- 11-Network Management and Monitoring Configuration Guide
- 02-NQA configuration
- 03-NTP configuration
- 04-PTP configuration
- 05-SNMP configuration
- 06-RMON configuration
- 07-Event MIB configuration
- 08-NETCONF configuration
- 09-Puppet configuration
- 10-Chef configuration
- 11-CWMP configuration
- 12-EAA configuration
- 13-Process monitoring and maintenance configuration
- 14-Sampler configuration
- 15-Mirroring configuration
- 16-NetStream configuration
- 17-IPv6 NetStream configuration
- 18-sFlow configuration
- 19-Information center configuration
- 20-GOLD configuration
- 21-Packet capture configuration
- 22-VCF fabric configuration
- 23-Ansible configuration
- 24-iNQA configuration
- 25-Packet trace configuration
- 26-NetAnalysis configuration
02-NQA configuration | 668.21 KB |
Configuring NQA operations on the NQA client
NQA operations tasks at a glance
Configuring the ICMP echo operation
Configuring the ICMP jitter operation
Configuring the DHCP operation
Configuring the HTTP operation
Configuring the UDP jitter operation
Configuring the SNMP operation
Configuring the UDP echo operation
Configuring the UDP tracert operation
Configuring the voice operation
Configuring the DLSw operation
Configuring the path jitter operation
Configuring optional parameters for the NQA operation
Configuring the collaboration feature
Configuring threshold monitoring
Configuring the NQA statistics collection feature
Configuring the saving of NQA history records
Scheduling the NQA operation on the NQA client
Configuring NQA templates on the NQA client
NQA template tasks at a glance
Configuring the TCP half open template
Configuring the HTTPS template
Configuring the RADIUS template
Configuring optional parameters for the NQA template
Display and maintenance commands for NQA
Example: Configuring the ICMP echo operation
Example: Configuring the ICMP jitter operation
Example: Configuring the DHCP operation
Example: Configuring the DNS operation
Example: Configuring the FTP operation
Example: Configuring the HTTP operation
Example: Configuring the UDP jitter operation
Example: Configuring the SNMP operation
Example: Configuring the TCP operation
Example: Configuring the UDP echo operation
Example: Configuring the UDP tracert operation
Example: Configuring the voice operation
Example: Configuring the DLSw operation
Example: Configuring the path jitter operation
Example: Configuring NQA collaboration
Example: Configuring the ICMP template
Example: Configuring the DNS template
Example: Configuring the TCP template
Example: Configuring the TCP half open template
Example: Configuring the UDP template
Example: Configuring the HTTP template
Example: Configuring the HTTPS template
Example: Configuring the FTP template
Example: Configuring the RADIUS template
Example: Configuring the SSL template
Configuring NQA
About NQA
Network quality analyzer (NQA) allows you to measure network performance, verify the service levels for IP services and applications, and troubleshoot network problems.
NQA operating mechanism
An NQA operation contains a set of parameters such as the operation type, destination IP address, and port number to define how the operation is performed. Each NQA operation is identified by the combination of the administrator name and the operation tag. You can configure the NQA client to run the operations at scheduled time periods.
As shown in Figure 1, the NQA source device (NQA client) sends data to the NQA destination device by simulating IP services and applications to measure network performance.
All types of NQA operations require the NQA client, but only the TCP, UDP echo, UDP jitter, and voice operations require the NQA server. The NQA operations for services that are already provided by the destination device such as FTP do not need the NQA server. You can configure the NQA server to listen and respond to specific IP addresses and ports to meet various test needs.
After starting an NQA operation, the NQA client periodically performs the operation at the interval specified by using the frequency command.
You can set the number of probes the NQA client performs in an operation by using the probe count command. For the voice and path jitter operations, the NQA client performs only one probe per operation and the probe count command is not available.
Collaboration with Track
NQA can collaborate with the Track module to notify application modules of state or performance changes so that the application modules can take predefined actions.
The NQA + Track collaboration is available for the following application modules:
· VRRP.
· Static routing.
· Policy-based routing.
· Smart Link
The following describes how a static route destined for 192.168.0.88 is monitored through collaboration:
1. NQA monitors the reachability to 192.168.0.88.
2. When 192.168.0.88 becomes unreachable, NQA notifies the Track module of the change.
3. The Track module notifies the static routing module of the state change.
4. The static routing module sets the static route to invalid according to a predefined action.
For more information about collaboration, see High Availability Configuration Guide.
Threshold monitoring
Threshold monitoring enables the NQA client to take a predefined action when the NQA operation performance metrics violate the specified thresholds.
Table 1 describes the relationships between performance metrics and NQA operation types.
Table 1 Performance metrics and NQA operation types
Performance metric |
NQA operation types that can gather the metric |
Probe duration |
All NQA operation types except UDP jitter, UDP tracert, path jitter, and voice |
Number of probe failures |
Round-trip time |
ICMP jitter, UDP jitter, and voice |
Number of discarded packets |
One-way jitter (source-to-destination or destination-to-source) |
One-way delay (source-to-destination or destination-to-source) |
Calculated Planning Impairment Factor (ICPIF) (see "Configuring the voice operation") |
Voice |
Mean Opinion Scores (MOS) (see "Configuring the voice operation") |
Voice |
NQA templates
An NQA template is a set of parameters (such as destination address and port number) that defines how an NQA operation is performed. Features can use the NQA template to collect statistics.
You can create multiple NQA templates on the NQA client. Each template must be identified by a unique template name.
NQA tasks at a glance
To configure NQA, perform the following tasks:
Perform this task on the destination device before you configure the TCP, UDP echo, UDP jitter, and voice operations.
3. Configuring NQA operations or NQA templates
¡ Configuring NQA operations on the NQA client
¡ Configuring NQA templates on the NQA client
After you configure an NQA operation, you can schedule the NQA client to run the NQA operation.
An NQA template does not run immediately after it is configured. The template creates and run the NQA operation only when it is required by the feature to which the template is applied.
Configuring the NQA server
To perform TCP, UDP echo, UDP jitter, and voice operations, you must configure the NQA server on the destination device. The NQA server listens and responds to requests on the specified IP addresses and ports.
You can configure multiple TCP or UDP listening services on an NQA server, where each corresponds to a specific IP address and port number.
The IP address and port number for a listening service must be unique on the NQA server and match the configuration on the NQA client.
1. Enter system view.
2. Enable the NQA server.
nqa server enable
By default, the NQA server is disabled.
3. Configure a TCP listening service.
nqa server tcp-connect ip-address port-number [ vpn-instance vpn-instance-name ] [ tos tos ]
This task is required for only TCP and DLSw operations. For the DLSw operation, the port number for the TCP listening service must be 2065.
4. Configure a UDP listening service.
nqa server udp-echo ip-address port-number [ vpn-instance vpn-instance-name ] [ tos tos ]
This task is required for only UDP echo, UDP jitter, and voice operations.
Enabling the NQA client
2. Enable the NQA client.
nqa agent enable
By default, the NQA client is enabled.
The NQA client configuration takes effect after you enable the NQA client.
To configure NQA operations, perform the following tasks:
1. Configuring an NQA operation
¡ Configuring the ICMP echo operation
¡ Configuring the ICMP jitter operation
¡ Configuring the DHCP operation
¡ Configuring the DNS operation
¡ Configuring the FTP operation
¡ Configuring the HTTP operation
¡ Configuring the UDP jitter operation
¡ Configuring the SNMP operation
¡ Configuring the TCP operation
¡ Configuring the UDP echo operation
¡ Configuring the UDP tracert operation
¡ Configuring the voice operation
¡ Configuring the DLSw operation
¡ Configuring the path jitter operation
2. (Optional.) Configuring optional parameters for the NQA operation
3. (Optional.) Configuring the collaboration feature
4. (Optional.) Configuring threshold monitoring
5. (Optional.) Configuring the NQA statistics collection feature
6. (Optional.) Configuring the saving of NQA history records
7. Scheduling the NQA operation on the NQA client
The ICMP echo operation measures the reachability of a destination device. It has the same function as the ping command, but provides more output information. In addition, if multiple paths exist between the source and destination devices, you can specify the next hop for the ICMP echo operation.
The ICMP echo operation sends an ICMP echo request to the destination device per probe.
2. Create an NQA operation and enter NQA operation view.
nqa entry admin-name operation-tag
3. Specify the ICMP echo type and enter its view.
type icmp-echo
4. Specify the destination IP address for ICMP echo requests.
IPv4:
destination ip ip-address
IPv6:
destination ipv6 ipv6-address
By default, no destination IP address is specified.
5. Specify the source IP address for ICMP echo requests. Choose one option as needed:
¡ Use the IP address of the specified interface as the source IP address.
source interface interface-type interface-number
By default, the source IP address of ICMP echo requests is the primary IP address of their output interface.
The specified source interface must be up.
¡ Specify the source IPv4 address.
source ip ip-address
By default, the source IPv4 address of ICMP echo requests is the primary IPv4 address of their output interface.
The specified source IPv4 address must be the IPv4 address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
¡ Specify the source IPv6 address.
source ipv6 ipv6-address
By default, the source IPv6 address of ICMP echo requests is the primary IPv6 address of their output interface.
The specified source IPv6 address must be the IPv6 address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
6. Specify the output interface or the next hop IP address for ICMP echo requests. Choose one option as needed:
¡ Specify the output interface for ICMP echo requests.
out interface interface-type interface-number
By default, the output interface for ICMP echo requests is not specified. The NQA client determines the output interface based on the routing table lookup.
¡ Specify the next hop IPv4 address.
next-hop ip ip-address
By default, no next hop IPv4 address is specified.
¡ Specify the next hop IPv6 address.
next-hop ipv6 ipv6-address
By default, no next hop IPv6 address is specified.
7. (Optional.) Set the payload size for each ICMP echo request.
data-size size
The default payload size is 100 bytes.
8. (Optional.) Specify the payload fill string for ICMP echo requests.
data-fill string
The default payload fill string is the hexadecimal string 00010203040506070809.
The ICMP jitter operation measures unidirectional and bidirectional jitters. The operation result helps you to determine whether the network can carry jitter-sensitive services such as real-time voice and video services.
The ICMP jitter operation works as follows:
1. The NQA client sends ICMP packets to the destination device.
2. The destination device time stamps each packet it receives, and then sends the packet back to the NQA client.
3. Upon receiving the responses, the NQA client calculates the jitter according to the timestamps.
The ICMP jitter operation sends a number of ICMP packets to the destination device per probe. The number of packets to send is determined by using the probe packet-number command.
The display nqa history command does not display the results or statistics of the ICMP jitter operation. To view the results or statistics of the operation, use the display nqa result or display nqa statistics command.
Before starting the operation, make sure the network devices are time synchronized by using NTP. For more information about NTP, see "Configuring NTP."
