09-High Availability Command Reference
HomeSupportReference GuidesCommand ReferencesH3C S5130S-HI[EI]&S5110V2&S3100V3-EI Switch Series Command References-R612x-6W10309-High Availability Command Reference
05-ERPS commands
05-ERPS commands 92.54 KB
ERPS commands
control-vlan
Use control-vlan to configure the control VLAN for an ERPS instance.
Use undo control-vlan to restore the default.
control-vlan vlan-id
undo control-vlan
An ERPS instance does not have control VLANs.
ERPS instance view
vlan-id: Specifies the control VLAN by its ID in the range of 2 to 4094.
The control VLAN must be a VLAN that has not been created on the device.
# Configure VLAN 100 as the control VLAN for instance 1 of ERPS ring 1.
[Sysname] erps ring 1
[Sysname-erps-ring1] instance 1
[Sysname-erps-ring1-inst1] control-vlan 100
instance
display erps
Use display erps to display brief ERPS ring information.
display erps
# Display brief ERPS ring information.
<Sysname> display erps
ERPS protocol status: Enabled
ERPS tcn-propagation: Enabled
Flags: R -- RPL, F -- Faulty, B -- Blocked,
       FS -- Forced switch, MS -- Manual switch
Ring   Instance   NodeRole   NodeState    Port0     Port1    Status
1      1          Owner      Idle         R,B                Enabled
1      2          Normal     Idle                            Disabled
2      1          Owner      Idle         R,B                Enabled
2      2          Normal     Idle                            Disabled
ERPS state:
·         Enabled—Globally enabled.
·         Disabled—Globally disabled.
State of the flush packet transparent transmission feature:
Ring
ERPS ring ID.
Instance
ERPS instance ID.
NodeRole
Node type:
·         Owner.
·         Neighbor.
·         Interconnection.
·         Normal.
NodeState
Node state:
·         Idle—The ERPS ring enters the idle state after initialization.
·         Protection—The ERPS ring enters the protection state when a link fails.
·         MS—Manual switching mode.
·         FS—Forced switching mode.
·         Pending—Transient mode between any two states.
·         -—ERPS is disabled for the ERPS instance or disabled globally.
Port0
State of port 0:
·         R—The port is an RPL port.
·         B—The port is blocked.
·         F—The port is unavailable and the link for the port is faulty.
·         FS—The port is in FS mode.
·         MS—The port is in MS mode.
·         -—The port is not an ERPS ring member port.
If this field is blank, the port is not in any of the previous states.
Port1
State of port 1:
Status
State of the ERPS instance:
·         Enabled.
·         Disabled.
display erps detail
Use display erps detail to display detailed ERPS ring information.
display erps detail ring ring-id [ instance instance-id ]
ring ring-id: Specifies an ERPS ring by its ID in the range of 1 to 255.
instance instance-id: Specifies an ERPS instance by its ID in the range of 1 to 64. If you do not specify this option, this command displays detailed information about all instances for the ERPS ring.
# Display detailed information about instance 1 of ERPS ring 1.
<Sysname> display erps detail ring 1 instance 1
Ring ID                : 1
Port0                  : GigabitEthernet1/0/1
Port1                  : GigabitEthernet1/0/2
Subring                : Yes
Default MAC            : Yes
Instance ID            : 1
Node role              : Owner
Node state             : Idle
Connect (ring/instance): (1/2), (2/3)
Control VLAN           : 100
Protected VLAN         : Reference-instance 0 to 2
Guard timer            : 500 ms
Hold-off timer         : 1 sec
WTR timer              : 5 min
Revertive operation    : Non-revertive
Enable status          : Yes, Active Status : Yes
R-APS level            : 1
Port                   PortRole               PortStatus
Port0                  RPL                    Block
Port1                  Non-RPL                Up
# Display detailed information about all instances of ERPS ring 1.
Ring ID               : 1
Subring               : Yes
Default MAC           : Yes
Instance ID           : 1
Node role             : Owner
Node state            : Idle
Connect(ring/instance): (1/2), (2/3)
Control VLAN          : 100
WTR timer             : 5 min
R-APS level           : 1
Port0                 RPL                    Block
Port1                 Non-RPL                Up
Instance ID           : 2
Node role             : Neighbor
Node state            : Idle
Control VLAN          : 200
Protected VLAN        : Reference-instance 3
Wtr timer             : 5 min
R-APS level           : 1
Port0                 RPL                    Block
Port1                 Non-RPL                Up
Port0
ERPS ring member port 0.
Port1
ERPS ring member port 1.
