H3C S12500X-AF Switch Series Hardware Reference-6W102
HomeSupportSwitchesS12500X-AF SeriesProduct LiteratureHardware Information & SpecificationsH3C S12500X-AF Switch Series Hardware Reference-6W102
01-Chassis Views and Technical Specifications
01-Chassis Views and Technical Specifications 1.76 MB
Chassis views and technical specifications
The H3C S12500X-AF Switch Series is a set of core switches designed for cloud computing data centers. It uses the advanced CLOS orthogonal switching fabric architecture to deliver the industry-leading switching performance, highest port density, richest cloud computing features, and highest availability.
Unless otherwise stated, MPUs, LPUs, and switching fabric modules are collectively referred to as "cards" in this document.
Chassis views
Figure 1 S12516X-AF
Figure 2 S12512X-AF
Figure 3 S12508X-AF
Figure 4 S12504X-AF
Figure 5 S12502X-AF
Figure 6 S12501X-AF
Chassis components
The device has an MPU section, service module section, power module section, fan tray section, and fabric module section. The following figure uses the S12516X-AF for illustration.
Figure 7 Front and rear views of the S12516X-AF switch
(1) MPU section
(2) LPU section
(3) Power module section
(4) Fan tray section
(5) Switching fabric module section
Table 1 Description for the switch sections
Section
Location identification
Installation description
MPU section
Pink color is used for you to identify the MPU installation location.
·     S12516X-AF, S12512X-AF, and S12508X-AF—The ejector lever pillow blocks on the MPU slots are pink marked. The MPU ejector levers are also pink marked to suggest the corresponding installation location.
·     S12504X-AF and S12502X-AF—The MPU slot numbers on the chassis are pink marked. The module identifiers on the MPUs are also pink marked to suggest the corresponding installation location.
The MPU section of an S12504X-AF switch is located below the LPU section.
An S12501X-AF switch has a built-in MPU, and does not require installing an MPU separately. An S12500X-AF switch has two MPU slots. You can install one MPU, or two MPUs for redundancy.
LPU section
The ejector lever pillow blocks on LPU slots are purple marked. The LPU edges and ejector levers are also purple marked to suggest the corresponding installation location.
·     S12516X-AF switch—16 LPU slots.
·     S12512X-AF switch—12 LPU slots.
·     S12508X-AF switch—8 LPU slots.
·     S12504X-AF switch—4 LPU slots.
·     S12502X-AF switch—2 LPU slots.
·     S12501X-AF switch—1 LPU slot.
N/A
·     S12516X-AF switch—16 power module slots, with eight on each side of the chassis rear.
·     S12512X-AF switch—12 power module slots, with six on each side of the chassis rear.
·     S12508X-AF switch—8 power module slots, with four on each side of the chassis rear.
·     S12504X-AF switch4 power module slots, with two on each side of the chassis rear.
·     S12502X-AF switch4 power module slots, with two on each side of the chassis rear.
·     S12501X-AF switch—2 power module slots on the right of the rear panel.
The switch supports N+N and N+1 power redundancy.
Fan tray section
The fan tray section is located at the rear of the chassis.
Each fan tray on the S12500X-AF switch series, except for the S12501X-AF and S12502X-AF, covers three switching fabric module slots. The S12501X-AF and S12502X-AF switches are integrated with a switching fabric module and do not provide switching fabric module slots.
The S12501X-AF switch has three fan tray slots FAN1, FAN2, and FAN3. To ensure correct operation, install three fan trays for the switch.
The other S12500X-AF switch models each have two fan tray slots FAN1 and FAN2. The switch can operate correctly with one fan tray. As a best practice, install fan trays in both slots for redundancy and to reduce noises.
The switching fabric module slots are behind fan trays. Each fan tray covers three switching fabric module slots.
The S12501X-AF and S12502X-AF switches have a built-in switching fabric module, and do not require installing a switching fabric module separately.
The other models come with all switching fabric module slots empty. Purchase two to six switching fabric modules for the switch. Purchase and install filler panels in the empty switching fabric module slots.
The S12516X-AF, S12512X-AF, S12508X-AF, and S12504X-AF switches use slots 18 to 23, 14 to 19, 10 to 15, and 6 to 11 for switching fabric modules, respectively.
·     To use an LSXM1TGS24FX1 LPU, the three lowest-numbered switching fabric module slots take precedence over other slots for module installation. For an LSXM1TGS24FX1 LPU to start up correctly, install a minimum of one switching fabric modules in the three lowest-numbered switching fabric module slots.
