H3C S3100-52P Ethernet Switch Operation Manual-Release 1500(V1.02)
HomeSupportSwitchesH3C S3100 Switch SeriesConfigure & DeployConfiguration GuidesH3C S3100-52P Ethernet Switch Operation Manual-Release 1500(V1.02)
05-IP Address and Performance Confiugration Operation
Chapter 1  IP Address Configuration
1.1  IP Address Overview
1.1.1  IP Address Classification and Representation
An IP address is a 32-bit address allocated to a device connected to the Internet. It consists of two fields: net-id and host-id. To facilitate IP address management, IP addresses are divided into five classes, as shown in Figure 1-1.
Figure 1-1 Five classes of IP addresses
Class A, Class B, and Class C IP addresses are unicast addresses. Class D IP addresses are multicast addresses and Class E addresses are reserved for future special use. The first three types are commonly used.
IP addresses are in the dotted decimal notation. Each IP address contains four decimal integers, with each integer corresponding to one byte (for example,10.110.50.101).
Some IP addresses are reserved for special use. The IP address ranges that can be used by users are listed in Table 1-1.
Table 1-1 Classes and ranges of IP addresses
Network type
Address range
IP network range available for users
A
0.0.0.0 to 127.255.255.255
1.0.0.0 to 126.0.0.0
l       An IP address with all 0s host ID is a network address and is used for network routing.
l      An IP address with all 1s host ID is a broadcast address and is used for broadcast to all hosts on the network.
l      The IP address 0.0.0.0 is used by hosts when they are booted but is not used afterward.
l      An IP address with all 0s network ID represents a specific host on the local network and can be used as a source address but cannot be used as a destination address.
l      All the IP addresses in the format of 127.X.Y.Z are reserved for loopback test and the packets sent to these addresses will not be output to lines; instead, they are processed internally and regarded as incoming packets.
B
128.0.0.0 to 191.255.255.255
128.0.0.0 to 191.254.0.0
C
192.0.0.0 to 223.255.255.255
192.0.0.0 to 223.255.254.0
D
224.0.0.0 to 239.255.255.255
None
Class D addresses are multicast addresses.
E
240.0.0.0 to 255.255.255.254
None
These IP addresses are reserved for future use.
Others
255.255.255.255
255.255.255.255
255.255.255.255 is used as a LAN broadcast address.
1.1.2  Subnet and Mask
The traditional IP address classification method wastes IP addresses greatly. In order to make full use of the available IP addresses, the concepts of mask and subnet were introduced.
A mask is a 32-bit number corresponding to an IP address. The number consists of 1s and 0s. These 1s and 0s can be arbitrarily combined in principle. However, a mask is usually defined as follows: the bits of the network number and subnet number are set to 1, and the bits of the host number are set to 0. The mask divides the IP address into two parts: subnet address and host address. In an IP address, the part corresponding to the "1" bits in the mask is the subnet address, and the part corresponding to the remaining "0" bits in the mask is the host address. If there is no subnet division, the subnet mask uses the default value. In this case, the length of 1s in the mask is equal to the net-id length. Therefore, for IP addresses of classes A, B and C, the default values of the corresponding subnet masks are 255.0.0.0, 255.255.0.0 and 255.255.255.0 respectively.
The mask can be used to divide a Class A network containing more than 16,000,000 hosts or a Class B network containing more than 60,000 hosts into multiple small networks. Each small network is called a subnet. For example, for the Class B network address 138.38.0.0, the mask 255.255.224.0 can be used to divide the network into eight subnets: 138.38.0.0, 138.38.32.0, 138.38.64.0, 138.38.96.0, 138.38.128.0, 138.38.160.0, 138.38.192.0 and 138.38.224.0 (see Figure 1-2). Each subnet can contain more than 8000 hosts.
Figure 1-2 Subnet division of the IP address
1.2  Configuring an IP Address
For a VLAN interface, an IP address can be obtained in one of the three ways:
l           Manually configured by using the IP address configuration command
l           Allocated by the BOOTP server
l           Allocated by the DHCP server
The three methods are mutually exclusive and the use of a new method will result in the IP address obtained by the old method being released. For example, if you obtain an IP address by using the IP address configuration command, and then use the ip address bootp-alloc command to apply for an IP address, the originally configured IP address is deleted and a new IP address will be allocated by BOOTP for the VLAN interface.
This chapter only introduces how to configure an IP address with the IP address configuration command. For the other two methods, refer to the “Management VLAN Configuration” module.
1.3  Configuring an IP Address for a VLAN Interface
Generally, it is enough to configure one IP address for a VLAN interface. However, you can configure up to five IP addresses for a VLAN interface so that the interface can be connected to several subnets. Among these IP addresses, one is the primary IP address and the others are secondary ones.
Table 1-2 Configure an IP address for a VLAN interface
Operation
Enter system view
Enter VLAN interface view
interface Vlan-interface vlan-id
Required
By default, a VLAN interface has no IP address.
After an IP address is assigned to the VLAN interface through BOOTP or DHCP, you cannot configure a secondary IP address for the VLAN interface.
1.4  Displaying IP Address Configuration
After the above configuration, you can execute the display command in any view to display the operating status and configuration on the interface to verify your configuration.
Table 1-3 Display IP address configuration
Operation
Display VLAN interface information
display ip interface [ brief [ interface-type [ interface-number ] ] | [ interface-type interface-number ] ]
You can execute the display command in any view.
1.5  IP Address Configuration Example
I. Network requirements
Set the IP address and subnet mask of VLAN-interface1 to 129.2.2.1 and 255.255.255.0 respectively.
