x01              | ok
11-Front NVMe    | no reading        | ns
AreaIntrusion    | 0x00              | ok
CPU1_DDR_VPP1    | 2.58 Volts        | ok
CPU1_DDR_VDDQ1   | 1.22 Volts        | ok
CPU1_Vcore       | 1.78 Volts        | ok
CPU2_DDR_VPP2    | 2.58 Volts        | ok
CPU2_DDR_VPP1    | 2.58 Volts        | ok
CPU2_DDR_VDDQ2   | 1.22 Volts        | ok
CPU2_DDR_VDDQ1   | 1.22 Volts        | ok
CPU1_DDR_VPP2    | 2.58 Volts        | ok
CPU1_DDR_VDDQ2   | 1.22 Volts        | ok
CPU2_Vcore       | 1.78 Volts        | ok
PSU1_VIN         | 231.60 Volts      | ok
PSU2_VIN         | 232.80 Volts      | ok
SYS_3V3          | 3.28 Volts        | ok
SYS_5V           | 5.12 Volts        | ok
SYS_3V_BAT       | 3.28 Volts        | ok
SYS_12V          | 12 Volts          | ok
HDD_BP3_12V      | no reading        | ns
HDD_BP2_12V      | no reading        | ns
HDD_BP1_12V      | no reading        | ns
PSU2_VOUT        | 12 Volts          | ok
PSU1_VOUT        | 11.88 Volts       | ok
CPU2_VDDQ1_PG    | 0x01              | ok
CPU1_VDDQ2_PG    | 0x01              | ok
CPU2_DDR_VPP2_PG | 0x01              | ok
CPU2_VDDQ2_PG    | 0x01              | ok
SYS_5V_STBY_PG   | 0x01              | ok
BP_1_PG          | 0x01              | ok
BP_2_PG          | 0x01              | ok
CPU1_DDR_VPP2_PG | 0x01              | ok
BP_3_PG          | 0x01              | ok
CPU1_DDR_VPP1_PG | 0x01              | ok
CPU2_DDR_VPP1_PG | 0x01              | ok
CPU1_VDDQ1_PG    | 0x01              | ok
CPU2_DIMM_B1     | Not Readable      | ns
CPU1_DIMM_A6     | 0x40              | ok
CPU2_DIMM_B5     | Not Readable      | ns
CPU2_DIMM_B2     | 0x40              | ok
CPU1_DIMM_A1     | Not Readable      | ns
CPU2_DIMM_B4     | Not Readable      | ns
CPU1_DIMM_A4     | Not Readable      | ns
CPU1_DIMM_A7     | Not Readable      | ns
CPU2_DIMM_B3     | Not Readable      | ns
CPU2_DIMM_B7     | Not Readable      | ns
CPU2_DIMM_B8     | Not Readable      | ns
CPU1_DIMM_A8     | Not Readable      | ns
CPU2_DIMM_B6     | 0x40              | ok
CPU1_DIMM_A5     | Not Readable      | ns
CPU1_DIMM_A2     | Not Readable      | ns
CPU1_DIMM_A3     | 0x40              | ok
Use this command to obtain information about a sensor type in a chassis.
ipmitool -I connect_type -H hostname -U username -P password sdr type
ipmitool -I connect_type -H hostname -U username -P password sdr type sdr_type
Table 4 Request field description
sdr_type
Specify a sensor type.
User role
User
Required permission
Information query
·     Obtain the list of supported sensor types in a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sdr type
Sensor Types:
        Temperature                 Voltage
        Current                     Fan
        Physical Security           Platform Security
        Processor                   Power Supply
        Power Unit                  Cooling Device
        Other                       Memory
        Drive Slot / Bay            POST Memory Resize
        System Firmwares            Event Logging Disabled
        Watchdog                    System Event
        Critical Interrupt          Button
        Module / Board              Microcontroller
        Add-in Card                 Chassis
        Chip Set                    Other FRU
        Cable / Interconnect        Terminator
        System Boot Initiated       Boot Error
        OS Boot                     OS Critical Stop
        Slot / Connector            System ACPI Power State
        Watchdog                    Platform Alert
        Entity Presence             Monitor ASIC
        LAN                         Management Subsystem Health
·     Obtain information about power supply sensors in a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sdr type "Power Supply"
PSU1_PIN         | 3Bh | ns  | 10.1 | No Reading
PSU1_Status      | 48h | ok  | 10.1 |
PSU2_PIN         | 3Eh | ok  | 10.2 | 105 Watts
PSU2_Status      | 49h | ok  | 10.2 | Presence detected
Total_Power      | 87h | ok  | 34.1 | 105 Watts
PSU_Redundancy   | 8Fh | ok  | 10.127 | Fully Redundant
FAN_Power        | 7Eh | ok  |  3.0 | 30 Watts
CPU_Power        | C2h | ok  |  3.5 | 20 Watts
MEM_Power        | FAh | ok  |  8.6 | 2 Watts
DISK_Power       | C1h | ok  | 19.0 | 6 Watts
Use sensor list to obtain the list of supported sensors in a chassis.
ipmitool -I connect_type -H hostname -U username -P password sensor list
User role
User
Required permission
Information query
# Obtain the list of supported sensors in a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sensor list
Sensor Name    | Reading    | Unit       | Status| Crit low  | Major low | Minor low | Minor high| Major high| Crit high
18-P/S 1 Zone    | 39.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
19-P/S 2 Zone    | 36.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
24-BMC Zone      | 44.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
32-Outlet_Temp 1 | 45.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
33-Outlet_Temp 2 | 41.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
16-P/S 1         | 36.000     | degrees C  | ok    | na        | na        | na        | 60.000    | 62.000    | na
17-P/S 2         | 36.000     | degrees C  | ok    | na        | na        | na        | 60.000    | 62.000    | na
02-CPU 1         | 52.000     | degrees C  | ok    | na        | na        | na        | na        | na        | na
03-CPU 2         | 51.000     | degrees C  | ok    | na        | na        | na        | na        | na        | na
04-CPU 1 DTS     | -40.000    | degrees C  | ok    | na        | na        | na        | -1.000    | na        | na
05-CPU 2 DTS     | -41.000    | degrees C  | ok    | na        | na        | na        | -1.000    | na        | na
06-P1 DIMM Ch1-3 | 36.000     | degrees C  | ok    | na        | na        | na        | 89.000    | 95.000    | na
07-P1 DIMM Ch4-6 | 38.000     | degrees C  | ok    | na        | na        | na        | 89.000    | 95.000    | na
08-P2 DIMM Ch1-3 | 39.000     | degrees C  | ok    | na        | na        | na        | 89.000    | 95.000    | na
25-PCI 1         | 60.000     | degrees C  | ok    | na        | na        | na        | 90.000    | 100.000   | na
26-PCI 2         | na         | degrees C  | na    | na        | na        | na        | 90.000    | 100.000   | na
28-PCI 1 Zone    | 44.000     | degrees C  | ok    | na        | na        | na        | 95.000    | 100.000   | na
29-PCI 2 Zone    | na         | degrees C  | na    | na        | na        | na        | 95.000    | 100.000   | na
10-Front HD Max  | 35.000     | degrees C  | ok    | na        | na        | na        | 60.000    | na        | na
12-Rear HD Max   | na         | degrees C  | na    | na        | na        | na        | 60.000    | na        | na
22-HD Controller | 38.000     | degrees C  | ok    | na        | na        | na        | 90.000    | 99.000    | 102.000
31-LOM Card      | 43.000     | degrees C  | ok    | na        | na        | na        | 90.000    | 100.000   | na
01-Inlet Temp    | 28.000     | degrees C  | ok    | na        | na        | na        | 50.000    | 52.000    | 54.000
23-Expander Card | na         | degrees C  | na    | na        | na        | na        | 100.000   | 120.000   | 125.000
13-Rear HD Zone  | na         | degrees C  | na    | na        | na        | na        | 95.000    | 100.000   | na
09-P2 DIMM Ch4-6 | 37.000     | degrees C  | ok    | na        | na        | na        | 89.000    | 95.000    | na
15-PCH           | 54.000     | degrees C  | ok    | na        | na        | na        | 92.000    | 102.000   | na
20-VR P1         | 43.000     | degrees C  | ok    | na        | na        | na        | 110.000   | 112.000   | na
21-VR P2         | 45.000     | degrees C  | ok    | na        | na        | na        | 110.000   | 112.000   | na
14-M.2 Zone      | na         | degrees C  | na    | na        | na        | na        | 95.000    | 100.000   | na
FAN5_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN4_R_Speed     | na         | RPM        | na    | na        | na        | na        | na        | na        | na
FAN5_R_Speed     | 5300.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN7_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN2_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN4_F_Speed     | na         | RPM        | na    | na        | na        | na        | na        | na        | na
FAN7_R_Speed     | 5200.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN3_R_Speed     | 5200.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN6_R_Speed     | 5300.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN1_R_Speed     | 5300.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN6_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN2_R_Speed     | 5300.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN3_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
FAN1_F_Speed     | 5000.000   | RPM        | ok    | na        | na        | na        | na        | na        | na
CPU1_Status      | 0x0        | discrete   | 0x8080| na        | na        | na        | na        | na        | na
CPU2_Status      | 0x0        | discrete   | 0x8080| na        | na        | na        | na        | na        | na
PSU1_PIN         | 95.000     | Watts      | ok    | na        | na        | na        | na        | na        | na
PSU2_PIN         | 85.000     | Watts      | ok    | na        | na        | na        | na        | na        | na
PSU1_Status      | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
PSU2_Status      | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN1_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN2_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN3_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN4_F_Status    | na         | discrete   | na    | na        | na        | na        | na        | na        | na
FAN5_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN6_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN7_F_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN1_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN2_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN3_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN4_R_Status    | na         | discrete   | na    | na        | na        | na        | na        | na        | na
FAN5_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN6_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
FAN7_R_Status    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
27-PCI 3         | na         | degrees C  | na    | na        | na        | na        | 90.000    | 100.000   | na
30-PCI 3 Zone    | na         | degrees C  | na    | na        | na        | na        | 95.000    | 100.000   | na
SEL_sensor       | 0x0        | discrete   | 0x0080| na        | na        | na        | na        | na        | na
Watchdog2        | 0x0        | discrete   | 0x0080| na        | na        | na        | na        | na        | na
OverCurrent      | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
11-Front NVMe    | na         | degrees C  | na    | na        | na        | na        | 70.000    | na        | na
AreaIntrusion    | 0x0        | discrete   | 0x0080| na        | na        | na        | na        | na        | na
CPU1_DDR_VPP1    | 2.580      | Volts      | ok    | na        | 2.340     | na        | na        | 2.760     | na
CPU1_DDR_VDDQ1   | 1.220      | Volts      | ok    | na        | 1.080     | na        | na        | 1.320     | na
CPU1_Vcore       | 1.780      | Volts      | ok    | na        | 1.330     | na        | na        | 1.880     | na
CPU2_DDR_VPP2    | 2.580      | Volts      | ok    | na        | 2.340     | na        | na        | 2.760     | na
CPU2_DDR_VPP1    | 2.580      | Volts      | ok    | na        | 2.340     | na        | na        | 2.760     | na
CPU2_DDR_VDDQ2   | 1.220      | Volts      | ok    | na        | 1.080     | na        | na        | 1.320     | na
CPU2_DDR_VDDQ1   | 1.220      | Volts      | ok    | na        | 1.080     | na        | na        | 1.320     | na
CPU1_DDR_VPP2    | 2.580      | Volts      | ok    | na        | 2.340     | na        | na        | 2.760     | na
CPU1_DDR_VDDQ2   | 1.220      | Volts      | ok    | na        | 1.080     | na        | na        | 1.320     | na
CPU2_Vcore       | 1.780      | Volts      | ok    | na        | 1.330     | na        | na        | 1.880     | na
PSU1_VIN         | 232.800    | Volts      | ok    | na        | na        | na        | na        | na        | na
PSU2_VIN         | 235.200    | Volts      | ok    | na        | na        | na        | na        | na        | na
SYS_3V3          | 3.280      | Volts      | ok    | na        | 2.960     | na        | na        | 3.600     | na
SYS_5V           | 5.120      | Volts      | ok    | na        | 4.480     | na        | na        | 5.520     | na
SYS_3V_BAT       | 3.280      | Volts      | ok    | na        | 2.000     | na        | na        | 3.680     | na
SYS_12V          | 12.000     | Volts      | ok    | na        | 10.800    | na        | na        | 13.200    | na
HDD_BP3_12V      | na         | Volts      | na    | na        | na        | na        | na        | na        | na
HDD_BP2_12V      | na         | Volts      | na    | na        | na        | na        | na        | na        | na
HDD_BP1_12V      | na         | Volts      | na    | na        | na        | na        | na        | na        | na
PSU2_VOUT        | 12.000     | Volts      | ok    | na        | na        | na        | na        | na        | na
PSU1_VOUT        | 11.880     | Volts      | ok    | na        | na        | na        | na        | na        | na
CPU2_VDDQ1_PG    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU1_VDDQ2_PG    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU2_DDR_VPP2_PG | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU2_VDDQ2_PG    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
SYS_5V_STBY_PG   | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
BP_1_PG          | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
BP_2_PG          | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU1_DDR_VPP2_PG | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
BP_3_PG          | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU1_DDR_VPP1_PG | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU2_DDR_VPP1_PG | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU1_VDDQ1_PG    | 0x0        | discrete   | 0x0180| na        | na        | na        | na        | na        | na
CPU2_DIMM_B1     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A6     | 0x0        | discrete   | 0x4080| na        | na        | na        | na        | na        | na
CPU2_DIMM_B5     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B2     | 0x0        | discrete   | 0x4080| na        | na        | na        | na        | na        | na
CPU1_DIMM_A1     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B4     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A4     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A7     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B3     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B7     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B8     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A8     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU2_DIMM_B6     | 0x0        | discrete   | 0x4080| na        | na        | na        | na        | na        | na
CPU1_DIMM_A5     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A2     | na         | discrete   | na    | na        | na        | na        | na        | na        | na
CPU1_DIMM_A3     | 0x0        | discrete   | 0x4080| na        | na        | na        | na        | na        | na
Table 5 Response field description
Status
Sensor status. Supported options:
·     na—A sensor is absent.
·     ok—A sensor is operating correctly.
·     nc—A minor error occurs on a sensor.
·     cr—A major error occurs on a sensor.
·     nr—A critical error occurs on a sensor. The error is not recoverable.
Use sensor get to obtain status information of a fan in a chassis.
ipmitool -I connect_type -H hostname -U username -P password sensor get FAN_Status
Table 6 Request field description
FAN_Status
Specify the name of a fan status sensor, for example, FAN1_Status and FAN2_Status.
User role
User
Required permission
Information query
Make sure the specified sensor name is correct. To obtain the names of supported sensors, execute the sensor list command.
# Obtain status information of a fan in a chassis.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sensor get FAN1_Status
Locating sensor record...
Sensor ID              : FAN1_Status (0x60)
 Entity ID             : 30.0
 Sensor Type (Discrete): Fan
 States Asserted       : Availability State
                         [Transition to Running]
sensor list
Use sensor get to obtain the rotation speed information of a fan.
ipmitool -I connect_type -H hostname -U username -P password sensor get FAN_Speed
Table 7 Request field description
FAN_Speed
Specify the name of a fan speed sensor, for example, FAN1_Speed and FAN2_Speed.
User role
User
Required permission
Information query
# Obtain the rotation speed information of a fan.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sensor get FAN1_Speed
Sensor ID              : FAN1_Speed (0x70)
 Entity ID             : 29.0
 Sensor Type (Analog)  : Fan
 Sensor Reading        : 3400 (+/- 0) RPM
 Status                : ok
 Lower Non-Recoverable : na
 Lower Critical        : na
 Lower Non-Critical    : na
 Upper Non-Critical    : na
 Upper Critical        : na
 Upper Non-Recoverable : na
 Assertion Events      :
 Assertions Enabled    :
sensor list
Use mc selftest to perform a server self-test on HDM.
ipmitool -I connect_type -H hostname -U username -P password mc selftest
User role
User
Required permission
Information query
# Perform a server self-test on HDM.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ mc selftest
Selftest: passed
Reset HDM
Use mc reset to reset HDM.
ipmitool -I connect_type -H hostname -U username -P password mc reset warm
Table 8 Request field description
warm
Specify warm reset. This operation resets HDM without disconnecting the system power.
User role
Administrator
Required permission
Maintenance
# Reset HDM.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ mc reset warm
Sent warm reset command to MC
Use sensor reading to obtain the reading of a sensor.
ipmitool -I connect_type -H hostname -U username -P password sensor reading sensor_id
Table 9 Request field description
sensor_id
Specify the sensor name.
User role
User
Required permission
Information query
This command can obtain reads of only available continuous-type sensors such as temperature, voltage, current, power, and speed sensors.
# Obtain the reading of a sensor.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sensor reading FAN5_F_Speed
FAN5_F_Speed     | 5000
sensor list
Use sensor thresh to set the alarm threshold for a sensor.
ipmitool -I connect_type -H hostname -U username -P password sensor thresh sensor_id threshold value
Table 10 Request field description
sensor_id
threshold
Specify the threshold type. Table 11 displays the available threshold types.
value
Specify the threshold value.
Table 11 Available threshold types
unr
Upper critical alarm threshold.
ucr
Upper major alarm threshold.
unc
Upper minor alarm threshold.
lnr
Lower critical alarm threshold.
lcr
Lower major alarm threshold.
lnc
Lower minor alarm threshold.
lower
Specifies all lower alarm thresholds in the following order: lower minor, lower major, and lower critical.
upper
Specifies all upper alarm thresholds in the following order: upper minor, upper major, and upper critical.
User role
Administrator
Required permission
Maintenance
CAUTION
CAUTION:
As a best practice, perform this task under professional guidance.
# Set the upper minor, upper major, and upper critical thresholds of the HDM temperature sensor to 70°C (158°F), 80°C (176°F), and 90°C (194°F), respectively.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sensor thresh "24-BMC Zone" upper  70 80 90
Locating sensor record '24-BMC Zone'...
Setting sensor "24-BMC Zone" Upper Non-Critical threshold to 70.000
Setting sensor "24-BMC Zone" Upper Critical threshold to 80.000
Setting sensor "24-BMC Zone" Upper Non-Recoverable threshold to 90.000
sensor list
Change history
Version
Change description
HDM-6.13
Use sel to obtain SEL information.
ipmitool -I connect_type -H hostname -U username -P password sel
User role
User
Required permission
Information query
# Obtain SEL information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ sel
SEL Information
Version          : 1.5 (v1.5, v2 compliant)
Entries          : 175
Free Space       : 62352 bytes
Percent Used     : 4%
Last Add Time    : 01/01/2018 08:00:27
Last Del Time    : Not Available
Overflow         : false
Supported Cmds   : 'Delete' 'Partial Add' 'Reserve' 'Get Alloc Info'
# of Alloc Units : 3639
Alloc Unit Size  : 18
# Free Units     : 3464
Largest Free Blk : 3464
Max Record Size  : 13
Use fru to obtain FRU information.
ipmitool -I connect_type -H hostname -U username -P password fru
User role
User
Required permission
Information query
# Obtain FRU information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ fru
FRU Device Description : Builtin FRU Device (ID 0)
 Chassis Type           : Rack Mount Chassis
 Chassis Part Number    : 0200A00T
 Chassis Serial         : 210200A00TH177000016
 Chassis Extra          : User Defined
 Chassis Extra          : 74EACB5A5D7C
 Chassis Extra          : 6
 Chassis Extra          : FC9612PW11
 Board Mfg Date        : Fri Jul 14 00:00:00 2017
 Board Mfg             : ABC
 Board Product         : RS23M2C3S
 Board Serial          : 02A3U0H176000003
 Board Part Number     : 0302A3U0
 Board Extra           : 210235A2DBH177000014
 Product Manufacturer  : Unis Huashan Technologies Co., Ltd.
 Product Name          : UniServer R2700 G3
 Product Part Number   : 0200A00T
 Product Serial        : 210200A00TH177000016
 Product Asset Tag     : @!!
FRU Device Description : Expander (ID 1)
 Device not present (Requested sensor, data, or record not found)
FRU Device Description : BackPanel1 (ID 2)
 Board Mfg Date        : Thu Apr 20 08:00:00 2017
 Board Mfg             : ABC
 Board Product         : RS33B08SA
 Board Serial          : 02A3GNH174000023
 Board Part Number     : 0302A3GN
 Board Extra           : 02A3GNH174000023
FRU Device Description : HBA_Raid (ID 12)
 Board Mfg Date        : Sat Jun 17 08:00:00 2017
 Board Mfg             : ABC
 Board Product         : RS33H2P8SA
 Board Serial          : 02A3H0H176000047
 Board Part Number     : 0302A3H0
 Board Extra           : 02A3H0H176000047
FRU Device Description : BackPanel2 (ID 13)
FRU Device Description : mLOM (ID 3)
 Unknown FRU header version 0xff
FRU Device Description : PcieCard1 (ID 5)
FRU Device Description : PcieCard2 (ID 8)
FRU Device Description : BackPanel3 (ID 14)
FRU Device Description : Riser1 (ID 16)
 Board Mfg Date        : Thu Jun  8 08:00:00 2017
 Board Mfg             : ABC
 Board Product         : RS33RGPX16
 Board Serial          : 02A3H9H176000059
 Board Part Number     : 0302A3H9
 Board Extra           : 02A3H9H176000059
FRU Device Description : Riser2 (ID 17)
FRU Device Description : M.2 (ID 15)
FRU Device Description : Mezzine (ID 19)
FRU Device Description : LP_Card (ID 20)
FRU Device Description : MB BMC (ID 21)
 Product Manufacturer  : ABC
 Product Name          : BMC
 Product Part Number   : HDM
 Product Version       : 1.11.09
FRU Device Description : MB BIOS (ID 22)
 Product Name          : BIOS
 Product Part Number   : C35
 Product Version       : 1.01.04
Use session info to obtain information about the current HDM sessions.
ipmitool -I connect_type -H hostname -U username -P password session info { active | all | id id | handle handle }
Table 12 Request field description
active
Specify active sessions.
all
Specify all sessions.
id id
Specify the ID of a user, in the 0xnnnnnnnn format.
handle handle
Specify a session handle, in the 0xnn format.
User role
User
Required permission
Information query
# Obtain information about active sessions.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ session info active
session handle                : 13
slot count                    : 36
active sessions               : 1
user id                       : 2
privilege level               : ADMINISTRATOR
session type                  : IPMIv2/RMCP+
channel number                : 0x01
console ip                    : 192.16.1.196
console mac                   : 2c:41:38:9f:9b:ab
console port                  : 2043
Use this command to obtain server power status and UID LED status.
ipmitool -I connect_type -H hostname -U username -P password raw 0x00 0x01
User role
User
Required permission
Information query
# Obtain server power status and UID LED status.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x01
 41 01 40 f0
Table 13 Response field description
Data[1]
Bits[7:1]: N/A
Bit[0]: Current power status. Supported options:
·     1b—Power-on.
·     0b—Power-off.
Data[2]
N/A
Data[3]
Bit[7]: Reserved.
Bit[6]: Indicates whether UID LED is supported. Supported options:
·     1b—Supported.
·     0b—Not supported.
Bits[5:4]: UID LED status.
·     Supported options for G3:
¡     00bOff.
¡     01b—Steady on.
¡     10b—Flashing.
¡     11b—Reserved.
·     Supported options for G5:
¡     00bOff.
¡     01b—Flashing.
¡     10b—Steady on.
¡     11bReserved.
Bits[3:0]: N/A
Data[4]
N/A
Change history
Version
Change description
HDM-2.0.04
Changed the UID LED status for G5 servers to the standard.
Use this command to set server UID LED status.
ipmitool -I connect_type -H hostname -U username -P password raw 0x00 0x04 0x00 uid_state
Table 14 Request field description
Request field
uid_state
Specify the status of UID LED. Supported options:
·     0x00: Off.
·     0x01: On.
Required permission
Remote control
# Set server UID LED status to off.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x04 0x00 0x00
# Set server UID LED status to on.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x04 0x00 0x01
Use this command to obtain FRU information and saves the information to the fru.bin file in the current directory.
ipmitool -I connect_type -H hostname -U username -P password fru read ID  directory/xxx.bin
Required permission
Information query
# Obtain system board FRU information and save the information to the current directory.
COMMAND>ipmitool -I lanplus -H 192.168.30.41 -U admin -P Password@_ fru read 0 ./fru.bin
Fru Size         : 992 bytes
Done
Change history
Version
Change description
HDM-2.0.07
Added this command.
User management
Use user list to obtain information about all HDM users.
ipmitool -I connect_type -H hostname -U username -P password user list
User role
Operator
Required permission
Information query
# Obtain information about all HDM users.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user list
ID  Name             Callin  Link Auth  IPMI Msg   Channel Priv Limit
1                    false   false      true       ADMINISTRATOR
2   admin            false   false      true       ADMINISTRATOR
Use user summary to obtain brief HDM user information.
ipmitool -I connect_type -H hostname -U username -P password user summary
User role
Operator
Required permission
Information query
# Obtain brief HDM user information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user summary
Maximum IDs         : 16
Enabled User Count  : 2
Fixed Name Count    : 2
Add an HDM user
Use user set name to add an HDM user.
ipmitool -I connect_type -H hostname -U username -P password user set name user_id username
Table 15 Request field description
user_id
Specify a user ID. Make sure the user ID is no larger than the value of the Maximum IDs field in the output from the user summary command.
username
Specify a username, a case-sensitive string of 1 to 16 characters. Only letters, digits, dots (.), hyphens (-), and underscores (_) are allowed.
Only an administrator user exists and the username is admin.
User role
Administrator
Required permission
User accounts
If the specified user ID already exists with a different username, the command changes the existing username of the user.
To add a user, you must also specify the password, enable HDM access, and specify the HDM user role for the user.
# Add an HDM user, set the user ID to 9, and specify the username as test.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user set name 9 test
# View information about all HDM users.
9   test             true    false      false      NO ACCESS
user set password
user enable
user priv
Use user set password to set the password for an HDM user.
ipmitool -I connect_type -H hostname -U username -P password user set password user_id password
Table 16 Request field description
user_id
Specify a user ID. Make sure the user ID already exists.
password
Specify the password string, a case-sensitive string. The password can contain 16 or 20 characters. Only letters, digits, spaces, and the following special characters are allowed: `~!@#$%^&*()_+-=[]\{}|;':",./<>?
No password is set for an HDM user.
User role
Administrator
Required permission
User accounts/Password modification
To add a user, you must specify a password for the user.
# Specify a password for the user whose ID is 9.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user set password 9 123
user set name
user enable
user priv
Use user test to verify an HDM user password.
ipmitool -I connect_type -H hostname -U username -P password user test user_id password_max_len_type password
Table 17 Request field description
user_id
Specify the user ID. Make sure the specified user ID already exists.
Specify the password length. Options include 16 and 20.
password
Specify the password.
User role
Administrator
Required permission
# Verify the password of the HDM user whose user ID is 9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user test 9 16 123
Success
// The system returns success for a valid password.
Disable HDM access
Use user disable to disable HDM access for a user.
ipmitool -I connect_type -H hostname -U username -P password user disable user_id
Table 18 Request field description
user_id
HDM access is enabled for the default user admin and disabled for manually added users.
User role
Administrator
Required permission
# Disable HDM access for the user whose user ID is 9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user disable 9
Enable HDM access
Use user enable to enable HDM access for a user.
Table 19 Request field description
user_id
User role
Administrator
Required permission
For a manually added user to access HDM, you must enable HDM access for the user.
