01-Installation Guide | 4.33 MB |
Examining the installation site
Installing the switch in a 19-inch rack
Rack-mounting procedures at a glance
Chassis dimensions and rack requirements
Mounting brackets, chassis rails, and grounding cable installation positions
Attaching the mounting brackets and chassis rails to the chassis
Connecting the grounding cable to the chassis
Attaching the slide rails to the rack
Mounting the switch in the rack
Installing and removing fan trays
Installing and removing power supplies
Connecting a power cord to an LSVM1AC650 or PSR450-12A power supply
Connecting a power cord to an LSVM1DC650 power supply
Accessing the switch for the first time
Connecting the switch to a configuration terminal
Connecting a DB9-to-RJ45 console cable
Connecting a USB-to-RJ45 console cable
Connecting a mini USB console cable
Maintenance and troubleshooting
Configuration terminal display issues
Preparing for installation
The S6550XE-HI switch series has one model: S6550XE-56HF-HI.
The S6550X-HI switch series has one model: S6550X-32Q-HI.
Safety recommendations
To avoid any equipment damage or bodily injury, read the following safety recommendations before installation. Note that the recommendations do not cover every possible hazardous condition.
· Before cleaning the switch, remove all power cords from the switch. Do not clean the switch with wet cloth or liquid.
· Do not place the switch near water or in a damp environment. Prevent water or moisture from entering the switch chassis.
· Do not place the switch on an unstable case or desk. The switch might be severely damaged in case of a fall.
· Ensure good ventilation of the equipment room and keep the air inlet and outlet vents of the switch free of obstruction.
· Make sure the operating voltage is in the required range.
· To avoid electrical shocks, do not open the chassis while the switch is operating or when the switch is just powered off.
· To avoid ESD damage, always wear an ESD wrist strap when replacing a power supply or fan tray.
You must install the switch indoors and make sure the following requirements are met:
· Adequate clearance is reserved at the air inlet and outlet vents for ventilation.
· The rack has a good ventilation system.
· Identify the hot aisle and cold aisle at the installation site, and make sure ambient air flows into the switch from the cold aisle and exhausts to the hot aisle.
· Identify the airflow designs of neighboring devices, and prevent hot air flowing out of the neighboring devices from entering the top device.
· The rack is sturdy enough to support the switch and its accessories.
· The rack is reliably grounded.
To ensure correct operation and long service life of your switch, install it in an environment that meets the requirements described in the following subsections.
Temperature/humidity
Maintain temperature and humidity in the equipment room at acceptable ranges.
· Lasting high relative humidity can cause poor insulation, electricity leakage, mechanical property change of materials, and metal corrosion.
· Lasting low relative humidity can cause washer contraction and ESD and cause issues including loose mounting screws and circuit failure.
· High temperature can accelerate the aging of insulation materials and significantly lower the reliability and lifespan of the switch.
For the temperature and humidity requirements, see hardware information and specifications for the switch.
Cleanliness
Dust buildup on the chassis might cause electrostatic adsorption and dust corrosion, resulting in poor contact of metal connectors and contact points. This might shorten the device's lifetime and even cause device failure in the worst case. Table 1 describes the dust concentration limits in the equipment room.
Table 1 Dust concentration limits in the equipment room for the switch
Dust |
Particle diameter |
Maximum allowable concentration |
Dust particles |
≥ 0.5 µm |
3.5 × 106 particles/m3 |
Dust particles |
≥ 5 µm |
3 × 104 particles/m3 |
Dust (suspension) |
≤ 75 µm |
0.2 mg/m3 |
Dust (sedimentation) |
75 µm to 150 µm |
1.5 mg/(m2h) |
To maintain cleanliness in the equipment room, follow these guidelines:
· Keep the equipment room away from pollution sources. Do not smoke, eat, or drink in the equipment room.
· Use double-glazed windows and seal doors and windows with dust-proof rubber strips. Use screen doors and window screens for doors and windows open to the outside and make sure the external windows are air tight.
· Use dustproof materials for floors, walls, and ceilings and use wallpaper or matt paint that does not produce powders.
· Clean the equipment room regularly and clean the air filters of the rack each month.
· Wear ESD clothing and shoe covers before entering the equipment room. Keep the ESD clothing and shoe covers clean and change them frequently.