Subring
ERPS subring status:
·         Yes—The ring is a subring.
·         No—The ring is not a subring.
Default MAC
Default MAC address status:
·         Yes—The last byte is 1 in the destination MAC address of R-APS packets.
·         No—The last byte is the ring ID in the destination MAC address of R-APS packets.
Node role
Node type:
·         Owner.
·         Neighbor.
·         Interconnection.
·         Normal.
Node state
Node state:
·         Idle—The ERPS ring enters the idle status after initialization.
Ring or instance associated with the ERPS instance.
Control VLAN
Control VLAN of the ERPS instance.
Protected VLAN
List of VLANs protected by the ERPS instance, which are represented by MSTIs.
To view the mapping between MSTIs and VLANs, use the display stp region-configuration command.
Guard timer
Guard timer in milliseconds.
Hold-off timer
Hold-off timer in milliseconds.
WTR timer
WTR timer in minutes.
Revertive operation
Revertive mode:
·         Non-revertive.
·         Revertive.
Enable status
ERPS status for the instance:
·         Yes—Enabled.
·         No—Disabled.
Active Status
Global ERPS status and ERPS status for the instance:
·         Yes—Enabled.
·         No—Disabled.
R-APS level
Level of the R-APS packets.
Port
PortRole
Port role:
·         RPL—The port is an RPL port.
·         Non-RPL—The port is not an RPL port.
Port Status
Port status:
·         Block—The port is blocked.
·         Up—The link is up.
·         Down—The link is down.
display erps statistics
Use display erps statistics to display ERPS packet statistics.
display erps statistics ring-id [ instance instance-id ]
instance instance-id: Specifies an ERPS instance by its ID in the range of 1 to 64. If you do not specify this option, this command displays packet statistics for all instances of the ERPS ring.
# Display packet statistics for all instances of ERPS ring 1.
<Sysname> display erps statistics ring 1
  Statistics for ERPS ring 1 instance 1:
  R-APS      Port0(Tx/Rx)             Port1(Tx/Rx)
  NR         1/1                      1/1
  NR,RB      0/1                      0/1
  SF         1/0                      1/0
  MS         0/0                      0/0
  FS         0/0                      0/0
  Total      2/2                      2/2
  Statistics for ERPS ring 1 instance 2:
  NR         1/1                      1/1
  NR,RB      0/1                      0/1
  SF         1/0                      1/0
  MS         0/0                      0/0
  FS         0/0                      0/0
  Total      2/2                      2/2
R-APS
Packet type.
Port0(Tx/Rx)
Packet statistics for port 0:
·         Tx—Transmitted packets.
·         Rx—Received packets.
Port1(Tx/Rx)
Packet statistics for port 1:
erps clear
Use erps clear to remove the MS mode and FS mode settings for an ERPS ring.
erps clear ring-id instance instance-id
After you configure this command, the owner node can ignore the WTR timer and immediately switch traffic to the recovered link upon link recovery.
This command also switches an ERPS ring in non-revertive mode to revertive mode.
# Remove the MS mode and FS mode settings for instance 1 on ERPS ring 1.
[Sysname] erps clear ring 1 instance 1
erps enable
Use erps enable to enable ERPS globally.
Use undo erps enable to restore the default.
erps enable
undo erps enable
ERPS is disabled globally.
# Enable ERPS.
[Sysname] erps enable
erps ring
Use erps ring to create an ERPS ring.
Use undo erps ring to delete an ERPS ring.
erps ring ring-id
undo erps ring ring-id
No ERPS rings exist.
Usage guideline
To delete an ERPS ring successfully, delete all ERPS instances on the ring first.
# Create ERPS ring 1.
instance
erps switch
Use erps switch to configure the switching mode for an ERPS ring.
erps switch { force | manual } ring ring-id instance instance-id { port0 | port1 }
force: Configures the forced switching mode.
manual: Configures the manual switching mode.
port0: Specifies the ERPS ring member port 0.
port1: Specifies the ERPS ring member port 1.
# Configure the forced switching mode for port 1 of instance 1 on ERPS ring 1.
[Sysname] erps switch force ring 1 instance 1 port0
erps tcn-propagation
Use erps tcn-propagation to enable flush packet transparent transmission for an interconnection node.
Use undo erps tcn-propagation to restore the default.
Flush packet transparent transmission is disabled for an interconnection node.
Usage guideline
This command must be used together with the sub-ring connect command.
# Enable flush packet transparent transmission for the interconnection node.
[Sysname] erps tcn-propagation
sub-ring connect
instance
Use instance to create an instance for an ERPS ring.