# Enable HDM access for the user whose user ID is 9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user enable 9
user set name
user set password
user priv
Use this command to delete an HDM user.
ipmitool -I connect_type -H hostname -U username -P password raw 0x06 0x45 user_id 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff
Table 20 Request field description
user_id
User role
Administrator
Required permission
User accounts
# Delete the HDM user whose user ID is 9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x06 0x45 0x09 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff 0xff
Use user priv to specify the HDM user role for a user.
ipmitool -I connect_type -H hostname -U username -P password user priv user_id privilege_level
The HDM user role of the default user admin is administrator and the HDM user role of a manually added user is none.
Table 21 Request field description
user_id
privilege_level
Specify the HDM user role. Supported options:
·     2—Specifies the user role. The user has read-only permission.
·     3—Specifies the operator role. The user has read permission to all features and has write permission to some features.
·     4Specifies the administrator role. The user has read and write permissions to all features.
·     6 to 10—Custom 1 to 5.
·     15—None. The user does not have network access permissions.
User role
Administrator
Required permission
User accounts
For a manually added user to access HDM, you must use this command to specify non-none HDM user role for the user.
Some ipmitool tools verify user permissions and support only one OEM permission (privilege_level=0x05). The ipmitool-1.8.8 supports configuring the privilege level in the range of 6 to 10.
# Specify the administrator role for the user whose ID is 9.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ user priv 9 4
user set name
user set password
user enable
user priv
Change history
HDM-2.0.04
Added user roles custom 1 to 5.
HDM IPv4 management
Use this command to obtain the IP address obtaining method for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0x04 0x00 0x00
Table 22 Request field description
Data[1]
G3:
·     0x01—Specifies the shared network port.
·     0x08Specifies the dedicated network port.
G5:
·     0x01—Specifies the dedicated network port.
·     0x08Specifies the shared network port.
User role
User
Required permission
Information query
# Obtain the IP address obtaining method for the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x01 0x04 0x00 0x00
 11 01
Table 23 Response field description
Data[1]
This field is fixed to 0x11.
Data[2]
IP address obtaining method. Supported options:
·     01Static IP.
·     02DHCP.
Change history
Version
Change description
HDM-2.0.03
The HDM user role was changed as follows:
G3:
G5:
·     0x08—Specifies the shared network port.
Use user priv to obtain the IP address of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0x03 0x00 0x00
Table 24 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Use a in-band system command to obtain the IP address the shared network port.
[root@localhost~]#ipmitool raw 0x0c 0x02 0x01 0x03 0x00 0x00
 11 c0 a8 32 a6
Table 25 Response field description
Data[1]
Data[2:5]
IP address of the network port, in hexadecimal notation.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to obtain the MAC address of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0x05 0x00 0x00
Table 26 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Obtain the MAC address of the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x01 0x05 0x00 0x00
 11 30 7b ac 76 0f 65
Table 27 Response field description
Data[1]
Data[2:7]
MAC address of the network port.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to obtain the subnet mask of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0x06 0x00 0x00
Table 28 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Obtain the subnet mask of the shared network port.
Table 29 Response field description
Data[1]
Data[2:5]
Subnet mask of the network port.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to obtain the gateway address.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0x0c 0x00 0x00
Table 30 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Obtain the gateway address of the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x01 0x0c 0x00 0x00
 11 c0 a8 32 01
Table 31 Response field description
Data[1]
Data[2:5]
IP address of the gateway, in hexadecimal notation.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to set the IP address obtaining method for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0x04 Data[2]
Table 32 Request field description
Data[1]
G3:
G5:
Data[2]
Specify IP obtaining method. Supported options:
·     01—Static IP.
·     02—DHCP.
User role
Administrator
Required permission
Basic configuration
# Set the IP obtaining method of the shared network port to DHCP.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0x04 0x02
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to specify a static IP address for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0x03 Data[2:5]
Table 33 Request field description
Data[1]
G3:
G5:
Data[2:5]
Specify an IP address, in hexadecimal notation.
No IP address is specified for a network port.
User role
Administrator
Required permission
Basic configuration
This command is available only when the IP obtaining method is static for the network port.
# Specify a static IP address for the shared network port.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0x03 0xc0 0x10 0x01 0x4e
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to specify a subnet mask for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0x06 Data[2:5]
Table 34 Request field description
Data[1]
G3:
G5:
Data[2:5]
Specify a subnet mask, in hexadecimal notation.
No subnet mask is specified for a network port.
User role
Administrator
Required permission
Basic configuration
# Specify a subnet mask for the shared network port.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0x06 0xff 0x00 0x00 0x00
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to specify a gateway address for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0x0c Data[2:5]
Table 35 Request field description
Data[1]
G3:
G5:
Data[2:5]
Specify a gateway address, in hexadecimal notation.
No gateway address is specified for a network port.
User role
Administrator
Required permission
Basic configuration
Make sure the gateway address is in the same network segment as the IP address of the network port.
# Specify a gateway address for the shared network port.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0x0c 0xc0 0xa8 0x32 0x01
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
HDM IPv6 management
Use this command to obtain the IPv6 address of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0xcf 0x00 0x00
Table 36 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x08 0x0cf 0x00 0x00
 11 fe 80 00 00 00 00 00 00 ee d6 8a ff fe 3c 0d 2f
Table 37 Response field description
Data[1]
Data[2:17]
IPv6 address of the network port, in hexadecimal notation.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0x38 0x00 0x80 Data[2:17] Data[18] 0x00
Table 38 Request field description
Data[1]
G3:
G5:
Data[2:17]
Specify an IPv6 address, in hexadecimal notation.
Data[18]
Specify the IPv6 prefix, in hexadecimal notation.
A port obtains an IPv6 address through DHCP.
User role
Administrator
Required permission
Basic configuration
In bonding mode, the specified IPv6 address also applies to the bond port (bond0).
# Specify a static IPv6 address for the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0x38 0x00 0x80 0x20 0x01 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x20 0x40 0x00
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to specify a prefix length for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0xc6 Data[2] Data[3]
Table 39 Request field description
Data[1]
G3:
G5:
Data[2]
Specify the position of the IPv6 prefix. This field is fixed to 0.
Data[3]
Specify the prefix length.
A port obtains a prefix length address through DHCP.
User role
Administrator
Required permission
Basic configuration
This command is available only when a static IPv6 address has been specified for the network port.
# Set the prefix length to 72 for the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0xc6 0x00 0x48
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to obtain the prefix length of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0xc6 0x00 0x00
Table 40 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Obtain the prefix length of the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x08 0xc6 0x00 0x00
 11 40
Table 41 Response field description
Data[1]
Data[2]
Prefix length, in hexadecimal notation.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to obtain the IPv6 address obtaining method for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x02 Data[1] 0xc4 0x00 0x00
Table 42 Request field description
Data[1]
G3:
G5:
User role
User
Required permission
Information query
# Obtain the IPv6 address obtaining method for the shared network port.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x02 0x01 0xc4 0x00 0x00
 11 01
Table 43 Response field description
Data[1]
Data[2]
IPv6 address obtaining method. Supported options:
·     01Static IP.
·     02DHCP.
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to set the IPv6 address obtaining method for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0xc4 Data[2]
Table 44 Request field description
Data[1]
G3:
G5:
Data[2]
Specify the IPv6 obtaining method. Supported options:
·     01Static IP.
·     02—DHCP.
User role
Administrator
Required permission
Basic configuration
You can use this command to change the IPv6 address obtaining method from static to DHCP. To change the method from DHCP to static, use the command as shown in "Specify a static IPv6 address for a network port."
# Change the IPv6 address obtaining method from static to DHCP for the shared network port.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0xc4 0x02
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
Use this command to specify the IPv6 gateway address for a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0c 0x01 Data[1] 0xc7 Data[2:17]
Table 45 Request field description
Data[1]
G3:
G5:
Data[2:17]
Specify an IPv6 gateway address, in hexadecimal notation.
No IPv6 gateway address is specified for a network port.
User role
Administrator
Required permission
Basic configuration
This command is available only when the IPv6 obtaining method is static for the network port.
Make sure the IPv6 gateway address is in the same network segment as the IPv6 address of the network port.
# Specify an IPv6 gateway address for the shared network port.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0c 0x01 0x01 0xc7 0x3f 0xfe 0x05 0x01 0xee 0xee 0x00 0x02 0x3a 0x91 0xd5 0xff 0xfe 0xec 0x60 0xd3
Change history
Version
Change description
HDM-2.0.03
G3:
G5:
System boot
Set the one-time next boot option
Use chassis bootdev to set the one-time next boot option.
ipmitool -I connect_type -H hostname -U username -P password chassis bootdev boot_mode boot_mode
Table 46 Request field description
boot_mode
Specify the boot option. Options include disk, cdrom, and pxe.
The server starts from the boot option configured in the BIOS.
User role
Operator
Required permission
Remote control
# Set the one-time next boot option to cdrom.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis bootdev cdrom
Set Boot Device to cdrom
Remove the configured one-time next boot option
Use chassis bootdev none to remove the configured one-time next boot option and enable the server to start from the boot option configured in the BIOS.
ipmitool -I connect_type -H hostname -U username -P password chassis bootdev none
User role
Operator
Required permission
Remote control
# Remove the configured one-time next boot option.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis bootdev none
Configure the server to enter the BIOS setup utility after startup
Use chassis bootdev bios to configure the server to enter the BIOS setup utility after startup.
ipmitool -I connect_type -H hostname -U username -P password chassis bootdev bios
The server starts up as configured in the BIOS.
User role
Operator
Required permission
Remote control
# Configure the server to enter the BIOS setup utility after startup.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ chassis bootdev bios
Set Boot Device to bios
Device extended commands
Hardware information
Obtain the number of present PCIe modules
Use this command to obtain the number of present PCIe modules, including storage controllers and AIC NVMe drives.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x1f
User role
User
Required permission
Information query
# Obtain the number of present PCIe modules.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x1f
 a2 63 00 03
Table 47 Response field description
Data[1:3]
Manufacturer ID. This field is fixed to a2 63 00.
Data[4]
Number of present PCIe modules, including special cards, such as NVMe modules and clock cards.
Obtain PCIe module information
Use this command to obtain information about PCIe modules, including storage controllers, GPUs, NICs, and U.2 NVMe drives.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x20 pcie_index
Table 48 Request field description
pcie_index
Specify the index of the PCIe module, starting from 0. The value range varies by device model.
User role
User
Required permission
Information query
# Obtain information about the PCIe module with index 2.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x20 0x02
 a2 63 00 03 00 86 80 d1 37 86 80 00 00 3d 3d 01
01 19 01 4e 49 43 2d 47 45 2d 34 50 2d 33 36 30
54 2d 4c 33 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 01 00 31 2e
31 37 36 37 2e 30 00 00 00 00 00 00 00 00 00 00
00 00 01 00 30 32 41 33 47 4b 48 31 37 42 30 30
30 32 36 37 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 30 33 30 32 41 33 47 4b 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 02 00
00 00 00 04 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 01 ff 00 00 00
Table 49 Response field description
Data[1:3]
Data[4:5]
Slot number.
Data[6:7]
Vendor ID.
Data[8:9]
Device ID.
Data[10:11]
Sub vendor ID.
Data[12:13]
Sub device ID.
Data[14:15]
Bus number. The lower bytes come first.
Data[16]
Current speed.
·     1—2.5GT/s.
·     2—5.0GT/s.
·     3—8.0GT/s.
·     4—16.0GT/s.
Data[17]
Current bandwidth.
·     1x1.
·     2x2.
·     4x4.
·     8x8.
·     16x16.
Data[18]
Max speed.
·     12.5GT/s.
·     25.0GT/s.
·     38.0GT/s.
·     416.0GT/s.
·     532.0GT/s.
·     25—2.5GT/s.
·     50—5.0GT/s.
·     80—8.0GT/s.
·     96—16.0GT/s.
·     160—16.0GT/s.
Data[19]
PCIe generation.
Data[20:59]
Product name.
Data[60]
PCIe status. Supported options:
·     0—Normal.
·     1—Abnormal.
·     2—Absent.
Data[61]
Page display. Supported options:
·     0—No.
·     1—Yes.
Data[62]
Alarm status. Options:
·     0—Normal.
·     1—Alarm triggered.
Data[63:70]
Reserved. This field is 0 by default.
Data[63:82]
Firmware version.
Data[83:84]
Network adapter port speed.
Data[85-116]
Serial number. The serial number has 32 characters and ends with \0.
Data[117-141]
Part number. The part number has 25 characters and ends with \0.
Data[142]
Reserved.
Data[143]
PciBaseClassCode.
Data[144]
PciSubClassCode.
Data[145]
PCIe bus range.
Data[146]
Device ID.
Data[147]
Function ID.
Data[148]
Network adapter ports.
Data[149]
CPU bus.
Data[150
CPU device.
Data[151]
CPU function.
Data[152]
CPU ID. 0xff represents invalid values.
Data[153-168]
Slot description.
Data[169]
PCIe device type.
·     0—Not present.
·     1—Ethernet.
·     2—GPU.
·     3—FC HBA.
·     4—IB.
·     5—RAID/HBA.
·     6—M.2 NVMe.
·     7—AIC NVMe.
·     8—Retimer.
·     9—Switch.
·     10—M.2.
·     11U2 NVME (not supported).
·     12—REDRIVER.
·     13QAT.
·     14Clock card.
·     15MOC card.
Data[170]
Card bandwidth. Maximum number of PCIe lanes supported.
Data[171-173]
Reserved[3]
Change history
Version
Change description
HDM-3.32 and HDM-6.04
Added options 1 to 5 for the MaxSpeed field.
HDM-2.51
Added the MOC card field for the PCIe device type.
HDM-2.28
Added the Clock card field for the PCIe device type.
HDM-2.27
Added the QAT field for the PCIe device type.
HDM-2.26
Added the Card bandwidth field.
HDM-2.17.00
Resolved the compatibility issue in 2.13.00 by moving the CPU bus, CPU device, and CPU function fields to the rear of the PortNum field.
HDM-2.16.00
Added the U2 NVME and REDRIVER fields for the PCIe device type.
HDM-2.13.00
Added the CPU bus, CPU device, and CPU function fields to the rear of the PciProgIF field, which caused compatibility issues.
HDM-2.13.00
Added the CPU ID, slot description, and PCIe device type fields.
HDM-1.30.17
Added the network adapter ports field.
HDM-1.30.09
Added the PciBaseClassCode, PciSubClassCode, PCIe bus range, device ID, and function ID fields.
HDM-1.30.08
Added the serial number and part number fields.
Obtain port information on an Ethernet adapter
Use this command to obtain information about ports on an Ethernet adapter.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x16 mlom_id
Table 50 Request field description
mlom_id
Specify the ID of an Ethernet adapter. For a 1U device, the ID is 3. For a 2U device, the ID is 9. For other devices, the ID is the number of the slot in which the Ethernet adapter resides.
User role
User
Required permission
Information query
# Obtain information about ports on the Ethernet adapter in slot 9.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x16 0x09
 a2 63 00 04 01 09 74 ea cb 5a 5d 7e 02 09 74 ea
 cb 5a 5d 7f 03 09 74 ea cb 5a 5d 80 04 09 74 ea
 cb 5a 5d 81 00 00 00 00 00 00 00 00 00 00 00 00
 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Table 51 Response field description
Data[1:3]
Data[4]
Number of ports on the Ethernet adapter.
Data[5:132]
Detailed port information, including port number (1 byte), reserved field (1 byte), and MAC address (6 bytes). Information about each port occupies eight bytes and a maximum of 16 ports are supported. If a port is absent, 0x00 is displayed in the output.
Obtain the number of supported CPUs and DIMMs
Use this command to obtain the number of supported CPUs and DIMMs.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0b
User role
User
Required permission
Information query
# Obtain the number of supported CPUs and DIMMs.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x0b
 a2 63 00 ff 02 18 0c 00 00 00 00 00 00
Table 52 Response field description
Data[1:3]
Data[4]
Base board type. Supported options:
·     20h—V5R1.
·     00h—UIS.
·     28h—CR16K.
·     ffh—Unknown.
This field is available only for G2 servers. For G3 or new products, ignore this field.
Data[5]
Maximum number of CPUs, in hexadecimal notation.
Data[6]
Maximum number of DIMMs, in hexadecimal notation.
Data[7]
Maximum number of DIMMs supported by each CPU, in hexadecimal notation.
Data[8:13]
Change history
Version
Change description
HDM-6.12
Added the application scope of Data[4] to indicate that the field has been discarded for new products.
Obtain CPU information
Use this command to obtain the presence status and parameters of a CPU.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x07 cpu_id
Table 53 Request field description
cpu_id
Specify the ID of a CPU, starting from 0. The value range varies by device model.
User role
User
Required permission
Information query
# Obtain CPU information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x07 0x01
 a2 63 00 01 01 00 00 49 6e 74 65 6c 28 52 29 20
 58 65 6f 6e 28 52 29 20 42 72 6f 6e 7a 65 20 33
 31 30 34 20 43 50 55 20 40 20 31 2e 37 30 47 48
 7a 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
 00 00 00 00 00 00 00 01 02 fc 00 a4 06 80 01 00
 18 00 21 06 06 06 00 00 00 00 00 00 00 00 00 00
 00
Table 54 Response field description
Data[1:3]
Data[4]
CPU number.
Data[5]
Presence status of the CPU. Supported options:
·     0hAbsent.
·     1hPresent.
Data[6]
Data source. Supported options:
·     00hBIOS.
·     01hAgent.
·     OthersReserved.
Date[7]
Version field. This field is reserved and is 0 by default.
Data[8:71]
CPU model. The model ends with \0.
Data[72]
CPU status. Supported options:
·     00hUnavailable.
·     01hGood.
Data[73]
Number of memory controller (MC).
Data[74:75]
Processor attributes. Supported options:
·     BIT0—Reserved.
·     BIT1—Unknown.
·     BIT2—64-bit capable.
·     BIT3—Multi-core.
·     BIT4—Hardware thread.
·     BIT5—Execute protection.
·     BIT6—Enhanced virtualization.
·     BIT7—Power/Performance control.
·     BIT8-15—Reserved.
Data[76:77]
Base frequency, in MHz.
Data[78:79]
L1 cache, in little endian format.
Data[80:81]
L2 cache, in little endian format.
Data[82:83]
L3 cache, in little endian format.
Data[84]
Total number of cores.
Data[85]
Number of available cores.
Data[86]
Number of threads.
Data[87]
Cache unit.
·     0, 1L1 cache unit.
·     2, 3L2 cache unit.
·     4, 5L3 cache unit.
Cache unit:
·     0—KB. (Default.)
·     1—MB.
·     2—GB.
Data[88:95]
CPU ID, in little endian format.
Data[96:103]
CPU SN, in little endian format. This field is not available for Intel and AMD server models.
Data[104:111]
CPU PPIN, in little endian format. This field is not available for Hygon server models.
Data[112-113]
Maximum CPU frequency, in MHz and in little endian format.
Data[114:129]
Reserved.
Change history
Version
Change description
HDM-6.05
Added description for support of Data[96-103] and Data[104-111] for CPUs.
HDM-3.36
Corrected the error description for Data[74-75]. The features supported by the processor should be analyzed and interpreted according to bit positions.
HDM-1.30.13
Added the maximum CPU frequency field.
HDM-1.30.08
Added the CPU SN and CPU PPIN fields.
Obtain memory information
Use this command to obtain memory information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x08 Memory_Index
Table 55 Request field description
Memory_Index
Specify the index of a DIMM.
User role
User
Required permission
Information query
# Obtain memory information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x08 0x00
a2 63 00 00 01 00 00 00 00 02 01 48 4d 41 38 32
47 52 37 44 4a 52 38 4e 2d 58 4e 20 20 20 00 1a
03 02 00 00 ad 00 40 00 00 6a 0a 80 0c 01 38 32
46 45 39 35 36 37 00 00 00 00 00 00 00 00 00 00
00
Table 56 Response field description
Data[1:3]
Data[4-55]
G3 memory information. For more information, see Table 57.
Data[56-193]
G5 memory information. For more information, see Table 58.
Table 57 G3 memory information
Data[4]
Channel number.
Data[5]
Presence status. Supported options:
·     00hAbsent.
·     01hPresent.
Data[6]
·     00h—BIOS.
·     01hAgent.
·     OthersReserved.
Data[7]
CPU number. Supported options:
·     00hCPU 1.
·     01hCPU 2.
Data[8]
Channel number.
Data[9]
DIMM number in the channel.
Data[10]
DIMM authentication status. Supported options:
·     00h—Absent.
·     01h—Genuine.
·     02hPiracy.
·     03hN/A.
Data[11]
DIMM status. Supported options:
·     0—Unavailable or disabled.
·     1Available.
·     2Abnormal.
·     3Not initialized.
Data[12:31]
Part number.
Data[32]
DIMM type. Supported options:
·     18hDDR3.
·     1ah—DDR4.
·     1bh—LPDDR.
·     1ch—LPDDR2.
·     1dh—LPDDR3.
·     1eh—LPDDR4.
·     Others—N/A.
Data[33]
Operating voltage. Supported options:
·     00h—1.1 V.
·     01h—1.35 V.
·     03h—1.2 V.
Data[34]
Bits[7:4]: Reserved.
Bits[3:0]: DIMM ranks.
Data[35]
Memory technology. Supported options:
·     00h—RDIMM.
·     01h—UDIMM.
·     02h—SODIMM.
·     09h—LRDIMM.
·     Others—N/A.
Data[36:37]
Vendor number.
Data[38:41]
DIMM capacity, in MiB.
Data[42:43]
Current speed, in MT/s.
Data[44:45]
Maximum speed, in MT/s.
Data[46]
Support for ECC. Supported options:
·     00h—Not supported.
·     01h—Supported.
Data[47:54]
Memory serial number.
Data[55]
Reserved. This field can be extended and is 0 by default.
Table 58 G5 memory information
Data[56]
DIMM ID.
Data[57]
·     00hAbsent.
·     01hPresent.
Data[58]
·     00h—BIOS.
·     01hAgent.
·     OthersReserved.
Data[59]
·     00hCPU 1.
·     01hCPU 2.
Data[60]
Channel number.
Data[61]
Data[62]
·     00h—Absent.
·     01h—Genuine.
·     02hPiracy.
·     03hN/A.
Data[63]
·     1Available.
·     2Abnormal.
·     3—Not initialized.
Data[64:95]
Part number
Data[96]
·     18hDDR3.
·     1ah—DDR4.
·     1bh—LPDDR.
·     1ch—LPDDR2.
·     1dh—LPDDR3.
·     1eh—LPDDR4.
·     Others—N/A.
Data[97]
·     00h—1.5 V.
·     01h—1.35 V.
·     03h—1.2 V.
Data[98]
Data[99:114]
·     00h—RDIMM.
·     01h—UDIMM.
·     02h—SODIMM.
·     09h—LRDIMM.
Data[115:116]
Vendor number.
Data[117:20]
Data[121:122]
Data[123:124]
Data[125]
·     01h—Supported.
Data[126:157]
Data[158:189]
Data[190]
Memory bit width.
Data[191]
Data bit width.
Data[192]
Reason why DIMMs are disabled.
Data[193]
DIMM disabling flag.
Change history
Version
Change description
HDM-6.16
Revised the display of memory information and reduced the length of the part number field for G3 servers.
HDM-6.16
·     Changed the unit of the memory capacity to MiB.
·     Changed the memory frequency to DIMM speed.
·     Revised the display of memory information and extended the length of the part number field.
HDM-6.15
Corrected the unit for the memory speed to MT/s.
HDM-2.0.05
Added Data[56:177] to obtain G5 memory information.
Obtain product generation
Use this command to obtain the product generation.
This command does not have operation log records.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x05 0xa2 0x63 0x00 0x02
User role
User
Required permission
Information query
Product compatibility
UIS, G3, and G5 products.
# Obtain product generation.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x05 0xa2 0x63 0x00 0x02
a2 63 00 34 40 00 5a 04 11 03 01 06 00 00 00 00
00 00 00
Table 59 Response field description
Data[1:3]
Data[4:9]
Reserved.
Data[10]
Product generation:
·     1—UIS.
·     3—G3.
·     5—G5.
Data[11:13]
Reserved.
Data[14]
Product generation of HDM software.
·     0HDM.
Data[15:19]
Reserved.
Change history
Version
Change description
HDM-6.05
No functional changes. Added Data[14] occupancy description, which can be used to distinguish generation information of HDM software. G3/G5 products still return 00h.
Obtain expander information
Use this command to obtain expander information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xA2 0x63 0x00 0x8d Exp_Index
Table 60 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code ( 0x8D).
Data[7]
Expander index.
Required permission
Information query
Not restricted to specific products.
# Obtain expander information.
ipmitool -H 127.0.0.1 -I lanplus -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x8d 0x01
Response values:
a2 63 00 02 01 46 72 6f 6e 74 42 61 63 6b 50 61
6e 65 6c 34 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 30 32 41 32 4e 33 31 32 33 34 35
36 37 38 39 30 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 30 33 30 32 41 32 4e 34 00 00 00
00 00 00 00 00 33 2e 30 30 2e 30 31 00 00 00 00
00 00 00 00 00 33 2e 33 32 2e 30 31 00 00 00 00
00 00 00 00 00
Data[1-3]
Data[4]
Number of expanders.
Data[5]
Expander index.
Data[6-37]
Expander location.
Data[38-69]
Expander serial number.
Data[70-101]
Expander part number.
Data[102-117]
Expander firmware version.
Data[118-133]
Current expander configuration file.
Change history
Version
Change description
HDM-2.25
Added this command.
Obtain server health status
Use this command to obtain the health status of the server and its subsystems.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x05 0xa2 0x63 0x00 0x0a
User role
User
Required permission
Information query
# Obtain the health status of the server and its subsystems.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x05 0xa2 0x63 0x00 0x0a
20 14 00 00 00 00 00 00 00 00 00 00 00 00 00 00
Table 61 Response field description
Data[1:3]
Manufacturer ID. This field is in the range of 0 to 2.
Data[4]
System health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[5]
Health status of the temperature subsystem. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[6]
Health status of the voltage subsystem. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[7]
Health status of the power subsystem. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[8]
Health status of the fan subsystem. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[9]
Health status of the physical drive system. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[10]
Health status of the TPM system. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[11]
System power status. Supported options:
·     00hOn.
·     01hOff.
Data[12]
Memory health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[13]
CPU health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[14]
PCI health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[15]
mLOM (G3)/OCP (G5) health status. Supported options:
·     00hThe mLOM/OCP network adapter is present.
·     01hThe mLOM/OCP network adapter is absent.
·     02hThe mLOM/OCP network adapter is present but failed to be identified.
·     03hThe mLOM/OCP network adapter is absent but the NIC port is present.
Data[16]
Electrical current health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[17]
Logical drive health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[18]
Health LED status. Supported options:
·     3—Amber.
·     2Red.
·     1Green.
·     0Off.
Data[19]
Reserved.
Data[20]
Server board health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Data[21]
Operating system health status. Supported options:
·     00hNormal.
·     01hMinor.
·     02hMajor.
·     03hCritical.
Change history
Version
Change description
HDM-2.51
Revised errors in the system power-on status ouput information.
HDM-2.16.00
Added support for G5 OCP health status.
HDM-2.13.00
Data[19] was reserved.
HDM-2.0.07
Added the operating system health status field.
HDM-1.30.14
Added the system module health status field.
HDM-1.30.13
Added the redirected page for the PCIe health LED field.
HDM-1.30.11
Added the health LED status field.
HDM-1.30.10
Added the logical drive status field.
Host
Obtain security bezel LED configuration
Use this command to obtain security bezel LED configuration.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x0c
Table 62 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Required permission
Information query
G5 rack servers that support security bezels.
# Obtain security bezel LED configuration.
a2 63 00 01 01 01 01 01 01 01 01
Table 63 Response field description
Data[1-3]
Data[4]
·     0Absent.
·     1Present.