3. Specify the ICMP jitter type and enter its view.
type icmp-jitter
4. Specify the destination IP address for ICMP packets.
5. Set the number of ICMP packets sent per probe.
probe packet-number packet-number
The default setting is 10.
6. Set the interval for sending ICMP packets.
probe packet-interval interval
The default setting is 20 milliseconds.
7. Specify how long the NQA client waits for a response from the server before it regards the response times out.
probe packet-timeout timeout
The default setting is 3000 milliseconds.
8. Specify the source IP address for ICMP packets.
By default, the source IP address of ICMP packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no ICMP packets can be sent out.
The DHCP operation measures whether or not the DHCP server can respond to client requests. DHCP also measures the amount of time it takes the NQA client to obtain an IP address from a DHCP server.
The NQA client simulates the DHCP relay agent to forward DHCP requests for IP address acquisition from the DHCP server. The interface that performs the DHCP operation does not change its IP address. When the DHCP operation completes, the NQA client sends a packet to release the obtained IP address.
The DHCP operation acquires an IP address from the DHCP server per probe.
3. Specify the DHCP type and enter its view.
type dhcp
4. Specify the IP address of the DHCP server as the destination IP address of DHCP packets.
5. Specify the output interface for DHCP request packets.
By default, the NQA client determines the output interface based on the routing table lookup.
6. Specify the source IP address of DHCP request packets.
By default, the source IP address of DHCP request packets is the primary IP address of their output interface.
The specified source IP address must be the IP address of a local interface, and the local interface must be up. Otherwise, no probe packets can be sent out.
The DNS operation simulates domain name resolution, and it measures the time for the NQA client to resolve a domain name into an IP address through a DNS server. The obtained DNS entry is not saved.
The DNS operation resolves a domain name into an IP address per probe.
3. Specify the DNS type and enter its view.
type dns
4. Specify the IP address of the DNS server as the destination IP address of DNS packets.
5. Specify the domain name to be translated.
resolve-target domain-name
The FTP operation measures the time for the NQA client to transfer a file to or download a file from an FTP server.
The FTP operation uploads or downloads a file from an FTP server per probe.
To upload (put) a file to the FTP server, use the filename command to specify the name of the file you want to upload. The file must exist on the NQA client.
To download (get) a file from the FTP server, include the name of the file you want to download in the url command. The file must exist on the FTP server. The NQA client does not save the file obtained from the FTP server.
Use a small file for the FTP operation. A big file might result in transfer failure because of timeout, or might affect other services because of the amount of network bandwidth it occupies.
3. Specify the FTP type and enter its view.
type ftp
4. Specify an FTP login username.
username username
By default, no FTP login username is specified.
5. Specify an FTP login password.
By default, no FTP login password is specified.
6. Specify the source IP address for FTP request packets.
By default, the source IP address of FTP request packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no FTP requests can be sent out.
7. Set the data transmission mode.
mode { active | passive }
The default mode is active.
8. Specify the FTP operation type.
operation { get | put }
The default FTP operation type is get.
9. Specify the destination URL for the FTP operation.
url url
By default, no destination URL is specified for an FTP operation.
Enter the URL in one of the following formats:
¡ ftp://host/filename.
¡ ftp://host:port/filename.
The filename argument is required only for the get operation.
10. Specify the name of the file to be uploaded.
filename file-name
By default, no file is specified.
This task is required only for the put operation.
The configuration does not take effect for the get operation.
The HTTP operation measures the time for the NQA client to obtain responses from an HTTP server.
The HTTP operation supports the following operation types:
· Get—Retrieves data such as a Web page from the HTTP server.
· Post—Sends data to the HTTP server for processing.
· Raw—Sends a user-defined HTTP request to the HTTP server. You must manually configure the content of the HTTP request to be sent.
The HTTP operation completes the operation of the specified type per probe.
3. Specify the HTTP type and enter its view.
type http
4. Specify the destination URL for the HTTP operation.
url url
By default, no destination URL is specified for an HTTP operation.
¡ http://host/resource
¡ http://host:port/resource
5. Specify an HTTP login username.
username username
By default, no HTTP login username is specified.
6. Specify an HTTP login password.
By default, no HTTP login password is specified.
7. Specify the HTTP version.
version { v1.0 | v1.1 }
By default, HTTP 1.0 is used.
8. Specify the HTTP operation type.
operation { get | post | raw }
The default HTTP operation type is get.
If you set the operation type to raw, the client pads the content configured in raw request view to the HTTP request to send to the HTTP server.
9. Configure the HTTP raw request.
a. Enter raw request view.
raw-request
Every time you enter raw request view, the previously configured raw request content is cleared.
b. Enter or paste the request content.
By default, no request content is configured.
To ensure successful operations, make sure the request content does not contain command aliases configured by using the alias command. For more information about the alias command, see CLI commands in Fundamentals Command Reference.
c. Save the input and return to HTTP operation view:
This step is required only when the operation type is set to raw.
10. Specify the source IP address for the HTTP packets.
By default, the source IP address of HTTP packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no request packets can be sent out.
The UDP jitter operation measures unidirectional and bidirectional jitters. The operation result helps you determine whether the network can carry jitter-sensitive services such as real-time voice and video services.
The UDP jitter operation works as follows:
1. The NQA client sends UDP packets to the destination port.
The UDP jitter operation sends a number of UDP packets to the destination device per probe. The number of packets to send is determined by using the probe packet-number command.
The UDP jitter operation requires both the NQA server and the NQA client. Before you perform the UDP jitter operation, configure the UDP listening service on the NQA server. For more information about UDP listening service configuration, see "Configuring the NQA server."
To ensure successful UDP jitter operations and avoid affecting existing services, do not perform the operations on well-known ports from 1 to 1023.
The display nqa history command does not display the results or statistics of the UDP jitter operation. To view the results or statistics of the UDP jitter operation, use the display nqa result or display nqa statistics command.
3. Specify the UDP jitter type and enter its view.
type udp-jitter
4. Specify the destination IP address for UDP packets.
The destination IP address must be the same as the IP address of the UDP listening service configured on the NQA server. To configure a UDP listening service on the server, use the nqa server udp-echo command.
5. Specify the destination port number for UDP packets.
destination port port-number
By default, no destination port number is specified.
The destination port number must be the same as the port number of the UDP listening service configured on the NQA server. To configure a UDP listening service on the server, use the nqa server udp-echo command.
6. Specify the source IP address for UDP packets.
By default, the source IP address of UDP packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no UDP packets can be sent out.
7. Specify the source port number for UDP packets.
source port port-number
By default, the NQA client randomly picks an unused port as the source port when the operation starts.
8. Set the number of UDP packets sent per probe.
9. Set the interval for sending UDP packets.
10. Specify how long the NQA client waits for a response from the server before it regards the response times out.
11. (Optional.) Set the payload size for each UDP packet.
data-size size
12. (Optional.) Specify the payload fill string for UDP packets.
data-fill string
The SNMP operation tests whether the SNMP service is available on an SNMP agent.
The SNMP operation sends one SNMPv1 packet, one SNMPv2c packet, and one SNMPv3 packet to the SNMP agent per probe.
3. Specify the SNMP type and enter its view.
type snmp
4. Specify the destination address for SNMP packets.
5. Specify the source IP address for SNMP packets.
By default, the source IP address of SNMP packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no SNMP packets can be sent out.
6. Specify the source port number for SNMP packets.
7. Specify the community name carried in the SNMPv1 and SNMPv2c packets.
community read { cipher | simple } community-name
By default, the SNMPv1 and SNMPv2c packets carry community name public.
Make sure the specified community name is the same as the community name configured on the SNMP agent.
The TCP operation measures the time for the NQA client to establish a TCP connection to a port on the NQA server.
The TCP operation requires both the NQA server and the NQA client. Before you perform a TCP operation, configure a TCP listening service on the NQA server. For more information about the TCP listening service configuration, see "Configuring the NQA server."
The TCP operation sets up a TCP connection per probe.
3. Specify the TCP type and enter its view.
type tcp
4. Specify the destination address for TCP packets.
The destination address must be the same as the IP address of the TCP listening service configured on the NQA server. To configure a TCP listening service on the server, use the nqa server tcp-connect command.
5. Specify the destination port for TCP packets.
By default, no destination port number is configured.
The destination port number must be the same as the port number of the TCP listening service configured on the NQA server. To configure a TCP listening service on the server, use the nqa server tcp-connect command.
6. Specify the source IP address for TCP packets.
By default, the source IP address of TCP packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no TCP packets can be sent out.
The UDP echo operation measures the round-trip time between the client and a UDP port on the NQA server.
The UDP echo operation requires both the NQA server and the NQA client. Before you perform a UDP echo operation, configure a UDP listening service on the NQA server. For more information about the UDP listening service configuration, see "Configuring the NQA server."
The UDP echo operation sends a UDP packet to the destination device per probe.
3. Specify the UDP echo type and enter its view.
type udp-echo
4. Specify the destination address for UDP packets.
The destination address must be the same as the IP address of the UDP listening service configured on the NQA server. To configure a UDP listening service on the server, use the nqa server udp-echo command.
8. (Optional.) Set the payload size for each UDP packet.
data-size size
The default setting is 100 bytes.
9. (Optional.) Specify the payload fill string for UDP packets.
data-fill string
The UDP tracert operation determines the routing path from the source device to the destination device.
The UDP tracert operation sends a UDP packet to a hop along the path per probe.
The UDP tracert operation is not supported on IPv6 networks. To determine the routing path that the IPv6 packets traverse from the source to the destination, use the tracert ipv6 command. For more information about the command, see Network Management and Monitoring Command Reference.
Before you configure the UDP tracert operation, you must perform the following tasks:
· Enable sending ICMP time exceeded messages on the intermediate devices between the source and destination devices. If the intermediate devices are H3C devices, use the ip ttl-expires enable command.
· Enable sending ICMP destination unreachable messages on the destination device. If the destination device is an H3C device, use the ip unreachables enable command.
For more information about the ip ttl-expires enable and ip unreachables enable commands, see Layer 3—IP Services Command Reference.
3. Specify the UDP tracert operation type and enter its view.
type udp-tracert
4. Specify the destination device for the operation. Choose one option as needed:
¡ Specify the destination device by its host name.
destination host host-name
By default, no destination host name is specified.
¡ Specify the destination device by its IP address.
By default, the destination port number is 33434.
This port number must be an unused number on the destination device, so that the destination device can reply with ICMP port unreachable messages.
6. Specify an output interface for UDP packets.
7. Specify the source IP address for UDP packets.
¡ Specify the IP address of the specified interface as the source IP address.
¡ Specify the source IP address.
The specified source interface must be up. The source IP address must be the IP address of a local interface, and the local interface must be up. Otherwise, no probe packets can be sent out.