·     To use an LSXM1TGS48C2HB1, LSXM1TGS48HB1, LSXM1TGS48HF1, LSXM1CGQ6QGHB1, LSXM1CGQ6QGHF1, or LSXM1TGS24QGMODHB1 LPU, the three highest-numbered switching fabric module slots take precedence over other slots for module installation. For the LPU to start up correctly, install a minimum of one switching fabric modules in the three highest-numbered switching fabric module slots.
·     To use an LSXM1QGS24HB1, LSXM1QGS36HB1, LSXM1TGS48QGHA1, or LSXM1TGS24CGMODHD1 LPU, the four highest-numbered switching fabric module slots take precedence over other slots for module installation. For the LPU to start up correctly, install a minimum of one switching fabric modules in the four highest-numbered switching fabric module slots.
Before you remove a switching fabric module, remove the fan tray that covers it.
No cards, fan trays, or power modules are provided with the switch. Order them as required. For the cards, fan trays, and power modules available for the switch, see "FRUs and compatibility matrixes."
Table 2 describes the slot arrangements for FRUs.
Table 2 FRU slots on each switch model
Model
MPU
LPU
Power module
Fan tray
S12516X-AF
Slots 0 and 1
Slots 2 to 17
Slots 18 to 23
Slots 18 to 20 are covered by FAN 1. Slots 21 to 23 are covered by FAN 2.
PWR 1 to PWR 16
FAN 1 and FAN 2
S12512X-AF
Slots 0 and 1
Slots 2 to 13
Slots 14 to 19
Slots 14 to 16 are covered by FAN 1. Slots 17 to 19 are covered by FAN 2.
PWR 1 to PWR 12
FAN 1 and FAN 2
S12508X-AF
Slots 0 and 1
Slots 2 to 9
Slots 10 to 15
Slots 10 to 12 are covered by FAN 1. Slots 13 to 15 are covered by FAN 2.
PWR 1 to PWR 8
FAN 1 and FAN 2
S12504X-AF
Slots 4 and 5
Slots 0 to 3
Slots 6 to 11
Slots 6 to 8 are covered by FAN 1. Slots 9 to 11 are covered by FAN 2.
PWR 1 to PWR 4
FAN 1 and FAN 2
S12502X-AF
Slots 0 and 1
Slots 2 and 3
N/A
PWR 1 to PWR 4
FAN 1 and FAN 2
S12501X-AF
N/A
Slot 0
N/A
PWR 1 and PWR 2
FAN 1 to FAN 3
Technical specifications
Weights and dimensions
The switch uses modular design. Its weight includes the chassis (mounting brackets and filler panels included) and its FRUs.
Table 3 Chassis weights and dimensions
Model
Weight
Height
Width
Depth
S12516X-AF
86.1 kg (189.81 lb)
931 mm (36.65 in)/21 RU
440 mm (17.32 in)
857 mm (33.74 in)
S12512X-AF
75.4 kg (166.23 lb)
753 mm (29.65 in)/17 RU
440 mm (17.32 in)
857 mm (33.74 in)
S12508X-AF
47.0 kg (103.62 lb)
531 mm (20.91 in)/12 RU
440 mm (17.32 in)
857 mm (33.74 in)
S12504X-AF
36.0 kg (79.37 lb)
264 mm (10.39 in)/6 RU
440 mm (17.32 in)
857 mm (33.74 in)
S12502X-AF
23.8 kg (52.47 lb)
133 mm (5.24 in)/3 RU
440 mm (17.32 in)
895 mm (35.24 in)
S12501X-AF
16.0 kg (35.27 lb)
88 mm (3.47 in)/2 RU
440 mm (17.32 in)
856 mm (33.70 in)
·     Rack height is measured in RUs. One RU is 44.45 mm (1.75 in).
·     Table 3 lists dimensions for the switch, excluding the mounting brackets, cable management brackets, cards, and power modules.