Data[5]
Logo LED:
·     0—Off.
·     1—On.
Data[6]
LED:
·     0—Off.
·     1—On.
Data[7]
Status sync:
·     0—Off.
·     1—On.
Data[8]
Health status sync:
·     0—Off.
·     1—On.
Data[9]
Energy saving mode:
·     0—Off.
·     1—On.
Data[10]
Decorative LEDs:
·     1—Breathing.
·     2—Flashing.
·     3—Steady on.
Data[11]
Decorative LEDs color:
·     1—White.
·     2—Orange.
·     3—Red.
Change history
Version
Change description
HDM-2.25
Added the health status sync field.
HDM-2.13.00
Added this command.
Set security bezel LEDs
Use this command to set security bezel LEDs.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x69 0x01 0x01 0x01 0x01 0x01 0x01 0x01
Table 64 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Set the logo LED state:
·     0—Off.
·     1—On.
Data[8]
Set the LED state:
·     0—Off.
·     1—On.
Data[9]
Set the status sync feature:
·     0—Off.
·     1—On.
Data[10]
Set the health status sync feature:
·     0—Off.
·     1—On.
Data[11]
Set the energy saving mode:
·     0—Off.
·     1—On.
X10000 G5 servers do not support this field.
Data[12]
Set the flashing mode of decorative LEDs:
·     1—Breathing.
·     2—Flashing.
·     3—Steady on.
Data[13]
Set the color of decorative LEDs:
·     1—White.
·     2—Orange.
·     3—Red.
X10000 G5 servers support only the white color.
Required permission
Basic configuration
# Set security bezel LEDs.
0xa2 0x63 0x00
Table 65 Response field description
Data[1-3]
Change history
Version
Change description
HDM-2.25
HDM-2.13.00
Added this command.
Obtain MCA policy information
Use this command to obtain MCA policy and ACD status information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x53 0x00 0x00
Table 66 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Manufacture ID. This field is fixed to a2 63 00.
Data[6]
Subcommand code.
Data[7]
Obtain the enabling status of MCA restart upon error occurrence and ACD.
Data[8]
Reserved.
User role
user
Required permission
Information obtaining
Only devices that use Intel CPUs support this command.
# Obtain MCA policy information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x53 0x00 0x00
0xa2 0x63 0x00 0x00 0x01
Table 67 Response field description
Data[1:3]
Data[4]
Enabling status of MCA restart upon error occurrence. Supported options:
·     0x01—Do not restart the server upon error occurrence.
·     0x00—Restart the server upon error occurrence.
Data[5]
ACD enabling status. Supported options:
·     0x01Enabled.
·     0x00Disabled.
Change history
Version
Change description
HDM-1.30.11
Added the ACD enabling status field.
Configure MCA policy settings
Use this command to configure the MCA policy and ACD.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x35 0x01/0x00 0x01
Table 68 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Data[8]
·     0x01Enable.
·     0x00Disable. Only G3 servers support the 0x00 option.
Required permission
Remote control
# Configure MCA policy settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x35 0x01 0x01
0xa2 0x63 0x00 0x00 0x00
Table 69 Response field description
Data[1:3]
Data[4:5]
Reserved.
Change history
Version
Change description
HDM-2.16.00
G5 servers do not support the 0x00 option for the ACD enabling status field.
HDM-1.30.15P02
Storage
Obtain storage controller information
Use this command to obtain storage controller information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x00 0x00 0x00 0x04 Ctrl_ID 0x00 0x00 0x00
Table 70 Request field description
Ctrl_ID
Specify the ID of a storage controller.
User role
User
Required permission
Information query
# Obtain storage controller information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 a2 63 00 41 01 00 00 01 00 00 00 00 00 00 ff 52
41 49 44 2d 4c 53 49 2d 39 33 36 31 2d 38 69 28
31 47 29 2d 41 31 2d 58 00 00 00 00 00 00 00 53
4b 37 31 33 37 32 32 39 35 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 31
47 42 00 00 00 00 00 00 00 00 00 00 00 00 00 4d
69 73 73 00 00 00 00 00 00 00 00 00 00 00 00 4d
69 73 73 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 34
2e 36 38 30 2e 30 30 2d 38 32 34 39 00 00 00 00
01 50 06 05 b0 0d 04 3e 90 30 2f 31 2f 35 2f 36
2f 31 30 2f 35 30 2f 36 30 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 3c 01
00 01 00 00 10 33 2e 31 37 30 35 2e 30 30 2d 30
30 30 32 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 32 34 2e 32 31 2e 30 2d 30 30 31
32 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 01 08 ff
Table 71 Response field description
Data[1:3]
Data[4:7]
Length of the remaining response fields.
Data[8:11]
Storage controller status. Supported options:
·     1—Normal.
·     2—Server powered off.
·     3—Storage controller absent.
·     4—Storage controller failed.
·     5—Initializing the BIOS.
Data[12:13]
Storage controller type. Supported options:
·     0—RAID.
·     1—HBA.
Data[14]
Logical driver (LD) offset.
Data[15]
Physical driver (PD) offset.
Data[16:47]
Storage controller name.
Data[48:95]
Storage controller serial number.
Data[96:111]
Cache capacity.
Data[112:127]
Cache module state. Supported options:
·     N/A.
·     Miss.
·     Fail.
·     Optimal.
·     Warning.
Data[128:159]
Supercapacitor status. Supported options:
·     N/A.
·     Miss.
·     Learn.
·     Fault.
·     Over_temp.
·     Learn_fail.
·     Fail.
·     Completed.
·     Charging.
·     Voltage_low.
Data[160:175]
Remaining power of the supercapacitor, in percent.
Data[176:207]
Storage controller firmware version.
Data[208]
Reserved.
Data[209]
Storage data validity. Supported options:
·     0—Invalid.
·     1—Valid.
Data[210:217]
Storage controller WWN.
Data[218:253]
Supported RAID levels.
Data[254]
Storage controller JBOD status. Supported options:
·     1—JBOD mode enabled.
·     0—JBOD mode disabled.
·     0xffInvalid status.
Data[255]
Storage controller temperature.
Data[256:257]
Storage controller PCIe slot number.
Data[258]
Storage controller mode:
·     0Unknown.
·     1—RAID.
·     2—HBA.
·     3—Mixed.
·     4—Non-RAID.
·     6—Auto volume.
·     7—Simple volume.
·     8—JBOD.
Data259]
Reserved.
Data[260:261]
Storage controller SubVendorID.
Data[262:293]
Adapter configuration version: character string.
Data[294:325]
Package version of the LSI storage controller.
Data[326:327]
Reserved.
Data[328]
Whether the controller is an LSI storage controller:
·     1—Yes.
·     0—No.
Data[329]
Number of internal ports of the storage controller.
0xff—Not supported.
Data[330]
Number of external ports of the storage controller.
0xff—Not supported.
Change history
Version
Change description
HDM-3.46
HDM-6.11
·     Added Voltage_low as a supercapacitor status.
·     Added Warning as a cache module status.
HDM-6.08
Added fields for numbers of internal ports and external ports of storage controllers.
HDM-3.37
Changed supercapacitor status Fatal to Fault for Data[128:159].
HDM-2.33
Added the Auto volume and Simple volume modes to the storage controller mode.
HDM-2.13.00
Added the LSI storage controller field.
HDM-2.10.00
Added the JBOD controller mode and the package version field.
HDM-2.0.03
Added the adapter configuration version field. 32 bytes were added to the response length.
HDM-1.30.11
Resolved the output alignment issue.
Obtain the number of LDs and their offset indexes
Use this command to obtain the number of LDs and their offset indexes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x01 0x00 0x00 0x04 Ctrl_ID 0x00 0x00 0x00
Table 72 Request field description
Ctrl_ID
0x00 0x00 0x00
Reserved keyword.
User role
User
Required permission
Information query
# Obtain the number of LDs and their offset indexes.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x01 0x00 0x00 0x04 0x00 0x00 0x00 0x00
a2 63 00 06 00 00 00 01 00 00 00 00 00
Table 73 Response field description
Data[1:3]
Data[4:7]
Data[8:11]
Number of LDs.
Data[12:N]
LD offset indexes. The length of this field depends on the number of LDs.
Obtain LD information
Use this command to obtain information about an LD.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x02 0x00 0x00 0x04 LD_Index[2] Ctrl_ID 0x00
Table 74 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Storage command code. 0x02 indicates the obtaining operation.
Data[8:9]
Reserved.
Data[10]
Length of the remaining request fields.
LD_Index[2]
Specify the index of the LD, a two-byte string.
Ctrl_ID
Data[14]
Reserved.
User role
User
Required permission
Information query
# Obtain information about an LD.
COMMAND>ipmitool -U admin -P Password@_ -I lanplus -H 192.168.10.18 raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x02 0x00 0x00 0x04 0x01 0x00 0x00 0x00
a2 63 00 f5 00 00 00 01 00 4f 70 74 69 6d 61 6c
00 00 00 00 00 00 00 00 00 52 41 49 44 20 30 00
00 00 00 00 00 00 00 00 00 38 39 33 2e 37 35 30
47 69 42 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 01 00 00 00 00 00 00
00 01 01 09 ff 00 00 00 00 00 00 00 00 00 00 00
Table 75 Response field description
Data[1:3]
Data[4:7]
Data[8:9]
Device ID.
Data[10:25]
Logical drive state. Supported options:
·     For a PMC storage controller:
¡     Optimal.
¡     Creating.
¡     Scrubbing.
¡     Zeroing.
¡     Rebuilding.
¡     Morphing.
¡     Verifying.
¡     Copying.
¡     Suboptimal.
¡     Degraded.
¡     Offline.
·     For an LSI storage controller:
¡     Optimal.
¡     Offline.
¡     Degraded.
¡     Rebuilding.
¡     Unknown.
·     For a 3SNIC storage controller:
¡     Normal.
¡     Fault.
¡     Degrade.
¡     Deleting.
¡     Delete_fail.
¡     Formatting.
¡     Initializing.
¡     Initialize_fail.
¡     Not_Formatted.
¡     Sanitizing.
¡     Write_protect.
Data[26:57]
RAID level of the logical drive.
Data[58:73]
Logical drive capacity.
Data[74:89]
Logical drive name.
Data[90]
Read policy. Supported options:
·     0—No read ahead.
·     1—Always read ahead.
·     2—No ahead.
·     3—Ahead.
Data[91]
Write policy. Supported options:
·     0Write through.
·     1Write back.
·     2Always write back.
·     3—Write back enforce.
Data[92]
Cache policy. This field is supported only by LSI storage controllers. Supported options:
·     0Direct IO.
·     1Cached IO.
·     0xFF—Invalid. No corresponding feature is available.
Data[93]
Access policy. Supported options:
·     0—Read write.
·     1—Read only.
·     2—Blocked.
Data[94]
Physical drive cache policy. Supported options:
·     0—Unchanged.
·     1—Enabled.
·     2—Disabled.
·     3On.
·     4Off.
·     5—Default.
Data[95]
Reserved.
Data[96:97]
Whether the current logical drive is the boot drive. Supported options:
·     1—True.
·     0—False.
Data[98]
Number of spans.
Data[99]
Number of member drives per span.
Data[100]
Strip size. Supported options:
·     5—16 KB. This option is available only for PMC storage controllers.
·     6—32 KB. This option is available only for PMC storage controllers and 3SNIC storage controllers.
·     7—64 KB.
·     8—128 KB.
·     9—256 KB.
·     10—512 KB.
·     11—1 MB.
Data[101]
Accelerator type (MCTP). This field is not available for HDM 1.11.xx versions. Supported options:
·     1None.
·     2—Controller cache.
·     3—IO bypass.
·     0xFFInvalid. The field displays 0xFF for LSI storage controllers, 3SNIC storage controllers, or unsupported PMC storage controllers.
Data[102]
Number of physical drives for the current logical drive.
Data[103:166]
Device ID of the physical drives for the current logical drive, 32 in total. Each device ID is two bytes.
Data[167:252]
Reserved.
Change history
Version
Change description
HDM-6.09
Add the description for logical drive status, read policy, write policy, and physical drive cache policy for logical drives under the 3SNIC storage controller.
HDM-1.30.16
Added the number of physical drives and device ID of physical drives for the current logical drive fields.
HDM-1.30.11
HDM-1.30.09
Added the strip size and accelerator type fields.
HDM-1.30.06
Added the number of spans and number of member drives per span fields.
HDM-1.11.29
Added the physical drive cache policy and boot drive fields.
Obtain the number of PDs and their offset indexes
Use this command to obtain the number of PDs and their offset indexes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x03 0x00 0x00 0x04 Cmd_Type LD_Index[2] Ctrl_ID
Table 76 Request field description
Cmd_Type
Specify the command type. Supported options:
·     0Discrete PD quantity and indexes.
·     1PD quantity of indexes for the specified LD.
LD_Index[2]
Specify the index of the LD, a two-byte string. The discrete type is not required.
Ctrl_ID
User role
User
Required permission
Information query
# Obtain the number of PDs and their offset indexes.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x03 0x00 0x00 0x04 0x00 0x00 0x00 0x00
a2 63 00 06 01 00 00 03 00 00 00 0c 00 0e 00 0f
Table 77 Response field description
Data[1:3]
Data[4:7]
Data[8:11]
Number of PDs.
Data[12:…]
PD offset indexes. The length of this field depends on the number of PDs.
Obtain PD information
Use this command to obtain information about a PD.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x04 0x00 0x00 0x04 0x00 PD_Index[2] Ctrl_ID
Table 78 Request field description
PD_Index[2]
Specify the index of the PD, a two-byte string. Obtain this field from the command for obtaining the number of PDs and their offset indexes.
Ctrl_ID
User role
User
Required permission
Information query
# Obtain information about a PD.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x04 0x00 0x00 0x04 0x00 0x0F 0x00 0x00
a2 63 00 4a 01 00 00 0f 00 03 00 55 6e 63 6f 6e
66 69 67 75 72 65 64 5f 47 6f 6f 64 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 36 2e 30 20 47
62 70 73 20 53 41 54 41 20 53 53 44 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 38 39 34 2e 32
35 47 69 42 00 00 00 00 00 00 00 41 54 41 20 20
20 20 00 00 00 00 00 31 39 34 34 32 34 41 37 38
30 31 35 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 20 44 31 4d 48 30 32 37 00
00 46 72 6f 6e 74 00 00 00 00 00 00 00 00 00 00
00 03 00 03 00 03 00 4d 69 63 72 6f 6e 5f 35 32
30 30 5f 4d 54 46 44 00 4e 41 00 00 00 00 00 00
39 36 30 47 42 00 00 00 00 00 00 00 00 00 00 00
1b 62 ff 64 57 00 00 00 00 00 00 00 00 00 00 00
00 00 00 03 00 00 00 03 11 22 33 44 00 00 00 00
00 00 00 00 00 30 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 03 00 03 00 01 00 00 00 00 00
00 00 00 03 11 22 33 44 00 00 00 00 00 00 00 00
00 4d 69 63 72 6f 6e 5f 35 32 30 30 5f 4d 54 46
44 44 41 4b 39 36 30 54 44 43 20 20 20 20 20 20
20 20 20 20 20 20 20 20 20 00 00 00 00 00 00 00
00
Table 79 Response field description
Data[1:3]
Data[4:7]
Data[8:9]
PD connection ID.
Data[10:11]
PD physical number.
Data[12:43]
Physical drive state. Supported options:
¡     Ready.
¡     Unconfigured_Good.
¡     Unconfigured_Bad.
¡     Hot_Spare.
¡     Offline.
¡     FAILED.
¡     Rebuilding.
¡     Optimal.
¡     Online.
¡     JBOD.
¡     Unknown.
¡     Predict_Fail.
¡     Copyback.
¡     Offline.
¡     PFA.
¡     Raw.
¡     Hotspare.
¡     Ready.
¡     Optimal.
¡     Unknown.
¡     Failed.
¡     Rebuilding.
¡     RebuildWait.
¡     Online.
¡     Offline.
¡     Fault.
¡     Ucfggood.
¡     Ucfgfault.
¡     Spare.
¡     Foreign.
¡     Diagnosing.
¡     Reconstructing.
¡     Copybacking.
¡     Cfgincompat.
¡     Unsupport.
¡     Unknown.
Data[44:75]
Type, 6.0 Gbps SATA SSD for example.
Data[76:91]
Capacity.
Data[92:103]
Vendor.
Data[104:135]
Serial number.
Data[136:145]
Firmware version.
Data[146:153]
Backplane location.
Data[154:161]
Reserved.
Data[162:163]
PD number in the BIOS.
Data[164:165]
PD number on the host.
Data[166:167]
PD slot number.
Data[168:184]
Product ID.
Data[185:192]
Location of the node in which the PD resides.
Data[193:208]
Advertised PD capacity.
Data[209]
Temperature.
Data[210]
Remaining lifetime, in percent.
Data[211]
Rebuilding progress, in the range of 0 to 100 in percent. The value 255 indicates that the field is invalid.
Data[212:215]
Total power-on hours.
Data[216:219]
Number of media errors.
Data[220:223]
Number of other errors.
Data[224:227]
Number of predictive failures.
Data[228]
Maximum interface speed. Supported options:
·     11.5 Gbs.
·     23 Gbs.
·     36 Gbs.
·     412 Gbs.
Data[229:244]
SasAddr, 2 × 64 bits.
Data[245:246]
PD state. This field is not supported by PMC storage controllers. Supported options:
·     0Whether the PD uses forced GUID.
·     1Whether the PD is in a logical drive.
·     2Whether the PD is a global hot backup drive.
·     3Whether the PD is a dedicated hot backup drive.
·     4Whether the PD is in foreign state.
·     5-11Reserved.
·     12-15Interface type:
¡     0—Unknown.
¡     1—parallel SCSI.
¡     2—SAS.
¡     3—SATA.
¡     4—FC.
Data[247:254]
Reserved. Eight bytes.
Data[255:260]
Reserved. Six bytes.
Data[261:262]
Reserved. Two bytes.
Data[263]
Negotiation rate:
·     1—1.5 Gbs.
·     2—3 Gbs.
·     3—6 Gbs.
·     4—12 Gbs.
Data[264]
Box ID to which a drive connected to the drive backplane belong.
A box ID is used to distinguish which expander chip the drive belongs to when the drive backplane is connected to multiple expander chips.
Data[265]
Hot spare status:
·     1—Global hot spare.
·     2—Dedicated hot spare.
·     3Non-hot spare.
·     4Roaming hot spare.
Data[266]
LED status of a driver:
·     0The LED is off.
·     1The LED is on.
·     0xFFNot supported.
Data[267]
Drive status for a driver:
·     0x01—OK
·     0x02—Fail
·     0x03—Rebuild
·     0x04—PredictiveFailureAnalysis
·     0x05—Hotspare
·     0x06—InAFailedArray
·     0x07—InACriticalArray
Data[268]
Inspection status:
·     0Not in inspection.
·     1—In inspection.
·     0xFF—Not supported.
Data[269]
Whether the physical drive is being rebuilt:
·     0The physical drive is not being rebuilt.
·     1The physical drive is being rebuilt.
Data[270]
Number of logical drives associated with the partial hot spare.
Data[271:272]
Bitmap of the logical drive to which the partial hot spare belongs.
Data[273:288]
SasAddr—SAS address.
Data[289]
Whether the physical drive is an M.2 on the Marvell adapter:
·     1Yes.
·     0No.
Data[290:337]
PD model information.
Change history
Version
Change description
HDM-6.10
Added roaming hot spare as a hot spare status for Data[265].
HDM-6.09
Revised the description for the physical drive status.
Added the physical drive state description for the 3SNIC storage controller.
HDM-3.37/HDM-6.02
Correct response Data[264-289].
HDM-3.37/HDM-6.0
Added the Data[290:337] field to record PD model information.
HDM-2.27
Added the Rebuilding and RebuildWait fields for status of physical drives managed by a PMC storage controller.
HDM-2.25
Added the negotiation rate field.
HDM-2.25
Added three reserved fields for internal use.
HDM-2.13.00
Added the Copyback field for status of physical drives managed by an LSI storage controller.
HDM-2.10.00
Added the PdType field.
HDM-1.30.16
Added the SasAddr field.
HDM-1.30.11
Added the maximum interface speed field and resolved the output alignment issue.
HDM-1.30.09
Added the rebuilding progress, total power-on hours, number of media errors, number of other errors, and number of predictive errors fields.
Obtain the number of storage controllers and their indexes and names
Use this command to obtain the number of storage controllers and their indexes and names.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x06 0x00 0x00 0x04 0x00 0x00 0x00 0x00
User role
User
Required permission
Information query
# Obtain the number of storage controllers and their indexes and names.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x0c 0x06 0x00 0x00 0x04 0x00 0x00 0x00 0x00
a2 63 00 f4 00 00 00 02 01 00 00 00 02 01 00 04
10 01 04 02 00 06 10 00 00 00 00 00 00 00 00 00
Table 80 Response field description
Data[1:3]
Data[4:7]
Data[8]
Number of storage controllers.
Data[9]
Storage controller state. Supported options:
·     1Normal.
·     2Server powered off.
·     3Storage controller absent.
·     4Storage controller failed.
·     5Initializing the BIOS.
Data[10:11]
Reserved.
Data[12]
ID offset index for controller 1.
Data[13]
RAID out-of-band configuration flag for controller 1. Supported options:
·     0PMC storage controller, PBSI firmware, not supported.
·     1—PMC storage controller, MCTP firmware, supported.
·     2—MR-type LSI storage controller, supported.
·     3—IR-type LSI storage controller, not supported.
·     4—IT-type LSI storage controller, not supported.
·     5Marvell SantaCruz controller, not supported.
Data[14:15]
Number of the PCIe slot that holds controller 1.
Data[16:17]
Model of controller 1. PMC storage controllers use values in the range of 0x0001 to 0x1000, LSI storage controllers use values in the range of 0x1001 to 0x2000, and MARVELL controller use values in the range of 0x2001 to 0x2fff.
Data[18]
ID offset index for controller 2.
Data[19]
RAID out-of-band configuration flag for controller 2. Supported options:
Data[20:21]
Number of the PCIe slot that holds controller 2.
Data[22:23]
Model of controller 2. PMC storage controllers use values in the range of 1 to 0x1000, and LSI storage controllers use the remaining values.
Data[24:...]
Extensible fields if over two storage controllers are present. The maximum value for N is 251.
Change history
Version
Change description
HDM-1.30.11
Resolved the output alignment issue and changed a reserved field to an out-of-band configuration flag field.
HDM-1.30.10
Added the out-of-band configuration flag field that can help identify the MR, IR, or IT type of LSI storage controllers, and resolved the output alignment issue.
Table 81 Description of some fields in versions earlier than HDM-1.30.10
Data[13]
Reserved.
Data[14:15]
Data[16:17]
Model of controller 1. PMC storage controllers use values in the range of 1 to 0x1000, and LSI storage controllers use the remaining values.
Data[18]
Data[19]
Reserved.
Data[20:21]
Data[22:23]
Data[24..]
Table 82 Description of some fields in version HDM-1.30.10
Data[13:14]
Data[15:16]
Data[17]
Data[18]
Data[19:20]
Data[21:22]
Data[23]
Data[24..]
Change history
Version
Change description
HDM-3.xx
Added support for Marvell controllers.
Set the physical drive status
Use this command to set the status of a physical drive.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0x20 0x14 0x00 0x26 0x00 0x00 0x00 0x04 Data[11:12] Data[13:14]
Table 83 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Manufacturer ID. This field is fixed to 20 14 00.
Data[6]
Subcommand code.
Data[7]
Storage command. 0x00 indicates the setting physical drive status operation.
Data[8:9]
Reserved.
Data[10]
Data[11]
Storage controller ID.
Data[12:13]
Physical drive ID. Obtain this field from the command for obtaining the number of PDs and their offset indexes.
Data[14]
Drive status. Supported options:
·     0—Unconfigured good.
·     1—Unconfigured bad.
·     0x40—JBOD.
User role
Administrator
Required permission
Remote control
# Set the physical drive status.
COMMAND> ipmitool -U admin -P Password@_ -I lanplus -H 192.168.10.18 raw 0x36 0x09 0x20 0x14 0x00 0x26 0x00 0x00 0x00 0x04 0x00 0x01 0x00 0x01
a2 63 00 00 00 00 00
Table 84 Response field description
Data[1:3]
Data[4:7]
Reserved.
Change history
Version
Change description
HDM-2.0.03
Added the JBOD drive status.
HDM-1.30.11
Configure a logical drive
Use this command to configure a logical drive.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0x20 0x14 0x00 0x26 0x01 0x00 0x00 0x35 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x05 0x09 0x00 0x00 0x00 0x00 0xC0 0x12 0x00 0x00 0x00 0x00 0x01 0x01 0x01 0x01 0x02 0x03 0x00 0xA8 0x00 0x00 0XA9 0x00 0x00 0xB0 0x00 0x01 0xB3 0x00 0x01 0xB7 0x00 0x01 0xBE 0x00
Table 85 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Storage command. 0x01 indicates the configuring logical drive operation.
Data[8:9]
Reserved.
Data[10]
Specify the length of the remaining request fields.
Data[11]
Specify the ID of the storage controller.
Data[12:27]
Specify the name of the logical drive.
HDM supports only up to 15 characters for a logical drive name. HDM displays only the first 15 characters of a logical drive name.
Set Data[27] to 0x00 to indicate the end of the string.
Data[28]
Specify the RAID level.
·     0—RAID0.
·     1—RAID1.
·     2—RAID5.
·     3—RAID6.
·     4—RAID00.
·     5—RAID10.
·     6—RAID50.
·     7—RAID60.
·     8—RAID1 ADM.
·     9—RAID10 ADM.
The supported RAID levels vary by storage controller model.
Data[29]
Specify the strip size. Supported options:
·     6—32 KB. This option is available only for PMC and 3SINC storage controllers.
·     7—64 KB.
·     8—128 KB.
·     9—256 KB.
·     10—512 KB.
·     11—1 MB.
Data[30]
Initialization method for LSI storage controlers. Supported options:
·     0No initialization.
·     1Quick initialization.
·     2Full initialization.
·     6—Background initialization.
·     7—Front initialization.
This field is not available for PMC storage controllers.
Initialization method for 3SINC storage controlers. Supported options:
·     0Front initialization.
·     1Fast initialization.
·     2—Background initialization.
Data[31]
Specify the physical drive cache policy for an LSI storage controller or the accelerator policy for a PMC storage controller. Supported options:
·     For an LSI storage controller, specify the physical drive cache policy. Supported options:
¡     0Unchanged.
¡     1Enabled.
¡     2Disabled.
·     For a PMC storage controller, specify the accelerator policy. Supported options:
¡     1Specifies the none policy to disable read/write cache.
¡     2Specifies the controller cache policy to enable read/write cache.
¡     3Specifies the IO bypass policy to enable the storage controller to use I/O bypass paths to enhance read/write performance. This feature is available only on SSDs.
·     For a 3SNIC storage controller, specify the physical drive cache policy. Supported options:
¡     3—On.
¡     4—Off.
¡     5—Default.
Data[32:39]
Specify the capacity, in 512 B. If you set this field to 0, the command assigns the maximum supported capacity to the logical drive.
Data[40]
Specify the read policy. Supported options:
·     For storage controllers except 3SNIC storage controllers:
¡     0No read ahead.
¡     1Always read ahead.
¡     2No ahead.
¡     3Ahead.
·     For 3SNIC storage controllers:
¡     2No ahead.
¡     3Ahead.
Data[41]
Specify the write policy. Supported options:
¡     0—Write through.
¡     1—Write back.
¡     2Always write back.
¡     3—Write back enforce.
¡     0—Write through.
¡     1—Write back.
¡     2—Write back enforce.
Data[42]
Specify the cache policy. Supported options:
·     0Direct IO.