Use undo instance to delete an instance from an ERPS ring.
undo instance instance-id
An ERPS ring does not have instances.
ERPS ring view
You can create multiple instances for an ERPS ring. Each instance has its own protected VLAN, control VLAN, and RPL owner. Each instance maintains its own state machine and data. You can locate an ERPS instance by its ring ID and VLAN ID.
# Create instance 1 for ERPS ring 1.
erps ring
instance enable
Use instance enable to enable ERPS for an ERPS instance.
Use undo instance enable to disable ERPS for an ERPS instance.
instance enable
ERPS is disabled for ERPS instances.
ERPS instance view
# Create ERPS instance 1 and enable ERPS for the instance.
[Sysname-erps-ring1-inst1] protected-vlan reference-instance 0 1 2
[Sysname-erps-ring1-inst1] instance enable
instance
node-role
Use node-role to configure the role for an ERPS node.
Use undo node-role to restore the default.
node-role { { owner | neighbor } rpl | interconnection } { port0 | port1 }
undo node-role
An ERPS node is a normal node.
ERPS instance view
owner: Configures the owner node.
neighbor: Configures the neighbor node.
interconnection: Configures the interconnection node for connecting the major ring and subring.
For the owner node to work correctly, you must configure only one owner node for an ERPS ring.
You can configure an interconnection node only for a subring.
# Configure instance 1 of ERPS ring 1 as an RPL owner node and configure port 0 as an RPL port.
[Sysname-erps-ring1-inst1] node-role owner rpl port0
port erps track
Use port erps track to associate an ERPS ring member port with a track entry.
Use undo port erps track to remove the association between an ERPS ring member port and a track entry.
port erps ring ring-id instance instance-id track track-entry-index
undo port erps ring ring-id instance instance-id track
An ERPS ring member port is not associated with track entries.
Interface view
track-entry-index: Specifies a track entry by its ID in the range of 1 to 1024. For more information about specifying the track entry ID, see the track cfd command in "Track commands."
An ERPS ring member port collaborates with link detection protocols through track entries. ERPS supports only the CC feature of CFD to implement link detection.
# Associate a track entry with GigabitEthernet 1/0/1 on the RPL owner node in instance 1 of ERPS ring 1.
[Sysname-erps-ring1] port0 interface gigabitethernet 1/0/1
[Sysname-erps-ring1-inst1] quit
[Sysname-erps-ring1] quit
[Sysname-GigabitEthernet1/0/1] port erps ring 1 instance 1 track 3
track cfd
port0
Use port0 to specify the first member port for an ERPS ring.
Use undo port0 to restore the default.
port0 interface interface-type interface-number
undo port0
No member ports exist in an ERPS ring.
ERPS ring view
interface interface-type interface-number: Specifies a Layer 2 Ethernet interface or a Layer 2 aggregate interface by its type and number.
Do not assign an interface to both an aggregation group and an ERPS ring. If you do so, the interface does not take effect on the ERPS ring and cannot be displayed by using the display erps detail command.
# Specify GigabitEthernet 1/0/1 as the first member port for ERPS ring 1.
port1
Use port1 to specify the second member port for an ERPS ring.
Use undo port1 to restore the default.
port1 interface interface-type interface-number
undo port1
ERPS ring view
# Specify GigabitEthernet 1/0/2 as the second member port for ERPS ring 1.
[Sysname-erps-ring1] port1 interface gigabitethernet 1/0/2
protected-vlan
Use protected-vlan to configure protected VLANs for an ERPS instance.
Use undo protected-vlan to delete protected VLANs for an ERPS instance.
undo protected-vlan [ reference-instance instance-id-list ]
No protected VLANs exist in an ERPS instance.
ERPS instance view
instance-id-list: Specifies a space-separated list of up to 10 MSTI items. Each item specifies an MSTI or a range of MSTIs in the form of instance-id1 to instance-id2. The value for instance-id2 must be greater than or equal to the value for instance-id1. The value range for the instance-id argument is 0 to 4094. The value 0 indicates CIST. You can use the display stp region-configuration command to display the VLAN-to-instance mappings. In PVST mode, the system automatically maps VLANs to MSTIs.
If you do not specify the reference-instance instance-id-list option, the undo protected-vlan command deletes all mappings between MSTIs and VLANs in the ERPS instance. The protected VLANs change if the mappings between the MSTIs and VLANs change.
# Configure the protected VLANs for instance 1 of ERPS ring 1.
r-aps level
Use r-aps level to configure the level for R-APS packets.
Use undo r-aps level to restore the default.
r-aps level level-value
undo r-aps level
The R-APS packet level is 7.