Corrosive gas limit
Corrosive gases can accelerate corrosion and aging of metal components. Make sure the corrosive gases in the equipment room do not exceed the concentration limits as shown in Table 2.
Table 2 Corrosive gas concentration limits in the equipment room
Gas |
Average concentration (mg/m3) |
Maximum allowable concentration (mg/m3) |
SO2 |
0.3 |
1.0 |
H2S |
0.1 |
0.5 |
Cl2 |
0.1 |
0.3 |
HCI |
0.1 |
0.5 |
HF |
0.01 |
0.03 |
NH3 |
1.0 |
3.0 |
O3 |
0.05 |
0.1 |
NOX |
0.5 |
1.0 |
CAUTION: As a best practice, control the corrosive gas in the equipment room at the average concentration values. Make sure the corrosive gas will not be in their maximum allowable concentration values for over 30 minutes per day. |
To control corrosive gases, use the following guidelines:
· As a best practice, do not build the equipment room in a place with a high concentration of corrosive gases.
· Make sure the equipment room is not connected to sewer, vertical shaft, or septic tank pipelines and keep it far away from these pipelines. The air inlets in the equipment room must be away from such pollution sources.
· Use environmentally friendly materials to decorate the equipment room. Avoid using organic materials that contain harmful gases, such as sulfur or chlorine-containing insulation cottons, rubber mats, sound-proof cottons, and avoid using plasterboards with high sulfur concentration.
· Place fuel (diesel or gasoline) engines separately. Do not place them in the same equipment room with the device. Make sure the air exhausted from the engines will not flow into the equipment room or towards the air inlets of the air conditioners.
· Place batteries separately. Do not place them in the same room with the device.
· Employ a professional company to monitor and control corrosive gases in the equipment room regularly.
EMI
All electromagnetic interference (EMI) sources, from outside or inside of the switch and application system, adversely affect the switch in the following ways:
· A conduction pattern of capacitance coupling.
· Inductance coupling.
· Electromagnetic wave radiation.
· Common impedance (including the grounding system) coupling.
To prevent EMI, use the following guidelines:
· If AC power is used, use a single-phase three-wire power receptacle with protection earth (PE) to filter interference from the power grid.
· Keep the switch far away from radio transmitting stations, radar stations, and high-frequency devices.
· Use electromagnetic shielding, for example, shielded interface cables, when necessary.
· To prevent signal ports from getting damaged by overvoltage or overcurrent caused by lightning strikes, route interface cables only indoors.
Laser safety
WARNING! · The switch is a Class 1M laser device. · Disconnected optical fibers or transceiver modules might emit invisible laser light. Do not stare into beams or view directly with optical instruments when the switch is operating. |
Installation tools
No installation tools are provided with the switch. Prepare the following tools yourself:
· Flat-head screwdriver.
· Phillips screwdriver.
· ESD wrist strap.
· Marker.
CAUTION: Keep the tamper-proof seal on a mounting screw on the chassis cover intact, and if you want to open the chassis, contact H3C for permission. Otherwise, H3C shall not be liable for any consequence caused thereby. |
Figure 1 Hardware installation flow
Figure 2 Rack-mounting procedure
NOTE: If a rack shelf is available, you can put the switch on the rack shelf and slide the switch to a position so that the mounting brackets make close contact with the front rack posts. Then use screws to secure the mounting brackets to the rack. |
Table 3 Chassis dimensions and installation requirements for the rack
Installation method |
Chassis dimensions |
Requirements for the distance between the front and rear rack posts |
Rack requirements |
S6550XE-56HF-HI |
Mounting brackets and long slide rails (provided) |
· Height—43.6 mm (1.72 in)/1 RU · Width—440 mm (17.32 in) · Depth—486 mm (19.13 in) ¡ 460 mm (18.11 in) for the chassis ¡ 26 mm (1.02 in) for the power supply/fan tray handle |
692 to 853 mm (27.24 to 33.58 in) |
To close the rack door easily after cabling the switch, make sure the rack meets the following requirements for depth: · A minimum of 800 mm (31.50 in) in depth (recommended) · A minimum of 130 mm (5.12 in) between the front rack post and the front door. · A minimum of 550 mm (21.65 in) between the front rack post and the rear door. |
Mounting brackets and super-short slide rails (optional, chassis rails not reaching out of the chassis) |
401 to 565 mm (15.79 to 22.24 in) |