8. Specify the source port number for UDP packets.
9. Set the maximum number of consecutive probe failures.
max-failure times
The default setting is 5.
10. Set the initial TTL value for UDP packets.
init-ttl value
The default setting is 1.
data-size size
12. (Optional.) Enable the no-fragmentation feature.
no-fragment enable
By default, the no-fragmentation feature is disabled.
The voice operation measures VoIP network performance.
The voice operation works as follows:
1. The NQA client sends voice packets at sending intervals to the destination device (NQA server).
The voice packets are of one of the following codec types:
¡ G.711 A-law.
¡ G.711 µ-law.
¡ G.729 A-law.
2. The destination device time stamps each voice packet it receives and sends it back to the source.
3. Upon receiving the packet, the source device calculates the jitter and one-way delay based on the timestamp.
The voice operation sends a number of voice packets to the destination device per probe. The number of packets to send per probe is determined by using the probe packet-number command.
The following parameters that reflect VoIP network performance can be calculated by using the metrics gathered by the voice operation:
· Calculated Planning Impairment Factor (ICPIF)—Measures impairment to voice quality on a VoIP network. It is decided by packet loss and delay. A higher value represents a lower service quality.
· Mean Opinion Scores (MOS)—A MOS value can be evaluated by using the ICPIF value, in the range of 1 to 5. A higher value represents a higher service quality.
The evaluation of voice quality depends on users' tolerance for voice quality. For users with higher tolerance for voice quality, use the advantage-factor command to set an advantage factor. When the system calculates the ICPIF value, it subtracts the advantage factor to modify ICPIF and MOS values for voice quality evaluation.
The voice operation requires both the NQA server and the NQA client. Before you perform a voice operation, configure a UDP listening service on the NQA server. For more information about UDP listening service configuration, see "Configuring the NQA server."
To ensure successful voice operations and avoid affecting existing services, do not perform the operations on well-known ports from 1 to 1023.
The display nqa history command does not display the results or statistics of the voice operation. To view the results or statistics of the voice operation, use the display nqa result or display nqa statistics command.
3. Specify the voice type and enter its view.
type voice
4. Specify the destination IP address for voice packets.
By default, no destination IP address is configured.
5. Specify the destination port number for voice packets.
6. Specify the source IP address for voice packets.
By default, the source IP address of voice packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no voice packets can be sent out.
7. Specify the source port number for voice packets.
8. Configure the basic voice operation parameters.
¡ Specify the codec type.
codec-type { g711a | g711u | g729a }
By default, the codec type is G.711 A-law.
¡ Set the advantage factor for calculating MOS and ICPIF values.
advantage-factor factor
By default, the advantage factor is 0.
9. Configure the probe parameters for the voice operation.
¡ Set the number of voice packets to be sent per probe.
The default setting is 1000.
¡ Set the interval for sending voice packets.
¡ Specify how long the NQA client waits for a response from the server before it regards the response times out.
The default setting is 5000 milliseconds.
10. Configure the payload parameters.
a. Set the payload size for voice packets.
data-size size
By default, the voice packet size varies by codec type. The default packet size is 172 bytes for G.711A-law and G.711 µ-law codec type, and 32 bytes for G.729 A-law codec type.
b. (Optional.) Specify the payload fill string for voice packets.
data-fill string
The DLSw operation measures the response time of a DLSw device.
It sets up a DLSw connection to the DLSw device per probe.
3. Specify the DLSw type and enter its view.
type dlsw
4. Specify the destination IP address for the probe packets.
5. Specify the source IP address for the probe packets.
By default, the source IP address of the probe packets is the primary IP address of their output interface.
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
The path jitter operation measures the jitter, negative jitters, and positive jitters from the NQA client to each hop on the path to the destination.
The path jitter operation performs the following steps per probe:
1. Obtains the path from the NQA client to the destination through tracert. A maximum of 64 hops can be detected.
2. Sends a number of ICMP echo requests to each hop along the path. The number of ICMP echo requests to send is set by using the probe packet-number command.
Before you configure the path jitter operation, you must perform the following tasks:
3. Specify the path jitter type and enter its view.
type path-jitter
The source IP address must be the IP address of a local interface, and the interface must be up. Otherwise, no ICMP echo requests can be sent out.
6. Configure the probe parameters for the path jitter operation.
a. Set the number of ICMP echo requests to be sent per probe.
b. Set the interval for sending ICMP echo requests.
c. Specify how long the NQA client waits for a response from the server before it regards the response times out.
7. (Optional.) Specify an LSR path.
lsr-path ip-address&<1-8>
By default, no LSR path is specified.
The path jitter operation uses tracert to detect the LSR path to the destination, and sends ICMP echo requests to each hop on the LSR path.
8. Perform the path jitter operation only on the destination address.
target-only
By default, the path jitter operation is performed on each hop on the path to the destination.
9. (Optional.) Set the payload size for each ICMP echo request.
data-size size
10. (Optional.) Specify the payload fill string for ICMP echo requests.
data-fill string
Unless otherwise specified, the following optional parameters apply to all types of NQA operations.
The parameter settings take effect only on the current operation.
2. Enter the view of an existing NQA operation.
3. Configure a description for the operation.
By default, no description is configured.
4. Set the interval at which the NQA operation repeats.
frequency interval
For a voice or path jitter operation, the default setting is 60000 milliseconds.
For other types of operations, the default setting is 0 milliseconds, and only one operation is performed.
When the interval expires, but the operation is not completed or is not timed out, the next operation does not start.
5. Specify the probe times.
probe count times
In an UDP tracert operation, the NQA client performs three probes to each hop to the destination by default.
In other types of operations, the NQA client performs one probe to the destination per operation by default.
This command is not available for the voice and path jitter operations. Each of these operations performs only one probe.
6. Set the probe timeout time.
probe timeout timeout
This command is not available for the ICMP jitter, UDP jitter, voice, or path jitter operations.
7. Set the maximum number of hops that the probe packets can traverse.
ttl value
The default setting is 30 for probe packets of the UDP tracert operation, and is 20 for probe packets of other types of operations.
This command is not available for the DHCP or path jitter operations.
8. Set the ToS value in the IP header of the probe packets.
tos value
The default setting is 0.
9. Enable the routing table bypass feature.
route-option bypass-route
By default, the routing table bypass feature is disabled.
This command does not take effect if the destination address of the NQA operation is an IPv6 address.
10. Specify the VPN instance where the operation is performed.
By default, the operation is performed on the public network.
Collaboration is implemented by associating a reaction entry of an NQA operation with a track entry. The reaction entry monitors the NQA operation. If the number of operation failures reaches the specified threshold, the configured action is triggered.
The collaboration feature is not available for the following types of operations:
· ICMP jitter operation.
· UDP jitter operation.
· UDP tracert operation.
· Voice operation.
· Path jitter operation.
3. Configure a reaction entry.
reaction item-number checked-element probe-fail threshold-type consecutive consecutive-occurrences action-type trigger-only
You cannot modify the content of an existing reaction entry.
4. Return to system view.
5. Associate Track with NQA.
For information about the configuration, see High Availability Configuration Guide.
6. Associate Track with an application module.
This feature allows you to monitor the NQA operation running status.
An NQA operation supports the following threshold types:
· average—If the average value for the monitored performance metric either exceeds the upper threshold or goes below the lower threshold, a threshold violation occurs.
· accumulate—If the total number of times that the monitored performance metric is out of the specified value range reaches or exceeds the specified threshold, a threshold violation occurs.
· consecutive—If the number of consecutive times that the monitored performance metric is out of the specified value range reaches or exceeds the specified threshold, a threshold violation occurs.
Threshold violations for the average or accumulate threshold type are determined on a per NQA operation basis. The threshold violations for the consecutive type are determined from the time the NQA operation starts.
The following actions might be triggered:
· none—NQA displays results only on the terminal screen. It does not send traps to the NMS.
· trap-only—NQA displays results on the terminal screen, and meanwhile it sends traps to the NMS.
To send traps to the NMS, the NMS address must be specified by using the snmp-agent target-host command. For more information about the command, see Network Management and Monitoring Command Reference.
· trigger-only—NQA displays results on the terminal screen, and meanwhile triggers other modules for collaboration.
In a reaction entry, configure a monitored element, a threshold type, and an action to be triggered to implement threshold monitoring.
The state of a reaction entry can be invalid, over-threshold, or below-threshold.
· Before an NQA operation starts, the reaction entry is in invalid state.
· If the threshold is violated, the state of the entry is set to over-threshold. Otherwise, the state of the entry is set to below-threshold.
The threshold monitoring feature is not available for the path jitter operations.
3. Enable sending traps to the NMS when specific conditions are met.
reaction trap { path-change | probe-failure consecutive-probe-failures | test-complete | test-failure [ accumulate-probe-failures ] }
By default, no traps are sent to the NMS.
The ICMP jitter, UDP jitter, and voice operations support only the test-complete keyword.
The following parameters are not available for the UDP tracert operation:
¡ The probe-failure consecutive-probe-failures option.
¡ The accumulate-probe-failures argument.
4. Configure threshold monitoring. Choose the options to configure as needed:
¡ Monitor the operation duration.
reaction item-number checked-element probe-duration threshold-type { accumulate accumulate-occurrences | average | consecutive consecutive-occurrences } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
This reaction entry is not supported in the ICMP jitter, UDP jitter, UDP tracert, or voice operations
¡ Monitor failure times.
reaction item-number checked-element probe-fail threshold-type { accumulate accumulate-occurrences | consecutive consecutive-occurrences } [ action-type { none | trap-only } ]
This reaction entry is not supported in the ICMP jitter, UDP jitter, UDP tracert, or voice operations.
¡ Monitor the round-trip time.
reaction item-number checked-element rtt threshold-type { accumulate accumulate-occurrences | average } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
Only the ICMP jitter, UDP jitter, and voice operations support this reaction entry.
¡ Monitor packet loss.
reaction item-number checked-element packet-loss threshold-type accumulate accumulate-occurrences [ action-type { none | trap-only } ]
¡ Monitor the one-way jitter.
reaction item-number checked-element { jitter-ds | jitter-sd } threshold-type { accumulate accumulate-occurrences | average } threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
¡ Monitor the one-way delay.
reaction item-number checked-element { owd-ds | owd-sd } threshold-value upper-threshold lower-threshold
¡ Monitor the ICPIF value.
reaction item-number checked-element icpif threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
Only the voice operation supports this reaction entry.
¡ Monitor the MOS value.
reaction item-number checked-element mos threshold-value upper-threshold lower-threshold [ action-type { none | trap-only } ]
The DNS operation does not support the action of sending trap messages. For the DNS operation, the action type can only be none.
NQA forms statistics within the same collection interval as a statistics group. To display information about the statistics groups, use the display nqa statistics command.
When the maximum number of statistics groups is reached, the NQA client deletes the oldest statistics group to save a new one.