·     1—Cached IO.
This field is not available for PMC storage controllers or 3SNIC storage controllers.
Data[43]
Specify the access policy. Supported options:
·     0Read/write.
·     1Read only.
·     2Blocked.
Data[44]
·     For an LSI storage controller, this field specifies the number of spans.
·     For a PMC storage controller, this field specifies the number of parity groups. If the RAID level is 50 or 60, set the number of parity groups to a value greater than 1. If any other RAID level is used, set the number to 0.
·     For a 3SNIC storage controller, this field specifies the number of spans. If the RAID level is 0, 1, 5, or 6, set the number of spans to 1. If the RAID level is 10, 50, or 60, set the number of spans to a value greater than 1.
Data[45]
·     For an LSI storage controller, specify the number of drives per span.
·     For a PMC storage controller, specify the total number of physical drives.
·     For a 3SNIC storage controller, specify the number of drives per span.
Data[46]
Specify the span ID for the first drive.
Data[47:48]
Specify the device ID of the first drive.
Other drive information.
User role
Administrator
Required permission
Remote control
# Configure a logical drive. For the fields not required for PMC storage controllers, fill in these fields with 0x00 or 0xFF and you cannot leave these fields empty.
COMMAND>ipmitool -H 192.168.0.113 -U admin -P Password@_ -I lanplus raw raw 0x36 0x09 0x20 0x14 0x00 0x26 0x01 0x00 0x00 0x35 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x05 0x09 0x00 0x00 0x00 0x00 0xC0 0x12 0x00 0x00 0x00 0x00 0x01 0x01 0x01 0x01 0x02 0x03 0x00 0xA8 0x00 0x00 0XA9 0x00 0x00 0xB0 0x00 0x01 0xB3 0x00 0x01 0xB7 0x00 0x01 0xBE 0x00
a2 63 00
Table 86 Response field description
Data[1:3]
Change history
Version
Change description
HDM-6.09
Edited the stripe size and the description for the initialization status.
Added the description for the initialization state, read policy, write policy, and physical drive cache policy for creating a logical drive under a 3SNIC storage controller.
N/A
Added guidelines for filling fields that are not required for PMC storage controllers.
HDM-1.30.07
Added the IO bypass option to the physical drive cache policy field.
HDM-1.12.05
Added support for configuring out-of-band configuration of PMC storage controllers.
Delete a logical drive
Use this command to delete a logical drive.
ipmitool -I connect_type -H hostname -U username -P password raw   0x36 0x09 0x20 0x14 0x00 0x26 0x02 0x00 0x00 0x03 Data[11] Data[12:13]
Table 87 Request field description
Data[1]
NetFn.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Storage command. 0x02 indicates the deleting logical drive operation.
Data[8:9]
Reserved.
Data[10]
Data[11]
Data[12:13]
Specify the index of the logical drive.
User role
Administrator
Required permission
Remote control
# Delete a logical drive.
COMMAND>ipmitool -H 192.168.0.113 -U admin -P Password@_ -I lanplus raw  0x36 0x09 0x20 0x14 0x00 0x26 0x02 0x00 0x00 0x03 0x02 0x00 0x00
a2 63 00
Table 88 Response field description
Data[1:3]
Configure logical drive attributes
Use this command to configure logical drive attributes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0x20 0x14 0x00 0x26 0x06 0x00 0x00 0x0b 0x00 0x00 0x00 0x01 0x00 0x00 0x00 0x00 0x00 0x00 0x00
Table 89 Request field description
Data[1]
NetFn.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Storage command. 0x06 indicates the configuring logical drive attributes operation.
Data[8:9]
Reserved.
Data[10]
Data[11]
Data[12:13]
Index of the logical drive, in little endian format.
Data[14]
1 indicates specifying parameters for logical drive attribute configuration.
Data[15]
Access policy:
·     0x0—Remain the current configuration
·     0x1—Read only
·     0x2—Blocked
·     0x3— Read write
·     0xFF—Retain the original configuration
Data[16]
0—No change to the current configuration
Data[17]
Write policy:
·     0—Write through
·     1—Write back
·     2—Always write back
Data[18]
Read policy:
·     0—No read ahead
Data[19]
Physical drive cache policy:
·     0x1Enable
·     0x2Disable
·     0x3—Unchanged
Data[20]
Cache policy:
0—No change by default
Data[21]
Whether a logical drive is a boot drive. Supported options:
¡     0x00No.
¡     0x01Yes.
·     For an PMC storage controller in MCTP mode:
¡     0x00—False.
¡     0x02—Primary.
¡     0x03—Secondary.
¡     0x04—Primary and Secondary.
User role
Administrator
Required permission
Remote control
# Configure logical drive attributes.
COMMAND> ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x09 0x2
0 0x14 0x00 0x26 0x06 0x00 0x00 0x0b 0x01 0x00 0x00 0x01 0x02 0x00 0x02 0x01 0x00 0x00 0x00
a2 63 00 10 00 00 00 00 00 00 00 00 00 00 00 00
Table 90 Response field description
Data[1:3]
Data[4:7]
Data[8:19]
Reserved.
Data[20:23]
Status code for the command response. Supported options:
¡     0x00—Succeeded.
¡     0x74—Succeeded. The command takes effect after the restart.
¡     0x03—Failed. The input options are invalid.
¡     Others—Failed.
¡     0x00—Succeeded.
¡     Other value—Failed.
Change history
Version
Change description
HDM-6.16
·     Added support for specifying a logical drive as a boot drive.
·     Revised the data range in the response.
·     Have the old command compatible with the new command.
HDM-6.06
The following settings are supported:
·     Data[19] supports setting more physical drive cache policies.
·     Data[15] supports more access policies.
·     Data[4:13] that was previously supported is supplemented and Data[14:17] status code is added.
HDM-2.33
Added this command.
Configure a physical hot spare drive
Use this command to configure a physical hot spare drive.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0x20 0x14 0x00 0x26 0x07 0x00 0x00 0x04 0x00 0x01 0x00 0x00
Table 91 Request field description
Data[1]
NetFn.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Storage command. 0x07 indicates the configuring hot spare for a physical drive operation.
Data[8:9]
Reserved.
Data[10]
Data[11]
Data[12]
0x00—Global hot spare. This option is not available for PMC storage controllers.
0x01—Dedicated hot spare. The Data[15-16] and subsequent fields are required only for this option. PMC storage controllers do not support assigning one drive to multiple logical disks as a hot spare.
0x02—Roaming hot spare. This option is supported by PMC storage controlers. The PMC storage controllers support specifying hot spares for only one logical drive.
0x03—Remove hot spare.
Data[13-14]
Index of the physical drive.
Data[15-16]
ID of the logical drive to which the dedicated hot spare drive belongs.
Data[17-….]
ID of the logical drive when a hot spare drive is configured for multiple logical drives.
Required permission
Remote control
# Configure a physical drive as the dedicated hot spare drive for logical drive 0 managed by the LSI storage controller.
COMMAND> ipmitool -U admin -P Password@_ -I lanplus -H 192.168.10.18 raw 0x36 0x09 0x20 0x14 0x00 0x26 0x07 0x00 0x00 0x06 0x00 0x01 0x00 0xef 0x00 0x00
Table 92 Response field description
Data[1:3]
Data[4:7]
This field is reserved.
Change history
Version
Change description
HDM-6.10
Added support for specifying roaming hot sapres.
HDM-6.01
Corrected the description for setting a dedicated hot spare.
HDM-2.85
Added this command.
Obtain the total drive usage
Use this command to obtain the total drive usage (disk usage in HDM).
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x56
Table 93 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Information query
To use this command, you must first run FIST SMS.
# Obtain the total drive usage.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x56
a2 63 00 00 00 70 e1 00 40 1e 00 00
Table 94 Response field description
Data[1:3]
Data[4]
Total drive usage.
Data[5-8]
Total drive capacity, in MB.
Data[9-12]
Used drive capacity, in MB.
Change history
Version
Change description
HDM-1.30.14
Added the total drive capacity and used drive capacity fields. The two fields are supported only in FIST SMS D018 and later versions.
HDM-1.11.29
Added this command.
Specify the drive usage
Use this command to specify the drive usage (disk usage in HDM). FIST SMS uses this command to send drive usage statistics to BMC.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x3d 0x00 0x00 0x70 0xe1 0x00 0x40 0x1e 0x00 0x00
Table 95 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Maximum drive usage, in the range of 0 to 100.
Data[8:11]
Total drive capacity.
Data[12:15]
Total used drive capacity.
User role
Administrator
Required permission
Remote control
# Specify the drive usage.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x09 0xa2 0x63 0x00 0x3d 0x00 0x00 0x70 0xe1 0x00 0x40 0x1e 0x00 0x00
a2 63 00
Table 96 Response field description
Data[1:3]
Change history
Version
Change description
HDM-1.30.14
HDM-1.11.29
Added this command.
BMC and BIOS interaction
Obtain the next boot option
Use this command to obtain the configured next boot option.
ipmitool -I connect_type -H hostname -U username -P password raw  0x00 0x09 0x05 0x00 0x00
Table 97 Request field description
Data[1]
NetFn.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Set selector.
Data[5]
Block selector.
User role
User
Required permission
Information query
# Obtain the configured next boot option.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x09 0x05 0x00 0x00
 01 05 80 08 00 00 00
Table 98 Response field description
Data[1]
Parameter version.
Data[2]
ParameterValid.
Data[3]
Bit[7]: Indicates whether the boot option is valid. Supported options:
·     0—Invalid.
·     1—Valid.
Bit[6]: Indicates the effective time of the boot option. Supported options:
·     0—One-time boot option.
·     1—Permanent boot option.
Bits[0:5]: N/A.
Data[4]
Bits[2:5]: Indicates the boot option. Supported options:
·     0000bNot configured.
·     0001b—PXE.
·     0110bUses BIOS configuration.
·     0010b—HDD.
·     0101b—CDROM.
·     1011bHard disk through remote connection.
Bits[0:1]: N/A.
Data[5]
Data[6]
Data[7]
Change history
Version
Change description
HDM-3.18
Added the Remote Connect Hard Drive field.
Set the next boot option
Use this command to set the next boot option.
ipmitool -I connect_type -H hostname -U username -P password raw 0x00 0x08 0x05 0x80 0x18 0x00 0x00 0x00
Table 99 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Bit[7]: Specify whether the boot option is valid. Supported options:
·     0—Invalid.
·     1—Valid.
Bit[6]: Specify the effective time of the boot option. Supported options:
Bit[5]: Specify the boot mode. Supported options:
·     0—Legacy.
·     1—UEFI.
The value for Bit[5] and Bit[6] cannot be set to 1 at the same time.
Bits[0:4]: N/A.
Data[5]
Bits[2:5]: Specify the boot option. Supported options:
·     0001b—PXE.
·     0010b—HDD.
·     0101b—CDROM.
·     1011bUses a hard disk through remote connection.
Bit[7]: 1 indicates restoring the BIOS default settings. This configuration takes effect after a BIOS reboot.
Note: Bits[2:5] and Bit[7] cannot be configured at the same time. BIOS restart is required between configuration of the two options. Bit[7] and the Bit[5] or Bit[6] fields of DATA[4] cannot be set to 1 at the same time.
Bits[0:1]: N/A.
Note: The BIOS configuration is not available for permanent boot option configuration.
Data[6]
Data[7]
Data[8]
User role
Operator
Required permission
Remote control
# Configure the device to use the boot options configured in the BIOS.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x08 0x05 0x80 0x18 0x00 0x00 0x00
# Configure the device to use the boot options configured in the CDROM.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x00 0x08 0x05 0xc0 0x14 0x00 0x00 0x00
Change history
Version
Change description
HDM-6.01
Optimized the description for Data[6], which takes effect after a BIOS reboot
HDM-3.18
Obtain the next boot mode
Use this command to obtain the next boot mode.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x2e
Table 100 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Information query
# Obtain the next boot mode.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x2e
Table 101 Response field description
Data[1:3]
Data[4]
Bit[0]: Indicates whether the next boot mode is valid. Supported options:
·     1Valid.
·     0Invalid.
Bits[1:3]: N/A.
Data[5]
Next boot mode. Supported options:
·     0x00—No override.
·     0x01—Legacy.
·     0x02—UEFI.
·     0x03—Auto.
Data[6]
Reserved.
Data[7]
Reserved.
Set the next boot mode
Use this command to set the next boot mode.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xa2 0x63 0x00 0x02 0x01 mode 0x00 0x00
Table 102 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Bit[0]: Specify whether the next boot mode is valid. Supported options:
·     1Valid.
·     0Invalid.
Bits[1:3]: N/A.
Data[8]
Specify the next boot mode. Supported options:
·     0x00—No override.
·     0x01—Legacy.
·     0x02—UEFI.
·     0x03—Auto.
Data[9]
Data[10]
User role
Operator
Required permission
Remote control
For this configuration to take effect, you must also specify the next boot option.
# Set the next boot mode.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0a 0xa2 0x63 0x00 0x02 0x01 0x01 0x00 0x00
a2 63 00
Table 103 Response field description
Data[1:3]
Obtain the power-on delay time
Use this command to obtain the power-on delay time.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x3F
Table 104 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Manufacturer ID. This field is fixed to a2 63 00.
Data[6]
Subcommand code.
User role
User
Required permission
Information query
Blade servers do not support this command.
# Obtain the power-on delay time.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x3f
a2 63 00 01 78 00 00 00 00 00 00
Table 105 Response field description
Data[1:3]
Data[4]
Power-on delay policy. Supported options:
·     0x00—Fixed delay time.
·     0x01—Random delay time.
·     0x02No delay. Not configurable when the AC recovery policy is off.
Data[5:6]
Delay time, in seconds.
When the value of Data[4] is 0x00, the delay time can only be 0, 15, 30, 45, or 60 seconds.
When the value of Data[4] is 0x01, the delay time is in the range of 1 to 120 seconds. 0 represents 120 seconds.
When the value of Data[4] is 0x02, this field is not available.
Data[7:11]
Reserved.
Change history
Version
Change description
2.16.00
Added support for obtaining the random delay time.
Set the power-on delay time
Use this command to set the power-on delay time.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xa2 0x63 0x00 0x03 Data[7] Data[8:9] 0x00 0x00 0x00 0x00 0x00
Table 106 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the power-on delay policy. Supported options:
·     0x02No delay.
Data[8:9]
Specify the delay time, in seconds.
When the value of Data[7] is 0x00, the delay time can only be 0, 15, 30, 45, or 60 seconds.
When the value of Data[7] is 0x01, the delay time is in the range of 1 to 120 seconds. 0 represents 120 seconds.
When the value of Data[7] is 0x02, this field is not available.
Data[10:14]
User role
Operator
Required permission
Power control
# Set the power-on delay time.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0a 0xa2 0x63 0x00 0x03 0x00 0x0f 0x00 0x00 0x00 0x00 0x00 0x00
a2 63 00
Table 107 Response field description
Data[1:3]
Change history
Version
Change description
2.16.00
Added support for setting the random delay time.
Obtain Port80 information
Use this command to obtain Port80 information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x09
Table 108 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Information query
# Obtain Port80 information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x09
a2 63 00 e8 00 01 00 a0 01 02 02 03 03 04 05 04
05 06 19 a1 a3 a3 a3 a3 a3 a3 a7 a9 a7 a7 a7 a7
 a8 a9 a9 aa ae af e0 e1 e4 e3 e1 e4 e3 e5 b0 b0
 b1 b4 b2 b3 b3 b6 b6 b6 b7 b7 b6 b7 b7 b7 b7 b7
 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7 b7
 b7 b7 b7 be b7 b8 b9 b9 b9 b9 b9 ba b9 bb b7 bc
 bf e6 e7 e8 e9 eb ec ed ee e7 e8 e9 eb ec ed ee
 4f 61 9a 78 68 70 79 d1 d2 d4 91 92 93 94 93 94
 93 94 93 94 95 93 94 93 94 95 93 94 93 94 93 94
 93 94 95 93 94 93 94 93 94 95 93 94 95 93 94 95
 93 94 95 93 94 95 96 ef 92 92 92 92 92 92 92 99
 91 d5 92 92 92 92 92 92 92 92 97 98 9d 9c b4 b4
 b4 b4 b4 b4 92 a0 a2 a2 a2 a2 a2 a2 a0 a2 a2 a2
 a2 a2 a2 a2 a2 99 92 92 92 92 92 92 92 ad b1 a0
Table 109 Response field description
Data[1:3]
Data[4:5]
Total number of POST codes.
Data[6]
Current host power status. Supported options:
·     1Powered-on.
·     0Powered-off.
Data[7]
Current Port80 status. Supported options:
·     0POST initial state.
·     1—POST start.
·     2—POST to setup.
·     3—POST to boot OS.
·     4—End of IPMI.
Data[8]
Current POST code.
Data[9:264]
Most recent 256 POST codes of the most recent startup.
Configure a BIOS setting
Use this command to configure a BIOS setting.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x19 index data
Table 110 Request field description (for Intel G3 servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the configuration item. Option include:
·     0x00—TurboMode.
·     0x01ProcessorEistEnable.
·     0x02—PackageCState.
·     0x03—ProcessorC1eEnable.
·     0x04—ProcessorVmxEnable.
·     0x05—ProcessorHyperThreadingDisable.
·     0x06—MlcSpatialPrefetcherEnable.
·     0x07—MlcStreamerPrefetcherEnable.
·     0x08NumaEn.
·     0x09—QpiLinkSpeed.
·     0x0a—DdrFreqLimit.
·     0x0b—PxeOpRom.
·     0x0c—PowerState.
·     0x0d—AltEngPerfBIAS.
·     0x0e—Bootmode.
·     0x0f—COD.
·     0x10—Snoop Mode.
·     0x11—Monitor/Mwait.
·     0x12—Enforce POR.
·     0x13—PXE Retry.
·     0x14—FirstBootDevice.
·     0x15—SecondBootDevice.
·     0x16BusinessPortStatus.
·     0x17—ProcessorCcxEnable.
·     0x18—SR_IOV_SUPPORT.
·     0x19—INTEL_VT_FOR_DIRECTED_IO.
·     0x1a—IPV4_PXE_SUPPORT.
·     0x1b—IPV6_PXE_SUPPORT.
·     0x1c—OS_ACPI_CX.
·     0x1d—CPU_C6_REPORT.
·     0x1e—CPUFlexRatioOverride.
·     0x1f—CPUCoreFlexRatio.
·     0x20—SpareErrTh, count threshold for ECC reporting.
·     0x21—SpareIntSelect, SMI ECC reporting enabling status.
·     0x22LeakyBktLo, least significant bits of the ECC reporting leaky bucket.
·     0x23—LeakyBktHi, most significant bits of the ECC reporting leaky bucket.
·     0x24PstateLimit.
Data[8]
TurboMode:
·     0—Disable.
·     1—Enable.
ProcessorEistEnable:
·     0—Disable.
·     1—Enable.
PackageCState:
·     0C0 support.
·     1C2 support.
·     2C6 support.
·     3C6 retsupport.
ProcessorC1eEnable:
·     0—Disable.
·     1—Enable.
ProcessorVmxEnable:
·     0—Disable.
·     1—Enable.
ProcessorHyperThreadingDisable:
·     0—Enable.
·     1—Disable.
MlcSpatialPrefetcherEnable:
·     0—Disable.
·     1—Enable.
MlcStreamerPrefetcherEnable:
·     0—Disable.
·     1—Enable.
NumaEn:
·     0—Disable.
·     1—Enable.
QpiLinkSpeed:
·     09.6 GT.
·     110.4 GT.
·     2Max.
DdrFreqLimit:
·     0Auto.
·     5—DDR_1333.
·     7—DDR_1600.
·     9—DDR_1866.
·     11—DDR_2133.
·     13—DDR_2400.
·     15—DDR_2666.
·     17—DDR_2933.
PxeOpRom:
·     1—UEFI.
·     2—Legacy.
PowerState:
·     0.
·     1.
·     2Removed.
AltEngPerfBIAS:
·     0—Performance.
·     7—Balanced performance.
·     8—Balanced power.
·     15—Power.
BootMode:
·     1—UEFI.
·     0—Legacy.
COD:
·     0.
·     1.
·     2.
Snoop Mode:
·     0.
·     1.
·     2.
·     3.
·     4.
Monitor/Mwait:
·     0.
·     1.
Enforce POR:
·     0—Enabled.
·     2—Disabled.
·     3Auto.
PXE Retry: Value range is 0 to 50.
FirstBootDevice:
·     0HDD.
·     1ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB FDD.
·     6USB LAN.
·     7Network.
·     8UEFI application.
·     9Disable.
SecondBootDevice:
·     0HDD.
·     1ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB FDD.
·     6USB LAN.
·     7Network.
·     9Disable.
BusinessPortStatus:
·     0Enable.
·     1Disable.
ProcessorCcxEnable:
·     0—Disable.
·     1—Enable.
SR_IOV_SUPPORT:
·     0—Disable.
·     1—Enable.
INTEL_VT_FOR_DIRECTED_IO:
·     0—Disable.
·     1—Enable.
IPV4_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
IPV6_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
OS_ACPI_CX:
·     0x00ACPI C2.
·     0x01ACPI C3.
CPU_C6_REPORT:
·     0x00—Disable.
·     0x01—Enable.
·     0xff—Auto.
CPUFlexRatioOverride:
·     0—Disable.
·     1—Enable.
CPUCoreFlexRatio: The value range is 0 to 100.
SpareErrTh: The value range is 0x00 to 0x7FFF.
SpareIntSelect:
·     0—Disable.
·     1SMI signal.
LeakyBktLo: The value range is 0x00 to 0x29.
LeakyBktHi: The value range is 0x00 to 0x29.
PStateLimit:
·     0—Disable.
·     1—Enable.
Table 111 Request field description (for Intel G5 servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
·     0x00—TurboMode.
·     0x01—ProcessorEistEnable.
·     0x08NumaEn.
·     0x0e—BootMode.
·     0x22—LeakyBktLo, least significant bits of the ECC reporting leaky bucket.
Data[8]
TurboMode:
·     0—Disable.
·     1—Enable.
·     0—Disable.
·     1—Enable.
ProcessorVmxEnable:
·     0—Disable.
·     1—Enable.
·     0For G3 servers, enable hyper-threading.
·     1For G3 servers, disable hyper-threading.
AltEngPerfBIAS:
·     0—Performance.
·     7—Balanced Performance.
·     8—Balanced Power.
·     15—Power.
BootMode:
·     0LEGACY.
·     1UEFI.
FirstBootDevice:
·     0—HDD.
·     1—ODD.
·     2—USBHDD.
·     3—USBODD.
·     4—USBKEY.
·     5—USBFDD.
·     6—USBLAN.
·     7—NETWORK.
·     8—UEFI_APPLICATION.
·     9—DISABLE.
NumaEn:
·     0—Disable.
·     1—Enable.
IPV4_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
IPV6_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
SpareIntSelect:
·     0—Disable.
·     1SMI signal.
Table 112 Request field description (for AMD G5 servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Index. For more information, see Table 113.
Data[8]
Data. For more information, see Table 113.
Table 113 Field values for 4950 G5 MILAN, 4950 G5 ROME, 5500 G5 ROME, and 5500 G5 MILAN
Data[7]
Index:
·     0x00—IOMMU.
·     0x01—Global C-state Control.
·     0x02—Determinism Control.
·     0x03—Determinism Slider.
·     0x04—DF Cstates.
·     0x05—NUMA nodes per socket.
·     0x06—Memory interleaving.
·     0x07—FirstBootDevice.
·     0x08—IPv4 PXE Support.
·     0x09—IPv6 PXE Support.
·     0x0e—BootMode.
Data[8]
Data:
·     IOMMU:
¡     0—Disable.
¡     1—Enable.
¡     2—Auto (default).
·     Global C-state Control:
¡     0—Disable (default).
¡     1—Enable.
¡     2—Auto.
·     Determinism Control:
¡     0—Manual (default).
¡     1—Auto.
·     Determinism Slider:
¡     0—Performance (default).
¡     1—Auto.
¡     2—Power.
·     DF Cstates:
¡     1—Enabled.
¡     2—Auto.
·     NUMA nodes per socket:
¡     0—NPS0.
¡     1—NPS1.
¡     2—NPS2.
¡     3—NPS4.
¡     4Auto (default).
·     Memory interleaving:
¡     1—Auto.
·     FirstBootDevice:
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device.
The current setting does not support being disabled.
·     IPv4 PXE Support:
¡     0—Disable.
¡     1—Enable (default).
·     IPv6 PXE Support:
¡     0—Disable
·     BootMode:
¡     0LEGACY.
¡     1UEFI.
The S4753 AMD G5 server is not supported in the current software version.
Table 114 Request field description (for Hygon servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Index. For more information, see Table 115 and Table 116.
Data[8]
Data. For more information, see Table 115 and Table 116.
Table 115 Field values for 4930 G5 and 4330 G5 (Hygon 3)
Data[7]
Index:
·     0x00—IOMMU.
·     0x02—Determinism Slider.
·     0x03—NUMA.
·     0x04—Memory interleaving.
·     0x05—FirstBootDevice.
·     0x06—NetBootIPVersion.
·     0x0e—BootMode.
Data[8]
Data:
·     IOMMU:
¡     0—Disable.
¡     1—Enable
¡     2—Auto (default).
¡     1—Enable
¡     2—Auto.
¡     0—Performance.
¡     1—Auto( default).
¡     2—Power.
·     NUMA:
¡     0—Disable.
¡     0—None.
¡     1—Channel.
¡     2—Die.
¡     3—Socket.
¡     4—Auto.
·     FirstBootDevice:
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device,
·     NetBootIPVersion:
¡     0—IPV4.
¡     1—IPV6.
¡     2—All.
·     BootMode:
¡     0—LegacyBoot.
¡     1—UEFIBoot.
Table 116 Field values for 4930 G5 and 4330 G5 (Hygon 2)
Data[7]
Index:
·     0x00—IOMMU.
·     0x01—GlobalCstateControl.
·     0x03—NumaNodes.
·     0x04—Memory Interleaving.
·     0x06—IPv4Support.
·     0x07—IPv6Support.
·     0x0e—BootMode.
Data[8]
Data:
·     IOMMU:
¡     0—Disable.
¡     1—Enable.
¡     2—Auto (default).
·     GlobalCstateControl:
¡     1—Enable.
¡     2—Auto.
¡     0—Performance.
¡     1—Auto( default).
¡     2—Power.
·     NumaNodes:
¡     0—Disable.
·     Memory Interleaving:
¡     0—None.
¡     1—Channel.
¡     2—Die.
¡     3—Socket.
¡     4—Auto.
·     FirstBootDevice:
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device.
·     IPv4Support:
¡     0—Disable.
·     IPv6Support:
¡     0—Disable.
·     BootMode:
¡     0—LegacyBoot.
¡     1—UEFIBoot.
User role
User
Required permission
Remote control
·     Only devices that use Intel CPUs support this command. Blade servers do not support this command.
·     For more information about support of AMD G5 servers for this command, see the parameter description for the corresponding server model. AMD G3 servers are not supported.
·     For information about support of Hygon 2 and Hygon 3 for this command, see the parameter description.
# Set BIOS configuration item QpiLinkSpeed to 1.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x19 0x09 0x01
a2 63 00
Table 117 Response field description
Data[1:3]
Change history
Version
Change description
HDM-6.13
Added support of BIOS boot modes UEFI and Legacy for BIOS options.
HDM-3.34
Added support of some AMD and Hygon products for BIOS options.
HDM-3.11
Added support for G5 Intel servers.
Obtain a BIOS setting
Use this command to obtain a BIOS setting.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x1a Data[7]
Table 118 Request field description (Intel G3 servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
·     0x00—TurboMode.
·     0x08NumaEn.
·     0x0b—PxeOpRom.