Table 4 Card weights and dimensions
Model
Weight
Height
Width
Depth
LSXM1SUPA1
5.9 kg (13.01 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1SUPB1
6.0 kg (13.23 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1SUPH1
4.9 kg (10.80 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM2SUPT1
4.9 kg (10.80 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1SUP02B1
2.0 kg (4.41 lb)
22.5 mm (0.89 in)
193.0 mm (7.60 in)
364.3 mm (14.34 in)
LSXM1SUP04B1
2.8 kg (6.17 lb)
39.8 mm (1.57 in)
200.5 mm (7.89 in)
411.0 mm (16.18 in)
LSXM1SUP04H1
2.8 kg (6.17 lb)
39.8 mm (1.57 in)
200.5 mm (7.89 in)
411.0 mm (16.18 in)
LSXM1X86SUPE1
10 kg (22.05 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1SUPE1
6.2 kg (13.67 lb)
43.7 mm (1.72 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1SFF16A1
7.0 kg (15.43 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
289.2 mm (11.39 in)
LSXM1SFF16B1
7.5 kg (16.53 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
289.2 mm (11.39 in)
LSXM1SFF16C1
8.5 kg (18.74 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
289.2 mm (11.39 in)
LSXM1SFF08A1
4.3 kg (9.48 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
289.2 mm (11.39 in)
LSXM1SFF08B1
4.8 kg (10.58 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
289.2 mm (11.39 in)
LSXM1SFF04B1
2.7 kg (5.95 lb)
39.8 mm (1.57 in)
243.0 mm (9.57 in)
289.2 mm (11.39 in)
LSXM1SFH16C1
9.1 kg (20.06 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
278.4 mm (10.96 in)
LSXM2SFH16C1
7.9 kg (17.42 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
278.4 mm (10.96 in)
LSXM1SFH16E1
9.7 kg (21.38 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
278.4 mm (10.96 in)
LSXM1SFH12C1
6.4 kg (14.11 lb)
39.8 mm (1.57 in)
675.2 mm (26.58 in)
278.4 mm (10.96 in)
LSXM1SFH12D1
7.5 kg (16.53 lb)
39.8 mm (1.57 in)
675.2 mm (26.58 in)
278.4 mm (10.96 in)
LSXM1SFH08C1
4.6 kg (10.14 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
278.4 mm (10.96 in)
LSXM1SFH08D1
4.9 kg (10.80 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
278.4 mm (10.96 in)
LSXM1SFH08E1
5.2 kg (11.46 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
278.4 mm (10.96 in)
LSXM1SFH04D1
2.8 kg (6.17 lb)
39.8 mm (1.57 in)
243.0 mm (9.57 in)
278.4 mm (10.96 in)
LSXM1SFT16E1
9.7 kg (21.38 lb)
39.8 mm (1.57 in)
853.0 mm (33.58 in)
278.4 mm (10.96 in)
LSXM2SFT08E1
5.2 kg (11.46 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
278.4 mm (10.96 in)
LSXM1SFK08F1
5.8 kg (12.79 lb)
39.8 mm (1.57 in)
453.0 mm (17.83 in)
278.4 mm (10.96 in)
LSXM1QGS24FE1
6.4 kg (14.11 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1TGS48FE1
5.7 kg (12.57 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1TGS48FX1
5.4 kg (11.90 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1TGS24FX1
4.7 kg (10.36 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1TGW48FX1
5.7 kg (12.57 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1GP48FX1
5.2 kg (11.46 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1QGS36FX1
6.5 kg (14.33 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM3QGS36FX1
8.3 kg (18.30 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1QGS24FX1
5.9 kg (13.00 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1QGS12FX1
5.5 kg (12.13 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1CGX8FX1
5.8 kg (12.79 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1CGP12FX1
9.2 kg (20.28 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
511.7 mm (20.15 in)
LSXM1CGP8FX1
6.2 kg (13.67 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1TGT48FX1
5.8 kg (12.79 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1GT48FX1
5.1 kg (11.24 lb)
39.8 mm (1.57 in)
399.2 mm (15.72 in)
511.9 mm (20.15 in)
LSXM1CGQ18QGHB1
9.4 kg (20.72 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ18QGHF1
9.7 kg (21.38 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ6QGHB1
6.6 kg (14.55 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ6QGHF1
6.9 kg (15.21 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ36HB1
11.1 kg (24.47 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ36HF1
12.3 kg (27.12 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ48HB1
12.1 kg (16.68 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1QGS48HB1
9.2 kg (20.28 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1QGS36HB1
7.8 kg (17.20 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1QGS24HB1
7.6 kg (16.75 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS48HB1
7.2 kg (15.87 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS48HF1
7.3 kg (16.09 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS48C2HB1
7.1 kg (15.65 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS48QGHA1
6.4 kg (14.11 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS24QGMODHB1
6.6 kg (14.55 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1TGS24CGMODHD1
6.9 kg (15.21 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ36TD1
9.5 kg (20.94 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM2TGS48HB2
7.5 kg (16.53 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM2CGQ18QGHB2
8.3 kg (18.30 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CGQ48KB1
9.3 kg (20.50 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
LSXM1CDQ24KB1
10 kg (22.05 lb)
50.0 mm (1.97 in)
432.6 mm (17.03 in)
519.8 mm (20.46 in)
Card dimensions are expressed as follows:
·     Height—Height of the front panel of the card.
