04-HH3C-LswMSTP-MIB | 165.85 KB |
HH3C-LswMSTP-MIB
About this MIB
Spanning tree protocols eliminate loops by selectively blocking ports to prune the loop structure into a loop-free tree structure.
This MIB defines private MIB objects for MSTP.
MIB file name
hh3c-splat-mstp.mib
Notifications
hh3cPortMstiStateForwarding
Basic information
OID |
Event |
Type |
Severity |
Recovery notification |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.1 |
A port transits to the forwarding state. |
Informational |
Warning |
OFF |
Notification triggers
This notification might be generated when a port transits to the forwarding state in the following situations:
The network topology changes after a new link is added.
The network topology changes after a port comes up or goes down.
System impact
The network topology changes.
Status control
ON
CLI: Use the stp port-log command.
OFF
CLI: Use the undo stp port-log command.
Object
OID (object name) |
Index |
Type |
Value range |
1.3.6.1.4.1.25506.8.35.14.19.1.1 (hh3cdot1sInstanceID) |
Instance ID. |
hh3cdot1sInstanceID |
INTEGER |
0..4094 |
1.3.6.1.4.1.25506.8.35.14.20.1.1 (hh3cdot1sMstiPortIndex) |
Port index. |
hh3cdot1sInstanceID hh3cdot1sMstiPortIndex |
INTEGER |
1..65535 |
Recommended action
To resolve this issue:
1.Check for link failures after the network topology becomes stable.
2.Identify whether the spanning tree feature is enabled on a new physical link.
3.Identify whether a spanning tree-enabled port in the network topology has come up or gone down.
4.Collect alarm information and configuration data, and then contact H3C Support for help.
hh3cPortMstiStateDiscarding
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.2 |
A port transits to the discarding state. |
Informational |
Warning |
OFF |
This notification might be generated when a port transits to the discarding state in the following situations:
The network topology is recalculated after a new link is added.
System impact
Status control
ON
OFF
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Port index. |
INTEGER |
1..65535 |
Recommended action
1.Identify whether a new physical link is added in the spanning tree network after the network topology becomes stable.
2.Collect alarm information and configuration data, and then contact H3C Support for help.
hh3cBridgeLostRootPrimary
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.3 |
The device loses its root bridge role after another device is elected as root bridge. |
Informational |
Warning |
ON |
This notification might be generated when the device loses its root bridge role after another device is elected as root bridge in the following situations:
A new link is added to the network topology.
The priority of a device changes in the network topology.
System impact
The network topology might not be presented as expected.
Status control
This notification cannot be disabled.
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Recommended action
1.Identify whether a new physical link is added in the spanning tree network.
2.Identify whether a priority change operation has been performed and verify that the operation is correct.
3.Collect alarm information and configuration data, and then contact H3C Support for help.
hh3cPortMstiRootGuarded
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.4 |
A root guard-enabled port receives a configuration BPDU with a higher priority. |
Informational |
Warning |
OFF |
This notification might be generated when the following events occur:
A root guard-enabled port receives a configuration BPDU with a priority higher than the current bridge.
The priority of a device in the network topology changes.
System impact
Status control
ON
CLI: Use the stp root-protection command.
MIB: Set hh3cdot1sMstiPortRootGuard to true(1).
OFF
MIB: Set hh3cdot1sMstiPortRootGuard to false(2).
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Port index. |
INTEGER |
1..65535 |
Recommended action
hh3cPortMstiBpduGuarded
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.5 |
A BPDU guard-enabled edge port receives configuration BPDUs. |
Informational |
Warning |
OFF |
This notification is generated when a BPDU guard-enabled edge port receives configuration BPDUs.
System impact
The user network connected to the port is interrupted.
Status control
ON
CLI: Use the stp bpdu-protection command.
MIB: Set hh3cdot1sMstBpduGuard to true(1).
OFF
MIB: Set hh3cdot1sMstBpduGuard to false(2).
Object
OID (object name) |
Index |
Type |
Value range |
1.3.6.1.2.1.17.2.15.1.1 (dot1dStpPort) |
Port index. |
dot1dStpPort |
INTEGER |
1..65535 |
Recommended action
● Verify that the downstream device is an endpoint device.
● Check for possible attacks from other devices.
hh3cPortMstiLoopGuarded
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.6 |
An alternate port or root port does not receive a BPDU upon BPDU reception timeout. |
Informational |
Warning |
OFF |
This notification might be generated when an alternate port or root port does not receive a BPDU upon BPDU reception timeout in the following situations:
The peer port does not send a BPDU to the local end before the BPDU reception time expires. The spanning tree feature might be disabled on the peer port.
The link connected to the peer end is congested. Verify that traffic can be forwarded correctly.
System impact
The alternate port or root port cannot forward service traffic.
Status control
ON
CLI: Use the stp loop-protection command.
MIB: Set hh3cdot1sMstiPortLoopGuard to true(1).
OFF
MIB: Set hh3cdot1sMstiPortLoopGuard to false(2).
