- 01-AAA configuration
- 02-802.1X configuration
- 04-Portal configuration
- 05-Web authentication configuration
- 06-Triple authentication configuration
- 07-Port security configuration
- 08-User profile configuration
- 10-Keychain configuration
- 11-Public key management
- 12-PKI configuration
- 13-IPsec configuration
- 14-SSH configuration
- 15-SSL configuration
- 16-Attack detection and prevention configuration
- 17-TCP attack prevention configuration
- 18-IP source guard configuration
- 19-ARP attack protection configuration
- 20-ND attack defense configuration
- 21-uRPF configuration
- 22-SAVI configuration
- 23-MFF configuration
- 24-FIPS configuration
- 25-Crypto engine configuration
- 26-MACsec configuration
- 27-802.1X client configuration
| 24-FIPS configuration | 113.11 KB |
Restrictions and guidelines: FIPS
Using the automatic reboot method to enter FIPS mode
Using the manual reboot method to enter FIPS mode
Manually triggering self-tests
Display and maintenance commands for FIPS
Example: Entering FIPS mode through automatic reboot
Example: Entering FIPS mode through manual reboot
Example: Exiting FIPS mode through automatic reboot
Example: Exiting FIPS mode through manual reboot
Configuring FIPS
About FIPS
Federal Information Processing Standards (FIPS) was developed by the National Institute of Standards and Technology (NIST) of the United States. FIPS specifies the requirements for cryptographic modules.
FIPS security levels
FIPS 140-2 defines four levels of security, named Level 1 to Level 4, from low to high. The device supports Level 2.
Unless otherwise noted, the term "FIPS" refers to Level-2 FIPS 140-2 in this document.
FIPS functionality
In FIPS mode, the device has strict security requirements. It performs self-tests on cryptography modules to verify that the modules are operating correctly.
A FIPS device also meets the functionality requirements defined in Network Device Protection Profile (NDPP) of Common Criteria (CC).
FIPS self-tests
To ensure correct operation of cryptography modules, FIPS provides self-test mechanisms, including power-up self-tests and conditional self-tests.
If a power-up self-test fails, the device where the self-test process exists reboots. If a conditional self-test fails, the device outputs a self-test failure message.
NOTE: If a self-test fails, contact H3C Support. |
Power-up self-tests
The power-up self-test examines the availability of FIPS-allowed cryptographic algorithms.
The device supports the following types of power-up self-tests:
· Known-answer test (KAT)
A cryptographic algorithm is run on data for which the correct output is already known. The calculated output is compared with the known answer. If they are not identical, the KAT test fails.
· Pairwise conditional test (PWCT)
¡ Signature and authentication test—The test is run when a DSA, RSA, or ECDSA asymmetrical key pair is generated. The system uses the private key to sign the specific data, and then uses the public key to authenticate the signed data. If the authentication is successful, the test succeeds.
¡ Encryption and decryption test—The test is run when an RSA asymmetrical key pair is generated. The system uses the public key to encrypt a plain text string, and then uses the private key to decrypt the encrypted text. If the decryption result is the same as the original plain text string, the test succeeds.
The power-up self-test examines the cryptographic algorithms listed in Table 1.
Table 1 Power-up self-tests list
Type |
Operations |
KAT |
Tests the following algorithms: · SHA1, SHA224, SHA256, SHA384, and SHA512. · HMAC-SHA1, HMAC-SHA224, HMAC-SHA256, HMAC-SHA384, and HMAC-SHA512. · AES. · RSA (signature and authentication). · ECDH. · DRBG. · GCM. · GMAC. |
PWCT |
Tests the following algorithms: · RSA (signature and authentication). · RSA (encryption and decryption). · DSA (signature and authentication). · ECDSA (signature and authentication). |
Conditional self-tests
A conditional self-test runs when an asymmetrical cryptographic module or a random number generator module is invoked. Conditional self-tests include the following types:
· PWCT signature and authentication—This test is run when a DSA or RSA asymmetrical key pair is generated. The system uses the private key to sign the specific data, and then uses the public key to authenticate the signed data. If the authentication is successful, the test succeeds.