·     Width—Width of the front panel of the card.
·     Depth—Depth from the front panel of the card to the connector (Including the connector, but excluding the ejector levers and captive screws).
Table 5 Weights and dimensions of the switching fabric module slot filler panels
Model
Weight
Height
Width
Depth
Switching fabric module slot filler panel for the S12516X-AF switch
2.8 kg (6.17 lb)
39.8 mm (1.57 in)
853.6 mm (33.60 in)
136.0 mm (5.35 in)
Switching fabric module slot filler panel for the S12512X-AF switch
2.0 kg (4.41 lb)
39.8 mm (1.57 in)
675.2 mm (26.58 in)
278.4 mm (10.96 in)
Switching fabric module slot filler panel for the S12508X-AF switch
1.6 kg (3.53 lb)
40.0 mm (1.57 in)
453.0 mm (17.83 in)
133.0 mm (5.24 in)
Switching fabric module slot filler panel for the S12504X-AF switch
0.9 kg (1.98 lb)
40.0 mm (1.57 in)
243.0 mm (9.57 in)
136.0 mm (5.35 in)
Table 6 Power module weights and dimensions
Model
Weight
Height
Width
Depth
PSR1800-56A
1.6 kg (3.52 lb)
41.0 mm (1.61 in)
82.6 mm (3.25 in)
297.7 mm (11.72 in)
PSR1800-56D
2.0 kg (4.40 lb)
41.0 mm (1.61 in)
82.6 mm (3.25 in)
297.7 mm (11.72 in)
PSR2400-54A
1.9 kg (4.19 lb)
41.0 mm (1.61 in)
100.0 mm (3.93 in)
332.0 mm (13.07 in)
PSR2400-54D
1.9 kg (4.19 lb)
41.0 mm (1.61 in)
100.0 mm (3.93 in)
332.0 mm (13.07 in)
PSR3000-54A
2.1 kg (4.63 lb)
41.0 mm (1.61 in)
100.0 mm (3.93 in)
332.0 mm (13.07 in)
PSR3000-54AHD
2.1 kg (4.63 lb)
41.0 mm (1.61 in)
100.0 mm (3.93 in)
332.0 mm (13.07 in)
Table 7 Fan tray weights and dimensions
Model
Weight
Height
Width
Depth
S12516X-AF fan tray—LSXM116XFAN
6.7 kg (14.77 lb)
144.0 mm (5.67 in)
927.0 mm (36.50 in)
183.0 mm (7.20 in)
S12516X-AF fan tray —LSXM116XFANH
8.4 kg (18.52 lb)
144.0 mm (5.67 in)
927.0 mm (36.50 in)
183.0 mm (7.20 in)
S12512X-AF fan tray—LSXM112XFAN
6.3 kg (13.89 lb)
144.0 mm (5.67 in)
750 mm (29.53 in)
183.0 mm (7.20 in)
S12512X-AF fan tray—LSXM112XFANH
6.3 kg (13.89 lb)
144.0 mm (5.67 in)
750 mm (29.53 in)
183.0 mm (7.20 in)
S12508X-AF fan tray—LSXM108XFAN
3.8 kg (8.38 lb)
144.0 mm (5.67 in)
527.0 mm (20.75 in)
183.0 mm (7.20 in)
S12508X-AF fan tray—LSXM108XFANH
4.4 kg (9.70 lb)
144.0 mm (5.67 in)
527.0 mm (20.75 in)
183.0 mm (7.20 in)
S12504X-AF fan tray—LSXM104XFAN
1.8 kg (3.97 lb)
144.0 mm (5.67 in)
263.0 mm (10.35 in)
97.0 mm (3.82 in)
S12504X-AF fan tray—LSXM104XFANH
3.0 kg (6.61 lb)
144.0 mm (5.67 in)
263.0 mm (10.35 in)
136.0 mm (5.35 in)
S12502X-AF fan tray—LSXM102XFAN
1.0 kg (2.20 lb)
123.0 mm (4.84 in)
214.0 mm (8.43 in)
123.0 mm (4.84 in)
S12502X-AF fan tray—LSXM102XFANH
1.6 kg (3.52 lb)
123.0 mm (4.84 in)
214.0 mm (8.43 in)
123.0 mm (4.84 in)
S12501X-AF fan tray— FAN-80B-1-A
0.9 kg (1.98 lb)
84.5 mm (3.33 in)
87 mm (3.43 in)
240.3 mm (9.46 in)
_Ref453143801 provides dimensions for a laid down fan tray. The fan tray depth includes the depth of the fan tray handle.