·     0x0c—PowerState, Hardware P-States.
·     0x0e—Bootmode.
·     0x0f—COD.
·     0x10—Snoop Mode.
·     0x12—Enforce POR.
·     0x13—PXE Retry.
·     0x1c—OS_ACPI_CX.
·     0x24PStateLimit.
Table 119 Response field description (Intel G3 servers)
Data[1:3]
Data[4]
TurboMode:
·     0—Disable.
·     1—Enable.
·     0—Disable.
·     1—Enable.
PackageCState:
·     0C0 support.
·     1C2 support.
·     2C6 support.
·     3C6 retsupport.
ProcessorC1eEnable:
·     0—Disable.
·     1—Enable.
ProcessorVmxEnable:
·     0—Disable.
·     1—Enable.
·     0—Enable.
·     1—Disable.
·     0—Disable.
·     1—Enable.
·     0—Disable.
·     1—Enable.
NumaEn:
·     0—Disable.
·     1—Enable.
QpiLinkSpeed:
·     09.6 GT.
·     110.4 GT.
·     2Max.
DdrFreqLimit:
·     0Auto.
·     5—DDR_1333.
·     7—DDR_1600.
·     9—DDR_1866.
·     11—DDR_2133.
·     13—DDR_2400.
·     15—DDR_2666.
·     17—DDR_2933.
PxeOpRom:
·     1—UEFI.
·     2—Legacy.
PowerState:
·     0.
·     1.
·     2Removed.
AltEngPerfBIAS:
·     0—Performance.
·     8—Balanced power.
·     15—Power.
BootMode:
·     1—UEFI.
·     0—Legacy.
COD:
·     0.
·     1.
·     2.
Snoop Mode:
·     0.
·     1.
·     2.
·     3.
·     4.
Monitor/Mwait:
·     0.
·     1.
Enforce POR:
·     0—Enabled.
·     2—Disabled.
·     3Auto.
FirstBootDevice:
·     0HDD.
·     1ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB floppy.
·     6USB LAN.
·     7Network.
·     8—UEFI application.
·     9—Disable.
SecondBootDevice:
·     0HDD.
·     1ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB floppy.
·     6USB LAN.
·     7Network.
·     9—Disable.
BusinessPortStatus:
·     0Enable.
·     1Disable.
ProcessorCcxEnable:
·     0—Disable.
·     1—Enable.
SR_IOV_SUPPORT:
·     0—Disable.
·     1—Enable.
·     0—Disable.
·     1—Enable.
IPV4_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
IPV6_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
OS_ACPI_CX:
·     0x00ACPI C2.
·     0x01ACPI C3.
CPU_C6_REPORT:
·     0x00—Disable.
·     0x01—Enable.
·     0xff—Auto.
·     0—Disable.
·     1—Enable.
SpareIntSelect:
·     0—Disable.
·     1SMI signal.
LeakyBktLo: The value range is 0x00 to 0x3f.
PStateLimit:
·     0—Disable.
·     1—Enable.
Table 120 Response field description (Intel G5 servers)
Data[1:3]
Data[4]
TurboMode:
·     0—Disable.
·     1—Enable.
·     0—Disable.
·     1—Enable.
ProcessorVmxEnable:
·     0—Disable.
·     1—Enable.
NumaEn:
·     0—Disable.
·     1—Enable.
AltEngPerfBIAS:
·     0—Performance.
·     8—Balanced Power.
·     15—Power.
FirstBootDevice:
·     0—HDD.
·     1—ODD.
·     2—USBHDD.
·     3—USBODD.
·     4—USBKEY.
·     5—USBFDD.
·     6—USBLAN.
·     7—NETWORK.
·     9—DISABLE.
FirstBootDevice:
·     0HDD.
·     1ODD.
·     4—USB key.
·     7Network.
·     9—Disable.
IPV4_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
IPV6_PXE_SUPPORT:
·     0—Disable.
·     1—Enable.
SpareIntSelect:
·     0—Disable.
·     1SMI signal.
BootMode:
·     0Legacy.
·     1UEFI.
Table 121 Request field description (AMD G5 servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Index. For more information, see Table 122.
Table 122 Field values for 4950 G5 MILAN, 4950 G5 ROME, 5500 G5 ROME, and 5500 G5 MILAN
Data[7]
Index:
·     0x00—IOMMU.
·     0x04—DF Cstates.
·     0x0e—BootMode.
Table 123 Request field description (Hygon servers)
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Index. For more information, see Table 124.
Table 124 Field values for 4930 G5 and 4330 G5 (Hygon 3)
Data[7]
Index:
·     0x00—IOMMU.
·     0x03—NUMA.
·     0x0e—BootMode.
Table 125 Field values for 4930 G5 and 4330 G5 (Hygon 2)
Data[7]
Index:
·     0x00—IOMMU.
·     0x03—NumaNodes.
·     0x06—IPv4Support.
·     0x07—IPv6Support.
·     0x0e—BootMode.
Table 126 Response field description for AMD G5 servers (4950 G5 MILAN, 4950 G5 ROME, 5500 G5 ROME, 5500 G5 MILAN)
Data[1:3]
Data[4]
Data:
·     0x00—IOMMU:
¡     0—Disable.
¡     1—Enable.
¡     2—Auto (default).
·     0x01—Global C-state Control:
¡     1—Enable.
¡     2—Auto.
·     0x02—Determinism Control:
¡     1—Auto.
·     0x03—Determinism Slider:
¡     1—Auto.
¡     2—Power.
·     0x04—DF Cstates:
¡     1—Enable.
¡     2—Auto.
·     0x05—NUMA nodes per socket:
¡     0—NPS0.
¡     1—NPS1.
¡     2—NPS2.
¡     3—NPS4.
¡     4—Auto (default).
·     0x06—Memory interleaving:
¡     0Disable (default).
¡     1—Auto.
·     0x07—FirstBootDevice:
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device,
·     0x08—IPv4 PXE Support:
¡     0—Disable.
·     0x09—IPv6 PXE Support:
¡     0—Disable
·     0x0e—BootMode.
¡     0—Legacy.
¡     1—UEFI.
Table 127 Response field description for Hygon servers (4930G5 and 4330G5) (Hygon 3)
Data[1:3]
Data[4]
Data:
·     0x00—IOMMU:
¡     0—Disable.
¡     1—Enable.
¡     2—Auto (default).
¡     1—Enable.
¡     2—Auto.
·     0x02—Determinism Slider:
¡     0—Performance.
¡     1—Auto (default).
¡     2—Power.
·     0x03NUMA:
¡     0Disable.
¡     1Enable (default).
·     0x04—Memory interleaving:
¡     0—None.
¡     1—Channel.
¡     2Die.
¡     3—Socket.
¡     4—Auto.
·     0x05—FirstBootDevice:
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device,
¡     0—IPv4.
¡     1—IPv6.
¡     2All.
·     0x0e—BootMode.
¡     0—Legacy.
¡     0—UEFI.
Table 128 Response field description for Hygon servers (4930 G5 and 4330 G5) (Hygon 2)
Data[1:3]
Data[4]
Data:
·     0x00—IOMMU:
¡     0—Disable.
¡     1—Enable.
¡     2—Auto (default).
·     0x01—GlobalCstateControl:
¡     1—Enable.
¡     2—Auto.
¡     0—Performance.
¡     1—Auto (default).
¡     2—Power.
·     0x03NumaNodes:
¡     0Disable.
¡     0—None.
¡     1—Channel.
¡     2Die.
¡     3—Socket.
¡     4—Auto.
¡     0—Hard Disk.
¡     1—Network.
¡     4—CD/DVD.
¡     7—Other Device,
·     0x06—IPv4Support.
¡     0Disable.
·     0x07—IPv4Support.
¡     0Disable.
·     0x0e—BootMode.
¡     0—Legacy.
¡     1—UEFI.
User role
User
Required permission
Information query
Product compatibility
# Obtain a BIOS setting.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x1a 0x09
a2 63 00 02
Change history
Version
Change description
HDM-6.13
HDM-3.34
HDM-3.11
Configure all BIOS settings
Use this command to configure all BIOS settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x1b Data[7] Data[8] Data[9] Data[10] Data[11] Data[12] Data[12] Data[13] Data[14] Data[15] Data[16] Data[17] Data[18] Data[19] Data[20] Data[21] Data[22] Data[23] Data[24] Data[25] Data[26] Data[27] Data[28] Data[29] Data[30] Data[31] Data[32] Data[33] Data[34] Data[35] Data[36] Data[37] Data[38] Data[39] Data[40] Data[41] Data[42] Data[43] Data[44]
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Configure the TurboMode item. Supported options:
·     0—Disable.
·     1—Enable.
Data[8]
Configure the ProcessorEistEnable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[9]
Configure the PackageCState item. Supported options:
·     0C0 support.
·     1C2 support.
·     2C6 support.
·     3C6 retsupport.
Data[10]
Configure the ProcessorC1eEnable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[11]
Configure the ProcessorVmxEnable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[12]
Configure the ProcessorHyperThreadingDisable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[13]
Configure the MlcSpatialPrefetcherEnable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[14]
Configure the MlcStreamerPrefetcherEnable item. Supported options:
·     0—Disable.
·     1—Enable.
Data[15]
Configure the NumaEn item. Supported options:
·     0—Disable.
·     1—Enable.
Data[16]
Configure the QpiLinkSpeed item. Supported options:
·     09.6 GT.
·     110.4 GT.
·     2Max.
Data[17]
Configure the DdrFreqLimit item. Supported options:
·     0Auto.
·     5—DDR_1333.
·     7—DDR_1600.
·     9—DDR_1866.
·     11—DDR_2133.
·     13—DDR_2400.
·     15—DDR_2666.
·     17—DDR_2933.
Data[18]
Configure the PxeOpRom item. Supported options:
·     1—UEFI.
·     2—Legacy.
Data[19]
Configure the PowerState item. Supported options:
·     0.
·     1.
·     2Removed.
Data[20]
Configure the AltEngPerfBIAS item. Supported options:
·     0—Performance.
·     8—Balanced power.
·     15—Power.
Data[21]
Configure the BootMode item. Supported options:
·     1—UEFI.
·     0—Legacy.
Data[22]
Configure the COD item. Supported options:
·     0.
·     1.
·     2.
Data[23]
Configure the Snoop Mode item. Supported options:
·     0.
·     1.
·     2.
·     3.
·     4.
Data[24]
Configure the Monitor/Mwait item. Supported options:
·     0.
·     1.
Data[25]
Configure the Enforce POR item. Supported options:
·     0—Enabled.
·     2—Disabled.
·     3Auto.
Data[26]
Configure the PXE Retry item.
Value range: 0 to 50.
Data[27]
Configure the FirstBootDevice item. Supported options:
·     0—HDD.
·     1—ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB FDD.
·     6—USB LAN.
·     7—Network.
·     9Disable.
Data[28]
Configure the SecondBootDevice item. Supported options:
·     0—HDD.
·     1—ODD.
·     2—USB HDD.
·     3—USB ODD.
·     4—USB key.
·     5—USB FDD.
·     6—USB LAN.
·     7—Network.
·     9Disable.
Data[29]
Configure the BusinessPortStatus item. Supported options:
·     0Enable.
·     1Disable.
Data[30]
Configure the ProcessorCcxEnable item. Supported options:
·     1Enable.
·     0Disable.
Data[31]
Configure the SR_IOV_SUPPORT item. Supported options:
·     1Enable.
·     0Disable.
Data[32]
Configure the INTEL_VT_FOR_DIRECTED_IO item. Supported options:
·     1Enable.
·     0Disable.
Data[33]
Configure the IPV4_PXE_SUPPORT item. Supported options:
·     1Enable.
·     0Disable.
Data[34]
Configure the IPV6_PXE_SUPPORT item. Supported options:
·     1Enable.
·     0Disable.
Data[35]
Configure the OS_ACPI_CX item. Supported options:
·     0x00ACPI C2.
·     0x01ACPI C3.
Data[36]
Configure the CPU_C6_REPORT item. Supported options:
·     0x00—Disable.
·     0x01—Enable.
·     0xff—Auto.
Data[37]
Configure the CPUFlexRatioOverride item. Supported options:
·     0x01Enable.
·     0x00Disable.
Data[38]
Configure the CPUCoreFlexRatio item.
Value range: 0 to 100.
Data[39]
Configure the SpareErrTh item, LS byte first.
Value range: 0x00 to 0xff.
Data[40]
Configure the SpareErrTh item, MS byte first.
Value range: 0x00 to 0x7f.
Data[41]
Configure the SpareIntSelect item. Supported options:
·     smi signalEnable.
·     0x00Disable.
Data[42]
Configure the LeakyBktLo item.
Value range: 0x00 to 0x3f.
Data[43]
Configure the LeakyBktHi item.
Value range: 0x00 to 0x29.
Data[44]
Configure the PStateLimit item. Supported options:
·     1Enable.
·     0Disable.
User role
User
Required permission
Remote control
Only devices that use Intel CPUs support this command. Devices that use AMD CPUs such as R4950 do not support this command. Blade servers do not support this command. G5 servers do not support this command.
# Configure all BIOS settings.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x1b 0x00 0x00 0x02 0x00 0x00 0x01 0x00 0x00 0x01 0x02 0x00 0x01 0xff 0x00 0x01 0x00 0x00 0x00 0x00 0x01 0x00 0x00 0x01 0x01 0x01 0x01 0x00 0x00 0x00 0x00 0x00 0x64 0x04 0x11 0x01 0x01 0x01 0x00
a2 63 00
Table 129 Response field description
Data[1:3]
DNS
Obtain host name setting
Use this command to obtain host name setting.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x01 Blockselect
Table 130 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
Not restricted to specific products.
# Obtain host name settings.
COMMAND>ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x01 0x00
01 09 6c 6f 63 61 6c 68 6f 73 74 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00
01
09
Table 131 Response field description
Data[1]
Host name setting method. Supported options:
·     0Manual.
·     1Auto.
Data[2]
Length of the host name.
Data[3:130]
Host name.
Obtain DNS registration settings
Use this command to obtain DNS registration settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x02 Blockselect
Table 132 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain DNS registration settings.
COMMAND>ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x02 0x00
21 01 00
21
01
Table 133 Response field description
Data[1:3]
DNS registration options.
Each byte represents a port.
Each bit in a byte represents the enabling status of an option. Value 1 indicates enabled and 0 indicates disabled.
Bit[0]: Enabling status of DNS registration.
Bit[1]: TSIG authentication.
Bit[2]: Multicast DNS.
Bit[4]: FQDN name registration.
Bit[5]: Host name registration.
Obtain DNS domain settings
Use this command to obtain DNS domain settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x03 Blockselect
Table 134 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain DNS domain settings.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x03 0x00
01 00 01 08
01
00
01
08
Table 135 Response field description
Data[1]
DHCP mode for a domain. Supported options:
·     0—Manual.
·     1Automatic.
Data[2]
Domain index (the port to obtain DNS domain information). Supported options:
·     0Shared network port (eth0).
·     1Dedicated network port (eth1).
Data[3]
IP priority of the domain. Supported options:
·     0DNS domain information will not be obtained.
·     1IPv4 address is preferred.
·     2IPv6 address is preferred.
Data[4]
Length of the domain name.
Obtain the domain suffix
Use this command to obtain the domain suffix.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x04 Blockselect
Table 136 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain the domain suffix.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x04 0x01
74 65 73 74 2e 63 6f 6d 00 00 00 00 00 00 00 00
Table 137 Response field description
Data[1:64]
Domain suffix.
Obtain the DNS sever settings
Use this command to obtain the DNS sever settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x05 Blockselect
Table 138 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain the DNS sever settings.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x05 0x00
01 01 01
01
01
01
Table 139 Response field description
Data[1]
DHCP mode of a DNS server. Supported options:
·     0Manual.
·     1Auto.
Data[2]
DNS index (the port to obtain DNS server information). Supported options:
Data[3]
IP priority of the DNS server. Supported options:
·     0DNS server information will not be obtained.
Obtain the IP addresses of DNS servers
Use this command to obtain the IP addresses of DNS servers.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x06 Blockselect
Table 140 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain the IP address of DNS server 1.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x06 0x01
c0 a8 0a c9
c0 a8 0a c9
# Obtain the IP address of DNS server 2.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x06 0x02
Table 141 Response field description
Data[1:N]
IP address of a DNS server.
N is 4 for an IPv4 address and 16 for an IPv6 address.
This field displays all 0s if the IP address of a DNS server is not specified.
Obtain the enabling status of DNS registration
Use this command to obtain the enabling status of DNS registration.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6b 0x09 Blockselect
Table 142 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
User
Required permission
Information query
# Obtain the enabling status of DNS registration.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6b 0x09 0x00
01
01
Table 143 Response field description
Data[1]
Enabling status of DNS registration. Supported options:
·     0—Disabled.
·     1—Enabled.
Configure the host name settings
Use this command to configure the host name settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x01 Blockselect HostSetting HostNameLen HostName
Table 144 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Specify the host name setting method. Supported options:
·     0Manual.
·     1Auto.
Data[6]
Set the length of the host name.
Data[7:x]
Specify the host name. The host name must end with 0x00, and the maximum length is 128 bytes.
User role
Administrator
Required permission
Basic configuration
# Configure the host name settings.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x01 0x00 0x00 0x09 0x6c 0x6f 0x63 0x61 0x6c 0x68 0x6f 0x73 0x74 0x00
00
09
Configure DNS registration options
Use this command to configure DNS registration options.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x02 Blockselect RegDNSConf
Table 145 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5:6]
Configure the DNS registration options.
Each bit in a byte represents whether to enable an option. Value 1 indicates to enable and 0 indicates to disable.
Bit[0]: DNS registration.
Bit[4]: FQDN name registration .
Bit[5]: Host name registration .
Data[7]
Reserved. This field is fixed to 0.
User role
Administrator
Required permission
Basic configuration
After you execute this command, you must commit the DNS configuration changes for the configuration to take effect.
# Enable DNS registration on the shared network port (eth0) without options specified, and enable DSN registration on the dedicated port(eth1) with the host name registration method specified.
COMMAND>ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x02 0x00 0x01 0x21 0x00
01
21
Configure DNS domain settings
Use this command to configure DNS domain settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x03 Blockselect DomainDHCP DomainIndex Domainpriority DomainLen
Table 146 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Specify the DHCP mode for a domain. Supported options:
·     0—Manual.
·     1Auto.
Data[6]
Specify the domain index (the port to obtain DNS domain information). Supported options:
Data[7]
Set the IP priority of the domain. Supported options:
Data[8]
If the DHCP mode for a DNS domain is auto, you cannot set the IP priority of the domain to 0.
If the DHCP mode for a DNS domain is manual, you must set the domain index and the IP priority of the domain to 0.
User role
Administrator
Required permission
Basic configuration
# Configure DNS domain settings.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x03 0x00 0x01 0x01 0x01 0x08
Set the domain suffix
Use this command to set the domain suffix.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x04 Blockselect DomainName
Table 147 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5:68]
Set the domain suffix.
User role
Administrator
Required permission
Basic configuration
# Set the domain suffix to test.com.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x04 0x01 0x74 0x65 0x73 0x74 0x2e 0x63 0x6f 0x6d
Configure DNS server settings
Use this command to configure DNS server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x05 Blockselect DNSDHCP DNSIndex IPPriority
Table 148 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Specify the DHCP mode for a DNS server. Supported options:
·     0Manual.
·     1Auto.
Data[6]
Specify the DNS index (the port to obtain DNS server information). Supported options:
Data[7]
Set the IP priority of the DNS server. Supported options:
If the DHCP mode for a DNS server is auto, you cannot set the IP priority of the DNS server to 0.
If the DHCP mode for a DNS server is manual, you must set the DNS index and the IP priority of the DNS server to 0.
User role
Administrator
Required permission
Basic configuration
# Configure DNS server settings.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x05 0x00 0x01 0x00 0x01
Specify the IP address of a DNS server
Use this command to specify the IP address of a DNS server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x06 Blockselect DNSIPAddr
Table 149 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5:N]
Specify the IP address of a DNS server.
User role
Administrator
Required permission
Basic configuration
When you configure this command, make sure the DHCP mode for the DNS server is manual.
# Specify the IP address of a DNS server.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x06 0x01 0xc0 0xa8 0x0a 0xc8
Commit DNS configuration changes
Use this command to commit DNS configuration changes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x07 Blockselect
Table 150 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
User role
Administrator
Required permission
Basic configuration
# Commit DNS configuration changes.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x07 0x00
Set the enabling status of DNS registration
Use this command to set the enabling status of DNS registration. The configuration takes effect after a restart.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6c 0x09 Blockselect DNSRegEnable
Table 151 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Enable or disable DNS registration. Supported options:
·     0—Disable.
·     1—Enable.
User role
Administrator
Required permission
Basic configuration
# Enable DNS registration.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x6c 0x09 0x00 0x01
Change history
Version
Change description
N/A
Added the description that this command takes effect only after a restart.
Firewall
Obtain IPv4 firewall rule information
Use this command to obtain information about an IPv4 firewall rule.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x77 0x01 EntryNo
Table 152 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Specify the number of an IPv4 firewall rule.
User role
Operator
Required permission
Information query
# Obtain information about an IPv4 firewall rule.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x77 0x01 0x00
0c 00 c0 a8 0a 58 c0 a8 0a 63 e3 07 03 0c 02 1f e3 07 03 14 02 1f
0c
00
c0 a8 0a 58
c0 a8 0a 63
e3 07 03 0c
02 1f
e3 07 03 14
02 1f
Table 153 Response field description
Data[1]
Type of the IPv4 firewall rule. Supported options:
·     0x00IPv4 address-based. It has no validity period or address range.
·     0x01IPv4 address-based. It has an address range but no validity period.
·     0x0bIPv4 address-based. It has a validity period but no address range.
·     0x0cIPv4 address-based. It has a validity period and address range.
·     0x1dIPv4 and MAC address-based. It has no validity period or address range.
·     0x1eIPv4 and MAC address-based. It has an address range but no validity period.
·     0x1fIPv4 and MAC address-based. It has a validity period but no address range.
·     0x20IPv4 and MAC address-based. It has a validity period and address range.
·     0x30MAC address-based. It has no validity period or address range.
·     0x32MAC address-based. It has a validity period but no address range.
Data[2]
State of the IPv4 firewall rule. Supported options:
·     0Blacklist rule.
·     1Whitelist rule.
Data[3:N]
Detailed information about the IPv4 firewall rule.
Change history
Version
Change description
HDM-1.30.09
Added support for whitelist rule and blacklist rule.
Modified the types of firewall rules.
Obtain IPv6 firewall rule information
Use this command to obtain information about an IPv6 firewall rule.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x77 0x04 EntryNo
Table 154 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Specify the number of an IPv6 firewall rule.
User role
Operator
Required permission
Information query
# Obtain information about an IPv6 firewall rule.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x77 0x04 0x00
28 00 3f fe 12 34 ee ee 01 00 00 00 00 00 00 00 12 34 3f fe 12 34 ee ee 01 00 00 00 00 00 00 00 23 45 a0 12 13 14 15 16 e3 07 09 1e 10 00 e3 07 0a 01 10 00
28
00
3f fe 12 34 ee ee 01 00 00 00 00 00 00 00 12 34  3ffe:1234:eeee:0100::1234
3f fe 12 34 ee ee 01 00 00 00 00 00 00 00 23 45  3ffe:1234:eeee:0100::2345
a0 12 13 14 15 16   0:12:13:14:15:16
e3 07 09 1e
10 00
e3 07 0a 01
10 00  16:00
Table 155 Response field description
Data[1]
Type of the IPv6 firewall rule. Supported options:
·     0x15IPv6 address-based. It has a validity period but no address range.
·     0x16IPv6 address-based. It has a validity period and address range.
·     0x40IPv6 address-based. It has no validity period or address range.
·     0x41IPv6 address-based. It has an address range but no validity period.
·     0x25IPv6 and MAC address-based. It has no validity period or address range.
·     0x26IPv6 and MAC address-based. It has an address range but no validity period.
·     0x27IPv6 and MAC address-based. It has a validity period but no address range.
·     0x28IPv6 and MAC address-based. It has a validity period and address range.
Data[2]
State of the IPv6 firewall rule. Supported options:
·     0Blacklist rule.
·     1Whitelist rule.
Data[3:N]
Detailed information about the IPv6 firewall rule.
Change history
Version
Change description
HDM-1.30.09
Network
Obtain the status of a network port
Use this command to obtain the status of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x00 setselect BlockSelect
Table 156 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Set selector.
Data[5]
Block selector.
User role
User
Required permission
Information query
# Enable both IPv4 and IPv6 on the shared network port (eth0).
COMMAND>ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x00 0x00 0x00
00 03
Table 157 Response field description
Data[1]
Index of a network port.
Data[2]
Status of the network port. Supported options:
·     0x00Both IPv4 and IPv6 are disabled.
·     0x01Only IPv4 is enabled.
·     0x02Only IPv6 is enabled.
·     0x03Both IPv4 and IPv6 are enabled.
Obtain bond settings
Use this command to obtain bond settings of a bond port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x01 setselect BlockSelect
Table 158 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain bond settings of a bond port.
COMMAND>ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x01 0x00 0x00
01 00 01 64 00 03 01
01
00
01
64 00
03
01
Table 159 Response field description
Data[1]
Enabling status of the bonding mode. Supported options:
·     1Enabled.
·     0Disabled.
Data[2]
Index of a bond port.
Data[3]
Type of the bonding mode. Supported options:
·     0x01Active/standby mode.
Data[4:5]
MII interval.
Data[6]
Network ports bonded in the bond port. Each bit in this field represents the index of a network port.
Data[7]
Enabling status of automatic configuration.
Obtain the enabling status of a bond port
Use this command to obtain the enabling status of a bond port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x02 setselect BlockSelect
Table 160 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain the enabling status of a bond port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x02 0x00 0x00
01 02
01
02
Table 161 Response field description
Data[1]
Enabling status of a bond port. Supported options:
·     1Enabled.
·     0Disabled.
Data[2]
Index of the bond port.
Obtain the number of network ports
Use this command to obtain the number of network ports.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x03 setselect BlockSelect
Table 162 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain the number of network ports.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x03 0x00 0x00
02 00 01 00 00 00
02
00 01 00 00 00
Table 163 Response field description
Data[1]
Total number of network ports.
Data[2:6]
Indexes of the network ports.
Obtain channel information of a network port
Use this command to obtain channel information of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x04 setselect BlockSelect
Table 164 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain channel information of a network port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x04 0x01 0x00
08
08
Table 165 Response field description
Data[1]
Channel number of a network port.
Change history
Version
Change description
HDM-2.0.03
G5: Network port eth0 uses channel 8 and network port eth1 uses channel 1.
G3: Network port eth0 uses channel 1 and network port eth1 uses channel 8.
Obtain the name of a network port
Use this command to obtain the name of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x05 setselect BlockSelect
Table 166 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain the name of a network port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x05 0x01 0x00
65 74 68 31 00 00 00 00 00 00 00 00 00 00 00 00
65 74 68 31
Table 167 Response field description
Data[1:N]
Name of a network port.
Obtain the primary port of a bond port
Use this command to obtain the primary port of a bond port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x72 0x06 setselect BlockSelect
Table 168 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5]
Parameter selector.
User role
User
Required permission
Information query
# Obtain the primary port of a bond port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x72 0x06 0x00 0x00
00 02
00
02
Table 169 Response field description
Data[1]
Data[2]
Index of the primary port for the bond port.
Each bit in the byte represents the index of a network port. The bit with value 1 indicates that the network port is the primary port.
Set the status of a network port
Use this command to set the status of a network port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x71 0x00 Param EthIndex EnableState
Table 170 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Specify the index of a network port.
Data[5]
Set the status of the network port. Supported options:
·     0x00Disable both IPv4 and IPv6.