Mounting brackets and super-short slide rails (optional, chassis rails reaching out of the chassis) |
499 to 692 mm (19.65 to 27.24 in) |
S6550X-32Q-HI |
Mounting brackets and long slide rails (optional) |
· Height—43.6 mm (1.72 in)/1 RU · Width—440 mm (17.32 in) · Depth—426 mm (16.77 in) ¡ 400 mm (15.75 in) for the chassis ¡ 26 mm (1.02 in) for the power supply/fan tray handle |
634 to 719 mm (24.96 to 28.31 in) |
To close the rack door easily after cabling the switch, make sure the rack meets the following requirements for depth: · A minimum of 800 mm (31.50 in) in depth (recommended) · A minimum of 130 mm (5.12 in) between the front rack post and the front door. A minimum of 550 mm (21.65 in) between the front rack post and the rear door. |
Front mounting brackets installed at the port side |
397 to 523 mm (15.63 to 20.59 in) |
504 to 612 mm (19.84 to 24.09 in) |
Front mounting brackets installed at the power supply side |
430 to 538 mm (16.93 to 21.18 in) |
Installation accessories
Table 4 Installation accessories
Mounting brackets (provided) |
Rack mounting rail kit |
Rack mounting rail kit product code |
1U high, one pair. See Figure 3. |
1U high, including one pair of long slide rails and one pair of chassis rails. See Figure 4. |
2150A050 |
1U high, including one pair of super-short slide rails and one pair of chassis rails. See Figure 5. |
2150A0CP |
Figure 4 1U long slide rail and chassis rail
(1) Chassis rail |
(2) Long slide rail |
Figure 5 1U super-short slide rail and chassis rail
(1) Chassis rail |
(2) Super-short slide rail |
The switch has one mounting position near the network ports and one mounting position near the power supplies for mounting brackets.
The S6550XE-56HF-HI switch provides a primary grounding point and an auxiliary grounding point. The primary grounding point has a grounding sign.
The S6550X-32Q-HI provides one grounding point. The grounding point has a grounding sign.
The following procedures uses an S6550XE-56HF-HI as an example.
Figure 6 Mounting brackets and grounding cable installation positions on the switch
(1) Power supply-side installation position for the mounting bracket |
(2) Primary grounding point |
(3) Auxiliary grounding point |
(4) Port-side installation position for the mounting bracket |
1. Place the wide flange of the mounting bracket against the chassis side panel. Align the mounting bracket installation holes with the screw holes in the chassis. Use the provided M4 screws to attach the mounting bracket to the chassis.
As a best practice, use a torque of 12 kgf-cm (1.18 Nm) to fasten M4 screws.
¡ To install the mounting brackets at the port-side mounting position, use the four front mounting holes in the mounting brackets. See Figure 7, Figure 8, and Figure 9.
¡ To install the mounting brackets at the power supply-side mounting position, use the four rear mounting holes in the mounting brackets. See Figure 10, Figure 11, and Figure 12.
2. Determine the installation position of the chassis rails based on the position of mounting brackets and the distance between the front and rear rack posts.
3. Place the chassis rail against the chassis side panel. Align the chassis rail installation holes with the screw holes. Use the provided M4 screws to attach the chassis rail to the chassis. See Figure 7 to Figure 12.
Figure 7 Attaching the mounting brackets and chassis rails to the switch (port-side mounting position for the mounting brackets, long slide rails)
Figure 12 Attaching the mounting brackets and chassis rails to the switch (power supply-side mounting position for the mounting brackets, super-short slide rails, chassis rails reaching out of the chassis)
NOTE: Use the same procedure to attach the mounting brackets and chassis rails to the two sides of the chassis. |
CAUTION: If you use a grounding point to ground the switch, you must connect the grounding cable to the grounding point before you mount the switch in the rack. |
The switch provides a primary grounding point and auxiliary grounding point on the left panel. The primary grounding point has a grounding sign and the auxiliary grounding point does not.
The grounding cable connection procedure is the same for the primary and auxiliary grounding points. The following procedure connects the grounding cable to the primary grounding point.
To connect the grounding cable to the primary grounding point:
1. Choose a grounding point as required.
When you install the mounting brackets at the port-side mounting position, choose the auxiliary grounding point. When you install the mounting brackets at the power supply-side mounting position, choose the primary grounding point.
