- 17-Network Management and Monitoring Configuration Guide
- 02-NQA configuration
- 03-NTP configuration
- 04-PoE configuration
- 05-SNMP configuration
- 06-RMON configuration
- 07-Event MIB configuration
- 08-NETCONF configuration
- 09-SmartMC configuration
- 10-CWMP configuration
- 11-EAA configuration
- 12-Process monitoring and maintenance configuration
- 13-Sampler configuration
- 14-Mirroring configuration
- 15-NetStream configuration
- 16-IPv6 NetStream configuration
- 17-sFlow configuration
- 18-Performance management configuration
- 19-Flow log configuration
- 20-Information center configuration
- 21-Packet capture configuration
- 22-Cloud connection configuration
04-PoE configuration | 167.36 KB |
Restrictions: Hardware compatibility with PoE
Restrictions and guidelines: PoE configuration
PoE configuration tasks at a glance
Prerequisites for configuring PoE
Enabling PoE for a PSE (multi-PSE device)
Enabling nonstandard PD detection
Configuring a PD disconnection detection mode (multi-PSE device)
Configuring the maximum PSE power (multi-PSE device)
Configuring the maximum PI power
Configuring the PoE priority policy
Configuring the PSE priority policy (multi-PSE device)
Configuring the PI priority policy
Configuring PSE power monitoring
Configuring a PI by using a PoE profile
Upgrading PSE firmware in service
Display and maintenance commands for PoE
Failure to set the priority of a PI to critical
Failure to apply a PoE profile to a PI
Configuring PoE
About PoE
Power over Ethernet (PoE) enables a network device to supply power to terminals over twisted pair cables.
PoE system
As shown in Figure 1, a PoE system includes the following elements:
· PoE power supply—A PoE power supply provides power for the entire PoE system.
· PSE—A power sourcing equipment (PSE) supplies power to PDs. PSE devices are classified into single-PSE devices and multiple-PSE devices.
¡ A single-PSE device has only one PSE firmware.
¡ A multiple-PSE device has multiple PSEs. A multiple-PSE device uses PSE IDs to identify different PSEs. To view the mapping between the ID and slot number of a PSE, execute the display poe device command.
· PI—A power interface (PI) is a PoE-capable Ethernet interface on a PSE.
· PD—A powered device (PD) receives power from a PSE. PDs include IP telephones, APs, portable chargers, POS terminals, and Web cameras. You can also connect a PD to a redundant power source for reliability.
Protocols and standards
· 802.3af-2003, IEEE Standard for Information Technology - Telecommunications and Information Exchange Between Systems - Local and Metropolitan Area Networks - Specific Requirements - Part 3: Carrier Sense Multiple Access with Collision Detection (CSMA/CD) Access Method and Physical Layer Specifications - Data Terminal Equipment (DTE) Power Via Media Dependent Interface (MDI)
· 802.3at-2009, IEEE Standard for Information technology-- Local and metropolitan area networks-- Specific requirements-- Part 3: CSMA/CD Access Method and Physical Layer Specifications Amendment 3: Data Terminal Equipment (DTE) Power via the Media Dependent Interface (MDI) Enhancements
The following matrixes show the support of hardware platforms for PoE:
Hardware |
PoE compatibility |
Remarks |
MSR810-10-PoE, MSR3610-I-IG, MSR3610-IE-IG |
Yes |
For interface module compatibility with devices, see the interface module manual. The following device models support interface module installation: · MSR3620 · MSR3640 · MSR3660 · MSR3620-10-WiNet · MSR3620-WiNet · MSR3660-WiNet |
Device models installed with one of the following interface modules: · SIC-4FSWP · DSIC-9FSWP · HMIM-24GSWP |
Yes |
Hardware |
PoE compatibility |
MSR2630-XS |
No |
MSR3600-28-XS |
No |
MSR3610-XS |
No |
MSR3620-XS |
No |
MSR3610-I-XS |
No |
MSR3610-IE-XS |
No |
Hardware |
PoE compatibility |
MSR810-LM-GL |
No |
MSR810-W-LM-GL |
No |
MSR830-6EI-GL |
No |
MSR830-10EI-GL |
No |
MSR830-6HI-GL |
No |
MSR830-10HI-GL |
No |
MSR2600-6-X1-GL |
No |
MSR3600-28-SI-GL |
No |
IMPORTANT: The MSR810-10-PoE, MSR3610-I-IG, and MSR3610-IE-IG routers are single-PSE devices and support only commands available for single-PSE devices. |
You can configure a PI through either of the following ways:
· Configure the settings directly on the PI.