·     0x01Enable only IPv4.
·     0x02Enable only IPv6.
·     0x03Enable both IPv4 and IPv6.
Note: 0x00 is not available for the dedicated network port.
User role
Administrator
Required permission
Basic configuration
# Enable both IPv4 and IPv6 on the dedicated network interface (eth1) of G3 servers.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x71 0x00 0x01 0x03
Configure the bond settings
Use this command to configure the bond setting for a bond port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x71 0x01 BondEnable BondIndex BondMode MiiInterval Slaves AutoConf
Table 171 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Enable or disable the bonding mode. Supported options:
·     1Enable.
·     0Disable.
Data[5]
Specify the index of a bond port.
Data[6]
Set the type of the bonding mode. Supported options:
·     0x01—Active/standby mode.
Data[7:8]
Set the MII interval.
Data[9]
Specify network ports to be bonded. Each bit in this field represents the index of a network port.
Data[10]
Enable or disable automatic configuration.
User role
Administrator
Required permission
Basic configuration
# Enable bond port 0, set the bonding mode type to active/standby mode, and add the shared network port (eth0) and the dedicated network port (eth1) to the bond port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x71 0x01 0x01 0x00 0x01 0x64 0x00 0x03 0x00
Set the primary port for a bond port
Use this command to set the primary port for a bond port.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x71 0x06 BondIndex ActiveIndex
Table 172 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Data[5]
Specify the index of a network port to act as the primary port in the bond port.
Each bit in the byte represents the index of a network port. To specify a network port as the primary port, set the bit of the network port to 1.
User role
Administrator
Required permission
Basic configuration
# Set the primary port to the shared network port (eth0) for a bond port.
COMMAND> ipmitool -I lanplus -H 172.16.88.88 -U admin -P Password@_ raw 0x32 0x71 0x06 0x00 0x01
Obtain the link status of dedicated and shared network ports
Use this command to obtain the link status of dedicated and shared network ports.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x6a
Table 173 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Information query
# Obtain the link status of dedicated and shared network ports.
COMMAND> ipmitool -H 127.0.0.1 -U admin –P Password@_ -I lanplus raw 0x36 0x0b 0xa2 0x63 0x00 0x6a
a2 63 00 01 04 00 01 00 00 00 00 00 00 00 00 00
00 00 00 00 00
Table 174 Response field description
Data[1:3]
Data[4]
Link status of the dedicated port. Supported options:
·     0x01Up.
·     0x00Down.
Data[5]
Number of shared ports.
Data[6]
Ports selected as the shared ports.
Data[7:21]
Link status of the shared ports. Supported options:
·     0x01—Up.
·     0x00—Down.
Change history
Version
Change description
HDM-1.30.12
Added this command.
Network-related settings
Obtain HDM network service information
Use this command to obtain information about an HDM network service.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x69 Data[0:3]
Table 175 Request field description
0x32
NetFn code.
0x69
Command code.
Data[0:3]
Specify the service ID. Supported options:
·     0x00000001Web.
·     0x00000002KVM.
·     0x00000004CD-media.
·     0x00000008FD-media.
·     0x00000010HD-media.
·     0x00000020SSH.
·     0x00000040Telnet.
·     0x00000080IPMI.
·     0x00000100SNMP.
·     0x00000400Remote XDP/iHDT.
·     0x00000800VNC.
User role
User
Required permission
Information query
# Obtain SSH service information.
COMMAND> ipmitool -I lanplus  -H 192.168.55.2 -U admin -P Password@_ raw 0x32 0x69 0x20 0x00 0x00 0x00
 20 00 00 00 01 46 46 46 46 46 46 46 46 46 46 46
 46 46 46 46 46 00 ff ff ff ff 16 00 00 00 58 02
 00 00 83 80 3c 00 00 00 08 07 00 00
Table 176 Response field description
Data[1:4]
Service ID. Supported options:
·     0x00000001Web.
·     0x00000002KVM.
·     0x00000020SSH.
·     0x00000040Telnet.
·     0x00000080IPMI.
·     0x00000100SNMP.
·     0x00000800VNC.
Data[5]
Enabling status of the service.
Data[6:22]
Interface name.
This field is a string in ACSII format. An interface will be padded with 0x00s if the interface name is not long enough.
Data[23:26]
Insecure service port.
The value of all-Fs indicates that the interface is a secure service port.
Data[27:30]
Secure service port.
The value of all-Fs  indicates that the interface is an insecure service port.
Data[31:34]
Session timeout time.
Data[35]
Maximum number of sessions. If this field displays 0xFF, the field value is invalid.
Bit[7]: If this bit is 1, the field cannot be modified.
Bits[6:0]: Maximum number of sessions.
Data[36]
Number of active sessions. If this field displays 0xFF, the field value is invalid.
Bits[6:0]: Number of active sessions.
Data[37:40]
Minimum session timeout time, in seconds.
Data[41:44]
Maximum session timeout time, in seconds.
Change history
Version
Change description
2.19
Added support for the iHDT service.
Configure HDM network service settings
Use this command to configure HDM network service settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6a Data[0:3] Data[4] Data[5:21] Data[22:25] Data[26:29] Data[30:33] Data[34] Data[34] Data[35]
Table 177 Request field description
0x32
NetFn code.
0x6a
Command code.
Data[0:3]
Specify a service ID. Supported options:
·     0x00000001Web.
·     0x00000002KVM.
·     0x00000020SSH.
·     0x00000040Telnet.
·     0x00000080IPMI.
·     0x00000100SNMP.
·     0x00000800VNC.
Data[4]
Enable or disable the service. Supported options:
·     0—Disable.
·     1—Enable.
Data[5:21]
Specify an interface name.
This field is required.
Data[22:25]
Specify the interface as an insecure service port.
To use the interface as a secure service port, set the field value to all Fs.
Data[26:29]
Specify the interface as a secure service port.
To use the interface as an insecure service port, set the field value to all Fs.
Data[30:33]
Set the session timeout time, in seconds.
The value of this field must be a multiple of 60.
Data[34]
Set the maximum number of sessions. Refer to the maximum number of sessions field in the obtained HDM network service information to set this field:
·     If the obtained field displays 0xFF, set this field to 0xFF.
·     If the highest bit of the obtained field is 1, set this field to 0.
Data[35]
Set the number of active sessions. Refer to the number of active sessions field in the obtained HDM network service information to set this field:
User role
Administrator
Required permission
Security
# Set the session timeout time to 900 seconds for the SSH service.
COMMAND> ipmitool -I lanplus  -H 192.168.55.2 -U admin -P Password@ raw 0x32 0x6a 0x20 0x00 0x00 0x00 0x01 0x46 0x46 0x46 0x46 0x46 0x46 0x46 0x46  0x46 0x46 0x46 0x46  0x46 0x46 0x46 0x46  0x00 0xff 0xff 0xff 0xff 0x16 0x00 0x00 0x00 0x84 0x03  0x00 0x00 0x00 0x00
# Obtain the SSH service information to verify that the session timeout time has been set to 900 seconds.
 46 46 46 46 46 00 ff ff ff ff 16 00 00 00 84 03
Table 178 Response field description
Data[0]
Completion code. Supported options:
·     0x00Command succeeded.
·     0xF5This code is returned if you change the VNC service settings when active VNC sessions exist.
Change history
Version
Change description
HDM-2.19
HDM-1.30.07
Added completion code 0xF5.
Configure LDAP settings
Use this command to configure LDAP settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xC9 0x00 0x00 Data[5:N]
Table 179 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter Selector
Data[4]
Block selector
Data[5:N]
Configuration data parameters. For more information about configuration parameters, see Table 180.
Table 180 Configuration data parameters
Parameter selector
Block selector
LDAP status
0
0x00
Data[5]: Set the LDAP authentication status.
Bits[7:1]: Reserved.
Bit[0]: Enable or disable LDAP authentication. Supported options:
·     0hDisable.
·     1hEnable.
Encryption type
1
0x00
Data[5]: Specify the encryption type.
Bits[7:2]: Reserved
Bit[1]: Specify StartTLS. Supported options:
·     0hDisable.
·     1hEnable.
Bit[0]: Specify SSL. Supported options:
·     0hDisable.
·     1hEnable.
Port number
2
0x00
Data[5:6]: Specify the LDAP service port number.
Default: 389.
Data type: Hexadecimal number.
Secondary port number
3
0x00
Data[5:6]: Specify the secondary LDAP service port number.
Server address
4
0x00
Data[5]: Set the Progress bit. Supported options:
·     1Set in progress.
·     0Reset and save.
4
0x01 to 0x03
Data[5:68]: Specify the address of the LDAP server.
Data type: String in ASCII format.
Each block can have a maximum of 64 bytes.
4
0x04
Data[5:67]: Specify the address of the LDAP server.
The maximum length of an IP or FQDN address is 255 bytes.
Secondary server address
5
0x00
·     1Set.
·     0Reset and save.
5
0x01 to 0x03
Data[5:68]: Specify the secondary address of the LDAP server.
5
0x04
Data[5;67]: Specify the secondary address of the LDAP server.
Password
6
0x00
Data[5:51]: Specify the password for the bind DN.
Bind DN
7
0x00
·     1Set in progress.
·     0Reset and save.
7
0x01 to 0x03
Data[5:68]: Specify a bind DN.
7
0x04
Data[5:67]: Specify a bind DN.
The maximum length of a bind DN is 255 bytes.
Search Base
8
0x00
·     1Set in progress.
·     0Reset and save.
8
0x01 to 0x03
Data[5:68]: Specify a search base.
8
0x04
Data[5:67]: Specify a search base.
The maximum length of a search base is 255 bytes.
User identification method
9
0x00
Data[5:11]: Set the user identification method. Supported options:
·     uid.
·     cn.
Default role
10
0x00
Data[5]: Set the default role. (Not realized.)
Adding a role group
11
0x00
·     1Set in progress.
·     0Reset and save.
11
0x01 to 0x04
Data[5]: Add a role group.
Data[6:N]: Configure role group parameters. For more information about role group parameters, see Table 181.
Server address configuration
12
0x00
Data[5]: Specify the type of the IP addresses for the LDAP server. Supported options:
·     0x00IP address.
·     0x01—FQDN address.
Table 181 Role group parameters (Data[1] refers to Data[6] in the whole command)
Parameter
Parameter Selector
Block selector
User ID
0
0x1
Data[1]:0
Data[2]: Specify a user ID. Supported options:
·     0hUser 1.
·     1hUser 2.
·     2hUser 3.
·     3hUser 4.
·     4hUser 5.
Role group name
1
0x1 to 0x3
Data[1]: 1.
Data[2:65]: Specify the group name.
1
0x4
Data[1]: 1.
Data[2:64]: Specify the group name.
The maximum length of a group name is 255 bytes.
Role group domain
2
0x1 to 0x3
Data[1]: 2.
Data[2:65]: Specify the role group domain.
Each domain can have a maximum of 64 bytes.
2
0x4
Data[1]: 2.
Data[2:64]: Specify the role group domain.
The maximum length of a group domain is 255 bytes.
Role group privilege
3
1
Data[1]: 3.
Data[2]: Specify the user role for the role group. Supported options:
·     10h—custom 5.
·     9h—custom 4.
·     8h—custom 3.
·     7h—custom 2.
·     6h—custom 1.
·     4h—administrator.
·     3h—operator.
·     2h—user.
Data[3:5]: Reserved.
Extended privileges for the role group
4
0x1
Data[1]: 4.
Data[2:5]: Specify extended privileges for the role group. For each bit in this byte, value 0 indicates to disable and value 1 indicates to enable.
Data[2]:
Bit[0]: KVM.
Bit[1]: VMedia.
Bit[2]: Network.
Bit[3]: User settings.
Bit[4]: Configuration and security.
Bit[5]: Power consumption.
Bit[6]: Maintenance.
Bit[7]: Health diagnosis.
Data[3]:
Bit[0]: Reserved.
Bit[1]: Specify remote control.
Bits[2:7]: Reserved.
Data[4:5]: Reserved.
User role
Administrator
Required permission
User accounts
To configure a parameter that does not contain blocks, you must set the block selector to 0.
You cannot pad an IP address with 0s. For example, you cannot pad 192.168.1.1 with 0s to change the IP address to 192.168.001.001.
When you specify the address for the LDAP server, make sure the address type is consistent with the address type specified in the server address configuration field.
Before you execute the command to configure a parameter that contains multiple blocks, you must first execute the command with the Progress bit set to 1. After you configure the parameter, you must execute the command with the Progress bit set to 0.
To add a role group, you must execute the command repeatedly to specify all the parameters in Table 181.
·     Configure extended LDAP settings.
# Enable LDAP authentication.
COMMAND>ipmitool raw 0x32 0xC9 0x00 0x00 0x01
# Set the LDAP encryption type.
COMMAND>ipmitool raw 0x32 0xC9 0x01 0x00 0x00
# Set the LDAP service port number to 389.
COMMAND>ipmitool raw 0x32 0xC9 0x02 0x00 0x85 0x01
# Specify 192.168.100.239 as the IP address of the LDAP server.
COMMAND>ipmitool raw 0x32 0xC9 0x04 0x00 0x01
COMMAND>ipmitool raw 0x32 0xC9 0x04 0x01 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x31 0x30 0x30 0x2e 0x32 0x33 0x39 0x00
COMMAND>ipmitool raw 0x32 0xC9 0x04 0x00 0x00
# Set the bind DN.
COMMAND>ipmitool raw 0x32 0xC9 0x07 0x00 0x01
COMMAND>ipmitool raw 0x32 0xC9 0x07 0x01 0x63 0x6E 0x3D 0x61 0x64 0x6D 0x69 0x6E 0x2C 0x64 0x63 0x3D 0x65 0x78 0x61 0x6D 0x70 0x6C 0x65 0x2C 0x64 0x63 0x3D 0x63 0x6F 0x6D
COMMAND>ipmitool raw 0x32 0xC9 0x07 0x00 0x00
# Set the password for the bind DN.
COMMAND>ipmitool raw 0x32 0xC9 0x06 0x00 0x31 0x32 0x33 0x34 0x35 0x36
# Set the search base for the bind DN.
COMMAND>ipmitool raw 0x32 0xC9 0x08 0x00 0x01
COMMAND>ipmitool raw 0x32 0xC9 0x08 0x01 0x64 0x63 0x3D 0x65 0x78 0x61 0x6D 0x70 0x6C 0x65 0x2C 0x64 0x63 0x3D 0x63 0x6F 0x6D
COMMAND>ipmitool raw 0x32 0xC9 0x08 0x00 0x00
# Set the user identification method used by the LDAP server to uid.
COMMAND>ipmitool raw 0x32 0xC9 0x09 0x00 0x75 0x69 0x64 0x00 0x00 0x00 0x00
# Set the type of the IP address for the LDAP server to IP.
COMMAND>ipmitool raw 0x32 0xC9 0x0C 0x00 0x00
·     Add a role group.
# Set the Progress bit for adding a role group.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x00 0x01
# Specify a user ID.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x01 0x00 0x01
# Set the role group name.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x01 0x01 0x74 0x65 0x73 0x74 0x67 0x72 0x6F 0x75 0x70 0x31
# Specify the search base.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x01 0x02 0x64 0x63 0x3D 0x65 0x78 0x61 0x6D 0x70 0x6C 0x65 0x2C 0x64 0x63 0x3D 0x63 0x6F 0x6D
# Specify the privilege for the role group.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x01 0x03 0x04 0x00 0x00 0x00
# Specify the extended privileges for the user group.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x01 0x04 0x01 0x00 0x00 0x00
# Reset the Progress bit to save the configuration.
COMMAND>ipmitool raw 0x32 0xC9 0x0B 0x00 0x00
Table 182 Response field description
Data[0]
·     0x94Invalid command.
·     0x80Unsupported parameter or disabled function.
·     0x81The Progress bit is set to in progress.
·     0x9DThe Progress bit is not set.
·     0x93Invalid IP address.
Change history
2.0.04
User roles custom 1 to custom 5 were added.
Configure Active Directory (AD) settings
Use this command to configure AD settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xC5 Data[3] Data[3] Data[5:N]
Table 183 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
Data[4]
Block selector.
Data[5:N]
Configuration data parameters. For more information about configuration data parameters, see Table 184.
Table 184 Configuration data parameters
Parameter selector
Block selector
AD status
0x00
0x00
Data[5]: Set the AD authentication status.
Bits[7:1]: Reserved
Bit[0]: Enable or disable AD authentication. Supported options:
·     0h—Disable.
·     1h—Enable.
SSL status
0x01
0x00
Data[5]: Set the SSL status.
Bit[0]: Enable or disable SSL. Supported options:
·     0h—Disable.
·     1h—Enable.
Timeout
0x02
0x00
Data[5:8]: Set the AD timeout time, in seconds.
RAC domain
0x03
0x00
·     1Set in progress.
·     0Reset and save.
0x03
0x01 to 0x03
Data[5:68]: Specify a RAC domain.
0x03
0x04
Data[5:67]: Specify a RAC domain.
The maximum length of a RAC domain name is 255 bytes.
AD type
0x04
0x00
Data[5]: Set the AD type.
Bits[7:2]: Reserved
Bit[1:0]: Specify an AD type. Supported options:
·     01h—Extended type. This value is not supported in the current software version.
·     02hStandard type.
DC filter 1
0x05
0x00
·     1Set in progress.
·     0Reset and save.
0x05
0x01 to 0x03
Data[5:68]: Specify DC filter 1.
0x05
0x04
Data[5:67]: Specify DC filter 1.
The maximum length of DC filter 1 is 255 bytes.
DC filter 2
0x06
0x00
·     1Set in progress.
·     0Reset and save.
0x06
0x01 to 0x03
Data[5:68]: Specify DC filter 2.
0x06
0x04
Data[5:67]: Specify DC filter 2.
The maximum length of DC filter 2 is 255 bytes.
DC filter 3
0x07
0x00
·     1Set in progress.
·     0Reset and save.
0x07
0x01 to 0x03
Data[5:68]: Specify DC filter 3.
0x07
0x04
Data[5:67]: Specify DC filter 3.
The maximum length of DC filter 3 is 255 bytes.
RAC user name
0x08
0x00
Data[5:68]: Specify a username.
RAC password
0x09
0x00
·     1Set in progress.
·     0Reset and save.
0x09
0x01
Data[5:68]: Specify the password for the user.
0x09
0x02
Data[5:67]: Specify the password for the user.
The maximum length of a bind DN is 127 bytes.
Adding a role group
0x0A
0x00
·     1Set in progress.
·     0Reset and save.
0x0A
0x01 to 0x04
For more information about role group parameters, see Table 185.
Table 185 Role group parameters (Data[1] refers to Data[6] in the whole command)
Parameter selector
Block selector
User ID
0x00
0x1
Data[1]: 0.
Role group name
0x01
0x1 to 0x3
Data[1]: 1.
Data[2:65]: Specify the role group name.
0x4
Data[1]: 1.
Data[2:64]: Specifies the role group name.
The maximum length of a role group name is 255 bytes.
Role group domain
0x02
0x1 to 0x3
Data[1]: 2.
0x4
Data[1]: 2.
0x03
0x1
Data[1]: 3.
Data[2]: Specify the user role for the role group. User roles of administrator, operator, and user are supported. Supported options:
·     10h—custom 5.
·     9h—custom 4.
·     8h—custom 3.
·     7h—custom 2.
·     6h—custom 1.
·     4h—administrator.
·     3h—operator.
·     2h—user.
0x04
0x1
Data[1]: 4.
Data[2]:
Bit[0]: KVM.
Bit[1]: VMedia.
Bit[2]: Network.
Data[3]:
Bit[0]: Reserved.
Bit[2:7]: Reserved.
User role
Administrator
Required permission
User accounts
To add a role group, you must execute the command repeatedly to specify all the parameters in Table 185.
·     Set the RAC domain to sit.com in in-band configuration way.
COMMAND>ipmitool raw 0x32 0xC5 0x03 0x00 0x01
COMMAND>ipmitool raw 0x32 0xC5 0x03 0x01 0x73 0x69 0x74 0x2E 0x63 0x6F 0x6D 0x00
COMMAND>ipmitool raw 0x32 0xC5 0x03 0x00 0x00
·     Add a role group.
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x00 0x00
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x01 0x00 0x01
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x01 0x01 0x74 0x65 0x73 0x74 0x67 0x72 0x6F 0x75 0x70 0x31 0x00
# Specify a RAC domain.
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x01 0x02 0x73 0x69 0x74 0x2E 0x63 0x6F 0x6D 0x00
# Specify the role group privilege.
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x01 0x03 0x04 0x00 0x00 0x00
# Specify extended privileges for the role group.
COMMAND>ipmitool raw 0x32 0xC5 0x0A 0x01 0x04 0x01 0x00 0x00 0x00
Table 186 Response field description
Data[1]
·     0x99Invalid username.
Change history
Version
Change description
HDM-2.0.04
HDM-1.30.12
Added this command.
Obtain permission of all user roles
Use this command to obtain permissions of all user roles.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x67
Table 187 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Manufacturer ID. This field is fixed to a2 63 00.
Data[6]
Subcommand code.
User role
User
Required permission
Information query
# Obtain permissions of all user roles.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xA2 0x63 0x00 0x67
a2 63 00 ff 01 b7 01 80 01 80 01 80 01 80 01 80 01 80 01
Table 188 Response field description
Data[1-3]
Data[4-5]
Permissions of user role Administrator.
Data[6-7]
Permissions of user role Operator.
Data[8-9]
Permissions of user role User.
Data[10-11]
Permissions of the custom 1 user role.
Data[12-13]
Permissions of the custom 2 user role.
Data[14-15]
Permissions of the custom 3 user role.
Data[16-17]
Permissions of the custom 4 user role.
Data[18-19]
Permissions of the custom 5 user role.
Change history
Version
Change description
HDM-2.0.04
Added this command.
Set permissions for a custom user role
Use this command to set permissions for a custom user role.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x51 0x01 0xe3 0x00
Table 189 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Custom user role ID:
·     0x01—Custom 1.
·     0x02—Custom 2.
·     0x03—Custom 3.
·     0x04—Custom 4.
·     0x05—Custom 5.
Data[8-9]
Permissions that a user role has:
Data8:
·     0—Remote control
·     1—Remote media.
·     2—Security.
·     3—User accounts
·     4—Basic configuration
·     5—Power control.
·     6—Maintenance
·     7—Information query.
Data9:
·     0—Password modification
·     1 to 7—Reserved.
User role
Admin
Required permission
User accounts
# Set permissions for the custom 1 user role.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x51 0x01 0xe3 0x00
0xa2 0x63 0x00
Table 190 Response field description
Data[1-3]
Change history
Version
Change description
HDM-2.0.04
Added this command.
SNMP
Obtain basic SNMP settings
Use this command to obtain basic SNMP settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x6e 0x00
Table 191 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Parameter selector.
User role
Administrator
Required permission
Information query
# Obtain basic SNMP settings.
COMMAND> ipmitool -I lanplus -H 192.168.1.238 -U admin -P Password@_ raw 0x32 0x6e 0x00
 00 01
31 31 31 31 32 32 32 32 00 00 00 00 00 00 00 00
00
32 32 32 32 33 33 33 33 00 00 00 00 00 00 00 00
00 00 00
Table 192 Response field description
Data[1]
Enabling status of SNMPv1. Supported options:
·     1Enabled.
·     0Disabled.
Data[2]
Enabling status of SNMPv2. Supported options:
·     1Enabled.
·     0Disabled.
Date[3:34]
Read community.
Data[35]
Reserved.
Date[36:67]
Write community.
Date[68]
Reserved.
Date[69]
Enabling status of long password. Supported options:
·     1Enabled.
·     0Disabled.
Date[70]
Reserved.
Configure basic SNMP settings
Use this command to configure basic SNMP settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x61 v1_Enable v2c_Enable rcommunity wcommunity Longpassword 0x00
Table 193 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Enable or disable SNMPv1. Supported options:
·     1Enable.
·     0Disable.
Data[4]
Enable or disable SNMPv2c. Supported options:
·     1Enable.
·     0Disable.
Date[5:37]
Read community.
Date[38:70]
Write community.
Date[71]
Enable or disable long password.
·     1Enable.
·     0Disable.
Date[72]
Reserved.
User role
Administrator
Required permission
Basic configuration
# Configure basic SNMP settings.
0x32 0x61 0x00 0x01
0x31 0x31 0x31 0x31 0x32 0x32 0x32 0x32 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00
0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00
0x00
0x32 0x32 0x32 0x32 0x33 0x33 0x33 0x33 0x00 0x00 0x00 0x00 0x00 0x00 0x00 0x00
0x00 0x00 0x00
Change history
Version
Change description
HDM-1.11.35
Merged two reserved fields to the Read community and Write community fields, respectively.
HDM-1.11.29
Added two reserved fields and changed the position of the Longpassword field.
Set the enabling status of SNMP traps
Use this command to set the enabling status of SNMP traps.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x01 SnmpTrapEnable
Table 194 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Enable or disable SNMP traps. Supported options:
·     1Enable.
·     0Disable.
User role
Administrator
Required permission
Basic configuration
# Disable SNMP traps.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x01 0x00
Change history
Version
Change description
HDM-1.30.08
Added this command.
Set the SNMP trap version
Use this command to set the SNMP trap version.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x02 SnmpTrapVersion
Table 195 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Set the SNMP trap version for a user.
Bits[0:1]: Specify an SNMP version. Supported options:
·     0SNMPv1.
·     1SNMPv2c.
·     2—SNMPv3.
Bits[2:7]: Specify a user ID.
User role
Administrator
Required permission
Basic configuration
To set the SNMP trap version to SNMPv3, you must specify an existing user that has the SNMP extended privilege.
# Set the SNMP trap version to SNMPv1.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x02 0x00
Change history
Version
Change description
HDM-1.30.08
Added this command.
Set the location of an SNMP trap node
Use this command to set the location of an SNMP trap node.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x05 0x65 0x65 0x65 0x00
Table 196 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7:N]
Location of the SNMP trap node.
This field is a string of 1 to 32 bytes and ended with \0.
User role
User
Required permission
Basic configuration
# Set the location of an SNMP trap node.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x05 0x65 0x65 0x65 0x00
Change history
Version
Change description
HDM-1.30.08
Added this command.
Set the SNMP trap contact information
Use this command to set the SNMP trap contact information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x06 0x65 0x65 0x65 0x00
Table 197 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7:N]
Set the contact information.
User role
User
Required permission
Basic configuration
# Set the SNMP trap contact.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x06 0x65 0x65 0x65 0x00
Change history
Version
Change description
HDM-1.30.08
Added this command.
Configure an SNMP community
Use this command to configure an SNMP community.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x07 0x65 0x65 0x65 0x00
Table 198 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7:N]
Specify the name of the SNMP community.
User role
User
Required permission
Basic configuration
# Configure an SNMP community.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x07 0x65 0x65 0x65 0x00
Change history
Version
Change description
HDM-1.30.08
Added this command.
Specify the severity levels of SNMP traps to be reported
Use this command to specify the severity levels of SNMP traps to be reported.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x08 Data[7]
Table 199 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand node.
Data[7]
Specify the severity levels. Supported options:
·     2All.
·     1Major + critical.
·     0Minor + major + critical.
User role
User
Required permission
Basic configuration
# Specify the severity levels of SNMP traps to be reported.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x08 0x00
Change history
Version
Change description
HDM-1.30.12
Modified the severity level of "major + critical" to "minor + major + critical".
HDM-1.30.08
Added this command.
Configure an SNMP trap server
Use this command to configure an SNMP trap server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x09 Data[7] Data[8] Data[9:10] Date[11] Date[12:N]
Table 200 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the ID of an SNMP trap server. Supported options:
·     1.
·     2.
·     3.
·     4.