ERPS instance view
level-value: Specifies the R-APS packet level in the range of 0 to 7.
The R-APS packet level must be the same for all nodes in an instance of an ERPS ring.
# Configure the R-APS packet level as 1 for instance 1 of ERPS ring 1.
[Sysname-erps-ring1-inst1] r-aps level 1
r-aps ring-mac
Use r-aps ring-mac to configure the ring ID as the last byte of the destination MAC address for R-APS packets.
Use undo r-aps ring-mac to restore the default.
r-aps ring-mac
undo r-aps ring-mac
The last byte of the destination MAC address is 1 for the R-APS packets.
ERPS ring view
# Configure the ID of ERPS ring 2 as the last byte of the destination MAC address for R-APS packets.
[Sysname] erps ring 2
[Sysname-erps-ring2] r-aps ring-mac
reset erps statistics
Use reset erps statistics to clear ERPS packet statistics.
reset erps statistics ring ring-id [ instance instance-id ]
instance instance-id: Specifies an ERPS instance by its ID in the range of 1 to 64. If you do not specify this option, this command clears packet statistics for all instances of the ERPS ring.
# Clear packet statistics for instance 1 of ERPS ring 1.
<Sysname> reset erps statistics ring 1 instance 1
revertive-operation
Use revertive-operation non-revertive to set the non-revertive mode for an ERPS ring.
Use undo revertive-operation to restore the default.
An ERPS ring operates in revertive mode.
ERPS instance view
In non-revertive mode, an owner node does not perform any operations when receiving NR packets. You can use the erps clear command to restore the revertive mode.
# Set the non-revertive mode for instance 1 of ERPS ring 1.
[Sysname-erps-ring1-inst1] revertive-operation non-revertive
ring-type sub-ring
Use ring-type sub-ring to configure the ERPS ring as a subring.
Use undo ring-type sub-ring to restore the default.
ring-type sub-ring
undo ring-type
An ERPS ring is a major ring.
ERPS ring view
# Configure ERPS ring 1 as a subring.
[Sysname-erps-ring1] ring-type sub-ring
sub-ring connect
Use sub-ring connect to associate the subring with an ERPS ring.
Use undo sub-ring connect to remove the association.
sub-ring connect ring ring-id instance instance-id
undo sub-ring connect ring ring-id instance instance-id
A subring is not associated with ERPS rings.
ERPS instance view
# Configure ERPS ring 1 as a subring for instance 1, and associate the subring with ERPS ring 2.
[Sysname-erps-ring2] instance 1
[Sysname-erps-ring2] quit
[Sysname-erps-ring1-inst1] sub-ring connect ring 2 instance 1
ring-type sub-ring
timer guard
Use timer guard to set the guard timer for an ERPS instance.
Use undo timer guard to restore the default.
timer guard guard-value
undo timer guard
The guard timer is 500 milliseconds for an ERPS instance.
ERPS instance view
guard-value: Specifies the guard timer in the range of 0 to 2000 milliseconds and in step of 10.
The guard timer starts when the link recovers. The system processes only the flush packets before the guard timer expires. The guard timer prevents SF messages from impacting the network.
# Set the guard timer to 30 milliseconds for instance 1 of ERPS ring 1.
[Sysname-erps-ring1-inst1] timer guard 30
timer hold-off
Use timer hold-off to set the hold-off timer for an ERPS instance.
Use undo timer hold-off to restore the default.
timer hold-off hold-off-value
undo timer hold-off
The hold-off timer is 0 milliseconds for an ERPS instance.
ERPS instance view
hold-off-value: Specifies the hold-off timer in the range of 0 to 10000 milliseconds and in step of 100.
The hold-off timer starts when the port detects a link fault. If the link fault persists when the hold-off timer expires, the port reports the link fault. The hold-off timer delays the fault report time and might impact the link recovery performance.
# Set the hold-off timer to 300 milliseconds for instance 1 of ERPS ring 1.
[Sysname-erps-ring1-inst1] timer hold-off 300
timer wtr
Use timer wtr to set the WTR timer for an ERPS instance.
Use undo timer wtr to restore the default.
timer wtr wtr-value
undo timer wtr
The WTR timer is 5 minutes for an ERPS instance.
ERPS instance view
wtr-value: Specifies the WTR timer in the range of 1 to 12 minutes and in step of 1.
This timer prevents intermittent link failures from impacting the network.
# Set the WTR timer to 3 minutes for instance 1 of ERPS ring 1.
[Sysname-erps-ring1-inst1] timer wtr 3