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Port index. |
INTEGER |
1..65535 |
Recommended action
● Verify that the spanning tree status of the upstream device is correct.
hh3cMstiNewRoot
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.7 |
A new root bridge is elected. |
Informational |
Warning |
OFF |
This notification might be generated when a new root bridge is elected in the following situations:
The current bridge joins a new network topology.
The priority of the current bridge increases.
The original root bridge fails.
The priority of the original root bridge decreases.
System impact
The network topology changes. Service traffic loss might occur.
Status control
ON
CLI: Use the snmp trap enable stp new-root command.
OFF
CLI: Use the undo snmp trap enable stp new-root command.
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
1.3.6.1.4.1.25506.8.35.14.19.1.4 (hh3cdot1sMstiDesignedRoot) |
Root bridge information. |
BridgeId |
BridgeId |
Recommended action
● Verify that the bridge priority configuration on devices is correct.
hh3cMstiTopologyChange
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.9 |
The network topology changes after the spanning tree state of ports changes. |
Informational |
Warning |
ON |
This notification might be generated when the spanning tree state changes of ports cause network topology changes in the following situations:
The network topology changes after the priority of a device changes.
Network topology change causes discarding port change after the cost value or priority of a port is changed.
System impact
Status control
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Recommended action
2.Identify whether a spanning tree-enabled port has come up or gone down in the network topology.
hh3cPortMstiLostEdge
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.10 |
An edge port receives BPDUs. |
Informational |
Warning |
ON |
This notification is generated when an edge port receives BPDUs and becomes a non-edge port.
System impact
The network topology might change.
Status control
Object
OID (object name) |
Index |
Type |
Value range |
Port number. |
INTEGER |
1..65535 |
1.3.6.1.2.1.2.2.1.2 (ifDescr) |
Interface name. |
ifIndex |
OCTET STRING |
OCTET STRING(0..255) |
Instance ID. |
INTEGER |
0..4094 |
Recommended action
1.Verify that the peer network attached to the edge port has changed and identify whether the received BPDUs are malicious attack packets.
hh3cMstiTcGuarded
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.11 |
The number of TC-BPDUs received by the device exceeds the upper threshold. |
Informational |
Warning |
ON |
This notification is generated when the number of TC-BPDUs received by the device exceeds the upper threshold within a TC-BPDU protection period.
System impact
The excessive TC-BPDUs do not immediately cause MAC and ARP entry deletion. The network topology does not change immediately.
Status control
ON
CLI: Use the stp tc-protection command.
OFF
CLI: Use the undo stp tc-protection command.
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
Recommended action
1.Identify whether the network topology is flapping.
2.Identify whether malicious attacks exist.
hh3cMstiProTcGuarded
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.12 |
Informational |
Warning |
ON |
System impact
Status control
ON
OFF
Object
OID (object name) |
Index |
Type |
Value range |
Instance ID. |
INTEGER |
0..4094 |
1.3.6.1.4.1.25506.8.35.14.22.1 (hh3cMstiTcGuardVal) |
Upper threshold |
N/A |
Integer32 |
Integer32 (1..255) |
Recommended action
hh3cPortPvstPvidInconsistent
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.17 |
PVID inconsistency. |
Informational |
Warning |
N/A (N/A) |
OFF |
This notification is generated when an interface receives a BPDU with a different PVID.
System impact
PVST calculation errors might occur.
Status control
ON
CLI: Use the stp ignore-pvid-inconsistency command.
OFF
CLI: Use the undo stp ignore-pvid-inconsistency command.
Object
OID (object name) |
Index |
Type |
Value range |
1.3.6.1.4.1.25506.8.35.14.22.2 (hh3cPvstPvid) |
PVID. |
N/A |
Integer32 |
Integer32 (1..4094) |
1.3.6.1.4.1.25506.8.35.14.22.3 (hh3cPvstPvidInPdu) |
PVID in packets. |
N/A |
Integer32 |
Interface name. |
ifIndex |
OCTET STRING |
OCTET STRING (0..255) |
Recommended action
1.Identify whether different PVIDs are required on two connected ports:
- If yes, use the stp ignore-pvid-inconsistency command to disable inconsistent PVID protection.
- If no, modify the different PVIDs to be the same.
hh3cPortPvstPortTypeInconsistent
Basic information
OID |
Event |
Type |
Severity |
Default status |
1.3.6.1.4.1.25506.8.35.14.0.18 |
Port type inconsistency. |
Informational |
Warning |
N/A (N/A) |
OFF |
This notification is generated when an access port receives a PVST BPDU from a trunk or hybrid port.
System impact
Status control
Object
OID (object name) |
Index |
Type |
Value range |
1.3.6.1.4.1.25506.8.35.14.22.6 (hh3cMstiVlanID) |
VLAN ID. |
N/A |
Integer32 |
Interface name. |
ifIndex |
OCTET STRING |
Recommended action
1.Identify whether the port types of the two ends are the same:
- If yes, proceed to step 2.
- If no, modify the port types to be the same. If the issue persists, proceed to step 2.
2.Collect alarm information, log messages, and configuration data, and then contact H3C Support for help.