·     5.
·     6.
·     7.
·     8.
Data[8]
Enable or disable the SNMP trap server. Supported options:
·     1Enable.
·     0Disable.
Data[9:10]
Specify the port number of the SNMP trap server.
Data[11]
Specify the mode of the SNMP trap server. Supported options:
·     0—IPv4.
·     1—IPv6 or domain name.
Data[12:76]
Specify the ASCII code for the IPv6 address or domain name of the SNMP trap server, up to 64 characters. If the string does not reach the maximum length, 0x00 must be added at the end as an end tag.
User role
User
Required permission
Basic configuration
# Configure IPv4 address 192.168.1.2 for the SNMP trap server.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw  0x36 0x0d 0xa2 0x63 0x00 0x09 0x02 0x01 0xA3 0x00 0x00 0xc0 0xa8 0x1 0x2
# Configure domain name www.12345.comv for the SNMP trap server.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x09 0x02 0x01 0xA3 0x00 0x01 0x77 0x77 0x77 0x2E 0x31 0x32 0x33 0x34 0x35 0x2E 0x63 0x6F 0x6D 0x00 0x00 0x00 0x00
# Configure IPv6 address fe80::2220:2220:2220:2220:1348 for the SNMP trap server.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x09 0x03 0x01 0xA3 0x00 0x01 0x66 0x65 0x38 0x30 0x3A 0x3A 0x32 0x32 0x32 0x30 0x3A 0x32 0x32 0x32 0x30 0x3A 0x32 0x32 0x32 0x30 0x3A 0x32 0x32 0x32 0x30 0x3A 0x31 0x33 0x34 0x38 0x00
Change history
Version
Change description
HDM-6.01
Added restrictions and guidelines for specifying IPv6 addresses or domain names for Data[12].
HDM-2.33
Added the support for the number of SNMP trap servers from 4 to 8.
HDM-1.30.08
Added this command.
Set the SNMP trap mode
Use this command to set the SNMP trap mode.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x0a 0x00
Table 201 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Trap mode:
·     1—Event OID mode.
·     0—Module OID mode.
User role
Admin
Required permission
Basic configuration
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x0a 0x00
Change history
Version
Change description
HDM-1.30.11
Added this command.
Set an SNMP v3 user
Use this command to set an SNMP v3 user.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0d 0xa2 0x63 0x00 0x0b 0x02 0x01 0x01 0x01 0x01 0x36 0x36 0x36 0x36 0x36 0x36 0x36 0x36
Table 202 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Specify the local user ID. Supported options:
·     2.
·     3.
·     4.
·     5.
·     6.
·     7.
·     8.
·     9.
·     10.
·     11.
·     12.
·     13.
·     14.
·     15.
·     16.
Data[8]
Enabling status of the SNMP v3 extended permissions. Supported options:
·     1Disabled.
·     0Enabled.
Data[9]
SNMP v3 read and write permissions. Supported options:
·     1—Read-only.
·     2—Read-write.
Data[10]
SNMP v3 authentication algorithm. Supported options:
·     1—SHA.
·     2—MD5.
Data[11]
SNMP v3 encryption algorithm. Supported options:
·     1—DES.
·     2—AES.
Data[12-51]
SNMP v3 independent password.
The independent password can contain 8 to 40 characters and must meet the advanced password policy requirements for local user passwords.
User role
Admin
Required permission
User accounts
Product compatibility
# Set an SNMP v3 user.
COMMAND> ipmitool -H 192.168.7.23 -I lanplus -U admin -P Password@_ raw 0x36 0x0d 0xa2 0x63 0x00 0x0b 0x02 0x01 0x01 0x01 0x01 0x36 0x36 0x36 0x36 0x36 0x36 0x36 0x36
Change history
Version
Change description
HDM B06D013
Added interface.
NTP
Obtain NTP server addresses
Use this command to obtain the IP addresses of NTP servers.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA7
User role
User
Required permission
Information query
The obtained IP addresses of NTP servers are in hexadecimal notation. As a best practice for better understanding, convert the format of the IP addresses to ASCII.
# Obtain the IP addresses of NTP servers.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA7
 00 31 2e 63 6e 2e 70 6f 6f 6c 2e 6e 74 70 2e 6f
 72 67 00 00 00 00 00 00 00 00 00 00 00 00 00 00
 00 32 2e 63 6e 2e 70 6f 6f 6c 2e 6e 74 70 2e 6f
 00
Table 203 Response field description
Data[1]
NTP status. Supported options:
·     0—NTP is off.
·     1—NTP is on, and synchronization succeeded.
·     2—NTP is on, but synchronization failed.
Data[2:129]
Primary NTP server.
Data[130:257]
Secondary NTP server.
Obtain the NTP time zone
Use this command to obtain the NTP time zone.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA6
User role
User
Required permission
Information query
The obtained NTP time zone is in hexadecimal notation. As a best practice for better understanding, convert the format of the time zone to ASCII.
# Obtain the current NTP time zone.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA6
55 54 43 2d 38
Table 204 Response field description
Data[1:N]
Time zone.
Specify the primary NTP server
Use this command to specify the primary NTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA8 0x01 Data[1:x]
Table 205 Request field description
Data[1:x]
Specify the address of the primary NTP server, a hexadecimal value of 1 to 127 bytes. Supported address types:
·     IPv4 address.
·     IPv6 address.
·     FQDN address.
The maximum value of N is 128.
The primary NTP server is at 1.cn.pool.ntp.org.
User role
Administrator
Required permission
Basic configuration
You can use the Notepad++ source code editor to convert an ASCII address to a hexadecimal address.
# Specify the host at ntp.h3c.com as the primary NTP server.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA8 0x01 0x6e 0x74 0x70 0x2e 0x68 0x33 0x63 0x2e 0x63 0x6f 0x6d
Change history
Version
Change description
HDM-1.12.05
Removed the fixed 128-byte length limit on the IP addresses of NTP servers.
Specify the secondary NTP server
Use this command to specify the secondary NTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA8 0x02 Data[1:x]
Table 206 Request field description
Data[1:x]
Specify the address of the secondary NTP server, a hexadecimal value of 1 to 127 bytes. Supported address types:
·     IPv4 address.
·     IPv6 address.
·     FQDN address.
The secondary NTP server is at 2.cn.pool.ntp.org.
User role
Administrator
Required permission
Basic configuration
# Specify the host at ntp2.h3c.com as the secondary NTP server.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA8 0x02 0x6e 0x74 0x70 0x32 0x2e 0x68 0x33 0x63 0x2e 0x63 0x6f 0x6d
Change history
Version
Change description
HDM-1.12.05
Specify the tertiary NTP server
Use this command to specify the tertiary NTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA8 0x05 Data[1:x]
Table 207 Request field description
Data[1:x]
Specify the address of the tertiary NTP server, a hexadecimal value of 1 to 127 bytes. Supported address types:
·     IPv4 address.
·     IPv6 address.
·     FQDN address.
No tertiary NTP server is specified.
User role
Administrator
Required permission
Basic configuration
# Specify the host at ntp3.h3c.com as the tertiary NTP server.
COMMAND> ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA8 0x05 0x6e 0x74 0x70 0x33 0x2e 0x68 0x33 0x63 0x2e 0x63 0x6f 0x6d
Change history
Version
Change description
HDM-1.30.12
Added this command.
Configure time synchronization with NTP servers
Use this command to configure time synchronization with NTP servers.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xA8 0x03 Data[1]
Table 208 Request field description
Data[1]
Enable or disable time synchronization with NTP servers. Supported options:
·     0x00Disable.
·     0x01Enable.
User role
Administrator
Required permission
Basic configuration
Before you enable time synchronization with NTP servers, make sure the NTP servers are reachable.
When time synchronization with NTP servers is enabled, the server automatically synchronizes the data and time with NTP servers.
When time synchronization is disabled, HDM uses the current time. HDM will synchronize the time with the BIOS after the server reboots.
# Disable time synchronization with NTP servers.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xA8 0x03 0x00
Set the time zone
Use this command to set the time zone.
ipmitool -I connect_type -H hostname -U username -P password raw 0x0A 0x5D Data[1:2]
Table 209 Request field description
Data[1:2]
Specify the UTC offset, in minutes. The value range is -720 to 840. Only hours and half hours are supported. The value must be in hexadecimal format.
User role
Administrator
Required permission
Basic configuration
To correctly set the time zone, you must correctly calculate the UTC offset, and then convert the offset to a value in hexadecimal and little endian format. For example, to set the time zone to UTC-8:00, perform the following steps:
1.     Calculate the UTC offset: -8*60=-480.
2.     Convert the offset to a value in hexadecimal notation 0xfe 0x20.
3.     Adjust the endianness of the value to little endian: 0x20 0xfe.
# Set the time zone to UTC-8:00.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x0A 0x5D 0x20 0xfe
Set the NTP refresh interval
Use this command to set the NTP refresh interval (the frequency at which the server synchronizes the time with NTP servers.)
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xa2 0x63 0x00 0x05 Data[7:10]
Table 210 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7:10]
Set the NTP refresh interval, in seconds.
Value range: 600 to 2592000.
User role
Administrator
Required permission
Basic configuration
Not restricted to specific products.
Data[1:3]
# Set the NTP refresh interval to 600 seconds.
COMMAND> ipmitool -H 127.0.0.1 -U jdroot -P JCss%6!8 -I lanplus raw 0x36 0x0a 0xa2 0x63 0x00 0x05 0x58 0x02 0x00 0x00
a2 63 00
Obtain the IP address of the tertiary NTP server
Use this command to obtain the IP address of the tertiary NTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x70
User role
User
Required permission
Information query
# Obtain the IP address of the tertiary NTP server.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x70
a2 63 00 33 2e 63 6e 2e 70 6f 6f 6c 2e 6e 74 70
 2e 6f 72 67 00 31 30 30 52 30 30 31 42 30 32 44
 30 32 37 53 50 30 34 5f 44 45 42 55 47 00 00 00
 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
 00 00 00
Table 211 Response field description
Data[1:3]
Data[4:131]
IP address of the tertiary NTP server, which is shorter than 128 bytes.
Change history
Version
Change description
HDM-1.11.36, HDM-1.30.12
Added this command.
Obtain the NTP synchronization interval
Use this command to obtain the NTP synchronization interval.
ipmitool -I connect_type -H hostname -U username -P password raw  0x36 0x0a 0xa2 0x63 0x00 0x0b
Table 212 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Required permission
Information query
# Obtain the NTP synchronization interval.
COMMAND> ipmitool -H 127.0.0.1 -U jdroot -P JCss%6!8 -I lanplus raw 0x36 0x0a 0xa2 0x63 0x00 0x0b
a2 63 00 58 02 00 00
Table 213 Response field description
Data[1:3]
Data[4:7]
Synchronization interval in seconds.
Change history
Version
Change description
HDM-2.13.00
Added this command.
HDM maintenance
Obtain HDM firmware information
Use this command to obtain HDM firmware information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xb4 0x01
User role
User
Required permission
Information query
# Obtain HDM firmware information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xB4 0x01
 01 01 01 42 4d 43 00 00 00 00 00 01 0b 0e 00 00
 00 00 00 01 48 44 4d 20 56 31 30 30 52 30 30 31
 42 30 32 44 30 31 34 5f 44 45 42 55 47 00 00 00
 00 00 00 00
Table 214 Response field description
Data[1]
Number of HDM firmware versions.
Information about the first HDM firmware version
Data[2]
ID.
Data[3]
Instance.
Data[4:11]
Device name. This field is a string fixed to BMC.
Data[12]
Major version, in decimal notation.
Data[13]
Minor version.
Data[14:19]
Aux version.
Data[14]: Small version.
Data[15]: SP version.
Data[16]: HP version
Data[17:19]: Reserved.
Major, minor, and aux versions together define a firmware version. The following are examples:
·     Major=0x01, Minor=0x00, Aux=0x080000000000 represent version 1.00.08.
·     Major=0x01, Minor=0x00, Aux=0x080100000000 represent version 1.00.08P01.
·     Major=0x01, Minor=0x00, Aux=0x080102000000 represent version 1.00.08P01H02.
Data[20]
Device.
Data[21:148]
Internal version. This field is a string, V500R001B01D002, for example.
Information about the Nth HDM firmware version (if any). N represents the number of an HDM firmware version.
Obtain BIOS firmware information
Use this command to obtain BIOS firmware information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xb4 0x02
User role
User
Required permission
Information query
# Obtain BIOS firmware information.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0xB4 0x02
 01 02 01 42 49 4f 53 00 00 00 00 01 00 1a 00 00
 00 00 00 01 56 31 30 30 52 30 30 31 42 30 31 44
 30 32 36 00 00 00 00 00 00 00 00 00 00 00 00 00
 00 00 00 00
Table 215 Response field description
Data[1]
Number of BIOS firmware versions.
Information about the first BIOS firmware version
Data[2]
Version ID.
Data[3]
Instance.
Data[4:11]
Device name. This field is a string fixed to BIOS.
Data[12]
Data[13]
Minor version.
Data[14:19]
Aux version.
Data[16]: HP version.
Data[20]
Device.
Data[21:148]
Information about the Nth BIOS firmware version (if any). N represents the number of an HDM firmware version.
Restore default HDM settings
Use this command to restore default HDM settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x66
Table 216 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
User role
Administrator
Required permission
Maintenance
# Restore default HDM settings.
0x32 0x66
Change history
Version
Change description
3.12
Changed the command description to restoring default HDM settings.
Restore factory HDM settings
Use this command to restore factory HDM settings, which is edited based on the default settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x66 0x01
Table 217 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Subcommand code.
User role
Administrator
Required permission
Maintenance
0x32 0x66 0x01
Change history
Version
Change description
HDM-2.19
Added this command.
Obtain PFR firmware information about a system board
Use this command to obtain PFR firmware information about a system board.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xb4 0x00 0x01
Required permission
Information query
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_raw 0x32 0xB4 0x00 0x01
01 86 01 50 46 52 43 50 4c 44 00 00 01 a5 00 00
00 00 00 01 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00
Data[1]
Number of PFR versions.
Information about the first PFR version
Data[2]
ID.
Data[3]
Instance.
Data[4:11]
Device name. This field is a string fixed to PFRCPLD.
Data[12]
Data[13]
Minor version.
Data[14:19]
Aux version.
Data[20]
Device.
Data[21:148]
Internal version. This field is a string.
Information about the Nth PFR version (if any). N represents the number of a PFR version.
Change history
Version
Change description
HDM-2.09.00
Added this command.
Obtain service USB device configuration
Use this command to obtain service USB device configuration.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xA2 0x63 0x00 0x89
Table 218 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Required permission
Information query
Only G5 servers that support the dedicated management interface support this command.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_raw 0x36 0x0b 0xA2 0x63 0x00 0x89
a2 63 00 00 00 00
Table 219 Response field description
Data[1-3]
Data[4]
Service USB device status:
·     0—Off.
·     1—On.
Data[5]
Presence status:
·     0—Absent.
·     1—Present.
·     2Operating.
Data[6]
Auto SDS log downloading:
·     0—Off.
·     1—On.
Change history
Version
Change description
HDM-2.25
Added this command.
Set service USB device configuration
Use this command to set service USB device configuration.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x71 0x01 0x01
Table 220 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Set the service USB device status:
·     0—Off.
·     1—On.
Data[8]
Set the auto SDS log downloading status:
·     0—Off.
·     1—On.
Required permission
Maintenance
# Set service USB device configuration.
COMMAND>ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x71 0x01 0x01
0xa2 0x63 0x00
Table 221 Response field description
Data[1-3]
Change history
Version
Change description
HDM-2.25
Added this command.
Obtain Wi-Fi service enabling status
Use this command to obtain Wi-Fi service enabling status.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0xa2
Table 222 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Required permission
Information query
Only servers that support the dedicated management interface support this command.
# View Wi-Fi service enabling status.
COMMAND> ipmitool -U admin -P Password@_ -I lanplus -H 192.168.10.18 raw 0x36 0x0b 0xA2 0x63 0x00 0xa2
00
Table 223 Response field description
Data[1:3]
Data[4]
Wi-Fi service enabling status:
·     0x00Disable.
·     0x01Enable.
Change history
Version
Change description
HDM-3.18
Added this command.
Set Wi-Fi service enabling status
Use this command to set Wi-Fi service enabling status.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0xa0 0x00
Table 224 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Set Wi-Fi service status:
·     0x00Disable.
·     0x01Enable.
Required permission
Basic configuration
# Set Wi-Fi service enabling status.
COMMAND> ipmitool -U admin -P Password@_ -I lanplus -H 192.168.10.18 raw 0x36 0x09 0xA2 0x63 0x00 0xa0 0x00
a2 63 00
Table 225 Response field description
Data[1:3]
Change history
Version
Change description
HDM-3.18
Added this command.
System maintenance
Obtain the SEL storage mode
Use this command to obtain the SEL storage mode. This mode defines the way how SEL processes new events when the maximum number (3639) of SEL logs is already reached.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x7e
Table 226 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
The SEL storage mode is circular.
User role
User
Required permission
Information query
# Obtain the SEL storage mode.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0x7e
 01
Table 227 Response field description
Data[1]
SEL storage mode. Supported options:
·     00Linear mode. In this mode, no new logs will be generated and old logs will not be cleared.
·     01Circular mode. In this mode, a new log is generated and overrides the oldest log.
Set the SEL storage mode
Use this command to set the SEL storage mode.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x7f Data[3]
Table 228 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Set the SEL storage mode. Supported options:
User role
Operator
Required permission
Basic configuration
# Set the SEL storage mode.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0x7f 0x01
Change history
Version
Change description
2.25
Changed the required permission to basic configuration.
Obtain overall information about SEL logs
Use this command to obtain overall information about SEL logs.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x12 0xA2 0x63 0x00 0x1c Data[7] Data[8:9]
Table 229 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Overall information about SEL logs.
Data[8:9]
Reserved.
User role
User
Required permission
Information query
# Obtain overall information about SEL logs.
COMMAND>ipmitool -H 127.0.0.1 -I lanplus -U admin -P Password@_ raw 0x36 0x12 0xA2 0x63 0x00 0x1c 0x20 0x00 0x00
a2 63 00 20 00 18 00 18 00 01 00
Table 230 Response field description
Data[1:3]
Data[4]
Used for error checking. It must be consistent with data [7] in the command.
Data[5]
Error code. Supported options:
·     0x00The request was returned successfully.
·     0xe1The request format is invalid.
·     0xe2No SEL logs exist. This code might be returned if SEL logs have been cleared.
·     0xe3The number of SEL logs exceeded 3639. This code might be returned if 3639 logs are displayed due to Web page alignment though the actual number of logs is less than 3639.
·     0xe4The SEL log with the specified record ID does not exist.
·     0xe5The specified packet of the specified SEL log does not exist.
·     0xe6The requested SEL log has been overwritten.
·     0xe7—Failed to open the log file.
·     0xe8—Failed to verify the event log. The record ID and log entry quantity do not match.
·     0xe9—SEL log overview was not obtained.
Data[6:7]
Number of SEL logs.
Data[8-9]
Record ID of the most recent SEL log.
Data[10:11]
Record ID of the first SEL log.
If SEL logs might be generated in circular mode, the record ID of the first SEL log can be greater than the record ID of the most recent log.
Obtain information about an SEL log
Use this command to obtain information about an SEL log, including the log length and the number of packets transmitted for the log.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x12 0xA2 0x63 0x00 0x1c 0x21 Data[8] Data[9:10]
Table 231 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code. SEL-specific.
Data[7]
Information about an SEL log.
Data[8]
Reserved.
Data[9:10]
Specify the record ID of the SEL log.
User role
User
Required permission
Information query
# Obtain information about an SEL log.
COMMAND>ipmitool -H 127.0.0.1 -I lanplus -U admin -P Password@_ raw 0x36 0x12 0xA2 0x63 0x00 0x1c 0x21 0x00 0x18 0x00
a2 63 00 21 00 01 00 3d 00
Table 232 Response field description
Data[1:3]
Data[4]
Data[5]
·     0xe5—The specified packet of the specified SEL log does not exist.
Data[6]
Number of packets for the SEL log.
Data[7]
Reserved.
Data[8:9]
Length of the SEL log.
Obtain information about a packet transmitted for an SEL log
Use this command to obtain information about a packet transmitted for an SEL log.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x12 0xA2 0x63 0x00 0x1c 0x22 Data[8] Data[9:10]
Table 233 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Information about a packet transmitted for an SEL log.
Data[8]
Request of the packet transmitted for the SEL log.
Data[9:10]
User role
User
Required permission
Information query
# Obtain information about a packet transmitted for an SEL log.
COMMAND>ipmitool -H 127.0.0.1 -I lanplus -U admin -P Password@_ raw 0x36 0x12 0xA2 0x63 0x00 0x1c 0x22 0x01 0x18 0x00
a2 63 00 22 00 3d 01 18 00 01 01 b4 dd d7 5e 43
50 55 31 5f 53 74 61 74 75 73 00 00 00 00 00 70
72 6f 63 65 73 73 6f 72 07 50 72 6f 63 65 73 73
6f 72 20 70 72 65 73 65 6e 63 65 20 64 65 74 65
63 74 65 64
Table 234 Response field description
Data[1:3]
Data[4]
Data[5]
Data[6]
Length of the packet, in bytes.
Value range: 1 to 100.
Data[7]
Information about the packet for error checking.
Data[8]
Content of the packet. The maximum value of N is 100.
The content includes the following fields:
·     Record IDTwo bytes. Value range: 0x0001 to 0x0E37 (in LSB).
·     Trigger typeOne byte. Supported options:
¡     0x00—Deasserted.
¡     0x01—Asserted.
·     Severity levelFour bytes. Supported options:
¡     0Information.
¡     1Minor.
¡     2Major.
¡     3Critical.
·     TimestampFour bytes, in LSB.
·     Sensor nameVariable length. The maximum length is 16 bytes.
·     Sensor typeVariable length.
·     Time descriptionVariable length.
Obtain information about the serial port connected to the SOL
Use this command to obtain information about the serial port connected to the SOL.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x57
Table 235 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Information query
# Obtain information about the serial port connected to the SOL.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x57
0xa2 0x63 0x00 0x01
Table 236 Response field description
Data[1:3]
Data[4]
Type of the serial port connected to the SOL. Supported options:
·     0x00BIOS serial port.
·     0x01BMC serial port.
·     0x02—Serial port of an H3C-proprietary RAID controller.
·     0x03Serial port of the smart Ethernet adapter.
Change history
Version
Change description
HDM-1.11.31P03
Added this command.
Obtain information about the serial port connected to a panel
Use this command to obtain information about the serial port connected to a panel.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xa2 0x63 0x00 0x58
Table 237 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
user
# Obtain information about the serial port connected to a panel.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xa2 0x63 0x00 0x58
0xa2 0x63 0x00 0x01
Table 238 Response field description
Data[1:3]
Data[4]
·     0x01Serial port of an Ethernet adapter.
·     0x02Serial port of an H3C-proprietary RAID controller.
Change history
Version
Change description
HDM-1.11.31P03
Added this command.
Set the severity levels for SMTP alert emails
Use this command to set the severity levels for SMTP alert emails.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x78 0x01 0x1c 0x00 0x00 Data[7]
Table 239 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Specify a channel number. Supported options:
·     0x01Channel 1.
·     0x08Channel 8.
Data[4]
Subcommand code.
Data[5]
Set selector.
Data[6]
Block selector.
Data[7]
Set the severity levels. Supported options:
·     0x00Critical.
·     0x01—Minor + major + critical.
·     0x02—All.
·     0x03Major + critical.
User role
Administrator
Required permission
Basic configuration
# Set the severity levels for SMTP alert emails.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x32 0x78 0x01 0x1c 0x00 0x00 0x02
Change history
Version
Change description
HDM-3.30
Added major + critical as an option to the severity level.
HDM-1.30.12
HDM-1.30.08
Added this command.
Obtain the severity levels for SMTP alert emails
Use this command to obtain the severity levels for SMTP alert emails.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x79 Data[3] 0x1c 0x00 0x00
Table 240 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
·     0x01Channel 1.
·     0x08Channel 8.
Data[4]
Subcommand code.
Data[5]
Set selector.
Data[6]
Block selector.
User role
User
Required permission
Information query
# Obtain the severity levels for SMTP alert emails.
0x02
Table 241 Response field description
Data[1]
Severity levels. Supported options:
·     0x00Critical.
·     0x02—All.
Change history
Version
Change description
HDM-3.30
HDM-1.30.12
HDM-1.30.08
Added this command.
Obtain the address of the SMTP server
Use this command to obtain the address of the SMTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x79 Data[3] 0x01 0x00 0x00
Table 242 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
·     0x01Channel 1.
·     0x08Channel 8.
Data[4]
Subcommand code.
Data[5]
Set selector.
Data[6]
Block selector.
User role
User
Required permission
Information query
# Obtain the address of the SMTP server.
COMMAND> ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x32 0x79 0X01 0x01 0X00 0x00
73 6d 74 70 2e 73 69 74 2e 63 6f 6d 00 00 00 00
Table 243 Response field description
Data[1:128]
Address of the SMTP server.
Change history
Version
Change description
HDM-1.30.09
Added support for FQDN address to the address types of the SMTP trap server and extended the address length (including the terminator) from 46 bytes to 128 bytes.
Specify the SMTP server
Use this command to specify the SMTP server.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0x78 Data[3] 0x01 0x00 0x00 Data[7:135]
Table 244 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
·     0x01Channel 1.
·     0x08Channel 8.
Data[4]
Subcommand code.
Data[5]
Set selector.
Data[6]
Block selector.
Data[7:135]
Specify the address of the SMTP server. Supported address types:
·     IPv4 address.
·     IPv6 address.
·     FQDN address.
The maximum length of the address is 128 bytes.
User role
Administrator
Required permission
Basic configuration
# Specify the host at smtp.sit.com as SMTP server.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x32 0x78 0X01 0x01 0X00 0x00 0x73 0x6D 0x74 0x70 0x2E 0x73 0x69 0x74 0x2E 0x63 0x6F 0x6D
Change history
Version
Change description
HDM-1.30.09
Obtain syslog information
Use this command to obtain syslog information.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x09
Table 245 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
Operator
# Obtain syslog information.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x0a 0xA2 0x63 0x00 0x09
a2 63 00 01 01 01 00 00 00 00 00 00 00 00 00 00
Data[1:3]
Data[4]
Enabling status of syslog. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Data[5]
Transmission type. Supported options:
·     0x01UDP.
·     0x02TCP.
·     0x03TLS (one-way authentication).
·     0x04TLS (two-way authentication).
Data[6]
Host identifier. Supported options:
·     0x01Host name.
·     0x02System board serial number. The 0x02 field represents product SN in HDM B03.
·     0x03Asset tag.
·     0x04Product SN.
Data[7:463]
Reserved.
Change history
Version
Change description
HDM-6.15
Syslog added eight bytes to the original information for eight server addresses.
Changed the syslog server address to 48-bit.
HDM-2.75
Added product serial number as an option to the host identifier.
HDM-1.30.18SP52
HDM B05
Changed product serial number in the host identifier to system board serial number.
HDM-1.30.10
Added transmission types TLS (one-way authentication) and TLS (two-way authentication).
HDM-1.30.08
Added this command.
Configure syslog settings
Use this command to configure syslog settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x4a 0x01 Data[8] Data[9]
Table 246 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Enable syslog.
Data[8]
Specify the transmission type. Supported options:
·     0x01UDP.
·     0x02TCP.
Data[9]
Specify the host identifier. Supported options:
·     0x01Host name.
·     0x03Asset tag.
·     0x04Product SN.