A statistics group is automatically deleted when its hold time expires.
The NQA statistics collection feature is not available for the UDP tracert operations.
If you use the frequency command to set the interval to 0 milliseconds for an NQA operation, NQA does not generate any statistics group for the operation.
3. Set the statistics collection interval.
statistics interval interval
The default setting is 60 minutes.
4. Set the maximum number of statistics groups that can be saved.
statistics max-group number
By default, the NQA client can save a maximum of two statistics groups for an operation.
To disable the NQA statistics collection feature, set the number argument to 0.
5. Set the hold time of statistics groups.
statistics hold-time hold-time
The default setting is 120 minutes.
This task enables the NQA client to save NQA history records. You can use the display nqa history command to display the NQA history records.
The NQA history record saving feature is not available for the following types of operations:
· Voice operation.
3. Enable the saving of history records for the NQA operation.
history-record enable
By default, this feature is enabled only for the UDP tracert operation.
4. Set the lifetime of history records.
history-record keep-time keep-time
A record is deleted when its lifetime is reached.
5. Set the maximum number of history records that can be saved.
history-record number number
The default setting is 50.
When the maximum number of history records is reached, the system will delete the oldest record to save a new one.
The NQA operation runs between the specified start time and end time (the start time plus operation duration). If the specified start time is ahead of the system time, the operation starts immediately. If both the specified start and end time are ahead of the system time, the operation does not start. To display the current system time, use the display clock command.
You cannot enter the operation type view or the operation view of a scheduled NQA operation.
A system time adjustment does not affect started or completed NQA operations. It affects only the NQA operations that have not started.
2. Specify the scheduling parameters for an NQA operation.
nqa schedule admin-name operation-tag start-time { hh:mm:ss [ yyyy/mm/dd | mm/dd/yyyy ] | now } lifetime { lifetime | forever } [ recurring ]
Some operation parameters for an NQA template can be specified by the template configuration or the feature that uses the template. When both are specified, the parameters in the template configuration take effect.
To configure NQA templates, perform the following tasks:
1. Perform at least one of the following tasks:
¡ Configuring the ICMP template
¡ Configuring the DNS template
¡ Configuring the TCP template
¡ Configuring the TCP half open template
¡ Configuring the UDP template
¡ Configuring the HTTP template
¡ Configuring the HTTPS template
¡ Configuring the FTP template
¡ Configuring the RADIUS template
¡ Configuring the SSL template
2. (Optional.) Configuring optional parameters for the NQA template
A feature that uses the ICMP template performs the ICMP operation to measure the reachability of a destination device. The ICMP template is supported on both IPv4 and IPv6 networks.
2. Create an ICMP template and enter its view.
nqa template icmp name
3. Specify the destination IP address for the operation.
IPv4:
IPv6:
4. Specify the source IP address for ICMP echo requests. Choose one option as needed:
By default, the primary IP address of the output interface is used as the source IP address of ICMP echo requests.
By default, the primary IPv4 address of the output interface is used as the source IPv4 address of ICMP echo requests.
By default, the primary IPv6 address of the output interface is used as the source IPv6 address of ICMP echo requests.
5. Specify the next hop IP address for ICMP echo requests.
IPv4:
IPv6:
By default, no IP address of the next hop is configured.
6. Configure the probe result sending on a per-probe basis.
reaction trigger per-probe
By default, the probe result is sent to the feature that uses the template after three consecutive failed or successful probes.
If you execute the reaction trigger per-probe and reaction trigger probe-pass commands multiple times, the most recent configuration takes effect.
If you execute the reaction trigger per-probe and reaction trigger probe-fail commands multiple times, the most recent configuration takes effect.
7. (Optional.) Set the payload size for each ICMP request.
data-size size
data-fill string
A feature that uses the DNS template performs the DNS operation to determine the status of the server. The DNS template is supported on both IPv4 and IPv6 networks.
In DNS template view, you can specify the address expected to be returned. If the returned IP addresses include the expected address, the DNS server is valid and the operation succeeds. Otherwise, the operation fails.
Create a mapping between the domain name and an address before you perform the DNS operation. For information about configuring the DNS server, see documents about the DNS server configuration.
2. Create a DNS template and enter DNS template view.
nqa template dns name
3. Specify the destination IP address for the probe packets.
IPv4:
IPv6:
By default, no destination address is specified.
4. Specify the destination port number for the probe packets.
By default, the destination port number is 53.
IPv4:
By default, the source IPv4 address of the probe packets is the primary IPv4 address of their output interface.
The source IPv4 address must be the IPv4 address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
IPv6:
By default, the source IPv6 address of the probe packets is the primary IPv6 address of their output interface.
The source IPv6 address must be the IPv6 address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
6. Specify the source port number for the probe packets.
By default, no source port number is specified.
7. Specify the domain name to be translated.
8. Specify the domain name resolution type.
resolve-type { A | AAAA }
By default, the type is type A.
A type A query resolves a domain name to a mapped IPv4 address, and a type AAAA query to a mapped IPv6 address.
9. (Optional.) Specify the IP address that is expected to be returned.
IPv4:
expect ip ip-address
IPv6:
expect ipv6 ipv6-address
By default, no expected IP address is specified.
A feature that uses the TCP template performs the TCP operation to test whether the NQA client can establish a TCP connection to a specific port on the server.
In TCP template view, you can specify the expected data to be returned. If you do not specify the expected data, the TCP operation tests only whether the client can establish a TCP connection to the server.
2. Create a TCP template and enter its view.
nqa template tcp name
IPv4:
IPv6:
4. Specify the destination port number for the operation.
IPv4:
By default, the primary IPv4 address of the output interface is used as the source IPv4 address of the probe packets.
The source IP address must be the IPv4 address of a local interface, and the interface must be up. Otherwise, no probe packets can be sent out.
IPv6:
By default, the primary IPv6 address of the output interface is used as the source IPv6 address of the probe packets.
6. (Optional.) Specify the payload fill string for the probe packets.
data-fill string
7. (Optional.) Configure the expected data.
expect data expression [ offset number ]
By default, no expected data is configured.
The NQA client performs expect data check only when you configure both the data-fill and expect-data commands.
A feature that uses the TCP half open template performs the TCP half open operation to test whether the TCP service is available on the server. The TCP half open operation is used when the feature cannot get a response from the TCP server through an existing TCP connection.
In the TCP half open operation, the NQA client sends a TCP ACK packet to the server. If the client receives an RST packet, it considers that the TCP service is available on the server.
2. Create a TCP half open template and enter its view.
nqa template tcphalfopen name
3. Specify the destination IP address of the operation.
IPv4:
IPv6:
4. Specify the source IP address for the probe packets.
IPv4:
IPv6:
5. Specify the next hop IP address for the probe packets.
IPv4:
IPv6:
By default, the IP address of the next hop is configured.
A feature that uses the UDP template performs the UDP operation to test the following items:
· Reachability of a specific port on the NQA server.
· Availability of the requested service on the NQA server.
In UDP template view, you can specify the expected data to be returned. If you do not specify the expected data, the UDP operation tests only whether the client can receive the response packet from the server.
The UDP operation requires both the NQA server and the NQA client. Before you perform a UDP operation, configure a UDP listening service on the NQA server. For more information about the UDP listening service configuration, see "Configuring the NQA server."
2. Create a UDP template and enter its view.
nqa template udp name
IPv4:
IPv6:
IPv4:
IPv6:
6. Specify the payload fill string for the probe packets.
data-fill string
7. (Optional.) Set the payload size for the probe packets.
data-size size
8. (Optional.) Configure the expected data.
Expected data check is performed only when both the data-fill command and the expect data command are configured.
A feature that uses the HTTP template performs the HTTP operation to measure the time it takes the NQA client to obtain data from an HTTP server.
The expected data is checked only when the data is configured and the HTTP response contains the Content-Length field in the HTTP header.
The status code of the HTTP packet is a three-digit field in decimal notation, and it includes the status information for the HTTP server. The first digit defines the class of response.
Before you perform the HTTP operation, you must configure the HTTP server.
2. Create an HTTP template and enter its view.
nqa template http name
3. Specify the destination URL for the HTTP template.
url url
By default, no destination URL is specified for an HTTP template.
4. Specify an HTTP login username.
username username
5. Specify an HTTP login password.
6. Specify the HTTP version.
7. Specify the HTTP operation type.
By default, the HTTP operation type is get.
8. Configure the content of the HTTP raw request.
raw-request
c. Return to HTTP template view.
The system automatically saves the configuration in raw request view before it returns to HTTP template view.
9. Specify the source IP address for the probe packets.
IPv4:
IPv6:
10. (Optional.) Configure the expected status codes.
expect status status-list
By default, no expected status code is configured.
11. (Optional.) Configure the expected data.
A feature that uses the HTTPS template performs the HTTPS operation to measure the time it takes for the NQA client to obtain data from an HTTPS server.
The expected data is checked only when the expected data is configured and the HTTPS response contains the Content-Length field in the HTTPS header.
The status code of the HTTPS packet is a three-digit field in decimal notation, and it includes the status information for the HTTPS server. The first digit defines the class of response.
Before you perform the HTTPS operation, configure the HTTPS server and the SSL client policy for the SSL client. For information about configuring SSL client policies, see Security Configuration Guide.
2. Create an HTTPS template and enter its view.
nqa template https name
3. Specify the destination URL for the HTTPS template.
url url
By default, no destination URL is specified for an HTTPS template.
¡ https://host/resource
¡ https://host:port/resource
4. Specify an HTTPS login username.
username username
By default, no HTTPS login username is specified.
5. Specify an HTTPS login password.
By default, no HTTPS login password is specified.
6. Specify an SSL client policy.
ssl-client-policy policy-name
By default, no SSL client policy is specified.
7. Specify the HTTPS version.
By default, HTTPS 1.0 is used.
8. Specify the HTTPS operation type.
By default, the HTTPS operation type is get.
If you set the operation type to raw, the client pads the content configured in raw request view to the HTTPS request to send to the HTTPS server.
9. Configure the content of the HTTPS raw request.
raw-request
c. Return to HTTPS template view.
The system automatically saves the configuration in raw request view before it returns to HTTPS template view.
10. Specify the source IP address for the probe packets.
IPv4:
IPv6:
12. (Optional.) Configure the expected status codes.
A feature that uses the FTP template performs the FTP operation. The operation measures the time it takes the NQA client to transfer a file to or download a file from an FTP server.
Configure the username and password for the FTP client to log in to the FTP server before you perform an FTP operation. For information about configuring the FTP server, see Fundamentals Configuration Guide.
2. Create an FTP template and enter its view.
nqa template ftp name
3. Specify an FTP login username.
username username
4. Specify an FTP login password.
password { cipher | simple } sting
IPv4:
IPv6:
6. Set the data transmission mode.
7. Specify the FTP operation type.
By default, the FTP operation type is get, which means obtaining files from the FTP server.