· Configure a PoE profile and apply it to the PI. If you apply a PoE profile to multiple PIs, these PIs have the same PoE features. If you connect a PD to another PI, you can apply the PoE profile of the original PI to the new PI. This method relieves the task of configuring PoE on the new PI.
You can only use one way to configure a parameter for a PI. To use the other way to reconfigure a parameter, you must first remove the original configuration.
You must use the same configuration method for the poe max-power max-power and poe priority { critical | high | low } commands.
To configure PoE, perform the following tasks:
1. Enabling PoE
a. Enabling PoE for a PSE (multi-PSE device)
2. (Optional.) Configuring PD detection
¡ Enabling nonstandard PD detection
¡ Configuring a PD disconnection detection mode (multi-PSE device)
3. (Optional.) Configuring the PoE power
¡ Configuring the maximum PSE power (multi-PSE device)
¡ Configuring the maximum PI power
4. (Optional.) Configuring the PoE priority policy
¡ Configuring the PSE priority policy (multi-PSE device)
¡ Configuring the PI priority policy
5. (Optional.) Configuring PSE power monitoring
6. (Optional.) Upgrading PSE firmware in service
To use a PoE profile to enable PoE and configure the priority and maximum power for a PI, see "Configuring a PI by using a PoE profile."
Before you configure PoE, make sure the PoE power supply and PSEs are operating correctly.
Enabling PoE
After you enable PoE for a PSE, the system reserves and supplies power to the PSE.
Follow these guidelines to determine whether you can enable PoE on a PSE:
· You can enable PoE for a PSE if the PSE will not result in PoE power overload. PoE overload occurs when the sum of the power consumption of all PSEs exceeds the maximum power of the PoE power supply.
· If the PSE will result in PoE power overload, you can enable PoE for the PSE only when the PSE priority policy is enabled on the PSE. For more information about the PSE priority policy, see "Configuring the PSE priority policy."
1. Enter system view.
2. Enable PoE for a PSE.
poe enable pse pse-id
By default, PoE is disabled on a PSE.
To enable PoE for multiple PSEs that support dynamic power allocation, do not enable PoE for the second PSE until power is dynamically allocated to the first PoE-enabled PSE.
Enabling PoE for a PI
After you enable PoE for a PI, the PI supplies power to the connected PD if the PI will not result in PSE power overload. PSE overload occurs when the sum of the power consumption of all PIs exceeds the maximum power of the PSE. For information about the maximum PSE power, see "Configuring the maximum PSE power."
If the PI will result in PSE power overload, the following restrictions apply:
· If the PoE priority policy is not enabled on the PI, the PI does not supply power to the connected PD.
· If the PoE priority policy is enabled on the PI, whether the PD will be powered depends on the priority of the PI.
For more information about the PI priority policy, see "Configuring the PI priority policy."
Power can be transmitted over a twisted pair cable in the following modes:
· Signal pair mode—Signal pairs (on pins 1, 2, 3, and 6) of the twisted pair cable are used for power transmission.
· Spare pair mode—Spare pairs (on pins 4, 5, 7, and 8) of the twisted pair cable are used for power transmission.
The device supports power transmission only over signal pairs.
A PI can supply power to a PD only when the PI and PD use the same power transmission mode. If the PI and PD use different power transmission modes, a converter is required.
2. Enter PI view.
3. Enable PoE for the PI.
poe enable
By default, PoE is disabled on a PI.
4. (Optional.) Configure a description for the PD connected to the PI.
poe pd-description text
By default, no description is configured for the PD connected to the PI.
PDs are classified into standard PDs and nonstandard PDs. Standard PDs are compliant with IEEE 802.3af and IEEE 802.3at. A PSE supplies power to a nonstandard PD only after nonstandard PD detection is enabled.
2. Enable nonstandard PD detection.
Single-PSE device:
poe legacy enable
Multi-PSE device:
poe legacy enable pse pse-id
By default, nonstandard PD detection is disabled for a PSE.
CAUTION: If you change the PD disconnection detection mode when the device is running, the connected PDs are powered off. Be aware of the impact of this operation before you perform it. |
A PSE detects PD disconnection in AC mode or DC mode. The AC mode uses less power than the DC mode.
2. Configure a PD disconnection detection mode.
poe disconnect { ac | dc }
The default PD disconnection detection mode is AC mode.
The maximum power of a PSE is the maximum power that the PSE can provide to all its attached PDs.
To avoid the PoE power overload situation, make sure the total power of all PSEs is less than the maximum PoE power.
The maximum power of the PSE must be greater than or equal to the total maximum power of all its critical PIs to guarantee these PIs power.