User role
Administrator
Required permission
Basic configuration
# Configure syslog settings.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x09 0xA2 0x63 0x00 0x4a 0x01 0x01 0x02
0xa2 0x63 0x00
Table 247 Response field description
Data[1:3]
Change history
Version
Change description
HDM-2.75
HDM-1.30.18SP52
HDM B05
HDM-1.30.10
HDM-1.30.08
Added this command.
Obtain syslog server settings
Use this command to obtain syslog server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x0a
Table 248 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
Operator
Required permission
Information query
# Obtain syslog server settings.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x0a 0xA2 0x63 0x00 0x0a
a2 63 00 00 00 00 00 00 00 00 00 02 02 00 00 31
32 37 2e 30 2e 30 2e 31 00 00 00 00 00 00 00 00
00 00 00 00 02 02 00 00 31 32 37 2e 30 2e 30 2e
31 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 02 02 00
00 31 32 37 2e 30 2e 30 2e 31 00 00 00 00 00 00
00 00 00 00 00 00 02 02 00 00 31 32 37 2e 30 2e
30 2e 31 00 00 00 00 00 00 00 00 00 00 00 00 00
00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 02
02 00 00 31 32 37 2e 30 2e 30 2e 31 00 00 00 00
00 00 00 00 00 00 00 00 02 02 00 00 31 32 37 2e
30 2e 30 2e 31 00 00 00 00 00 00 00 00 00 00 00
00 02 02 00 00 31 32 37 2e 30 2e 30 2e 31 00 00
00 00 00 00 00 00 00 00 00 00 02 02 00 00 31 32
37 2e 30 2e 30 2e 31 00 00 00 00 00 00 00 00 00
Table 249 Response field description
Data[1:3]
Data[4]
·     0x00Disabled.
·     0x01Enabled.
Data[5:7]
Reserved.
Data[8]
Status of channel 1. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Data[9]
Types of logs to be sent. Supported options:
·     0x00No logs to send.
·     0x01Operation log.
·     0x02Event log.
·     0x03Event log + operation log.
·     0x04Security log.
·     0x05Security log + operation log.
·     0x06Security log + event log.
·     0x07All types of logs.
Data[10:11]
Reserved.
Data[12:15]
Port number of channel 1. For example, 0x02 0x02 0x00 0x00 represents port 514.
Data[16:64]
IP address of channel 1. Supported address types:
·     IPv4 address.
·     IPv6 address.
The maximum length of the IP address is 48 bytes.
For example, 0x31 0x39 0x32 0x2e 0x31 0x036 0x38 0x2e 0x31 0x2e 0x31 represents IPv4 address 192.168.1.1.
Data[65:121]
Information about channel 2, including enabling status, log types, reserved fields, port number, and IP address.
Data[122:178]
Information about channel 3, including enabling status, log types, reserved fields, port number, and IP address.
Data[179:235]
Information about channel 4, including enabling status, log types, reserved fields, port number, and IP address.
Data[236-292]
Information about channel 5, including enabling status, log types, reserved fields, port number, and IP address.
Data[293-349]
Information about channel 6, including enabling status, log types, reserved fields, port number, and IP address.
Data[350-406]
Information about channel 7, including enabling status, log types, reserved fields, port number, and IP address.
Data[407-463]
Information about channel 8, including enabling status, log types, reserved fields, port number, and IP address.
Change history
Version
Change description
HDM-6.15
HDM-2.33
Added the support for the number of syslog servers to 8.
HDM-1.30.10
HDM-1.30.08
Added this command.
Configure syslog server settings
Use this command to configure syslog server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x4b Data[7] Data[8] Data[9] Data[10:11] Data[12:15] Data[16:N]
Table 250 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the number of a channel in the range of 1 to 8.
Data[8]
Enable or disable the channel. Supported options:
·     0x00Disable.
·     0x01Enable.
Data[9]
Specify the types of logs to be sent. Supported options:
·     0x02Event log.
·     0x04Security log.
Data[10:11]
Reserved.
Data[12:15]
Specify the port number of the channel.
Data[16:N]
Specify the IP address of the channel. Supported address types:
·     IPv4 address.
·     IPv6 address.
For example, IPv4 address 127.0.0.1 in dotted decimal notation can be converted to 0x31 0x32 0x37 0x2e 0x30 0x2e 0x30 0x2e 0x31 in ASCII code format.
For example, IPv6 address fe80::aac9:8aff:fe74:40ef in hexadecimal notation can be converted to 0x66 0x65 0x38 0x30 0x3a 0x3a 0x61 0x61 0x63 0x39 0x3a 0x38 0x61 0x66 0x66 0x3a 0x66 0x65 0x37 0x34 0x3a 0x34 0x30 0x65 0x66 0x00 in ASCII code format.
The maximum length of the IPv4 or IPv6 address is 48 bytes.
The IP address entered must be appended with a 0x00 terminator at the end.
User role
Administrator
Required permission
Basic configuration
# Configure the syslog server settings. Enable channel 1 to send event log and operation log for port 514 at 127.0.0.1.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x09 0xa2 0x63 0x00 0x4b 0x01 0x01 0x03 0x00 0x00 0x02 0x02 0x00 0x00 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x33 0x30 0x2e 0x33 0x33 0x00
a2 63 00
# Configure the syslog server settings. Enable channel 1 to send event log and operation log for port 514 at fe80::aac9:8aff:fe74:40ef.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U admin -P Password@_ raw 0x36 0x09 0xa2 0x63 0x00 0x4b 0x01 0x01 0x03 0x00 0x00 0x02 0x02 0x00 0x00 0x66 0x65 0x38 0x30 0x3a 0x3a 0x61 0x61 0x63 0x39 0x3a 0x38 0x61 0x66 0x66 0x3a 0x66 0x65 0x37 0x34 0x3a 0x34 0x30 0x65 0x66 0x00
a2 63 00
Table 251 Response field description
Data[1:3]
Change history
Version
Change description
HDM-6.12
Added the IPv6 description.
HDM-6.08
Supplemented the description for Data[16-N], and add an explanation for the requirement of the terminator.
HDM-2.33
Added support for the number of syslog servers to 8.
HDM-1.30.08
Added this command.
Obtain SDR server settings
Use this command to obtain SDR server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x84
Table 252 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Required permission
Information query
# Obtain SDR server settings.
COMMAND>ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x84
a2 63 00 01 02 02 02 00 00 2c 01 00 00 31 39 32
2e 31 36 38 2e 33 34 2e 32 31 37 00 00 00 00 00
Table 253 Response field description
Data[1:3]
Data[4]
Enabling status of SDR. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Data[5]
Connection type. Supported options:
·     0x01—UDP.
·     0x02—TCP.
Data[6-9]
Port number, in little endian format. For example, 0x02 0x02 0x00 0x00 indicates port 514.
Data[10-13]
Message sending interval, in little endian format. For example, 0x2c 0x01 0x00 0x00 indicates 300 seconds.
Data[14-61]
IP address. For example, 31 39 32 2e 31 36 38 2e 33 34 2e 32 31 37 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 00 indicates IP address 192.168.34.217.
Change history
Version
Change description
HDM-2.13.00
Added this command.
Configure SDR server settings
Use this command to configure SDR server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x66 0x01 0x02 0x02 0x02 0x00 0x00 0x2c 0x01 0x00 0x00 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x33 0x34 0x2e 0x32 0x31 0x37
Table 254 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Configure SDR server status. Supported options:
·     0x00—Disable.
·     0x01—Enable.
Data[8]
·     0x01—UDP.
·     0x02—TCP.
Data[6-9]
Data[10-13]
Data[14-61]
Required permission
Basic configuration
# Configure the SDR server settings.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U root -P root raw 0x36 0x09 0xa2 0x63 0x00 0x66 0x01 0x02 0x02 0x02 0x00 0x00 0x2c 0x01 0x00 0x00 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x33 0x34 0x2e 0x32 0x31 0x37
0xa2 0x63 0x00
Table 255 Response field description
Data[1:3]
Change history
Version
Change description
HDM-2.13.00
Added this command.
Obtain serial server settings
Use this command to obtain serial server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x0d
Table 256 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
Operator
Required permission
Information query
# Obtain serial server settings.
COMMAND>ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0a 0xA2 0x63 0x00 0x0d
a2 63 00 01 02 02 02 00 00 31 39 32 2e 31 36 38
Table 257 Response field description
Data[1:3]
Data[4]
Enabling status of serial port. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Data[5]
·     0x01—UDP.
·     0x02—TCP.
Data[6-9]
Data[10-57]
Change history
Version
Change description
HDM-1.30.15P19
HDM-2.33
Added this command.
Configure serial server settings
Use this command to configure serial server settings.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xa2 0x63 0x00 0x6e 0x01 0x02 0x02 0x02 0x00 0x00 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x33 0x34 0x2e 0x32 0x31 0x37
Table 258 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
·     0x00—Disable.
·     0x01—Enable.
Data[8]
·     0x01—UDP.
·     0x02—TCP.
Data[6-9]
Data[10-57]
User role
Administrator
Required permission
Basic configuration
# Configure the serial server settings.
COMMAND>ipmitool -I lanplus -H 127.0.0.1 -U root -P root raw 0x36 0x09 0xa2 0x63 0x00 0x6e 0x01 0x02 0x02 0x02 0x00 0x00 0x31 0x39 0x32 0x2e 0x31 0x36 0x38 0x2e 0x33 0x34 0x2e 0x32 0x31 0x37
0xa2 0x63 0x00
Table 259 Response field description
Data[1:3]
Change history
Version
Change description
HDM-1.30.15P19
HDM-2.33
Added this command.
Fans
Set the fan speed mode
Use this command to set the fan speed mode to optimize its cooling, noise control, and energy efficiency performance.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x03 0xa2 0x63 0x00 0x60 speed_mode span_mode
Table 260 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Set the fan speed.
Value range: 0x00 to 0x13, where 0x00 represents the first speed mode in HDM.
Data[8]
Set the fan speed mode. Supported options:
·     0Silent mode. To specify this mode, make sure the fan speed is 0x00.
·     1Balanced mode. To specify this mode, make sure the fan speed is 0x03.
·     2Powerful mode. To specify this mode, make sure the fan speed is 0x13.
·     3Custom cooling mode.
User role
User
Required permission
Power control
By default, blade servers, except for the B5700 G5, do not support this command.
By default, non-blade servers support this command by default.
For this command to take effect, you must reload the configuration file for fans.
# Set the fan speed to 0x12.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x03 0xa2 0x63 0x00 0x60 0x12 0x03
a2 63 00 12
Table 261 Response field description
Data[1:3]
Data[4]
Fan speed.
Value range: 0x00 to 0x13.
Change history
Version
Change description
HDM-6.05
HDM-3.40
Added support for the B5700 G5 blade server.
HDM-1.30.1
Added the fan speed mode field.
Obtain the fan speed mode
Use this command to obtain the fan speed mode.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x03 0xa2 0x63 0x00 0x61
Table 262 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
By default, non-blade servers support this command.
Required permission
Information query
# Obtain the fan speed mode to custom mode 6.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x03 0xa2 0x63 0x00 0x61
a2 63 00 05 03
Table 263 Response field description
Data[1:3]
Data[4]
Fan speed.
Level range: 1 to 20.
Data[5]
Change history
Version
Change description
HDM-6.05
HDM-3.40
Reload the configuration file for fans
Use this command to reload the configuration file for fans.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x03 0x20 0x14 0x00 0x22
Table 264 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Power control
# Reload the configuration file for fans.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x03 0x20 0x14 0x00 0x22
a2 63 00
Table 265 Response field description
Data[1:3]
Change history
Version
Change description
HDM-6.05
HDM-3.40
Obtain FlyFish fan version
Use this command to obtain FlyFish fan version.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xA2 0x63 0x00 0x90 [0x00-0x09]
Table 266 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Fan ID, in the range of 0 to 9.
Required permission
Information query
R5500G5 AMD and R5500G5 Intel servers.
# Obtain FlyFish fan version.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x0b 0xA2 0x63 0x00 0x90 0x00
a2 63 00 56 31 2E 30 30 2E 31 30 00 00 00 00 00
Data[1:3]
Data[4-27]
Upgrade firmware version in string. For example, V1.00.10.
Change history
Version
Change description
HDM-2.33
Added this command.
Power supplies
Obtain the maximum number of supported power supplies
Use this command to obtain the maximum number of supported power supplies.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x00
Table 267 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Power control
# Obtain the maximum number of power supplies.
a2 63 00 04
Table 268 Response field description
Data[1:3]
Data[4]
Maximum number of power supplies supported by the system.
Obtain the presence, AC input, and DC input status of a power supply
Use this command to obtain the presence, AC input, and DC input status of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x02 UcDev
Table 269 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the ID of a power supply, starting from 0.
User role
User
Required permission
Power control
# Obtain the presence, AC input, and DC input status of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x02 0x01
a2 63 00 01 01 01
Table 270 Response field description
Data[1:3]
Data[4]
Presence status of the power supply. Supported options:
·     1Present.
·     0Absent.
Data[5]
AC input status. Supported options:
·     1Normal.
·     0Abnormal.
Data[6]
DC input status. Supported options:
·     1Normal.
·     0Abnormal or no DC input.
Obtain the cold backup state of a power supply
Use this command to obtain the cold backup state of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x03 UcDev
Table 271 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
User role
User
Required permission
Power control
# Obtain the cold backup state of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x03 0x01
a2 63 00 00
Table 272 Response field description
Data[1:3]
Data[4]
Clod backup state. Supported options:
·     0The active power supplies supply power to the server together in a balanced way.
·     1The power supply is the active power supply in cold backup.
·     2The power supply is standby power supply 1 in cold backup.
·     3The power supply is standby power supply 2 in cold backup.
·     4The power supply is standby power supply 3 in cold backup.
Configure a power supply to enter in cold backup
Use this command to configure a power supply to enter in cold backup.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x04 UcDev ucColdVal
Table 273 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Data[8]
Specify a cold backup state. Supported options:
User role
User
Required permission
Power control
# Configure a power supply to enter in cold backup.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x04 0x01 0x03
a2 63 00 03
Table 274 Response field description
Data[1:3]
Data[4]
Cold backup state. Supported options:
·     0x2The power supply is standby power supply 1 in cold backup.
·     0x3The power supply is standby power supply 2 in cold backup.
·     0x4The power supply is standby power supply 3 in cold backup.
Configure a power supply to exit from cold backup
Use this command to configure a power supply to exit from cold backup.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x05 UcDev ucColdVal
Table 275 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Manufacturer ID. This field is fixed to a2 63 00.
Data[6]
Subcommand code.
Data[7]
Data[8]
Specify a clod backup state. Supported options:
·     0x00All power supplies are in the 0x01 state.
·     0x01The active power supplies supply power to the server together with in a balanced way.
User role
User
Required permission
Power control
# Configure a power supply to exit from cold backup.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x05 0x01 0x01
a2 63 00 01
Table 276 Response field description
Data[1:3]
Data[4]
Obtain the maximum output power of a power supply
Use this command to obtain the maximum output power of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x08 UcDev
Table 277 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
User role
User
Required permission
Power control
# Obtain the maximum output power of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x08 0x01
a2 63 00 26 02
Table 278 Response field description
Data[1:3]
Data[4:5]
Maximum output power of the power supply, in W. This field is in litter endian.
Obtain the current output power of a power supply
Use this command to obtain the current output power of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x0e UcDev
Table 279 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
User role
User
Required permission
Power control
# Obtain the current output power of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x0e 0x01
a2 63 00 0a 01
Table 280 Response field description
Data[1:3]
Data[4:5]
Current output power of the power supply, in W. This field is in litter endian.
Obtain the range of the power cap value
Use this command to obtain the range of the power cap value.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x10
Table 281 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
User role
User
Required permission
Power control
# Obtain the range of the power cap value.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x10
a2 63 00 26 02 96 00
Table 282 Response field description
Data[1:3]
Data[4:5]
Maximum power cap value, in W. This field is in litter endian.
Data[6:7]
Minimum power cap value, in W. This field is in litter endian.
Obtain the power information of a power supply
Use this command to obtain the power information (including the input power, output power, input current, input voltage, and output voltage) of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0x20 0x14 0x00 0x12 UcDev
Table 283 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Specify the number of a power supply, starting from 0.
User role
User
Required permission
Power control
# Obtain the power information (including the input power, output power, input current, input voltage, and output voltage) of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x12 0x01
a2 63 00 52 00 5d 00 b5 01 e8 00 57 2f
Table 284 Response field description
Data[1:3]
Data[4:5]
Output power, in W and in little endian format.
Data[6:7]
Input power, in W and in little endian format.
Data[8:9]
Input current, in mA and in little endian format.
Data[10:11]
Input voltage, in V and in little endian format.
Data[12:13]
Output voltage, in mV and in little endian format.
Obtain the firmware revision of a power supply
Use this command to obtain the firmware revision of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x14 UcDev
Table 285 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
User role
User
Required permission
Power control
# Obtain the firmware revision of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0xa2 0x63 0x00 0x14 0x01
a2 63 00 31 4d 2e 30 30 30 39 2e 30 30 32 34 2e 30 30 32
Table 286 Response field description
Data[1:3]
Data[4:19]
Firmware information of the power supply, a string.
Obtain model match information for all presented power supplies
Use this command to obtain model match information for all presented power supplies, including whether the power supplies are H3C power supplies and are of the same model.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x01
User role
User
Required permission
Power control
# Obtain model match information for all presented power supplies.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0xa2 0x63 0x00 0x01
a2 63 00 00
Table 287 Response field description
Data[1:3]
Data[4]
Match information of all presented power supplies. Supported options:
·     00hAll the power supplies are H3C power supplies and of the same mode.
·     01hNot all the power supplies are H3C power supplies and of the same mode.
Obtain the manufacturer information of a power module
Use this command to obtain the manufacturer information of a power module.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x06 power_id
Table 288 Request field description
power_id
User role
User
Required permission
Power control
# Obtain the manufacturer information of a power module.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0xa2 0x63 0x00 0x06 0x01
a2 63 00 46 53 50 2d 47 52 4f 55 50
Table 289 Response field description
Data[1:3]
Data[4:N]
Manufacturer of the power supply, a hexadecimal value of 1 to 16 bytes. For better understanding, convert the string format to ASCII.
Obtain the model of a power supply
Use this command to obtain the model of a power supply.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x07 power_id
Table 290 Request field description
power_id
User role
User
Required permission
Power control
# Obtain the model of a power supply.
COMMAND>ipmitool -I lanplus -H 192.168.50.166 -U admin -P Password@_ raw 0x36 0x06 0xa2 0x63 0x00 0x07 0x01
a2 63 00 50 53 52 35 35 30 2d 31 32 41
Table 291 Response field description
Data[1:3]
Data[4:N]
Model of the power supply.
The maximum length of this field is 16 bytes.
This string is in hexadecimal format. For better understanding, convert the string format to ASCII.
Obtain power supply information displayed on the Web interface
Use this command to obtain power supply information displayed on the Web interface.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x0d power_id
Table 292 Request field description
power_id
User role
User
Required permission
Power control
COMMAND>ipmitool.exe  -I lanplus -H 10.99.205.177 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x0d 0x01
 a2 63 00 01 00 00 50 53 52 35 35 30 2d 31 32 41
 00 00 00 00 00 00 32 31 30 32 33 31 41 38 4b 58
 48 31 37 43 30 30 30 30 31 32 00 00 00 00 00 00
 00 00 00 00 00 00 26 02 01 01
Data[1:3]
Data[4]
Presence status. 1 represents present.
Data[5]
Health status:
·     0—Healthy.
·     1—Unhealthy.
Data[6]
Cold backup state:
·     0x00The power supply is the active power supply in cold backup.
·     0x01The power supply is the standby power supply in cold backup.
·     0xff—Invalid state.
Data[7:22]
Power supply model in ASCII format.
Data[23:70]
Power supply SN in ASCII format.
Data[71:72]
Data[73]
Power input mode:
·     0—No power input.
·     1—AC input.
·     2—High-voltage DC input.
·     3—Low-voltage DC input.
Data[74]
Whether active/standby switchover is supported by the power supply:
·     0Not supported.
·     1Supported.
Obtain GPU power capping information
Use this command to obtain GPU power capping information.
ipmitool -I connect_type -H hostname -U username -P password -N 10 raw 0x36 0x06 0xa2 0x63 0x00 0x21
Table 293 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Required permission
Power control
R5500 G5 AMD and Intel servers.
# Obtain GPU power capping information.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ -N 10 raw 0x36 0x06 0xa2 0x63 0x00 0x21
a2 63 00 01 d0 07 01 a0 0f e8 03
Table 294 Response field description
Data[1:3]
Data[4]
GPU power capping enabling status. Supported options:
·     1—Enabled.
·     0—Disabled.
Data[5-6]
GPU power cap value, in the range of 1000 W to 4000 W and in little endian format.
For example, 0xd0 0x07 represents 2000 W.
Data[7]
Policy upon power capping failure. Supported options:
·     0x01—Shutdown upon power capping failure.
·     0x00—No shutdown upon power capping failure.
Data[8-9]
Maximum power cap value, in little endian format.
Data[10-11]
Minimum power cap value, in little endian format.
Change history
Version
Change description
HDM-2.33
Added this command.
Configure GPU power capping
Use this command to configure GPU power capping.
ipmitool -I connect_type -H hostname -U username -P password -N 10 raw 0x36 0x06 0xa2 0x63 0x00 0x22 0x00 0x01 0xd0 0x07 0x01
Table 295 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
Power supply ID (PSUID, reserved).
Data[8]
Configure GPU power capping enabling status. Supported options:
·     1—Enable.
·     0—Disable.
When you disable GPU power capping, the power cap value and policy upon power capping failure remain most-recent-configured values.
Data[9-10]
Data[11]
Configure policy upon power capping failure. Supported options:
·     0x01—Shut down upon power capping failure.
·     0x00Not shut down upon power capping failure.
Required permission
Power control
# Configure GPU power capping.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ -N 10 raw 0x36 0x06 0xa2 0x63 0x00 0x22 0x00 0x01 0xd0 0x07 0x01
a2 63 0x00
Table 296 Response field description
Data[1:3]
Change history
Version
Change description
HDM-2.33
Added this command.
Obtain power information of the past day or week
Use this command to obtain power information of the past day or week.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x06 0xa2 0x63 0x00 0x23 0x00 0x00/0x01
Table 297 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3:5]
Data[6]
Subcommand code.
Data[7]
PSUID is 0x00 by default. The information obtaining does not depend on the presence of the power supply.
Data[8]
Time during which the power information is obtained. Supported options:
·     0x00—Past one day.
·     0x01—Past one week.
Required permission
Power control
# Obtain power information of the past one day or one week.
COMMAND>ipmitool -I lanplus -H 192.168.31.32 -U admin -P Password@_ raw 0x36 0x06 0x20 0x14 0x00 0x23 0x00 0x00
a2 63 00 3d 03 02 00 53 00
Table 298 Response field description
Data[1:3]
Data[4-5]
Maximum power value, in little endian format.
For example, 0xc5 0x03 represents 965 W.
Data[6-7]
Minimum power value, in little endian format.
For example, 0x01 0x00 represents 1 W.
Data[8-9]
Average power value, in little endian format.
For example, 0x40 0x02 represents 576 W.
Change history
Version
Change description
HDM-2.55
Added this command.
KVM and virtual media
Obtain the status of KVM encryption
Use this command to obtain the status of KVM encryption.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xc0 0x04
Table 299 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Status of KVM encryption.
User role
Administrator
Required permission
Information query
Product compatibility
# Obtain the status of KVM encryption.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x32 0xc0 0x04
 00
Table 300 Response field description
Data[1]
Status of KVM encryption. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Change history
Version
Change description
HDM-1.30.07
Added this command.
Set the status of KVM encryption
Use this command to set the status of KVM encryption.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xc1 0x04 Data[4]
Table 301 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Data[4]
Enable or disable KVM encryption. Supported options:
·     0x00Disable.
·     0x01Enable.
User role
Administrator
Required permission
Remote control
# Set the status of KVM encryption.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x32 0xc1 0x04 0x00
Change history
Version
Change description
HDM-1.30.07
Added this command.
Obtain the status of virtual media encryption
Use this command to obtain the status of virtual media encryption.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xca 0x0b
Table 302 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Status of virtual media encryption.
User role
Administrator
Required permission
Information query
# Obtain the status of virtual media encryption.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x32 0xca 0x0b
00
Table 303 Response field description
Data[1]
Status of virtual media encryption. Supported options:
·     0x00Disabled.
·     0x01Enabled.
Change history
Version
Change description
HDM-1.30.07
Added this command.
Set the status of virtual media encryption
Use this command to set the status of virtual media encryption.
ipmitool -I connect_type -H hostname -U username -P password raw 0x32 0xcb 0x0b Data[4]
Table 304 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Data[4]
Enable or disable virtual media encryption. Supported options:
·     0x00Disable.
·     0x01Enable.
User role
Administrator
Required permission
Remote control
# Set the status of virtual media encryption.
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x32 0xcb 0x0b 0x00
Table 305 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3]
Data[4]
·     0x00Disable.
·     0x01Enable.
Change history
Version
Change description
HDM-1.30.07
Added this command.
Obtain KVM modes
Use this command to obtain KVM modes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x0b 0xA2 0x63 0x00 0x8c
Table 306 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Required permission
Information query
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x36 0x0b 0xA2 0x63 0x00 0x8c
a2 63 0x00 0x00 0x00 0x00 0x00
Table 307 Response field description
Data[1-3]
Data[4]
KVM sharing mode. Supported options:
·     0x00—Shared.
·     0x01Dedicated.
Data[5]
KVM encryption mode. Supported options:
·     0x00Not encrypted.
Data[6]
H5 KVM sharing mode. Supported options:
·     0x00—Shared.
·     0x01Dedicated.
Data[7]
H5 KVM encryption mode. Supported options:
·     0x01Encrypted.
Change history
Version
Change description
HDM-2.25
Added this command.
Set KVM modes
Use this command to set KVM modes.
ipmitool -I connect_type -H hostname -U username -P password raw 0x36 0x09 0xA2 0x63 0x00 0x82 <KvmShareMode> <KvmSecureMode> <H5KvmShareMode> <H5KvmSecureMode>
Table 308 Request field description
Data[1]
NetFn code.
Data[2]
Command code.
Data[3-5]
Data[6]
Subcommand code.
Data[7]
Set the KVM sharing mode. Supported options:
·     0x00—Shared.
·     0x01Dedicated.
Data[8]
Set the KVM encryption mode. Supported options:
0x00—Not encrypted.
Data[9]
Set the H5 KVM sharing mode. Supported options:
·     0x00—Shared.
·     0x01Dedicated.
Data[10]
Set the H5 KVM encryption mode. Supported options:
·     0x00—Not encrypted.
·     0x01—Encrypted.
Required permission
Remote control
COMMAND>ipmitool -I lanplus -H 192.168.181.20 -U admin -P Password@_ raw 0x36 0x09 0xA2 0x63 0x00 0x82 0x00 0x00 0x00 0x00
a2 63 0x00
Table 309 Response field description
Data[1-3]
Change history
Version
Change description
HDM-2.25
Added this command.
Using IPMItool to obtain chassis status
As shown in Figure 2, the HDM of the R4900 G3 server is connected to the PC through the dedicated network port. Make sure the HDM IP address can communicate with the PC IP address.
·     HDM management software information:
¡     IP address: 172.16.18.69
¡     Administrator account: admin
¡     Administrator password: Password@_
·     PC IP address : 172.16.18.1
Figure 2 Network diagram
Using IPMItool software
1.     Download the IPMItool tool that is compatible with Windows OS such as IPMItool v1.8.18 on the client.
2.     Access Windows cmd.
Figure 3 Windows cmd
Using IPMItool to obtain chassis information
Execute the ipmitool -I lanplus -H 172.16.18.69 -U admin -P Password@_ chassis status command to obtain chassis status information.
Figure 4 Obtaining chassis status information