8. Specify the destination URL for the FTP template.
url url
By default, no destination URL is specified for an FTP template.
When you perform the get operation, the file name is required.
When you perform the put operation, the filename argument does not take effect, even if it is specified. The file name for the put operation is determined by using the filename command.
9. Specify the name of a file to be transferred.
filename filename
A feature that uses the RADIUS template performs the RADIUS authentication operation to check the availability of the authentication service on the RADIUS server.
The RADIUS authentication operation workflow is as follows:
1. The NQA client sends an authentication request (Access-Request) to the RADIUS server. The request includes the username and the password. The password is encrypted by using the MD5 algorithm and the shared key.
2. The RADIUS server authenticates the username and password.
¡ If the authentication succeeds, the server sends an Access-Accept packet to the NQA client.
¡ If the authentication fails, the server sends an Access-Reject packet to the NQA client.
3. The NQA client determines the availability of the authentication service on the RADIUS server based on the response packet it received:
¡ If an Access-Accept packet is received, the authentication service is available on the RADIUS server.
¡ If an Access-Reject packet is received, the authentication service is not available on the RADIUS server.
Before you configure the RADIUS template, specify a username, password, and shared key on the RADIUS server. For more information about configuring the RADIUS server, see AAA in Security Configuration Guide.
2. Create a RADIUS template and enter its view.
nqa template radius name
IPv4:
IPv6:
By default, the destination port number is 1812.
5. Specify a username.
username username
By default, no username is specified.
6. Specify a password.
By default, no password is specified.
7. Specify a shared key for secure RADIUS authentication.
key { cipher | simple } string
By default, no shared key is specified for RADIUS authentication.
8. Specify the source IP address for the probe packets.
IPv4:
IPv6:
A feature that uses the SSL template performs the SSL operation to measure the time required to establish an SSL connection to an SSL server.
Before you configure the SSL template, you must configure the SSL client policy. For information about configuring SSL client policies, see Security Configuration Guide.
2. Create an SSL template and enter its view.
nqa template ssl name
IPv4:
IPv6:
By default, the destination port number is not specified.
5. Specify an SSL client policy.
6. Specify the source IP address for the probe packets.
IPv4:
IPv6:
Unless otherwise specified, the following optional parameters apply to all types of NQA templates.
The parameter settings take effect only on the current NQA template.
2. Enter the view of an existing NQA template.
nqa template { dns | ftp | http | https | icmp | radius | ssl | tcp | tcphalfopen | udp } name
3. Configure a description.
frequency interval
If the operation is not completed when the interval expires, the next operation does not start.
5. Set the probe timeout time.
6. Set the TTL for the probe packets.
ttl value
The default setting is 20.
This command is not available for the ARP template.
7. Set the ToS value in the IP header of the probe packets.
tos value
8. Specify the VPN instance where the operation is performed.
9. Set the number of consecutive successful probes to determine a successful operation event.
reaction trigger probe-pass count
The default setting is 3.
If the number of consecutive successful probes for an NQA operation is reached, the NQA client notifies the feature that uses the template of the successful operation event.
10. Set the number of consecutive probe failures to determine an operation failure.
reaction trigger probe-fail count
If the number of consecutive probe failures for an NQA operation is reached, the NQA client notifies the feature that uses the NQA template of the operation failure.
Task |
Command |
Display history records of NQA operations. |
display nqa history [ admin-name operation-tag ] |
Display the current monitoring results of reaction entries. |
display nqa reaction counters [ admin-name operation-tag [ item-number ] ] |
Display the most recent result of the NQA operation. |
display nqa result [ admin-name operation-tag ] |
Display NQA server status. |
display nqa server status |
Display NQA statistics. |
display nqa statistics [ admin-name operation-tag ] |
NQA configuration examples
As shown in Figure 2, configure an ICMP echo operation on the NQA client (Device A) to test the round-trip time to Device B. The next hop of Device A is Device C.
# Assign IP addresses to interfaces, as shown in Figure 2. (Details not shown.)
# Configure static routes or a routing protocol to make sure the devices can reach each other. (Details not shown.)
# Create an ICMP echo operation.
[DeviceA] nqa entry admin test1
[DeviceA-nqa-admin-test1] type icmp-echo
# Specify 10.2.2.2 as the destination IP address of ICMP echo requests.
[DeviceA-nqa-admin-test1-icmp-echo] destination ip 10.2.2.2
# Specify 10.1.1.2 as the next hop. The ICMP echo requests are sent through Device C to Device B.
[DeviceA-nqa-admin-test1-icmp-echo] next-hop ip 10.1.1.2
# Configure the ICMP echo operation to perform 10 probes.
[DeviceA-nqa-admin-test1-icmp-echo] probe count 10
# Set the probe timeout time to 500 milliseconds for the ICMP echo operation.
[DeviceA-nqa-admin-test1-icmp-echo] probe timeout 500
# Configure the ICMP echo operation to repeat every 5000 milliseconds.
[DeviceA-nqa-admin-test1-icmp-echo] frequency 5000
# Enable saving history records.
[DeviceA-nqa-admin-test1-icmp-echo] history-record enable
# Set the maximum number of history records to 10.
[DeviceA-nqa-admin-test1-icmp-echo] history-record number 10
[DeviceA-nqa-admin-test1-icmp-echo] quit
# Start the ICMP echo operation.
[DeviceA] nqa schedule admin test1 start-time now lifetime forever
# After the ICMP echo operation runs for a period of time, stop the operation.
[DeviceA] undo nqa schedule admin test1
# Display the most recent result of the ICMP echo operation.
[DeviceA] display nqa result admin test1
NQA entry (admin admin, tag test1) test results:
Send operation times: 10 Receive response times: 10
Min/Max/Average round trip time: 2/5/3
Square-Sum of round trip time: 96
Last succeeded probe time: 2011-08-23 15:00:01.2
Extended results:
Packet loss ratio: 0%
Failures due to timeout: 0
Failures due to internal error: 0
Failures due to other errors: 0
# Display the history records of the ICMP echo operation.
[DeviceA] display nqa history admin test1
NQA entry (admin admin, tag test) history records:
Index Response Status Time
370 3 Succeeded 2007-08-23 15:00:01.2
369 3 Succeeded 2007-08-23 15:00:01.2
368 3 Succeeded 2007-08-23 15:00:01.2
367 5 Succeeded 2007-08-23 15:00:01.2
366 3 Succeeded 2007-08-23 15:00:01.2
365 3 Succeeded 2007-08-23 15:00:01.2
364 3 Succeeded 2007-08-23 15:00:01.1
363 2 Succeeded 2007-08-23 15:00:01.1
362 3 Succeeded 2007-08-23 15:00:01.1
361 2 Succeeded 2007-08-23 15:00:01.1
The output shows that the packets sent by Device A can reach Device B through Device C. No packet loss occurs during the operation. The minimum, maximum, and average round-trip times are 2, 5, and 3 milliseconds, respectively.
Example: Configuring the ICMP jitter operation
As shown in Figure 3, configure an ICMP jitter operation to test the jitter between Device A and Device B.
1. Assign IP addresses to interfaces, as shown in Figure 3. (Details not shown.)
2. Configure static routes or a routing protocol to make sure the devices can reach each other. (Details not shown.)
3. Configure Device A:
# Create an ICMP jitter operation.
[DeviceA-nqa-admin-test1] type icmp-jitter
# Specify 10.2.2.2 as the destination address for the operation.
[DeviceA-nqa-admin-test1-icmp-jitter] destination ip 10.2.2.2
# Configure the operation to repeat every 1000 milliseconds.
[DeviceA-nqa-admin-test1-icmp-jitter] frequency 1000
[DeviceA-nqa-admin-test1-icmp-jitter] quit
# Start the ICMP jitter operation.
# After the ICMP jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the ICMP jitter operation.
Min/Max/Average round trip time: 1/2/1
Square-Sum of round trip time: 13
Last packet received time: 2015-03-09 17:40:29.8
Extended results:
Packets out of sequence: 0
Packets arrived late: 0
ICMP-jitter results:
RTT number: 10
Min positive SD: 0 Min positive DS: 0
Max positive SD: 0 Max positive DS: 0
Positive SD number: 0 Positive DS number: 0
Positive SD sum: 0 Positive DS sum: 0
Positive SD average: 0 Positive DS average: 0
Positive SD square-sum: 0 Positive DS square-sum: 0
Min negative SD: 1 Min negative DS: 2
Max negative SD: 1 Max negative DS: 2
Negative SD number: 1 Negative DS number: 1
Negative SD sum: 1 Negative DS sum: 2
Negative SD average: 1 Negative DS average: 2
Negative SD square-sum: 1 Negative DS square-sum: 4
SD average: 1 DS average: 2
One way results:
Max SD delay: 1 Max DS delay: 2
Min SD delay: 1 Min DS delay: 2
Number of SD delay: 1 Number of DS delay: 1
Sum of SD delay: 1 Sum of DS delay: 2
Square-Sum of SD delay: 1 Square-Sum of DS delay: 4
Lost packets for unknown reason: 0
# Display the statistics of the ICMP jitter operation.
[DeviceA] display nqa statistics admin test1
NQA entry (admin admin, tag test1) test statistics:
NO. : 1
Start time: 2015-03-09 17:42:10.7
Life time: 156 seconds
Send operation times: 1560 Receive response times: 1560
Square-Sum of round trip time: 1563
Extended results:
RTT number: 1560
Min positive SD: 1 Min positive DS: 1
Max positive SD: 1 Max positive DS: 2
Positive SD number: 18 Positive DS number: 46
Positive SD sum: 18 Positive DS sum: 49
Positive SD average: 1 Positive DS average: 1
Positive SD square-sum: 18 Positive DS square-sum: 55
Min negative SD: 1 Min negative DS: 1
Negative SD number: 24 Negative DS number: 57
Negative SD sum: 24 Negative DS sum: 58
Negative SD average: 1 Negative DS average: 1
Negative SD square-sum: 24 Negative DS square-sum: 60
SD average: 16 DS average: 2
One way results:
Min SD delay: 1 Min DS delay: 1
Number of SD delay: 4 Number of DS delay: 4
Sum of SD delay: 4 Sum of DS delay: 5
Square-Sum of SD delay: 4 Square-Sum of DS delay: 7
Example: Configuring the DHCP operation
As shown in Figure 4, configure a DHCP operation to test the time required for Switch A to obtain an IP address from the DHCP server (Switch B).