2. Unpack the grounding cable and grounding screws.
3. Use the two grounding screws to attach the two-hole grounding lug of the grounding cable to the grounding holes at the grounding point. Use a screwdriver to fasten the screws. See Figure 13.
As a best practice, use a torque of 20 kgf-cm (1.96 Nm) to fasten the grounding screws.
Figure 13 Connecting the grounding cable to the primary grounding point
1. Identify the slide rail installation position in the rack.
2. Install cage nuts (user-supplied) in the mounting holes in the rack posts.
3. Align the screw holes in one slide rail with the cage nuts in a rear rack post. Use user-supplied M6 screws to attach the slide rail to the post. See Figure 14.
As a best practice, use a torque of 30 kgf-cm (2.94 Nm) to fasten M6 screws.
4. Repeat the preceding steps to attach the other slide rail to the other rear rack post.
Keep the two slide rails at the same height so the slide rails can attach into the chassis rails.
Figure 14 Installing the slide rails
This task requires two people.
To mount the switch in the rack:
1. Wear an ESD wrist strap and make sure it makes good skin contact and is reliably grounded.
2. Verify that the mounting brackets and chassis rails have been securely attached to the switch chassis.
3. Verify that the slide rails have been correctly attached to the rear rack posts.
4. Attach cage nuts (user-supplied) to the front rack posts and make sure they are at the same level as the slide rails.
5. One person performs the following operations:
a. Supporting the bottom of the switch, aligns the chassis rails with the slide rails on the rack posts.
b. Pushes the switch slowly to slide the chassis rails along the slide rails until the mounting brackets are flush with the rack posts.
IMPORTANT: If you use long slide rails to rack-mount the switch, make sure the front ends of the long slide rails reach out of the chassis rails for a maximum of 20 mm (0.79 in). If you use super-short slide rails to rack-mount the switch, make sure the front ends of the super-short slide rails reach inside the chassis rails for a minimum of 90 mm (3.54 in) after installation. |
6. Another person uses user-supplied M6 screws to attach the mounting brackets to the rack.
Figure 15 Mounting the switch in the rack (port-side mounting position for the mounting brackets)
Figure 16 Mounting the switch in the rack (power supply-side mounting position for the mounting brackets)
Grounding the switch
CAUTION: · Correctly connecting the grounding cable is crucial to lightning protection and EMI protection. · Connect the grounding cable to the grounding system in the equipment room. Do not connect it to a fire main or lightning rod. · As a best practice to guarantee the grounding effect, use the grounding cable provided with the switch to connect to the grounding strip in the equipment room. |
The power input end of the switch has a noise filter, whose central ground is directly connected to the chassis to form the chassis ground (commonly known as PGND). You must securely connect this chassis ground to the earth so the faradism and leakage electricity can be safely released to the earth to minimize EMI susceptibility of the switch.
To connect the grounding cable to a grounding strip:
1. Attach the two-hole grounding lug of the grounding cable to a grounding point on the chassis. For more information, see "Connecting the grounding cable to the chassis."
2. Remove the hex nut of a grounding post on the grounding strip.
3. Attach the ring terminal of the grounding cable to the grounding post on the grounding strip, and secure the ring terminal to the grounding post with the hex nut.
Figure 17 Connecting the grounding cable to a grounding strip
(1) Hex nut |
(2) Ring terminal |
(3) Grounding post |
(4) Grounding strip |
NOTE: The grounding terminals in this figure are for illustration only. |
CAUTION: The switch has multiple fan tray slots. To ensure good ventilation of the switch, follow these guidelines to install and remove fan trays: · The switch is provided with the fan tray slots empty. Before powering on the switch, make sure all fan tray slots have fan trays installed and the fan trays are the same model. · Make sure all slots have a module or filler panel installed when the switch is operating. · If multiple fan trays fail on an operating switch, do not remove the fan trays at the same time. Replace the fan trays one after another and finish replacing each fan tray within 3 minutes. |
The installation and removal procedures are the same for the LSWM1FANSA, LSWM1FANSAB, and FAN-40F-1-A fan trays. The following installation and removal procedures use the LSWM1FANSA fan tray as an example.