· Continuous random number generator test—Runs when a random number is generated. The system compares the generated random number with the previously generated random number. If the two numbers are the same, the test fails. This test also runs when a DSA or RSA asymmetrical key pair is generated.
Requirements for key pairs and passwords
Before you reboot the device to enter FIPS mode, the system automatically removes all key pairs configured in non-FIPS mode and all FIPS-incompliant digital certificates. FIPS-incompliant digital certificates are MD5-based certificates with a key modulus length less than 2048 bits. You cannot log in to the device through SSH after the device enters FIPS mode. To log in to the device in FIPS mode through SSH, log in to the device through a console port and create a key pair for the SSH server.
The password for entering the device in FIPS mode must comply with the password control policies, such as password length, complexity, and aging policy. When the aging timer for a password expires, the system prompts you to change the password. If you adjust the system time after the device enters FIPS mode, the login password might expire before the next login, because the original system time is typically much earlier than the actual time.
Configuration rollback guidelines
Configuration rollback is supported in FIPS mode and also during a switch between FIPS mode and non-FIPS mode. After a configuration rollback between FIPS mode and non-FIPS mode, perform the following tasks:
1. Delete the local user and configure a new local user. Local user attributes include password, user role, and service type.
2. Save the current configuration file.
3. Specify the current configuration file as the startup configuration file.
4. Reboot the device. The new configuration takes effect after the reboot. During this process, do not exit the system or perform other operations.
If a device enters FIPS or non-FIPS mode through automatic reboot, configuration rollback fails. To support configuration rollback, you must execute the save command after the device enters FIPS or non-FIPS mode.
IRF compatibility
All devices in an IRF fabric must be operating in the same mode, whether in FIPS mode or non-FIPS mode.
To enable FIPS mode for an IRF fabric, you must reboot the entire IRF fabric.
Feature changes in FIPS mode
After the system enters FIPS mode, the following feature changes occur:
· The user login authentication mode can only be scheme.
· The FTP/TFTP server and client are disabled.
· The Telnet server and client are disabled.
· The HTTP server is disabled.
· SNMPv1 and SNMPv2c are disabled. Only SNMPv3 is available.
· The SSL server supports only TLS1.0, TLS1.1, and TLS1.2.
· The SSH server does not support SSHv1 clients or DSA key pairs.
· The generated RSA and DSA key pairs must have a modulus length of 2048 bits.
When the device acts as a server to authenticate a client through the public key, the key pair for the client must also have a modulus length of 2048 bits.
· The generated ECDSA key pairs must have a modulus length of more than 256 bits.
When the device acts as a server to authenticate a client through the public key, the key pair for the client must also have a modulus length of more than 256 bits.
· SSH, SNMPv3, IPsec, and SSL do not support DES, 3DES, RC4, or MD5.
· The password control feature cannot be disabled globally. The undo password-control enable command does not take effect.
· An AAA shared key, IKE pre-shared key, or SNMPv3 authentication key must have at least 15 characters and must contain uppercase and lowercase letters, digits, and special characters.
· The password for a device management local user and password for switching user roles must comply with the password control policies. By default, the password must have at least 15 characters and must contain uppercase and lowercase letters, digits, and special characters.
Entering FIPS mode
About entering FIPS mode
For the device to enter FIPS mode, you can use one of the following methods:
· Automatic reboot—The system automatically performs the following operations:
a. Prompts you to specify the username and password for the next login.
b. Creates a default FIPS configuration file named fips-startup.cfg.
c. Specifies the default FIPS configuration file as the startup configuration file.
d. Reboots and loads the default FIPS configuration file to enter the FIPS mode.
· Manual reboot—You must complete the required configuration tasks and reboot the device manually.
After you execute the fips mode enable command, the system prompts you to choose a reboot method.
· If you do not make a choice within 30 seconds or press Ctrl+C, the system enables FIPS mode and waits for you to manually complete the FIPS mode configuration tasks. You must complete the tasks or execute the undo fips mode enable command before saving the running configuration and rebooting the device. If you fail to do so, the device enters FIPS mode after startup and you cannot log in to the device.
· If you select the automatic reboot method, you can press Ctrl+C to abort both the interactive FIPS mode configuration process and the fips mode enable command.