Table 8 Interface module adapter weights and dimensions
Model
Weight
Height
Width
Depth
LSXM1IMA
3.3 kg (7.28 lb)
50.0 mm (1.97 in)
433.0 mm (17.05 in)
479.0 mm (18.86 in)
Module power consumption and system power consumption
Card power consumption
The power consumption of the cards depends on the card model and state. Table 9 shows the power consumption for different card models.
·     The static power consumption of a card refers to the power consumed by the card when the card is running but all ports on the card are down and when no transceiver module is available on the optical interface of the card.
·     The dynamic power consumption of a card refers to the power consumed by the card when all the ports on the card are link up and send broadcasts.
Table 9 Card power consumption
Model
Minimum static power consumption
Maximum dynamic power consumption
LSXM1SUPA1
46 W
55 W
LSXM1SUPB1
39 W
50 W
LSXM1SUPH1
39 W
50 W
LSXM1SUPE1
52 W
70 W
LSXM2SUPT1
28 W
34 W
LSXM1SUP02B1
20 W
21 W
LSXM1SUP04B1
46 W
50 W
LSXM1SUP04H1
46 W
50 W
LSXM1X86SUPE1
107 W
183 W
LSXM1SFF16A1
138 W
161 W
LSXM1SFF16B1
195 W
240 W
LSXM1SFF16C1
251 W
310 W
LSXM1SFF08A1
71 W
90 W
LSXM1SFF08B1
129 W
165 W
LSXM1SFF04B1
69 W
85 W
LSXM1SFH16C1
286 W
415 W
LSXM2SFH16C1
194 W
308 W
LSXM1SFH16E1
487 W
816 W
LSXM1SFH12C1
162 W
241 W
LSXM1SFH12D1
270 W
405 W
LSXM1SFH08C1
84 W
135 W
LSXM1SFH08D1
159 W
255 W
LSXM1SFH08E1
267 W
328 W
LSXM1SFK08F1
203 W
335 W
LSXM1SFH04D1
86 W
140 W
LSXM1SFT16E1
419 W
691 W
LSXM2SFT08E1
265 W
446 W
LSXM1QGS24FE1
310 W
505 W
LSXM1TGS48FE1
160 W
260 W
LSXM1TGS48FX1
160 W
275 W
LSXM1TGS24FX1
86 W
145 W
LSXM1TGW48FX1
174 W
279 W
LSXM1GP48FX1
115 W
165 W
LSXM1QGS36FX1
396 W
645 W
LSXM3QGS36FX1
396 W
645 W
LSXM1QGS24FX1
270 W
465 W
LSXM1QGS12FX1
143 W
225 W
LSXM1CGX8FX1
286 W
335 W
LSXM1CGP12FX1
388 W
610 W
LSXM1CGP8FX1
253 W
410 W
LSXM1TGT48FX1
160 W
345 W
LSXM1GT48FX1
122 W
145 W
LSXM1CGQ18QGHB1
361 W
565 W
LSXM1CGQ18QGHF1
286 W
530 W
LSXM1CGQ6QGHB1
145 W
204 W
LSXM1CGQ6QGHF1
145 W
204 W
LSXM1CGQ48HB1
792 W
1290 W
LSXM1CGQ36HB1
608 W
935 W
LSXM1CGQ36HF1
585 W
1100 W
LSXM1QGS48HB1
360 W
605 W
LSXM1QGS36HB1
264 W
414 W
LSXM1QGS24HB1
214 W
375 W
LSXM1TGS48HB1
163 W
275 W
LSXM1TGS48HF1
156 W
258 W
LSXM1TGS48C2HB1
163 W
275 W
LSXM1TGS48QGHA1
87 W
287 W
LSXM1TGS24QGMODHB1
125 W
296 W
LSXM1TGS24CGMODHD1
147 W
236 W
LSXM1CGQ36TD1
590 W
1050 W
LSXM2TGS48HB2
111 W
210 W
LSXM2CGQ18QGHB2
256 W
525 W
LSXM1CGQ48KB1
395 W
765 W
LSXM1CDQ24KB1
469 W
1020 W
IMPORTANT
IMPORTANT:
High-performance fan trays are required when the switch uses the LSXM1CGQ18QGHF1, LSXM1CGQ48HB1, LSXM1CGQ36HB1, LSXM1CGQ36HF1, LSXM1CGQ36TD1, LSXM1CGQ48KB1, or LSXM1CDQ24KB1 cards. For information about high-performance fan trays, see "Fan trays".