Installing a fan tray
CAUTION: To prevent damage to the fan tray or the connectors on the backplane, insert the fan tray gently. If you encounter a hard resistance while inserting the fan tray, pull out the fan tray and insert it again. |
Select fan trays for the switch as needed. For the available fan trays and their specifications, see hardware information and specifications for the switch.
To install a fan tray:
2. Unpack the fan tray and verify that the fan tray model is correct.
3. Orient the fan tray with the "TOP" mark on top. Grasp the handle of the fan tray with one hand and support the fan tray bottom with the other, and slide the fan tray along the guide rails into the slot until the fan tray is fully seated in the slot and has a firm contact with the backplane. See Figure 18.
Figure 18 Installing an LSWM1FANSA fan tray in the switch
Removing a fan tray
WARNING! · Ensure electricity safety and never touch the rotating fans when you hot-swap a fan tray. · To prevent a fan from causing loud noise, do not touch the fan blades and rotation axis, even if the fan is not rotating. |
To remove a fan tray:
2. Grasp the handle of the fan tray with one hand and pull the fan tray part way out of the slot. Support the fan tray bottom with the other and pull the fan tray completely out of the slot.
3. Put the removed fan tray in an antistatic bag.
Figure 19 Removing an LSWM1FANSA fan tray
WARNING! · To avoid bodily injury and device damage, strictly follow the procedures in Figure 20 and Figure 21 to install and remove a power supply. · Provide a separate circuit breaker for each power supply. |
Figure 20 Installation procedure
Installing a power supply
CAUTION: · Follow the forward inertia of the power supply when inserting it into the chassis, and make sure the power supply has firm contact with the connectors on the backplane. · To prevent damage to the connectors inside the switch chassis, insert the power supply gently. If you encounter a hard resistance while inserting the power supply, pull out the power supply and insert it again. |
To install a power supply:
2. Remove the filler panel, if any, from the target power supply slot, as shown in Figure 22.
Figure 22 Removing a filler panel
3. Unpack the power supply and verify that the power supply model is correct.
4. Correctly orient the power supply with the words on the power supply upward. Grasp the handle of the power supply with one hand and support its bottom with the other, and slide the power supply slowly along the guide rails into the slot.
The slot is foolproof. If you cannot insert the power supply into the slot, re-orient the power supply rather than use excessive force to push it in.
Figure 23 Installing a power supply (LSVM1AC650)
Removing a power supply
CAUTION: When the switch has two power supplies in 1+1 redundancy mode, removing one power supply does not affect the operation of the switch. When the switch has only one power supply installed, removing the power supply powers off the switch. |
To remove a power supply:
2. Remove the power cord from the power supply. To remove a DC power cord, squeeze the tabs on the power cord connector with your thumb and forefinger, and then pull the connector out, as shown in Figure 24.
3. Hold the handle on the power supply with one hand, pivot the latch on the power supply to the right with your thumb, and pull the power supply part way out of the slot, as shown in Figure 25.
4. Supporting the power supply bottom with one hand, slowly pull the power supply out with the other hand.
5. Put the removed power supply in an antistatic bag for future use.
6. If you are not to install a new power supply, install a filler panel in the slot to ensure good ventilation in the switch, as shown in Figure 26.
Figure 24 Removing the DC power cord
(1) Press the tabs on the power cord connector with your thumb and forefinger |
(2) Pull the power cord connector out |
Figure 25 Removing the power supply
(1) Pivot the latch to the right with your thumb |
(2) Pull the power supply out |
Figure 26 Installing a filler panel
Connecting the power cords
WARNING! Provide a circuit breaker for each power input. When you connect a power cord, make sure the circuit breaker is switched off. |
The procedure is the same for connecting a power cord to an LSVM1AC650 and a PSR450-12A power supply. The following procedure connects a power cord to an LSVM1AC650.
To connect a power cord:
1. Insert the female connector of the power cord supplied with the power supply into the power receptacle on the power supply.
2. Use a cable tie to secure the power cord to the handle of the power supply, as shown in Figure 27.
3. Connect the other end of the power cord to a power outlet.
Figure 27 Connecting a power cord to the LSVM1AC650 power supply
(1) Cable tie |
(2) Tighten the cable tie to secure the power cord to the handle of the power supply |
1. Align the power cord plug with the power receptacle on the power supply, and insert the plug into the receptacle (see Figure 28).