To ensure login password effectiveness under the password control policies, set the correct system time.
1. Enter system view.
2. Enable FIPS mode.
fips mode enable
By default, the FIPS mode is disabled.
3. After the reboot method choice prompt appears, enter Y within 30 minutes.
The system starts the interactive FIPS mode configuration process.
4. Enter the login username and password as prompted.
The password must have a minimum of 15 characters and must contain uppercase and lowercase letters, digits, and special characters. After you enter the username and password, the device performs the following operations:
¡ Creates a device management local user that uses the entered username and password.
¡ Assigns the user the terminal service and the network-admin user role.
¡ Saves the running configuration and specifies the configuration file as the startup configuration file.
¡ Reboots, loads the startup configuration file, and enters FIPS mode.
To log in to the device, you must enter the configured username and password. After login, you are identified as the FIPS mode crypto officer.
1. To ensure login password effectiveness under the password control policies, set the correct system time.
2. Configure the password control feature.
a. Enable the password control feature globally.
b. Configure password control policies.
- Set the number of character types a password must contain to 4.
- Set the minimum number of characters for each type to one character.
- Set the minimum length for a user password to 15 characters.
For more information about the password control feature, see password control in Security Configuration Guide.
3. Configure a local user.
¡ Create a device management local user.
¡ Specify a password that complies with the password control policies.
¡ Assign the terminal service to the user.
¡ Assign the network-admin user role to the user.
fips mode enable
3. After the reboot method choice prompt appears, enter N.
The system enables FIPS mode and waits for you to complete the FIPS mode configuration tasks. Before rebooting the device to enter FIPS mode, do not execute any commands except for save and commands used to prepare for entering FIPS mode. If you execute any other commands, the commands might not take effect.
4. Save the running configuration and specify the configuration file as the startup configuration file.
5. Delete the .mdb startup configuration file.
When loading a .mdb configuration file, the device loads all settings in the file. The settings that are not supported in FIPS mode might affect device operation.
6. Reboot the device.
The device reboots, loads the startup configuration file, and enters FIPS mode. To log in to the device, you must enter the configured username and password. After login, you are identified as the FIPS mode crypto officer.
About triggering self-tests
You can manually trigger FIPS self-tests to verify operation of cryptography modules anytime as required. The triggered self-tests are the same as the power-up self-tests. If the self-tests fail, the device where the self-test process exists reboots.
2. Trigger self-tests.
fips self-test
Exiting FIPS mode
About exiting FIPS mode
After you disable FIPS mode and reboot the device, the device operates in non-FIPS mode.
For the device to exit FIPS mode, you can use one of the following reboot methods:
· Automatic reboot—The system automatically creates a default non-FIPS configuration file named non-fips-startup.cfg, specifies the file as the startup configuration file, and reboots to enter non-FIPS mode. You can log in to the device without providing username or password.
· Manual reboot—You must manually complete the configuration tasks for entering non-FIPS mode, and then reboot the device. To log in to the device after the reboot, you must enter user information as required by the authentication mode settings.
The following are the default authentication mode settings:
¡ VTY line—Password authentication.
¡ AUX line—Authentication is disabled.
You can modify the authentication settings as needed.
Using the automatic reboot method to exit FIPS mode
2. Disable FIPS mode.
3. Select the automatic reboot method.
Using the manual reboot method to exit FIPS mode
3. Select the manual reboot method.
4. Configure login authentication settings.
¡ If you logged in to the device through SSH, perform the following tasks without disconnecting the current user line:
- Set the authentication mode to scheme for VTY lines.
- Specify the username and password. If you do not specify the username or password, the device uses the current username and password.
¡ If you logged in to the device through a console port, configure login authentication settings for the current type of user lines as described in the following table:
Current login method |
Login authentication requirements |
Scheme |
Set the authentication to scheme and specify the username and password. If you do not specify the username or password, the device uses the current username and password. |
Password |
Set the authentication to password and specify the password. If you do not specify the password, the device uses the current password. |
None |
Set the authentication to none. |
5. Save the running configuration and specify the file as the startup configuration file.
6. Delete the .mdb startup configuration file.
7. Reboot the device.
Task |
Command |
Display the version number of the device algorithm base. |
display crypto version |
Display the FIPS mode state. |
display fips status |
FIPS configuration examples
Use the automatic reboot method to enter FIPS mode, and use a console port to log in to the device in FIPS mode.