# Create a DHCP operation.
[SwitchA] nqa entry admin test1
[SwitchA-nqa-admin-test1] type dhcp
# Specify the DHCP server address (10.1.1.2) as the destination address.
[SwitchA-nqa-admin-test1-dhcp] destination ip 10.1.1.2
# Enable the saving of history records.
[SwitchA-nqa-admin-test1-dhcp] history-record enable
[SwitchA-nqa-admin-test1-dhcp] quit
# Start the DHCP operation.
[SwitchA] nqa schedule admin test1 start-time now lifetime forever
# After the DHCP operation runs for a period of time, stop the operation.
[SwitchA] undo nqa schedule admin test1
# Display the most recent result of the DHCP operation.
[SwitchA] display nqa result admin test1
Send operation times: 1 Receive response times: 1
Min/Max/Average round trip time: 512/512/512
Square-Sum of round trip time: 262144
Last succeeded probe time: 2011-11-22 09:56:03.2
Extended results:
# Display the history records of the DHCP operation.
[SwitchA] display nqa history admin test1
NQA entry (admin admin, tag test1) history records:
1 512 Succeeded 2011-11-22 09:56:03.2
The output shows that it took Switch A 512 milliseconds to obtain an IP address from the DHCP server.
Example: Configuring the DNS operation
As shown in Figure 5, configure a DNS operation to test whether Device A can perform address resolution through the DNS server and test the resolution time.
# Assign IP addresses to interfaces, as shown in Figure 5. (Details not shown.)
# Create a DNS operation.
[DeviceA-nqa-admin-test1] type dns
# Specify the IP address of the DNS server (10.2.2.2) as the destination address.
[DeviceA-nqa-admin-test1-dns] destination ip 10.2.2.2
# Specify host.com as the domain name to be translated.
[DeviceA-nqa-admin-test1-dns] resolve-target host.com
[DeviceA-nqa-admin-test1-dns] history-record enable
[DeviceA-nqa-admin-test1-dns] quit
# Start the DNS operation.
# After the DNS operation runs for a period of time, stop the operation.
# Display the most recent result of the DNS operation.
Min/Max/Average round trip time: 62/62/62
Square-Sum of round trip time: 3844
Last succeeded probe time: 2011-11-10 10:49:37.3
Extended results:
# Display the history records of the DNS operation.
1 62 Succeeded 2011-11-10 10:49:37.3
The output shows that it took Device A 62 milliseconds to translate domain name host.com into an IP address.
Example: Configuring the FTP operation
As shown in Figure 6, configure an FTP operation to test the time required for Device A to upload a file to the FTP server. The login username and password are admin and systemtest, respectively. The file to be transferred to the FTP server is config.txt.
# Assign IP addresses to interfaces, as shown in Figure 6. (Details not shown.)
# Create an FTP operation.
[DeviceA-nqa-admin-test1] type ftp
# Specify the URL of the FTP server.
[DeviceA-nqa-admin-test-ftp] url ftp://10.2.2.2
# Specify 10.1.1.1 as the source IP address.
[DeviceA-nqa-admin-test1-ftp] source ip 10.1.1.1
# Configure the device to upload file config.txt to the FTP server.
[DeviceA-nqa-admin-test1-ftp] operation put
[DeviceA-nqa-admin-test1-ftp] filename config.txt
# Set the username to admin for the FTP operation.
[DeviceA-nqa-admin-test1-ftp] username admin
# Set the password to systemtest for the FTP operation.
[DeviceA-nqa-admin-test1-ftp] password simple systemtest
[DeviceA-nqa-admin-test1-ftp] history-record enable
[DeviceA-nqa-admin-test1-ftp] quit
# Start the FTP operation.
# After the FTP operation runs for a period of time, stop the operation.
# Display the most recent result of the FTP operation.
Min/Max/Average round trip time: 173/173/173
Square-Sum of round trip time: 29929
Last succeeded probe time: 2011-11-22 10:07:28.6
Extended results:
Failures due to disconnect: 0
Failures due to no connection: 0
# Display the history records of the FTP operation.
1 173 Succeeded 2011-11-22 10:07:28.6
The output shows that it took Device A 173 milliseconds to upload a file to the FTP server.
Example: Configuring the HTTP operation
As shown in Figure 7, configure an HTTP operation on the NQA client to test the time required to obtain data from the HTTP server.
# Assign IP addresses to interfaces, as shown in Figure 7. (Details not shown.)
# Create an HTTP operation.
[DeviceA-nqa-admin-test1] type http
# Specify the URL of the HTTP server.
[DeviceA-nqa-admin-test1-http] url http://10.2.2.2/index.htm
# Configure the HTTP operation to get data from the HTTP server.
[DeviceA-nqa-admin-test1-http] operation get
# Configure the operation to use HTTP version 1.0.
[DeviceA-nqa-admin-test1-http] version v1.0
[DeviceA-nqa-admin-test1-http] history-record enable
[DeviceA-nqa-admin-test1-http] quit
# Start the HTTP operation.
# After the HTTP operation runs for a period of time, stop the operation.
# Display the most recent result of the HTTP operation.
Min/Max/Average round trip time: 64/64/64
Square-Sum of round trip time: 4096
Last succeeded probe time: 2011-11-22 10:12:47.9
Extended results:
# Display the history records of the HTTP operation.
1 64 Succeeded 2011-11-22 10:12:47.9
The output shows that it took Device A 64 milliseconds to obtain data from the HTTP server.
Example: Configuring the UDP jitter operation
As shown in Figure 8, configure a UDP jitter operation to test the jitter, delay, and round-trip time between Device A and Device B.
1. Assign IP addresses to interfaces, as shown in Figure 8. (Details not shown.)
3. Configure Device B:
# Enable the NQA server.
[DeviceB] nqa server enable
# Configure a listening service to listen to UDP port 9000 on IP address 10.2.2.2.
[DeviceB] nqa server udp-echo 10.2.2.2 9000
4. Configure Device A:
# Create a UDP jitter operation.
[DeviceA-nqa-admin-test1] type udp-jitter
# Specify 10.2.2.2 as the destination address of the operation.
[DeviceA-nqa-admin-test1-udp-jitter] destination ip 10.2.2.2
# Set the destination port number to 9000.
[DeviceA-nqa-admin-test1-udp-jitter] destination port 9000
[DeviceA-nqa-admin-test1-udp-jitter] frequency 1000
[DeviceA-nqa-admin-test1-udp-jitter] quit
# Start the UDP jitter operation.
# After the UDP jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP jitter operation.
Min/Max/Average round trip time: 15/32/17
Square-Sum of round trip time: 3235
Last packet received time: 2011-05-29 13:56:17.6
Extended results:
UDP-jitter results:
RTT number: 10
Min positive SD: 4 Min positive DS: 1
Max positive SD: 21 Max positive DS: 28
Positive SD number: 5 Positive DS number: 4
Positive SD sum: 52 Positive DS sum: 38
Positive SD average: 10 Positive DS average: 10
Positive SD square-sum: 754 Positive DS square-sum: 460
Min negative SD: 1 Min negative DS: 6
Max negative SD: 13 Max negative DS: 22
Negative SD number: 4 Negative DS number: 5
Negative SD sum: 38 Negative DS sum: 52
Negative SD average: 10 Negative DS average: 10
Negative SD square-sum: 460 Negative DS square-sum: 754
SD average: 10 DS average: 10
One way results:
Max SD delay: 15 Max DS delay: 16
Min SD delay: 7 Min DS delay: 7
Number of SD delay: 10 Number of DS delay: 10
Sum of SD delay: 78 Sum of DS delay: 85
Square-Sum of SD delay: 666 Square-Sum of DS delay: 787
SD lost packets: 0 DS lost packets: 0
# Display the statistics of the UDP jitter operation.
NO. : 1
Start time: 2011-05-29 13:56:14.0
Life time: 47 seconds
Send operation times: 410 Receive response times: 410
Min/Max/Average round trip time: 1/93/19
Square-Sum of round trip time: 206176
Extended results:
UDP-jitter results:
RTT number: 410
Min positive SD: 3 Min positive DS: 1
Max positive SD: 30 Max positive DS: 79
Positive SD number: 186 Positive DS number: 158
Positive SD sum: 2602 Positive DS sum: 1928
Positive SD average: 13 Positive DS average: 12
Positive SD square-sum: 45304 Positive DS square-sum: 31682
Max negative SD: 30 Max negative DS: 78
Negative SD number: 181 Negative DS number: 209
Negative SD sum: 181 Negative DS sum: 209
Negative SD average: 13 Negative DS average: 14
Negative SD square-sum: 46994 Negative DS square-sum: 3030
SD average: 9 DS average: 1
One way results:
Max SD delay: 46 Max DS delay: 46
Number of SD delay: 410 Number of DS delay: 410
Sum of SD delay: 3705 Sum of DS delay: 3891
Square-Sum of SD delay: 45987 Square-Sum of DS delay: 49393
Example: Configuring the SNMP operation
As shown in Figure 9, configure an SNMP operation to test the time the NQA client uses to get a response from the SNMP agent.
1. Assign IP addresses to interfaces, as shown in Figure 9. (Details not shown.)
3. Configure the SNMP agent (Device B):
# Set the SNMP version to all.
[DeviceB] snmp-agent sys-info version all
# Set the read community to public.
[DeviceB] snmp-agent community read public
# Set the write community to private.
[DeviceB] snmp-agent community write private
# Create an SNMP operation.
[DeviceA-nqa-admin-test1] type snmp
# Specify 10.2.2.2 as the destination IP address of the SNMP operation.
[DeviceA-nqa-admin-test1-snmp] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-snmp] history-record enable
[DeviceA-nqa-admin-test1-snmp] quit
# Start the SNMP operation.
# After the SNMP operation runs for a period of time, stop the operation.
# Display the most recent result of the SNMP operation.
Min/Max/Average round trip time: 50/50/50
Square-Sum of round trip time: 2500
Last succeeded probe time: 2011-11-22 10:24:41.1
Extended results:
# Display the history records of the SNMP operation.
1 50 Succeeded 2011-11-22 10:24:41.1
The output shows that it took Device A 50 milliseconds to receive a response from the SNMP agent.
Example: Configuring the TCP operation
As shown in Figure 10, configure a TCP operation to test the time required for Device A to establish a TCP connection with Device B.
1. Assign IP addresses to interfaces, as shown in Figure 10. (Details not shown.)
# Configure a listening service to listen to TCP port 9000 on IP address 10.2.2.2.
[DeviceB] nqa server tcp-connect 10.2.2.2 9000
# Create a TCP operation.
[DeviceA-nqa-admin-test1] type tcp
# Specify 10.2.2.2 as the destination IP address.
[DeviceA-nqa-admin-test1-tcp] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-tcp] destination port 9000
[DeviceA-nqa-admin-test1-tcp] history-record enable
[DeviceA-nqa-admin-test1-tcp] quit
# Start the TCP operation.
# After the TCP operation runs for a period of time, stop the operation.
# Display the most recent result of the TCP operation.
Min/Max/Average round trip time: 13/13/13
Square-Sum of round trip time: 169
Last succeeded probe time: 2011-11-22 10:27:25.1
Extended results:
# Display the history records of the TCP operation.
1 13 Succeeded 2011-11-22 10:27:25.1
The output shows that it took Device A 13 milliseconds to establish a TCP connection to port 9000 on the NQA server.