Fan tray power consumption
The switch uses fan trays that can automatically adjust the fan speed based on the device temperature. The power consumed by a fan tray depends on the fan speed.
Table 10 Fan tray power consumption
Switch model
Fan tray model
Minimum fan tray power consumption
Maximum fan tray power consumption
S12516X-AF
LSXM116XFAN
33 W
793 W
LSXM116XFANH
187 W
2570 W
S12512X-AF
LSXM112XFAN
28 W
660 W
LSXM112XFANH
124 W
1709 W
S12508X-AF
LSXM108XFAN
17 W
395 W
LSXM108XFANH
86 W
1239 W
S12504X-AF
LSXM104XFAN
14 W
255 W
LSXM104XFANH
19.4 W
588 W
S12502X-AF
LSXM102XFAN
10 W
144 W
LSXM102XFANH
17 W
269 W
S12501X-AF
FAN-80B-1-A
5 W
87 W
System power consumption
The system power consumption of the switch depends on the type and number of cards and the fan tray power consumption.
·     The minimum system power consumption is the total static power consumption of all cards plus the minimum fan tray power consumption.
·     The maximum system power consumption is the total dynamic power consumption of all cards plus the maximum fan tray power consumption.
For example, for an S12516X-AF switch that has two LSXM1SUPB1 MPUs, two LSXM1QGS24FX1 LPUs, six LSXM1SFF16B1 switching fabric modules, and two LSXM116XFAN fan trays, the minimum system power consumption of the switch is 2 × 39 + 2 × 270 + 6 × 195 + 2 × 33 = 1854 W. The maximum system power consumption of the switch is 2 × 50 + 2 × 465 + 6 × 240 + 2 × 793 = 4056 W.
Heat dissipation
Heat dissipation is measured in BTU/h, and 1 W equals 3.4121 BTU/h.
The heat dissipation of a switch depends on its power consumption. To calculate heat dissipation of the switch, assume 90% power consumption is converted to heat, and the efficiency of the power module is 90%. Heat dissipation/hour of the switch is 0.9 × (total power consumption of the cards plus power consumption of the fan tray)/0.9 × 3.4121.
For the power consumption of the cards and fan trays of the H3C S12500X-AF switches, see "Module power consumption and system power consumption."
Environmental specifications
Table 11 Environmental specifications
Operating
Non-operating
Temperature
0°C to 40°C (32°F to 104°F)
–40°C to +70°C (–40°F to +158°F)
Relative humidity
(noncondensing)
5% to 95%
5% to 95%
Noise
The switch uses fan trays that can automatically adjust the fan speed based on the device temperature The sound pressure levels vary by fan speed. For more information, see Table 12.
Table 12 Sound pressure levels
Switch model
Sound pressure level in the acceptable temperature range
S12516X-AF
67.8 dBA
S12512X-AF
60.8 dBA
S12508X-AF
62.1 dBA
S12504X-AF
67.5 dBA
S12502X-AF
62.4 dBA
S12501X-AF
66.0 dBA
The sound pressure levels are measured according to the method specified in ISO 7779 at the bystander position.
Chassis ordering information
To purchase an S12500X-AF chassis, contact the sales agent or H3C sales personnel.
Table 13 S12500X-AF chassis ordering information
Product code
Product name
0235A1EL
S12516X-AF
H3C S12516X-AF Ethernet Switch Host
0235A1QW
S12512X-AF
H3C S12512X-AF Ethernet Switch Host
0235A1EU
S12508X-AF
H3C S12508X-AF Ethernet Switch Host
0235A1GF
S12504X-AF
H3C S12504X-AF Ethernet Switch Host
0235A1QT
S12502X-AF
H3C S12502X-AF Ethernet Switch Host
0235A2DM
S12501X-AF
H3C S12501X-AF Ethernet Switch Host
  • Become a Partner