# If you want to save the current configuration, execute the save command before you enable FIPS mode.
# Enable FIPS mode and choose the automatic reboot method to enter FIPS mode. Set the username to root and the password to 12345zxcvb!@#$%ZXCVB.
[Sysname] fips mode enable
FIPS mode change requires a device reboot. Continue? [Y/N]:y
Reboot the device automatically? [Y/N]:y
The system will create a new startup configuration file for FIPS mode. After you set the login username and password for FIPS mode, the device will reboot automatically.
Enter username(1-55 characters):root
Enter password(15-63 characters):
Confirm password:
Waiting for reboot... After reboot, the device will enter FIPS mode.
After the device reboots, enter a username of root and a password of 12345zxcvb!@#$%ZXCVB. The system prompts you to configure a new password. After you configure the new password, the device enters FIPS mode. The new password must be different from the previous password. It must include at least 15 characters, and contain uppercase and lowercase letters, digits, and special characters. For more information about the requirements for the password, see the system output.
Press ENTER to get started.
login: root
Password:
First login or password reset. For security reason, you need to change your password. Please enter your password.
old password:
new password:
confirm:
<Sysname>
# Display the FIPS mode state.
<Sysname> display fips status
FIPS mode is enabled.
# Display the default configuration file.
<Sysname> more fips-startup.cfg
local-user root class manage
service-type terminal
fips mode enable
return
<Sysname>
Use the manual reboot method to enter FIPS mode, and use a console port to log in to the device in FIPS mode.
# Enable the password control feature globally.
# Set the number of character types a password must contain to 4, and set the minimum number of characters for each type to one character.
[Sysname] password-control composition type-number 4 type-length 1
# Set the minimum length of user passwords to 15 characters.
[Sysname] password-control length 15
# Add a local user account for device management, including a username of test, a password of 12345zxcvb!@#$%ZXCVB, a user role of network-admin, and a service type of terminal.
[Sysname-luser-manage-test] password simple 12345zxcvb!@#$%ZXCVB
[Sysname-luser-manage-test] authorization-attribute user-role network-admin
[Sysname-luser-manage-test] service-type terminal
# Enable FIPS mode, and choose the manual reboot method to enter FIPS mode.
Reboot the device automatically? [Y/N]:n
Change the configuration to meet FIPS mode requirements, save the configuration to the next-startup configuration file, and then reboot to enter FIPS mode.
# Save the current configuration to the root directory of the storage medium, and specify it as the startup configuration file.
[Sysname] save
[Sysname] quit
# Delete the startup configuration file in binary format.
<Sysname> delete flash:/startup.mdb
Delete flash:/startup.mdb?[Y/N]:y
Deleting file flash:/startup.mdb...Done.
# Reboot the device.
<Sysname> reboot
login: test
Password:
old password:
new password:
confirm:
<Sysname>
After logging in to the device in FIPS mode through a console port, use the automatic reboot method to exit FIPS mode.
# Disable FIPS mode.
[Sysname] undo fips mode enable
The system will create a new startup configuration file for non-FIPS mode and then reboot automatically. Continue? [Y/N]:y
Waiting for reboot... After reboot, the device will enter non-FIPS mode.
After the device reboots, you can enter the system.
<Sysname>
After logging in to the device in FIPS mode through the console port with username test and password 12345zxcvb!@#$%ZXCVB, use the manual reboot method to exit FIPS mode.
The system will create a new startup configuration file for non-FIPS mode, and then reboot automatically. Continue? [Y/N]:n
Change the configuration to meet non-FIPS mode requirements, save the configuration to the next-startup configuration file, and then reboot to enter non-FIPS mode.
[Sysname] save
[Sysname] quit
<Sysname> reboot
After the device reboots, authentication is disabled for console login by default. You can press Enter to enter non-FIPS mode without authentication.
login: test
Password:
Last successfully login time:…
<Sysname>