Example: Configuring the UDP echo operation
As shown in Figure 11, configure a UDP echo operation on the NQA client to test the round-trip time to Device B. The destination port number is 8000.
1. Assign IP addresses to interfaces, as shown in Figure 11. (Details not shown.)
# Configure a listening service to listen to UDP port 8000 on IP address 10.2.2.2.
[DeviceB] nqa server udp-echo 10.2.2.2 8000
# Create a UDP echo operation.
[DeviceA-nqa-admin-test1] type udp-echo
[DeviceA-nqa-admin-test1-udp-echo] destination ip 10.2.2.2
# Set the destination port number to 8000.
[DeviceA-nqa-admin-test1-udp-echo] destination port 8000
[DeviceA-nqa-admin-test1-udp-echo] history-record enable
[DeviceA-nqa-admin-test1-udp-echo] quit
# Start the UDP echo operation.
# After the UDP echo operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP echo operation.
Min/Max/Average round trip time: 25/25/25
Square-Sum of round trip time: 625
Last succeeded probe time: 2011-11-22 10:36:17.9
Extended results:
# Display the history records of the UDP echo operation.
1 25 Succeeded 2011-11-22 10:36:17.9
The output shows that the round-trip time between Device A and port 8000 on Device B is 25 milliseconds.
Example: Configuring the UDP tracert operation
As shown in Figure 12, configure a UDP tracert operation to determine the routing path from Device A to Device B.
1. Assign IP addresses to interfaces, as shown in Figure 12. (Details not shown.)
3. Execute the ip ttl-expires enable command on the intermediate devices and execute the ip unreachables enable command on Device B.
# Create a UDP tracert operation.
[DeviceA-nqa-admin-test1] type udp-tracert
[DeviceA-nqa-admin-test1-udp-tracert] destination ip 10.2.2.2
# Set the destination port number to 33434.
[DeviceA-nqa-admin-test1-udp-tracert] destination port 33434
# Configure Device A to perform three probes to each hop.
[DeviceA-nqa-admin-test1-udp-tracert] probe count 3
# Set the probe timeout time to 500 milliseconds.
[DeviceA-nqa-admin-test1-udp-tracert] probe timeout 500
# Configure the UDP tracert operation to repeat every 5000 milliseconds.
[DeviceA-nqa-admin-test1-udp-tracert] frequency 5000
# Specify HundredGigE 1/0/1 as the output interface for UDP packets.
[DeviceA-nqa-admin-test1-udp-tracert] out interface hundredgige 1/0/1
# Enable the no-fragmentation feature.
[DeviceA-nqa-admin-test1-udp-tracert] no-fragment enable
# Set the maximum number of consecutive probe failures to 6.
[DeviceA-nqa-admin-test1-udp-tracert] max-failure 6
# Set the TTL value to 1 for UDP packets in the start round of the UDP tracert operation.
[DeviceA-nqa-admin-test1-udp-tracert] init-ttl 1
# Start the UDP tracert operation.
# After the UDP tracert operation runs for a period of time, stop the operation.
# Display the most recent result of the UDP tracert operation.
Send operation times: 6 Receive response times: 6
Min/Max/Average round trip time: 1/1/1
Last succeeded probe time: 2013-09-09 14:46:06.2
Extended results:
Packet loss in test: 0%
UDP-tracert results:
TTL Hop IP Time
1 3.1.1.1 2013-09-09 14:46:03.2
2 10.2.2.2 2013-09-09 14:46:06.2
# Display the history records of the UDP tracert operation.
Index TTL Response Hop IP Status Time
1 2 2 10.2.2.2 Succeeded 2013-09-09 14:46:06.2
1 2 1 10.2.2.2 Succeeded 2013-09-09 14:46:05.2
1 2 2 10.2.2.2 Succeeded 2013-09-09 14:46:04.2
1 1 1 3.1.1.1 Succeeded 2013-09-09 14:46:03.2
1 1 2 3.1.1.1 Succeeded 2013-09-09 14:46:02.2
1 1 1 3.1.1.1 Succeeded 2013-09-09 14:46:01.2
Example: Configuring the voice operation
As shown in Figure 13, configure a voice operation to test jitters, delay, MOS, and ICPIF between Device A and Device B.
1. Assign IP addresses to interfaces, as shown in Figure 13. (Details not shown.)
# Create a voice operation.
[DeviceA-nqa-admin-test1] type voice
[DeviceA-nqa-admin-test1-voice] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-voice] destination port 9000
[DeviceA-nqa-admin-test1-voice] quit
# Start the voice operation.
# After the voice operation runs for a period of time, stop the operation.
# Display the most recent result of the voice operation.
Send operation times: 1000 Receive response times: 1000
Min/Max/Average round trip time: 31/1328/33
Square-Sum of round trip time: 2844813
Last packet received time: 2011-06-13 09:49:31.1
Extended results:
Voice results:
RTT number: 1000
Max positive SD: 204 Max positive DS: 1297
Positive SD number: 257 Positive DS number: 259
Positive SD sum: 759 Positive DS sum: 1797
Positive SD average: 2 Positive DS average: 6
Positive SD square-sum: 54127 Positive DS square-sum: 1691967
Max negative SD: 203 Max negative DS: 1297
Negative SD number: 255 Negative DS number: 259
Negative SD sum: 759 Negative DS sum: 1796
Negative SD average: 2 Negative DS average: 6
Negative SD square-sum: 53655 Negative DS square-sum: 1691776
SD average: 2 DS average: 6
One way results:
Max SD delay: 343 Max DS delay: 985
Min SD delay: 343 Min DS delay: 985
Sum of SD delay: 343 Sum of DS delay: 985
Square-Sum of SD delay: 117649 Square-Sum of DS delay: 970225
Voice scores:
MOS value: 4.38 ICPIF value: 0
# Display the statistics of the voice operation.
NO. : 1
Start time: 2011-06-13 09:45:37.8
Life time: 331 seconds
Send operation times: 4000 Receive response times: 4000
Min/Max/Average round trip time: 15/1328/32
Square-Sum of round trip time: 7160528
Extended results:
Voice results:
RTT number: 4000
Max positive SD: 360 Max positive DS: 1297
Positive SD number: 1030 Positive DS number: 1024
Positive SD sum: 4363 Positive DS sum: 5423
Positive SD average: 4 Positive DS average: 5
Positive SD square-sum: 497725 Positive DS square-sum: 2254957
Max negative SD: 360 Max negative DS: 1297
Negative SD number: 1028 Negative DS number: 1022
Negative SD sum: 1028 Negative DS sum: 1022
Negative SD average: 4 Negative DS average: 5
Negative SD square-sum: 495901 Negative DS square-sum: 5419
One way results:
Max SD delay: 359 Max DS delay: 985
Min SD delay: 0 Min DS delay: 0
Sum of SD delay: 1390 Sum of DS delay: 1079
Square-Sum of SD delay: 483202 Square-Sum of DS delay: 973651
Voice scores:
Max MOS value: 4.38 Min MOS value: 4.38
Max ICPIF value: 0 Min ICPIF value: 0
Example: Configuring the DLSw operation
As shown in Figure 14, configure a DLSw operation to test the response time of the DLSw device.
# Assign IP addresses to interfaces, as shown in Figure 14. (Details not shown.)
# Create a DLSw operation.
[DeviceA-nqa-admin-test1] type dlsw
[DeviceA-nqa-admin-test1-dlsw] destination ip 10.2.2.2
[DeviceA-nqa-admin-test1-dlsw] history-record enable
[DeviceA-nqa-admin-test1-dlsw] quit
# Start the DLSw operation.
# After the DLSw operation runs for a period of time, stop the operation.
# Display the most recent result of the DLSw operation.
Min/Max/Average round trip time: 19/19/19
Square-Sum of round trip time: 361
Last succeeded probe time: 2011-11-22 10:40:27.7
Extended results:
# Display the history records of the DLSw operation.
1 19 Succeeded 2011-11-22 10:40:27.7
The output shows that the response time of the DLSw device is 19 milliseconds.
Example: Configuring the path jitter operation
As shown in Figure 15, configure a path jitter operation to test the round trip time and jitters from Device A to Device B and Device C.
# Assign IP addresses to interfaces, as shown in Figure 15. (Details not shown.)
# Execute the ip ttl-expires enable command on Device B and execute the ip unreachables enable command on Device C.
# Create a path jitter operation.
[DeviceA-nqa-admin-test1] type path-jitter
[DeviceA-nqa-admin-test1-path-jitter] destination ip 10.2.2.2
# Configure the path jitter operation to repeat every 10000 milliseconds.
[DeviceA-nqa-admin-test1-path-jitter] frequency 10000
[DeviceA-nqa-admin-test1-path-jitter] quit
# Start the path jitter operation.
# After the path jitter operation runs for a period of time, stop the operation.
# Display the most recent result of the path jitter operation.
Hop IP 10.1.1.2
Basic Results
Min/Max/Average round trip time: 9/21/14
Square-Sum of round trip time: 2419
Extended Results
Path-Jitter Results
Jitter number: 9
Min/Max/Average jitter: 1/10/4
Positive jitter number: 6
Min/Max/Average positive jitter: 1/9/4
Sum/Square-Sum positive jitter: 25/173
Negative jitter number: 3
Min/Max/Average negative jitter: 2/10/6
Sum/Square-Sum positive jitter: 19/153
Hop IP 10.2.2.2
Basic Results
Min/Max/Average round trip time: 15/40/28
Square-Sum of round trip time: 4493
Extended Results
Path-Jitter Results
Jitter number: 9
Example: Configuring NQA collaboration
As shown in Figure 16, configure a static route to Switch C with Switch B as the next hop on Switch A. Associate the static route, a track entry, and an ICMP echo operation to monitor the state of the static route.