The plug and receptacle are foolproof. If you cannot insert the plug into the receptacle, re-orient the plug rather than use excessive force to push it in.
3. Connect the other end of the power cord to the DC power source.
Figure 28 Connecting a power cord to the LSVM1DC650 power supply
Verifying the installation
After you complete the installation, verify that:
· There is enough space for heat dissipation around the switch, and the rack is stable.
· The grounding cable is securely connected.
· The correct power source is used.
· The power cords are correctly connected.
· All the interface cables are cabled indoors. If any cable is routed outdoors, verify that the socket strip with lightning protection and lightning arresters for network ports have been correctly connected.
You can connect an S6550XE-56HF-HI switch to a configuration terminal by using the serial console port or the mini USB console port. Only the mini USB console port is active if you connect both the serial console port and mini USB console port.
You can connect an S6550X-32Q-HI switch to a configuration terminal by using the serial console port.
In Figure 29, the switch is connected to a configuration terminal (PC as an example) from the serial console port.
Figure 29 Connecting the switch to a configuration terminal
Table 5 describes the three types of console cables that can used for connecting the switch to a configuration terminal. As a best practice, use a serial console cable for connection. The switch is not provided with a serial console cable or a mini USB console cable. Prepare an H3C console cable or prepare a mini USB console cable yourself.
Table 5 Connection methods and console cables
Connection method |
Console cable type |
Configuration terminal-side connector |
Switch-side connector |
Product code |
Using the serial console port for connection |
DB9-to-RJ45 console cable |
DB-9 female connector |
RJ-45 connector |
04042967 |
USB-to-RJ45 console cable |
USB connector |
RJ-45 connector |
0404A1EE |
Using the mini USB console port for connection (applicable only to S6550XE-56HF-HI) |
Mini USB console cable |
USB connector |
Type-B mini USB connector |
N/A |
CAUTION: Follow these guidelines when you connect a DB9-to-RJ45 console cable: · Identify the mark on the serial console port and make sure you are connecting to the correct port. · The serial ports on PCs do not support hot swapping. To connect a PC to an operating switch, first connect the PC end. To disconnect a PC from an operating switch, first disconnect the switch end. |
A DB9-to-RJ45 serial console cable is an 8-core shielded cable, with a crimped RJ-45 connector at one end for connecting to the serial console port of the switch, and a DB-9 female connector at the other end for connecting to the serial port on a configuration terminal.
Figure 30 DB9-to-RJ45 console cable
Table 6 DB9-to-RJ45 console cable signal pinout
RJ-45 |
Signal |
DB-9 |
Signal |
1 |
RTS |
8 |
CTS |
2 |
DTR |
6 |
DSR |
3 |
TXD |
2 |
RXD |
4 |
SG |
5 |
SG |
5 |
SG |
5 |
SG |
6 |
RXD |
3 |
TXD |
7 |
DSR |
4 |
DTR |
8 |
CTS |
7 |
RTS |
To connect the switch to a configuration terminal (for example, a PC) by using a DB9-to-RJ45 console cable:
1. Plug the DB-9 female connector of the DB9-to-RJ45 console cable to the serial port on the PC.
2. Connect the RJ-45 connector to the serial console port on the switch.
IMPORTANT: · To use a USB-to-RJ45 console cable to connect the switch to a configuration terminal, first download and install the USB-to-RJ45 console driver on the configuration terminal and then connect the USB-to-RJ45 console cable to the configuration terminal. · If you have connected a USB-to-RJ45 console cable to the configuration terminal before installing the driver, remove and reconnect the USB-to-RJ45 console cable to the configuration terminal after driver installation. |
The following installs the driver on a Windows operating system. To install the driver on other operating systems, see the installation guide in the driver compression package named by using the corresponding operating system.
To connect the switch to a configuration terminal by using a USB-to-RJ45 console cable:
1. Click the following link, or copy it to the address bar on your browser and download the USB-to-RJ45 console driver.
http://www.h3c.com/en/home/USB_to_RJ45_Console/
2. View the TXT file Read me in the Windows folder to identify whether the Windows operating system on the configuration terminal supports the driver.