II. Network diagram
Figure 1-3 IP address configuration
III. Configuration procedure
# Configure an IP address for VLAN-interface1.
<H3C> system-view
[H3C] interface Vlan-interface 1
[H3C-Vlan-interface1] ip address 129.2.2.1 255.255.255.0
1.6  Troubleshooting
Symptom: The switch cannot ping the host directly-connected to a port.
Solution: You can perform troubleshooting as follows:
l           Check the configuration of the switch, and then use the display arp command to check whether the host has an corresponding ARP entry in the ARP table maintained by the Switch.
l           Check the VLAN that includes the switch port connecting the host. Check whether the VLAN has been configured with the VLAN interface. Then check whether the IP addresses of the VLAN interface and the host are on the same network segment.
l           If the configuration is correct, enable ARP debugging on the switch, and check whether the switch can correctly send and receive ARP packets. If it can only send but cannot receive ARP packets, errors may occur at the Ethernet physical layer.
Chapter 2  IP Performance Configuration
2.1  IP Performance Configuration
2.1.1  Introduction to IP Performance Configuration
IP performance configuration mainly refers to TCP attribute configuration. The TCP attributes that can be configured include:
l           synwait timer: This timer is started when TCP sends a syn packet. If no response packet is received before the timer times out, the TCP connection will be terminated. The timeout time of the synwait timer ranges from 2 to 600 seconds and is 75 seconds by default.
l           finwait timer: This timer is started when the TCP connection turns from the FIN_WAIT_1 state to the FIN_WAIT_2 state. If no FIN packet is received before the timer times out, the TCP connection will be terminated. The timeout time of the finwait timer ranges from 76 to 3,600 seconds and is 675 seconds by default.
l           The connection-oriented socket receive/send buffer size ranges from 1 to 32 KB and is 8 KB by default.
2.1.2  Introduction to FIB
Every switch stores a forwarding information base (FIB). FIB is used to store the forwarding information of the switch and guide Layer 3 packet forwarding.
You can know the forwarding information of the switch through the FIB table. Each FIB entry includes: destination address/mask length, next hop, current flag, timestamp, and outbound interface.
When the switch is running normally, the contents of the FIB and the routing table are the same. For routing and routing tables, refer to the “Routing Protocol” module of this manual.
2.1.3  TCP Attributes Configuration
Table 2-1 Configure TCP attributes
Operation
Enter system view
Configure timeout time for the synwait timer in TCP
Required
By default, the timeout time of the TCP synwait timer is 75 seconds.
Configure timeout time for the finwait timer in TCP
Required
By default, the timeout time of the TCP finwait timer is 675 seconds.
Configure the socket receive/send buffer size of TCP
tcp window window-size
Required
By default, the receive/send buffer size is 8 KB.
2.1.4  Subnet-Directed Broadcast Suppression Configuration
Broadcast packets include the general broadcast packets and the subnet-directed broadcast packets. For a subnet-directed broadcast packet, its destination IP address is a sub network address, but its source IP address is not in this sub network segment.
You can perform the following configuration to determine whether to receive the subnet-directed broadcast packets.
Table 2-2 Configure to receive subnet-directed broadcast packets
Operation
Enter system view
Receive subnet-directed broadcast packets
ip forward-broadcast
Optional
By default, the subnet-directed packets will be suppressed.
2.2  Displaying and Maintaining IP Performance
After the above configurations, you can execute the display command in any view to display the running status to verify your IP performance configuration.
Table 2-3 Display IP performance
Operation
Display TCP connection status
display tcp status
Display TCP connection statistics
display tcp statistics
Display UDP traffic statistics
display udp statistics
Display IP traffic statistics
display ip statistics
Display ICMP traffic statistics
display icmp statistics
Display the current socket information of the system
display ip socket [ socktype sock-type ] [ task-id socket-id ]
Display the forwarding information base (FIB) entries
display fib
Display the FIB entries matching the destination IP address
display fib ip_address1 [ { mask1 | mask-length1 } [ ip_address2 { mask2 | mask-length2 } | longer ] | longer ]
Display the FIB entries filtering through a specific ACL
display fib acl number
Display the FIB entries in the buffer which begin with, include or exclude the specified character string.
display fib | { begin | include | exclude } text
Display the FIB entries filtering through a specific prefix list
display fib ip-prefix listname
Display the total number of the FIB entries
display fib statistics
Use the reset command in user view to clear the IP, TCP, and UDP traffic statistics.
Table 2-4 Maintain IP performance
Configuration
Clear IP traffic statistics
reset ip statistics
You can execute the reset command in user view.
Clear TCP traffic statistics
reset tcp statistics
Clear UDP traffic statistics
reset udp statistics
2.3  Troubleshooting
Symptom: IP packets are forwarded normally, but TCP and UDP cannot work normally.
Solution: Enable the corresponding debugging information output to view the debugging information.
l           Use the display command to display the IP performance and check whether the PC runs normally.
l           Use the terminal debugging command to enable debugging information to be output to the console.
l           Use the debugging udp packet command to enable the UDP debugging to trace UDP packets.
<H3C> terminal debugging
<H3C> debugging udp packet
The UDP packets are shown in the following format:
UDP output packet:
Source IP address:202.38.160.1
Source port:1024
Destination IP Address 202.38.160.1
Destination port: 4296
l           Use the debugging tcp packet command to enable the TCP debugging to trace TCP packets.
<H3C> debugging tcp packet
Then the TCP packets received or sent will be displayed in the following format in real time:
TCP output packet:
Source port:1024
Sequence number :4185089
Ack number: 0
Flag  :SYN
Packet length :60
Data offset: 10
  • Become a Partner
  • Partner Resources