1. Assign IP addresses to interfaces, as shown in Figure 16. (Details not shown.)
2. On Switch A, configure a static route, and associate the static route with track entry 1.
[SwitchA] ip route-static 10.1.1.2 24 10.2.1.1 track 1
3. On Switch A, configure an ICMP echo operation:
# Create an NQA operation with administrator name admin and operation tag test1.
# Configure the NQA operation type as ICMP echo.
[SwitchA-nqa-admin-test1] type icmp-echo
# Specify 10.2.1.1 as the destination IP address.
[SwitchA-nqa-admin-test1-icmp-echo] destination ip 10.2.1.1
# Configure the operation to repeat every 100 milliseconds.
[SwitchA-nqa-admin-test1-icmp-echo] frequency 100
# Create reaction entry 1. If the number of consecutive probe failures reaches 5, collaboration is triggered.
[SwitchA-nqa-admin-test1-icmp-echo] reaction 1 checked-element probe-fail threshold-type consecutive 5 action-type trigger-only
[SwitchA-nqa-admin-test1-icmp-echo] quit
# Start the ICMP operation.
4. On Switch A, create track entry 1, and associate it with reaction entry 1 of the NQA operation.
[SwitchA] track 1 nqa entry admin test1 reaction 1
# Display information about all the track entries on Switch A.
[SwitchA] display track all
Track ID: 1
State: Positive
Duration: 0 days 0 hours 0 minutes 0 seconds
Notification delay: Positive 0, Negative 0 (in seconds)
Tracked object:
NQA entry: admin test1
Reaction: 1
# Display brief information about active routes in the routing table on Switch A.
Destinations : 13 Routes : 13
0.0.0.0/32 Direct 0 0 127.0.0.1 InLoop0
10.1.1.0/24 Static 60 0 10.2.1.1 Vlan3
10.2.1.0/24 Direct 0 0 10.2.1.2 Vlan3
10.2.1.0/32 Direct 0 0 10.2.1.2 Vlan3
10.2.1.2/32 Direct 0 0 127.0.0.1 InLoop0
10.2.1.255/32 Direct 0 0 10.2.1.2 Vlan3
127.0.0.0/32 Direct 0 0 127.0.0.1 InLoop0
127.255.255.255/32 Direct 0 0 127.0.0.1 InLoop0
224.0.0.0/4 Direct 0 0 0.0.0.0 NULL0
224.0.0.0/24 Direct 0 0 0.0.0.0 NULL0
255.255.255.255/32 Direct 0 0 127.0.0.1 InLoop0
The output shows that the static route with the next hop 10.2.1.1 is active, and the status of the track entry is positive.
# Remove the IP address of VLAN-interface 3 on Switch B.
[SwitchB-Vlan-interface3] undo ip address
Track ID: 1
State: Negative
Tracked object:
Reaction: 1
Destinations : 12 Routes : 12
The output shows that the static route does not exist, and the status of the track entry is negative.
Example: Configuring the ICMP template
As shown in Figure 17, configure an ICMP template for a feature to perform the ICMP echo operation from Device A to Device B.
# Assign IP addresses to interfaces, as shown in Figure 17. (Details not shown.)
# Create ICMP template icmp.
[DeviceA] nqa template icmp icmp
[DeviceA-nqatplt-icmp-icmp] destination ip 10.2.2.2
[DeviceA-nqatplt-icmp-icmp] probe timeout 500
# Configure the ICMP echo operation to repeat every 3000 milliseconds.
[DeviceA-nqatplt-icmp-icmp] frequency 3000
# Configure the NQA client to notify the feature of the successful operation event if the number of consecutive successful probes reaches 2.
[DeviceA-nqatplt-icmp-icmp] reaction trigger probe-pass 2
# Configure the NQA client to notify the feature of the operation failure if the number of consecutive failed probes reaches 2.
[DeviceA-nqatplt-icmp-icmp] reaction trigger probe-fail 2
Example: Configuring the DNS template
As shown in Figure 18, configure a DNS template for a feature to perform the DNS operation. The operation tests whether Device A can perform the address resolution through the DNS server.
# Assign IP addresses to interfaces, as shown in Figure 18. (Details not shown.)
# Create DNS template dns.
[DeviceA] nqa template dns dns
# Specify the IP address of the DNS server (10.2.2.2) as the destination IP address.
[DeviceA-nqatplt-dns-dns] destination ip 10.2.2.2
[DeviceA-nqatplt-dns-dns] resolve-target host.com
# Set the domain name resolution type to type A.
[DeviceA-nqatplt-dns-dns] resolve-type A
# Specify 3.3.3.3 as the expected IP address.
[DeviceA-nqatplt-dns-dns] expect ip 3.3.3.3
[DeviceA-nqatplt-dns-dns] reaction trigger probe-pass 2
[DeviceA-nqatplt-dns-dns] reaction trigger probe-fail 2
Example: Configuring the TCP template
As shown in Figure 19, configure a TCP template for a feature to perform the TCP operation. The operation tests whether Device A can establish a TCP connection to Device B.
1. Assign IP addresses to interfaces, as shown in Figure 19. (Details not shown.)
# Create TCP template tcp.
[DeviceA] nqa template tcp tcp
[DeviceA-nqatplt-tcp-tcp] destination ip 10.2.2.2
[DeviceA-nqatplt-tcp-tcp] destination port 9000
[DeviceA-nqatplt-tcp-tcp] reaction trigger probe-pass 2
[DeviceA-nqatplt-tcp-tcp] reaction trigger probe-fail 2
Example: Configuring the TCP half open template
As shown in Figure 20, configure a TCP half open template for a feature to test whether Device B can provide the TCP service for Device A.
1. Assign IP addresses to interfaces, as shown in Figure 20. (Details not shown.)
# Create TCP half open template test.
[DeviceA] nqa template tcphalfopen test
[DeviceA-nqatplt-tcphalfopen-test] destination ip 10.2.2.2
[DeviceA-nqatplt-tcphalfopen-test] reaction trigger probe-pass 2
[DeviceA-nqatplt-tcphalfopen-test] reaction trigger probe-fail 2
Example: Configuring the UDP template
As shown in Figure 21, configure a UDP template for a feature to perform the UDP operation. The operation tests whether Device A can receive a response from Device B.
1. Assign IP addresses to interfaces, as shown in Figure 21. (Details not shown.)
# Create UDP template udp.
[DeviceA] nqa template udp udp
[DeviceA-nqatplt-udp-udp] destination ip 10.2.2.2
[DeviceA-nqatplt-udp-udp] destination port 9000
[DeviceA-nqatplt-udp-udp] reaction trigger probe-pass 2
[DeviceA-nqatplt-udp-udp] reaction trigger probe-fail 2
Example: Configuring the HTTP template
As shown in Figure 22, configure an HTTP template for a feature to perform the HTTP operation. The operation tests whether the NQA client can get data from the HTTP server.
# Assign IP addresses to interfaces, as shown in Figure 22. (Details not shown.)
# Create HTTP template http.
[DeviceA] nqa template http http
# Specify http://10.2.2.2/index.htm as the URL of the HTTP server.
[DeviceA-nqatplt-http-http] url http://10.2.2.2/index.htm
# Set the HTTP operation type to get.
[DeviceA-nqatplt-http-http] operation get
[DeviceA-nqatplt-http-http] reaction trigger probe-pass 2
[DeviceA-nqatplt-http-http] reaction trigger probe-fail 2
Example: Configuring the HTTPS template
As shown in Figure 23, configure an HTTPS template for a feature to test whether the NQA client can get data from the HTTPS server (Device B).
# Assign IP addresses to interfaces, as shown in Figure 23. (Details not shown.)
# Configure an SSL client policy named abc on Device A, and make sure Device A can use the policy to connect to the HTTPS server. (Details not shown.)
# Create HTTPS template test.
[DeviceA] nqa template https https
# Specify http://10.2.2.2/index.htm as the URL of the HTTPS server.
[DeviceA-nqatplt-https-https] url https://10.2.2.2/index.htm
# Specify SSL client policy abc for the HTTPS template.
[DeviceA-nqatplt-https- https] ssl-client-policy abc
# Set the HTTPS operation type to get (the default HTTPS operation type).
[DeviceA-nqatplt-https-https] operation get
# Set the HTTPS version to 1.0 (the default HTTPS version).
[DeviceA-nqatplt-https-https] version v1.0
[DeviceA-nqatplt-https-https] reaction trigger probe-pass 2
[DeviceA-nqatplt-https-https] reaction trigger probe-fail 2
Example: Configuring the FTP template
As shown in Figure 24, configure an FTP template for a feature to perform the FTP operation. The operation tests whether Device A can upload a file to the FTP server. The login username and password are admin and systemtest, respectively. The file to be transferred to the FTP server is config.txt.
# Assign IP addresses to interfaces, as shown in Figure 24. (Details not shown.)
# Create FTP template ftp.
[DeviceA] nqa template ftp ftp
[DeviceA-nqatplt-ftp-ftp] url ftp://10.2.2.2
[DeviceA-nqatplt-ftp-ftp] source ip 10.1.1.1
[DeviceA-nqatplt-ftp-ftp] operation put
[DeviceA-nqatplt-ftp-ftp] filename config.txt
# Set the username to admin for the FTP server login.
[DeviceA-nqatplt-ftp-ftp] username admin
# Set the password to systemtest for the FTP server login.
[DeviceA-nqatplt-ftp-ftp] password simple systemtest
[DeviceA-nqatplt-ftp-ftp] reaction trigger probe-pass 2
[DeviceA-nqatplt-ftp-ftp] reaction trigger probe-fail 2
Example: Configuring the RADIUS template
As shown in Figure 25, configure a RADIUS template for a feature to test whether the RADIUS server (Device B) can provide authentication service for Device A. The username and password are admin and systemtest, respectively. The shared key is 123456 for secure RADIUS authentication.
# Assign IP addresses to interfaces, as shown in Figure 25. (Details not shown.)
# Configure the RADIUS server. (Details not shown.)
# Create RADIUS template radius.
[DeviceA] nqa template radius radius
# Specify 10.2.2.2 as the destination IP address of the operation.
[DeviceA-nqatplt-radius-radius] destination ip 10.2.2.2
# Set the username to admin.
[DeviceA-nqatplt-radius-radius] username admin
# Set the password to systemtest.
[DeviceA-nqatplt-radius-radius] password simple systemtest
# Set the shared key to 123456 in plain text for secure RADIUS authentication.
[DeviceA-nqatplt-radius-radius] key simple 123456
[DeviceA-nqatplt-radius-radius] reaction trigger probe-pass 2
[DeviceA-nqatplt-radius-radius] reaction trigger probe-fail 2
Example: Configuring the SSL template
As shown in Figure 26, configure an SSL template for a feature to test whether Device A can establish an SSL connection to the SSL server on Device B.
# Assign IP addresses to interfaces, as shown in Figure 26. (Details not shown.)
# Configure an SSL client policy named abc on Device A, and make sure Device A can use the policy to connect to the SSL server on Device B. (Details not shown.)
# Create SSL template ssl.
[DeviceA] nqa template ssl ssl
# Set the destination IP address and port number to 10.2.2.2 and 9000, respectively.
[DeviceA-nqatplt-ssl-ssl] destination ip 10.2.2.2
[DeviceA-nqatplt-ssl-ssl] destination port 9000
# Specify SSL client policy abc for the SSL template.
[DeviceA-nqatplt-ssl-ssl] ssl-client-policy abc
[DeviceA-nqatplt-ssl-ssl] reaction trigger probe-pass 2