2. Configure the maximum power for a PSE.
poe pse pse-id max-power max-power
By default, the maximum power of a PSE is 37 W.
The maximum PI power is the maximum power that a PI can provide to the connected PD. If the PD requires more power than the maximum PI power, the PI does not supply power to the PD.
2. Enter PI view.
3. Configure the maximum power for the PI.
By default, the maximum PI power is 15400 milliwatts.
The PSE priority policy performs priority-based power allocation in PoE power overload situations. The priority levels of a PSE are critical, high, and low in descending order. If the PoE power is sufficient, you do not need to enable the PSE priority policy.
When PoE power overload occurs, the system supplies power to PSEs as follows:
· If you have not enabled the PSE priority policy, the PoE self-protection mechanism is triggered.
· If you have enabled the PSE priority policy, the system supplies power to PSEs as follows:
¡ If a PSE being powered causes PoE power overload, the system stops supplying power to the PSE.
¡ If a new PSE causes PoE power overload, the system supplies power to PSEs in priority descending order. If the new PSE has the same priority as a PSE being powered, the PSE being powered takes precedence. If multiple PSEs being powered have the same priority, the one with the smallest PSE ID takes precedence.
Before you configure a PSE with critical priority, make sure the remaining power from the maximum PoE power minus maximum powers of PSEs with critical priority is greater than the maximum power of the PSE. This restriction does not apply to PSEs with high and low priorities.
Configuration for PSEs whose power is preempted remains unchanged.
2. Enable the PSE priority policy.
poe pse-policy priority
By default, the PSE priority policy is disabled.
3. (Optional.) Configure a priority for a PSE.
poe priority { critical | high | low } pse pse-id
By default, the priority for a PSE is low.
The PI priority policy enables the PSE to perform priority-based power allocation to PIs when PSE power overload occurs. The priority levels for PIs are critical, high, and low in descending order.
When PSE power overload occurs, the PSE supplies power to PDs as follows:
· If the PI priority policy is disabled, the PSE supplies power to PDs depending on whether you have configured the maximum PSE power.
¡ If you have configured the maximum PSE power, the PSE does not supply power to the newly-added or existing PD that causes PSE power overload.
¡ If you have not configured the maximum PSE power, the PoE self-protection mechanism is triggered. The PSE stops supplying power to all PDs.
· If the PI priority policy is enabled, the PSE supplies power to PDs as follows:
¡ If a PD being powered causes PSE power overload, the PSE stops supplying power to the PD.
¡ If a newly-added PD causes PSE power overload, the PSE supplies power to PDs in priority descending order of the PIs to which they are connected.
¡ If the newly-added PD and a PD being powered have the same priority, the PD being powered takes precedence.
¡ If multiple PIs being powered have the same priority, the PIs with smaller IDs takes precedence.
Before you configure a PI with critical priority, make sure the remaining power from the maximum PSE power minus the maximum powers of the existing PIs with critical priority is greater than maximum power of the PI.
Configuration for a PI whose power is preempted remains unchanged.
2. Enable the PI priority policy.
poe pd-policy priority
By default, the PI priority policy is disabled.
3. Enter PI view.
4. (Optional.) Configure a priority for the PI.
By default, the priority for a PI is low.
Configuring PoE monitoring
The system monitors PSE power utilization and sends notification messages when PSE power utilization exceeds or drops below the threshold. If PSE power utilization crosses the threshold multiple times in succession, the system sends notification messages only for the first crossing. For more information about the notification message, see "Configuring SNMP."
2. Configure a power alarm threshold for a PSE.
Single-PSE device:
poe utilization-threshold value
Multi-PSE device:
poe utilization-threshold value pse pse-id
By default, the power alarm threshold for a PSE is 80%.
To modify a PoE profile applied on a PI, first remove the PoE profile from the PI.
You can configure a PI either on the PI or by using a PoE profile. The poe max-power max-power and poe priority { critical | high | low } commands must be configured using the same method.
Configuring a PoE profile
2. Create a PoE profile and enter its view.
poe-profile profile-name [ index ]
By default, no PoE profiles exist.
3. Enable PoE.
poe enable
By default, PoE is disabled.
4. (Optional.) Configure the maximum PI power.
5. (Optional.) Configure a PI priority.
The default priority is low.
This command takes effect only after the PI priority policy is enabled.
Applying a PoE profile
You can apply a PoE profile to multiple PIs in system view or a single PI in PI view. If you perform the operation in both views for the same PI, the most recent operation takes effect.
You can apply only one PoE profile to a PI.