3. If the Windows operating system supports the driver, install PL23XX-M_LogoDriver_Setup_v200_20190815.exe.
4. Click Next on the welcome page of the driver installation wizard.
Figure 31 Driver installation wizard
5. Click Finish after the drive installation is completed.
Figure 32 Finishing the driver installation
6. Connect the standard USB connector of the cable to the USB port of the configuration terminal.
7. Connect the RJ-45 connector of the cable to the console port of the switch.
A mini USB console cable has a mini USB connector at one end to connect to the mini USB console port of the switch, and a standard USB connector at the other end to connect to the USB port on the configuration terminal.
To connect the switch to a configuration terminal, for example a PC, by using a mini USB console cable:
1. Connect the standard USB connector to the USB port of the PC.
2. Connect the mini USB connector to the mini USB console port of the switch.
3. Click the following link, or copy it to the address bar on the browser to log in to download and install the USB console driver on the configuration terminal.
http://www.h3c.com/en/home/USB_Console/
4. Select a driver program according to the operating system you use:
¡ XR21V1410_XR21B1411_Windows_Ver1840_x86_Installer.EXE—32-bit operating system.
¡ XR21V1410_XR21B1411_Windows_Ver1840_x64_Installer.EXE—64-bit operating system.
5. Click Next on the installation wizard.
Figure 33 Device Driver Installation Wizard
6. Click Continue Anyway if the following dialog box appears.
Figure 34 Software Installation
7. Click Finish.
Figure 35 Completing the device driver installation wizard
Setting terminal parameters
To configure and manage the switch through the console port, you must run a terminal emulator program, TeraTermPro or PuTTY, on your configuration terminal. You can use the emulator program to connect a network device, a Telnet site, or an SSH site. For more information about the terminal emulator programs, see the user guides for these programs
Configure the terminal parameters as follows:
· Bits per second—9600.
· Data bits—8.
· Stop bits—1.
· Parity—None.
· Flow control—None.
Powering on the switch
1. Before powering on the switch, verify that the following conditions are met:
¡ All the fan tray slots have a fan tray installed.
¡ The power cords are connected correctly.
¡ The input power voltage is as required by the switch.
¡ The console cable is connected correctly.
¡ The configuration terminal (a PC, for example) has started, and its serial port settings are consistent with the console port settings on the switch.
2. Power on the switch.
During the startup process, you can access BootWare menus to perform tasks such as software upgrade and file management. The BootWare interface and menu options vary by software version. For more information about BootWare menu options, see the software-matching release notes for the device.
3. After the startup completes, you can access the CLI to configure the switch.
For more information about the configuration commands and CLI, see the configuration guides and command references that come with the switch.
Power supply failure
Symptom
The power supply status LED on an LSVM1AC650 or LSVM1DC650 power supply is not steady green or flashing green.
The power supply status LED on a PSR450-12A power supply is not steady green.
For more information about the LEDs on a power supply, see H3C LSVM1AC650 & LSVM1DC650 Power Modules User Manual or H3C PSR450 Power Module Series User Manual.
Solution
To resolve the issue:
1. Verify that the power cord is connected correctly.
2. Verify that the power source is as required by the switch.
3. Verify that the operating temperature of the switch is in the acceptable range and the power supply has good ventilation.
4. If the issue persists, contact H3C Support.
To replace a power supply, see "Installing and removing power supplies."
Fan tray failure
CAUTION: The S6550XE-HI switch has five fan tray slots. The S6550X-HI switch has four fan tray slots. If multiple fan trays fail when the switch is operating, do not remove the fan trays at the same time. Replace the fan trays one after another and finish replacing each fan tray within 3 minutes. |
You can observe the system status LED on the switch to determine whether a fan tray failure has occurred. The system outputs alarm messages when a fan tray failure occurs.
See "Installing and removing fan trays" to replace the fan tray. If the issue persists, contact H3C Support.
No display
Symptom
The configuration terminal displays nothing when the switch is powered on.
Solution
1. Verify that the power system is operating correctly.
2. Verify that the console cable is connected correctly.
3. Verify that the console cable does not have any issues and the terminal settings are correct.
Garbled display
Symptom
The configuration terminal has a garbled display.
Solution
1. Verify that the following settings are configured for the terminal:
¡ Baud rate—9,600.
¡ Data bits—8.
¡ Parity—None.
¡ Stop bits—1.
¡ Flow control—None.
2. If the issue persists, contact H3C Support.