Applying a PoE profile in system view
2. Apply a PoE profile to PIs.
apply poe-profile { index index | name profile-name } interface interface-range
By default, a PoE profile is not applied to a PI.
Applying a PoE profile in PI view
2. Enter PI view.
3. Apply the PoE profile to the interface.
You can upgrade the PSE firmware in service in the following modes:
· Refresh mode—Updates the PSE firmware without deleting it. You can use the refresh mode in most cases.
· Full mode—Deletes the current PSE firmware and reloads a new one. Use the full mode if the PSE firmware is damaged and you cannot execute any PoE commands.
If the PSE firmware upgrade fails because of interruption such as a device reboot, you can restart the device and upgrade it in full mode again. After the upgrade, restart the device manually for the new PSE firmware to take effect.
2. Upgrade the PSE firmware in service.
Single-PSE device:
poe update { full | refresh } filename
Multi-PSE device:
poe update { full | refresh } filename [ pse pse-id ]
Task |
Command |
Display general PSE information. |
In standalone mode: display poe device In IRF mode: display poe device [ slot slot-number ] |
Display the power supplying information for the specified PI. |
display poe interface [ interface-type interface-number ] |
Display power information for PIs. |
display poe interface power [ interface-type interface-number ] |
Display power information for the PoE power supply and all PSEs. |
In standalone mode: display poe power-usage In IRF mode: display poe power-usage [ slot slot-number ] |
Display detailed PSE information. |
Single-PSE device: display poe pse Multi-PSE device: display poe pse [ pse-id ] |
Display the power supplying information for all PIs on a PSE. |
Multi-PSE device: display poe pse pse-id interface |
Display power information for all PIs on a PSE. |
Multi-PSE device: display poe pse pse-id interface power |
Display all information about the PoE profile. |
display poe-profile [ index index | name profile-name ] |
Display all information about the PoE profile applied to the specified PI. |
display poe-profile interface interface-type interface-number |
PoE configuration examples
Example: Configuring PoE
As shown in Figure 2, the device has PSE 4 and PSE 7, in slot 1 and 2, respectively. Configure PoE to meet the following requirements:
· PSE 4 has a maximum power of 400 watts.
· The device supplies power to IP phones and APs.
· The device supplies power preferentially to IP phone B when power overload occurs.
· Power supplied to AP B does not exceed 9000 milliwatts.
# Enable the PI priority policy.
<PSE> system-view
[PSE] poe pd-policy priority
# Enable PoE for the PSE.
<PSE> system-view
[PSE] poe enable pse 10
[PSE] poe enable pse 16
# Set the maximum power of PSE 10 to 400 watts.
[PSE] poe pse 10 max-power 400
# Enable PoE on GigabitEthernet 1/0/1 and GigabitEthernet 2/0/1.
[PSE] interface gigabitethernet 1/0/1
[PSE-GigabitEthernet1/0/1] poe enable
[PSE-GigabitEthernet1/0/1] quit
[PSE] interface gigabitethernet 2/0/1
[PSE-GigabitEthernet2/0/1] poe enable
[PSE-GigabitEthernet2/0/1] quit
# Enable PoE on GigabitEthernet 1/0/2, and set its power priority to critical.
[PSE] interface gigabitethernet 1/0/2
[PSE-GigabitEthernet1/0/2] poe enable
[PSE-GigabitEthernet1/0/2] poe priority critical
[PSE-GigabitEthernet1/0/2] quit
# Enable PoE on GigabitEthernet 2/0/2, and set its maximum power to 9000 milliwatts.
[PSE] interface gigabitethernet 2/0/2
[PSE-GigabitEthernet2/0/2] poe enable
[PSE-GigabitEthernet2/0/2] poe max-power 9000
# Verify that the device is supplying power correctly to the IP phones and APs, and the IP phones and APs are operating correctly.
Troubleshooting PoE
Symptom
Power supply priority configuration for a PI failed.
Solution
To resolve the issue:
1. Identify whether the remaining guaranteed power of the PSE is lower than the maximum power of the PI. If it is, increase the maximum PSE power or reduce the maximum power of the PI.
2. Identify whether the priority has been configured through other methods. If the priority has been configured, remove the configuration.
3. If the issue persists, contact H3C Support.
Symptom
PoE profile application for a PI failed.
Solution
1. Identify whether some settings in the PoE profile have been configured. If they have been configured, remove the configuration.
2. Identify whether the settings in the PoE profile meet the requirements of the PI. If they do not, modify the settings in the PoE profile.
3. Identify whether another PoE profile is already applied to the PI. If it is, remove the application.
4. If the issue persists, contact H3C Support.